The defrosts are every couple of hours. I think it reverses the flow? Anyway it causes the flow temp to drop so it ramps up the power to heat it up, overshoots a bit and settles back down. It's very consistent.Â
Each of these peaks/troughs uses up about 130 Wh more energy than if the ASHP had kept going steadily.Â
Â
I'll have a look at these settings you mention.Â
KevÂ
Thanks Kev,
The fact that the water flow temperature appears to be reasonably constant when the ASHP is running constantly, would indicate that the upper and lower limits are not being reached, so are not affecting the operation. The limits are probably why the heat pump stops for a short period after the defrost cycle has been completed.
Defrost operates in the same way as my A2A ASHP, in that it speeds up for a while during defrost and often stops the compressor for a short period before restarting.
Looking at the thermistor adjustment procedure, it would appear that it is just an offset similar to the weather compensation, rather than a full calibration. If you wish, you could adjust the water flow temperature indication (THW6) and the water return temperature indication (THW7) on the FTC controller to match the readings on your MMSP heat meter. You would then be able to see how the measurements vary as the required water flow temperature is varied by the weather compensation. A word of warning. Try making a 1C adjustment and note the affect, since a large adjustment may cause a change in the indoor temperature, before the controller readjusts. You will also need to adjust the weather compensation curve to match the new readings.
When time allows, I would suggest that you go through the FTC controller settings and note the values on a copy of the Engineers Form shown on pages 40 to 42. It may then be possible to see further ways in which your system could be optimised.
OK. I'll do a summary at the end of the month but here's the last few days. This is having most of the house 21-22C all day and night. Tonight's going to be over 40 I think:
Date | kWh | Ambient |
22/11/21 | 33.2 | 3.9 |
23/11/21 | 22.5 | 6 |
24/11/21 | 18.9 | 6.9 |
25/11/21 | 34.2 | 3.5 |
26/11/21 | 28.9 | 4.4 |
27/11/21 | 36.6 | 2.7 |
Kev
Posted by: @derek-mThanks Kev,
The fact that the water flow temperature appears to be reasonably constant when the ASHP is running constantly, would indicate that the upper and lower limits are not being reached, so are not affecting the operation. The limits are probably why the heat pump stops for a short period after the defrost cycle has been completed.
Defrost operates in the same way as my A2A ASHP, in that it speeds up for a while during defrost and often stops the compressor for a short period before restarting.
Looking at the thermistor adjustment procedure, it would appear that it is just an offset similar to the weather compensation, rather than a full calibration. If you wish, you could adjust the water flow temperature indication (THW6) and the water return temperature indication (THW7) on the FTC controller to match the readings on your MMSP heat meter. You would then be able to see how the measurements vary as the required water flow temperature is varied by the weather compensation. A word of warning. Try making a 1C adjustment and note the affect, since a large adjustment may cause a change in the indoor temperature, before the controller readjusts. You will also need to adjust the weather compensation curve to match the new readings.
When time allows, I would suggest that you go through the FTC controller settings and note the values on a copy of the Engineers Form shown on pages 40 to 42. It may then be possible to see further ways in which your system could be optimised.
You're assuming the installers didn't leave me this with their comprehensive handover pack and commissioning notes?
Â
Â
Â
Â
Â
Â
Â
Â
Â
And you'd be right. 😆Â
Posted by: @kev-mOK. I'll do a summary at the end of the month but here's the last few days. This is having most of the house 21-22C all day and night. Tonight's going to be over 40 I think:
Date kWh Ambient 22/11/21 33.2 3.9 23/11/21 22.5 6 24/11/21 18.9 6.9 25/11/21 34.2 3.5 26/11/21 28.9 4.4 27/11/21 36.6 2.7 Kev
Thanks again Kev,
The above shows how a few degrees change in ambient air temperature can affect the operation and efficiency of an ASHP.
Will be very interested in the summary of NovemberÂ
I'm awaiting an isg for mine so I can monitor and tweak remotely, currently out of stock so every time I want to adjust mine I need to go into the loft!
