LG Therma V R32 Monobloc. Setup advice inc flow temperature & weather compensation
- Grade 2 Listed building (90sq m) with modern extension (75sq m)
- Oil c/h upgraded to LG Therma V R32 16kw Monobloc ASHP in 2020
- 100l buffer tank + 300l h/w tank
- standard LG RS3 controller
- 27 solar pv panels + batteries
- Modernised but old stone walls, single glazed, insulated floor, thatched roof
- u/f heating downstairs (pipes set for oil heating) & 3 zones
- Radiators upstairs with TRVs (target temp cool say 17deg)
- Digital Thermostat in main room (kitchen - used a lot - target temp 20 deg day).
- Standard thermostats for 2 other rooms (mostly unused - so maintain low temp only) (target temp cool say 15deg)
- Standard programmer (2 way for radiators & u/f heating)
- Double glazed, insulated floor, insulated roof & walls
- u/f heating (pipes set for oil heating) & 3 zones
- single storey
- Digital Thermostat in main room (lounge & used a lot) (target day temp say 20deg)
- Digital thermostats for 2 other rooms (mostly less used - so maintain low temp only) (target day temp say 19deg)
- Standard programmer (1 way for all u/f heating)
- WFH - so assumed need heat all day
- Keep it running 24x7
- trial & error on flow temps. Installer set at 50deg i think. Progressively reduced to current 37deg
- flow temp at 37deg is sufficient - except in recent coldest snap
- Using digital thermostats main living areas drop overnight 1 or 2deg. Depends on external temps.
- During mild Nov using typical 35kw daily
- During Dec using typical 50kw daily
- During cold snap using typical 70-75kw daily with peak day 90kw
- AI is currently off. Should it be?
- Assume "Seasonal Auto Temp" is therefore offering no weather compensation – please advise.
- Can access installer menu but so far not changed anything
- Any suggestions please? Happy to use trial & error
- Particularly interested in other views on best flow temp and whether i should use some weather compensation?
- Not deeply technical but can follow instructions or use common sense!
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
should also mention that during cold snap the ashp seemed to perform well and provided most of our heating needs. We needed a boost sometimes and rather than increase flow temperature we used a convector heater for an hour or two and in the afternoons & evenings quite often used a woodburner. Wood burner was nice option for ambiance as well as boosting heat.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441should also mention that during cold snap the ashp seemed to perform well and provided most of our heating needs. We needed a boost sometimes and rather than increase flow temperature we used a convector heater for an hour or two and in the afternoons & evenings quite often used a woodburner. Wood burner was nice option for ambiance as well as boosting heat.
I would suggest that you have a read through the manual and ensure that your system is set for weather compensation, then gradually adjust the settings so that the weather compensation curve matches your home's heat loss as close as possible. This should provide efficient operation.
You want to avoid the thermostats doing anything and keeping as many radiators etc open.
So set them as say 30c and then adjust the WC until it keeps the room at your desired temp. If all the rooms gets too hot, turn the curve down. If just one room then turn the flow to that room down
That way it’ll run low and slow rather than stop starting.
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
@derek-m thats easier said than done.
The installer manual is unfathomable to me and the user manual is pretty useless also - unless one has a decent base understanding. Installers unfortunately don't seem to see it as part of the process to help with knowledge transfer.
I'm hoping that someone with direct knowledge of LG Therma V controls can help with some pointers.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441@derek-m thats easier said than done.
The installer manual is unfathomable to me and the user manual is pretty useless also - unless one has a decent base understanding. Installers unfortunately don't seem to see it as part of the process to help with knowledge transfer.
I'm hoping that someone with direct knowledge of LG Therma V controls can help with some pointers.
I fully agree that the LG manual leaves a great deal to be desired.
I have attached a copy of the Installer Settings section of the manual, which you may or may not have. Read through the manual and raise any question for items about which you are uncertain.
@derek-m many thanks.
