I've been running the system now on weather compensation only for a few weeks and as I said before, it's working well for us. Some of that time I've had the heating running 24/7 and some off for 5 hours 12-5am.  I've messed around a bit with the HW but we use so little at the moment (electric showers and dishwasher) it should make little difference. This is the story so far
Â
Blue is running the ASHP 24 hrs a day, red is 5am to midnight. I removed a couple of early outliers from when I was experimenting. An exponential trend is the best fit. You can see that at the colder end, it makes a difference with the heating off at night; at the warmer end less so. I think this is because when it's cold, having the ASHP off for 5 hours makes a big dent in overall consumption. This is offset a bit by a big peak at 5am to heat the flow from cold but not completely. When it's warmer the overnight consumption is low, so not so much saved and at 5am the ASHP still has to raise the flow from room temperature to its target.Â
The other thing to bear in mind is that I don't force the house to warm up; it does it as and when with the weather compensation flows. If I were using auto adaptation I think the flow temp would increase until the house warmed up, which would give me a warmer house but lessen any saving from having the 12-5am break. We're happy with this as we don't want the house too warm at night. (We also have TRVs on the bedroom radiators that we can adjust if we want.)
What I'm going to do next is try something I've never done, which is to use a fixed flow temperature of 45C and control the house via the thermostats.  This is something a lot of people do with ASHPs and how some suppliers set up new installations. The next week or so looks quite benign for weather so an ideal time. I'm willing to experiment but don't want to bankrupt myself. I'll set both my zones for 21C constantly and I'll leave the heating off 12-5am as I've been doing most recently. I'll put the thermostats where the temperature is most stable, i.e. not in the hall/kitchen. I'll plot the results on the chart above and see what I get. Â
Any predictions? Mine is that it will cost me more! My average flow temp is about 35C to bumping it to 45C is going to make a difference. What I'm not sure about is the effect of the thermostat switching the ASHP on and off but we'll see.  Â
  Â
Posted by: @kev-mAny predictions? Mine is that it will cost me more! My average flow temp is about 35C to bumping it to 45C is going to make a difference. What I'm not sure about is the effect of the thermostat switching the ASHP on and off but we'll see.  Â
  Â
I did a similar experiment but using a 50ºC flow. That used 930kWh over 30 days vs 855kWh using the compensation curve. Both 30 day periods had an average 6.4ºC ambient outside temp.
Posted by: @kev-mAny predictions? Mine is that it will cost me more!
  Â
I would agree. Also, thanks for keeping this thread updated, very useful data.
Â
I wonder what your current weather compensation curve is set to?
Doesn't seem to making a huge difference. Couple of kW?Â
Here are the results of my experiment to compare (1) Weather compensation only and (2) Constant flow temp and thermostats. Both methods kept the house at c. 21C and switched the heating off 12-5am.Â
The weather compensation method seems to use less energy. If you look at some detail, you can see why. Â
The weather compensation energy use is very steady, apart from a blip due to HW. The thermostat energy use is much more variable. The flow is allowed to cool several times and it takes a lot of energy to raise the temperature. 100 on the left scale corresponds to 6kW.Â
In terms of 'feel'; the thermostat method results in noticeable rises and falls in room temperature with radiators varying between hot and cold whereas with weather compensation the room is more constant and the radiators are always warm.Â
The house warms up in the morning a little quicker using the thermostats. However, my previous experiment showed that I could leave the weather compensation method running all night at very little increased cost.
In terms of COP, my actual COP is showing as 7.1 (weather comp) and 5.4 (thermostats). I don't believe these numbers (someone is coming today to investigate) but their relative sizes are probably right. If I said 3.55 and 2.7 that might be believable. Â
Anyway, I'm convinced by weather compensation and I've now gone back.Â
Any requests for further experiments? 😉 I may try bumping up the weather compensation curve a couple of degrees and letting the thermostats limit the room temperature as a bit of a compromise. Â
 Â
Â
Â
I have one of those and still await delivery of the Mitsubishi wireless receiver unit. When i arrives the intention is to swap out the Heatmiser Neostat the installer thought was preferable.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
I thought you were getting the full monty wireless controller. This is just a room thermistor. I have to wire this in to the main FTC6 control box and mount it in the living area. I can then use the wired in controller in the airing cupboard to control the temperature. This is the cheap (£16.99) version!
@kev-m you’re correct Kev. My mistake.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 46 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Who’s Caved and Switched the Heating On Already?
In the last week, the external temperature in south Man...
By GrahamF , 5 minutes ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 30 minutes ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 1 hour ago
-
RE: Big Changes Coming to Our Heat Pump System
@editor No pressure then 🤣 🤣
By Brendon Uys , 2 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 3 hours ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 4 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Referring to the problem of rooms with diff...
By Tasos , 5 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 6 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 1 day ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 2 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 3 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 3 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 3 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 3 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 3 days ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 4 days ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 4 days ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 5 days ago