Legionella cycle: Heat Pump or Immersion Heater?
Hi,
I've had my Grant ASHP for about 6 months now, and am slowly adjusting the set-up to hopefully more reasonable values.
Initially, DHW was set to temp of 55°C to run at 05:00, 11:00, and 15:00 (each for 1 hour), with a separate immersion heater element also running for an hour each Monday at 01:00 (for legionella sterilisation I assumed).
I've gradually reduced this until now I have it running from 15:00 to 16:00 only, set to 45°C, with the legionella cycle now running at 16:00 on Monday, directly after the ASHP has finished heating the water to 45°C.
My thinking now is that the immersion heater element runs at COP of 1 (at best); and the HP runs at COP of 1 (at the very worst) so it actually makes more sense for the HP to do all of the legionella work i.e. on Mondays set the DHW to 60°C (the maximum it will permit) for 1 hour at 15:00, and no longer use the immersion heater at all.
Does this seem reasonable? I also think that 60°C is possibly too high, and something like 58°C would be fine. At the moment the HW is at about 58°C by 17:00 on Monday, and stays above 55°C until almost midnight. That seems more than adequate to kill legionella (over 55°C for 7 hours).
Grant Aerona 3 10kW
Posted by: @mikeflMy thinking now is that the immersion heater element runs at COP of 1 (at best); and the HP runs at COP of 1 (at the very worst) so it actually makes more sense for the HP to do all of the legionella work i.e. on Mondays set the DHW to 60°C (the maximum it will permit) for 1 hour at 15:00, and no longer use the immersion heater at all.
Does this seem reasonable? I also think that 60°C is possibly too high, and something like 58°C would be fine. At the moment the HW is at about 58°C by 17:00 on Monday, and stays above 55°C until almost midnight. That seems more than adequate to kill legionella (over 55°C for 7 hours).
When I was looking at legionella cycles a while back, I found a lot of variation in opinion regarding how often to run the cycle. Regs say one thing, others point out that the bottom of traditional cylinders rarely if ever reaches the required temperature. The actual temperature and duration required to kill the bacteria though was pretty much consistent.
If you can reach the required temperature using your heat pump then yes it makes a lot more sense to use it rather than the immersion coil. The only exception I can think of to this is if you have solar panels and a diverter, which essentially will do it for free (or a loss of export)
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoodyIf you can reach the required temperature using your heat pump then yes it makes a lot more sense to use it rather than the immersion coil. The only exception I can think of to this is if you have solar panels and a diverter, which essentially will do it for free (or a loss of export)
For what its worth Vaillant R290 heat pumps (I discovered a few weeks ago) are designed to do the legionella cycle in the heat pump only, and appear (unlike many other HPs) not even to be capable of controlling the immersion. So thats the decision Vaillant made once they got to the point of having a FT high enough.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I have a Grant ASHP and have the HW output from it set at 60degC for 75 minutes daily. This will charge my 250litre pre-plumb Grant cylinder to 55degC usually within 1hr, and it maintains this temperature for many hours if no hot water is drawn off. It's more thorough at heating the cylinder than the built in 3kW immersion. If I use the immersion the built in immersion thermostat starts to cycle on and off but the tank content thermostat never reaches above 54degC. The immersion stat is set to it's highest setting, supposedly 65degC.
Also, the tank contents cool much more quickly with no hot water drawn off compared to when I heat using the ASHP. That to me proves that the immersion heating is not very thorough. I have more faith in the ASHP providing better Legionella protection daily to 55degC than the 3kW immersion weekly to 54degC! The ASHP heating coil is lower down than the immersion element and a much larger surface area.
The ASHP will give a CoP of 2-2.5 in heating, so is much more energy efficient than the immersion. I have solar PV+battery and a diverter. Initially I thought using the diverter would be most cost effective, but charging the battery using solar, and then using it to power the ASHP is more economical. I'm using less than half kWh than direct immersion, and can export more surplus PV that way at 15p/kWh. 'Every little helps!' 😀
-
HOT TIP - DHW Cylinder Thermostat
2 years ago
-
Why run a disinfectant cycle ?
3 years ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 39 Online
- 5,736 Members
Podcast Picks
Latest Posts
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
That's a valid point, of course nobody wants the inconv...
By downfield , 15 minutes ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
For best results with induction hobs use stainless stee...
By Scalextrix , 29 minutes ago
-
RE: Who’s Caved and Switched the Heating On Already?
Central heating still switched off and will be until Oc...
By AllyFish , 3 hours ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Please read to the very end of this post, I shift my po...
By JamesPa , 3 hours ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 3 hours ago
-
RE: Midea ASHP – how to set weather compensation
I think it is a bug in the code, it comes on even when ...
By cathodeRay , 17 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 19 hours ago
-
RE: Buffers, hot water and cooling
@jamespa Your reasonably close! Especially with warmer ...
By dgclimatecontrol , 21 hours ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 1 day ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 2 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 2 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 2 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
@scalextrix Name plate capacity
By HCas , 2 days ago
-
RE: Solar Thermal DHW and ASHP
I was originally contemplating a solar thermal installa...
By jamespetts , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
My system installed in July 2024 has produced 6.4mWh in...
By jamespetts , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@judith thanks for your suggestions. Starting from col...
By GrahamF , 3 days ago
-
RE: Inventor (Midea) Heat Pump short cycling advice
I switched to "fan coil mode" to be able to set water t...
By immunity , 3 days ago
-
RE: DESNZ doing a survey which asks the right questions!
Without a survey their only source of data is probably ...
By JamesPa , 3 days ago