Currently I have "Heat" setting with flow temp 37deg and h/w 45 deg
The "Settings" are almost same as shown in your pdf
1. If I understand correctly I need to change "Heat" to "Auto"? That changes the flow temp to show "AI"
2. Looking through the Installer Settings I'm trying to understand the relevant ones for weather compensation and to set best efficiency.
3. After "Screed Drying setting" there are 3 settings (not in pdf) that I guess may be relevant.. currently set as:
Outdoor Temp for Auto Mode
-4 Min 15 Max
Indoor Air Temp for Auto Mode
16 Min 21 Max
LWT for Auto Mode
20 Min 65 Max
4. I'm not sure if I should simply change to Auto/AI as 1. above or should check/change anything else?
5. In the pdf after "Smart Grid(SG) setting it shows "Seasonal auto temp setting" and "Modbus Address"
But neither of these show in my "Settings" menu. Is that ok?
would it help if I post any other current settings?
Thanks!
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@bobbt9866 - with your LG expertise, is this something you could assist Tim with and point him in the right direction?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @tim441@derek-m many thanks.
Currently I have "Heat" setting with flow temp 37deg and h/w 45 deg
The "Settings" are almost same as shown in your pdf
1. If I understand correctly I need to change "Heat" to "Auto"? That changes the flow temp to show "AI"
2. Looking through the Installer Settings I'm trying to understand the relevant ones for weather compensation and to set best efficiency.
3. After "Screed Drying setting" there are 3 settings (not in pdf) that I guess may be relevant.. currently set as:
Outdoor Temp for Auto Mode
-4 Min 15 MaxIndoor Air Temp for Auto Mode
16 Min 21 MaxLWT for Auto Mode
20 Min 65 Max4. I'm not sure if I should simply change to Auto/AI as 1. above or should check/change anything else?
5. In the pdf after "Smart Grid(SG) setting it shows "Seasonal auto temp setting" and "Modbus Address"
But neither of these show in my "Settings" menu. Is that ok?
would it help if I post any other current settings?
Thanks!
The more I see of the LG controller and the manuals, the less I am impressed.
Make a note of the original settings should you decide to make any changes.
Going through the various parameters in order, these are the ones that I feel may be relevant.
Select Temperature Sensor, should be set to 'Water'.
Water Heating Set Temperature, this is the temperature range over which the warm water produced by the heat pump can be varied.
Heater Priority, set to 'Boost heater only ON'.
Heating Temperature Setting, set to 'Outlet'.
I am not certain if 'Seasonal auto temp' will appear in the list if the controller is set to Auto/AI mode, I suspect that you will have to give it a try. The instructions in the manual must rate as the worst ever produced and are about as clear as mud.
If anyone is unfortunate to have an LG system and has been able to decipher the LG code, I would welcome your assistance in setting weather compensation.
If you set the temperature sensor option to air+water, this will enable a blended mixture of load compensation and weather compensation. In other words, the LG controller will be the thermostat.
This is only relevant if the controller is in a habitable space.
There is a massive thread on buildhub about the Therma V. Well worth a read.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
I will post my changes & experiences here in case it helps others.... I welcome further input from anyone that has had experience with either flow temp changes or weather compensation in particular on LG Therma V. I will check buildhub and try to extract important suggestions here.
Select Temperature Sensor, was set to 'Water'. So no change so far. LG controller located in a bathroom outside airing cupboard. Bathroom has u/f heating and a towel rad so not sure if it will get meaningful air temps (unless relocated)?
Water Heating Set Temperature, this is currently set to 20 (no change so far). Any views?
Heater Priority, Currently set to 'Main & Boost On'. Will review for potential change to 'Boost heater only ON'. But want to understand potential impact!
Heating Temperature Setting, was set to 'Outlet'. So no change
'Seasonal auto temp' does not seem to appear in the list if the controller is set to Auto/AI mode or Heat mode. So not sure if that's a documentation error or due to different software? But is probably important?!
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Heater Priority, Currently set to 'Main & Boost On'. Will review for potential change to 'Boost heater only ON'. But want to understand potential impact!