My system has weather compensation and a curve monitor, any guidance on which settings I should potentially use?Â
My latest tweaks (can't resist 😆)
Weather compensation curve recalibrated so I can set my offset from -4 back to zero
DHW set to come on 12 noon-2pm only. We still have electric showers and don't use much HW. Better it comes on when it's a bit warmer out
And (most radically), heating is programmed to be off 12am-6am. I know the 'slow and steady wins the race' theory for ASHPs and I know the ASHP will have to work hard when it wakes up. But.... I have radiators, a relatively large ASHP and the house has a relatively low thermal mass. Six hours doing nothing will take a big chunk out of the kWh. It also just doesn't feel right heating the 12 other radiators when there's nobody there. If it's too cold in the night or morning I'll revert back. I also won't tell Mrs M and see if she notices or not. Risky, very risky ....  Â
Well that sort of worked. The heating went off as planned. But it warmed up overnight and while the heating came on as planned, the radiators weren't really warm enough to heat the house quickly. Temperature was only down slightly though and a quick boost on the controller did the trick. It's going to be a cheaper day today thankfully. Â
Posted by: @kev-mWell that sort of worked. The heating went off as planned. But it warmed up overnight and while the heating came on as planned, the radiators weren't really warm enough to heat the house quickly. Temperature was only down slightly though and a quick boost on the controller did the trick. It's going to be a cheaper day today thankfully. Â
I have seen some users in the large government sponsored trials at the moment turn off their heat pumps overnight, but they have high temperature heat pumps and turn them back on a bit earlier than you did.
Whether they spend more over a year would very much depend on individual usage requirements as they are obviously giving up quite a bit of efficiency by having their heat pumps off perhaps several times a day. I can't imagine many users going down this route but it will be interesting to see what comes out of the trials if anything is published.Â
Are you going to try it a few more times to get some more data points for your setup?Â
Posted by: @kev-mMy latest tweaks (can't resist 😆)
Weather compensation curve recalibrated so I can set my offset from -4 back to zero
DHW set to come on 12 noon-2pm only. We still have electric showers and don't use much HW. Better it comes on when it's a bit warmer out
And (most radically), heating is programmed to be off 12am-6am. I know the 'slow and steady wins the race' theory for ASHPs and I know the ASHP will have to work hard when it wakes up. But.... I have radiators, a relatively large ASHP and the house has a relatively low thermal mass. Six hours doing nothing will take a big chunk out of the kWh. It also just doesn't feel right heating the 12 other radiators when there's nobody there. If it's too cold in the night or morning I'll revert back. I also won't tell Mrs M and see if she notices or not. Risky, very risky ....  Â
@kev-m
Interested in the first sentence of your post.  I too wish to return my offset back to zero in order to reclaim the full range of adjustment available to me.  Currently I have set it to +4 and occasionally even +6 in this very cold snap.  However I don’t know how to do it.  I’m assuming it’s an adjustment to the compensation curve?  All I know is putting on + figures makes the house warmer.  Can you tell me please what I need to do in order for my current +4 can actually be my zero.  In other words I reset to zero but it’s operating at the current +4.  Hopefully that question makes sense.  SWMBO is giving me a bit of grief suggesting it isn’t warm enough and even wanted the log burner in the lounge lit last night.  I had a wisdom tooth extracted yesterday and feeling grumpy and under the weather (comp’ curve) so some peace would be good.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
- 22 Forums
- 2,096 Topics
- 46.1 K Posts
- 38 Online
- 3,383 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Commencing on an ASHP Installation Process
I should perhaps have mentioned this in my post, as I'd...
By Sheriff Fatman , 7 hours ago
-
RE: Mitsubishi cycling while on chilled water output
@jamespa you are so much faster than me, happy to see g...
By ASHP-BOBBA , 7 hours ago
-
@jamespa Thanks for the advice - very helpful. I had al...
By abam48 , 18 hours ago
-
RE: Weather compensated secondary circuits with Biomass
Hi @andycoo we do an LK 110 standalone weather compensa...
By Sune , 18 hours ago
-
RE: Adding battery storage to SolarEdge PV system
@chandykris No need to apologise at all! I forgot to ad...
By Toodles , 1 day ago
-
RE: Say hello and introduce yourself
Yes please do Suggesting a loss in the region...
By JamesPa , 2 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
Can we have some links to those you're considering plea...
By Transparent , 2 days ago
-
As I have reported elsewhere we turned on the cooling o...
By downfield , 2 days ago
-
@hughf, I think we’ll organise an RHH session at Instal...
By Mars , 3 days ago
-
@el3b Hi, sorry to hear that, it is advisable to instal...
By ASHP-BOBBA , 3 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn Out of intrigue, the thread reads as though Ai...
By Sheriff Fatman , 4 days ago
-
RE: Mitsubishi Ecodan Fails to Heat Water despite temperature drop
@m1kegibson If you are able to access the service me...
By HarriUp , 4 days ago
-
RE: When will heat pumps and install prices come down?
... which of course is impossible because the world mov...
By JamesPa , 4 days ago
-
RE: Battery storage to run Heat Pump.
I would be surprised if the battery chemistry is going ...
By Transparent , 5 days ago