Keystone COPs? I'm not getting the efficiencies I expected on my Ecodan.
Hi all. A new member here, and a new Ecodan owner as of a few weeks ago.
Having done a fair bit of reasearch in to all things heat pump, I was fairly convinced I'd be seeing COPs of 3.5-4 or more at ambient temps of circa 8 degrees C - not so. I've yet to see a 3 in the number, and I'm sure you'd see less cycles at the Tour de France.
Having read some threads here, that does not seem that uncommon where the Ecodan is concerned?
You may already have read the "How to run this efficiently with zero understanding" forum(and the excellent contribution from some very knowledegable people) but you have the same concerns that i have had.
I was struggling to see cop's of even 2 but have now got to around 2.5-2.7 and having to accept that's as good as it will get.
I managed to get through to Mitsubishi support last week and he concluded that in winter time under 3 was to be expected in my circumstances, he also confirmed that he supported Auto mode over weather compensation.(I have more issues with cycling in weather comp)
Just check your thermistors are correctly placed where they should be and insulated.
Yeah I have read it (along with quite a few others). In fact I just posted on your thread (awaiting moderation).
I'm also seeing better performance in room temp mode. Out of interest, what were your 'circumstances' that lead Mitsubishi support to the conclusion that you would likely not achieve 3 or above in winter?
I don't recognise the complaint in the opening post. Our system still has unresolved installation problems (some uninsulated pipe outside!) yet achieves COP of 3.6 at about 6°c ambient outdoors. Here's yesterday:
It's important to remember that people are more likely to post on forums like this when something is wrong and either their performance goes through the floor (as mine did after a firmware update) or bills go through the roof.
The Ecodan "black box" of auto-adaptation mode can be a source of problems (I think matching the "interval" setting to the home is as important as getting the WC curve vaguely correct) in addition to all the normal heat pump incompetent installer problems, such as the primary control in a cupboard or barn and "traditional" on/off thermostats used to run it at a fixed max design flow. Problems in the mirror may appear larger than reality...
Posted by: @mjrIt's important to remember that people are more likely to post on forums like this when something is wrong and either their performance goes through the floor (as mine did after a firmware update) or bills go through the roof.
I'm sorry if my original post come over that way. It was not my intention. I'm very happy with my installation and how it's performing, I joined here as I'd like to understand more what makes it 'tick' so that I may be able to get the absolute maximum efficiency from it. It's apparent there are a fair few very knowledgeable members here to learn from.
I haven't been tracking outdoor temp vs COP for that long, but so far I've been getting ~3.75-ish at 8C outdoor temp:
The above is the average daily outdoor temp on the x-axis, and the COP according to MELCloud on the y-axis.
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
Or is it “Good COP bad COP”?
there’s something of a deception when looking at COP alone IMO.
when we first powered up our heat pump we were using an on/off thermostat and had no screen data on kw consumption or production.
after some changes we discovered we were operating at a COP of 1.49 - full speed pumps, low DT etc.
we are now 5 days into a settled Auto Adaptive mode.
The BAD COP in my mind is the apparent deception of 24 hour operation even with a night time set back…..
BAD COP - with a 19c setback at night, 4c outside, we were getting a COP of 3.17 with 24kwh consumption.
GOOD COP -However by selecting a setback of 17c we damaged our COP to 3.4 but only used 16kwh. Basically switching off the HP until about 4am.
We have since also lowered our daytime room temp to 19c and got the COP to 3.73 for the last 24 hours. 6c outside using 15kwh.
Im sure the COP police 👮♀️ might be able to shed some light…
COP is useful because you can work it out in the short term and optimising it should, all else being equal, reduce the amount of kWh used. It's a handy target for quick fixes over a day or two.
Of course, the problem is that all else is never equal. Not least, the weather keeps changing!
Posted by: @sunandairOr is it “Good COP bad COP”?
there’s something of a deception when looking at COP alone IMO.
when we first powered up our heat pump we were using an on/off thermostat and had no screen data on kw consumption or production.
after some changes we discovered we were operating at a COP of 1.49 - full speed pumps, low DT etc.
we are now 5 days into a settled Auto Adaptive mode.
The BAD COP in my mind is the apparent deception of 24 hour operation even with a night time set back…..
BAD COP - with a 19c setback at night, 4c outside, we were getting a COP of 3.17 with 24kwh consumption.
GOOD COP -However by selecting a setback of 17c we damaged our COP to 3.4 but only used 16kwh. Basically switching off the HP until about 4am.
We have since also lowered our daytime room temp to 19c and got the COP to 3.73 for the last 24 hours. 6c outside using 15kwh.
Im sure the COP police 👮♀️ might be able to shed some light…
Maybe I'm misunderstanding, but what do you mean by "damaged our COP" here? You say it's gone up from 3.17 to 3.4?
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
@scrchngwsl well spotted you’re absolutely right. I must have read .17 as bigger than .4
So possibly a lower setback, may also favour a Good COP? the question rolls on…
@sunandair A priori, a lower setback ought to improve the COP because the flow temperatures can be reduced to correspond to the lower heat demand. Lower flow temp = better COP.
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 34 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Humming sound on new install.
Ok took some pics. It’s seems level one end front to ba...
By AdamK , 7 minutes ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 2 hours ago
-
I didn't want to say that, bus since you have said it n...
By JamesPa , 2 hours ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
I think so but I don't know for certain. A cascade as ...
By JamesPa , 4 hours ago
-
RE: Midea ASHP – how to set weather compensation
Mostly, I think, but with some caveats. I set the TI...
By cathodeRay , 5 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I have been working on network resilience for a while. ...
By Scalextrix , 7 hours ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 23 hours ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 1 day ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 1 day ago
-
RE: Who’s Caved and Switched the Heating On Already?
@allyfish Dogs have owners - Cats keep staff. You are o...
By Toodles , 1 day ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 1 day ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 1 day ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 2 days ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 2 days ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 3 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 3 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 3 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 3 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
@scalextrix Name plate capacity
By HCas , 3 days ago