Is this referring to Immersion Heater? So if I change to Boost only will the hot water heat more slowly (from ASHP) and not use immersion in normal usage? This would not be a problem for us as we are normally just 2 people at home and the tank is good size (300l).
Is Boost Only used just for the legionella cycle?
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
3 days ago
-
Servicing LG Therma V
6 months ago
-
LG Therma V. Software upgrades, AI (weather compensation), SCOP
12 months ago
-
Flow temperature up and down like a yo-yo
1 year ago
-
Daikin EDLA14D3V3 COP is now below 1
2 years ago
- 21 Forums
- 1,865 Topics
- 40.7 K Posts
- 117 Online
- 2,184 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump? Or already have one but it’s not performing as it should? Rob is here to help!
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
Latest Posts
-
RE: Not a good January? My heat pump used 840 KWh of electricity
@tim441 East Midlands Uk. Yes to weather compensation. ...
By Carpenterstation , 11 minutes ago
-
RE: Controversial opinions - pure weather compensation, buffer tank, heat loss, oversized heat pumps
Hi @stuartornum, would you be willing to share your WC ...
By Grantmethestrength , 2 hours ago
-
Octopus intelligent Go, IOG. maximising slots
Agile user for most of last year but now moved to IOG. ...
By Tim441 , 3 hours ago
-
RE: Agile: average import cost vs other tariffs?
@toodles Partial answer to my own question!EV is 100% f...
By Tim441 , 3 hours ago
-
RE: New Mitsubishi system, several concerns but just a newbie…..
Got home from work today. Same scenario. Nothing callin...
By Carpenterstation , 5 hours ago
-
RE: Grant Aerona3 with Octopus Cosy tariff
We have a Grant Aerona3 as well. We are not on Octopus ...
By davidm06 , 5 hours ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
@jamespa Perfectly possible re the pipes from the Buffe...
By Alfapat , 5 hours ago
-
RE: New Project! ASHP, Solar PV + Battery, MVHR!
@nickmorgan We have a Sunamp Thermino eP210; this may b...
By Toodles , 5 hours ago
-
RE: Air source heat pump roll call
User name: ASHP-AeronaASHP model: Grant Aerona3 13kW HP...
By ASHP-Aerona , 6 hours ago
-
RE: ASHP & Radiator Sizing - Measuring Heat Loss
That's correct. You probably will need to measure flow...
By JamesPa , 6 hours ago
-
RE: Tesla Powerwall charge level.
@gary that’s what I am hoping - whatever he said he is ...
By andy_e , 7 hours ago
-
RE: Do thick walls make for warm houses?
@transparent understood, thanks very much. I'll create ...
By nickmorgan , 8 hours ago
-
-
You can only get 4kw out of the inverter, regardless of...
By Uk_pete_2000 , 10 hours ago
-
RE: Looking for some advice – no viable installer/system – I'm stuck
Wow, thats a lot of gas - you said 120 sq m is that the...
By JamesPa , 11 hours ago
-
RE: 4 port buffer tank connections
In the coming weeks, I’ll be scheduling another session...
By Mars , 13 hours ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@grantmethestrength, thanks so much for the feedback. I...
By Mars , 14 hours ago
-
RE: Is there a problem with SolarEdge monitoring?
@johnr thanks. After not being able to login for at lea...
By Mars , 15 hours ago
-
RE: Is the Grant controller a thermostat?
@davidm06 no doubt you're right, the house is newish an...
By damonc , 1 day ago
Latest Topics
-
Octopus intelligent Go, IOG. maximising slots
By Tim441 3 hours ago
-
Grant Aerona3 with Octopus Cosy tariff
By ASHP-Aerona 6 hours ago
-
New Project! ASHP, Solar PV + Battery, MVHR!
By nickmorgan 7 hours ago
-
By Curlykatie 10 hours ago
-
ASHP & Radiator Sizing - Measuring Heat Loss
By IanMK13 1 day ago
-
By DavidAlgarve 2 days ago
-
Octopus design temperatures confusion
By AndrewJ 2 days ago
-
Is there a problem with SolarEdge monitoring?
By Mars 2 days ago