(@chandykris)
Estimable Member Member
567 kWhs
Joined: 8 months ago
Posts: 61
Topic starter  

Our heat pump (6 kW for a heat loss of 5.4 kW) got commissioned a couple of days ago. We had some installation issues, but all resolved now and the heat pump is up and running merrily. The performance is good, getting a good COP and really pleased how quiet the heat pump operates.

All but one room feel nice and toasty. The four bedrooms, a study, two additional living rooms, the bathrooms, WCs and couple of hallways are all between 20 and 22 degrees. But, the biggest room in the house, the open plan kitchen living dining room gets to about 17.5 degrees, that's it. It's got loads of windows, skylights, patio doors etc, but they were all factored in the heat loss calculation. The installer highlighted that the position of the sofa could be blocking the radiant heat. The sofa was positioned just in front of a big K22 radiator. So, I have moved away the sofa completely but still the temperature is steadily around that 17.5 degrees mark.

The radiators were bled and balanced as part of the installation. They installed 6 new radiators (including this one in the open plan area) and reused four radiators we had downstairs for the upstairs bedrooms. All in all, there are 14 radiators and two towel rails, and all but one seem to be doing the job. Any ideas on what could be the issue, or whether I can try something to narrow down what the problem could be. Appreciate your help.

This topic was modified 1 month ago 2 times by ChandyKris

16 * 435 watts PV
6.6 kWh Growatt battery
1 EV - Mercedes EQB
6 kW Aira Heat Pump


   
Quote
(@jamespa)
Famed Member Moderator
10711 kWhs
Veteran
Joined: 2 years ago
Posts: 2018
 

Posted by: @chandykris

The radiators were bled and balanced as part of the installation. They installed 6 new radiators (including this one in the open plan area) and reused four radiators we had downstairs for the upstairs bedrooms. All in all, there are 14 radiators and two towel rails, and all but one seem to be doing the job. Any ideas on what could be the issue, or whether I can try something to narrow down what the problem could be. Appreciate your help.

If the rads are sized correctly then I would normally say that it could (most probably, but not certainly, is) be an emitter balancing issue.  However you say the rads were balanced.

Can you measure the inlet and outlet temperature of the radiator in the cold room, how do these compare to other rads?.  Are there any TRVs in use, if so where?  Is the lockshield valve on the rad in the cold room fully open.  What is the diameter of the main pipework to the radiators?   You may have to turn all the other rads down a bit to force more water through the one in question, but without a bit more diagnostic info its difficult to say.

This post was modified 1 month ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@chandykris)
Estimable Member Member
567 kWhs
Joined: 8 months ago
Posts: 61
Topic starter  

Thanks @jamespa for the pointers. There are TRVs on all the rads, but they all are fully open. We have 10 mm microbore to the radiators. Let me check the lockshield valve, hopefully that solves the problem. If not, will check with the installers after a few days.

16 * 435 watts PV
6.6 kWh Growatt battery
1 EV - Mercedes EQB
6 kW Aira Heat Pump


   
👍
1
ReplyQuote
(@judith)
Honorable Member Member
2549 kWhs
Joined: 1 year ago
Posts: 298
 

@chandyKris We had to turn one of the bedroom radiators to nearly off to force the water to flow to the lounge two. At first the installer did the balancing but frankly the day was too hot for success even with all the windows open. So he had another go when we returned from holiday and we fiddled further a week afterwards.

It’s very fiddly when the lock shield is nearly closed so you might get further control if the trvs do the fine adjustment at the end. But using the lock shields is best then it’s permanent. But you’ll get some pointers about which other radiators to close up by using the trvs as a temporary measure. Then open the trvs again and close more on the lock shield on that radiator. It’s a slow job!

2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC


   
👍
1
ReplyQuote
(@chandykris)
Estimable Member Member
567 kWhs
Joined: 8 months ago
Posts: 61
Topic starter  

Thanks @judith. Definitely, the upstairs bedrooms get a lot warmer, they are all exceeding 22 degrees and staying at that temperature steadily. I have turned down the TRVs in the bedrooms temporarily and check whether that increases the temperature in this downstairs room. I have also raised a support request with Aira, so hopefully they should call and investigate the issue.

16 * 435 watts PV
6.6 kWh Growatt battery
1 EV - Mercedes EQB
6 kW Aira Heat Pump


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
12942 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 2276
 

Posted by: @chandykris

We have 10 mm microbore to the radiators.

Why?

That limits the amount of energy which can be delivered.
So large emitters are more likely to struggle.

 

Posted by: @chandykris

I have turned down the TRVs in the bedrooms temporarily

I appreciate why you have used the TRVs at this stage.

But the final solution will need to be using the lockshield valves to restrict flow to each emitter.

 

Posted by: @chandykris

Definitely, the upstairs bedrooms get a lot warmer, they are all exceeding 22 degrees and staying at that temperature steadily.

It's likely that those upstairs bedrooms are being warmed by heat rising from the room(s) below.

I wonder if that was properly taken into account within the initial energy survey.

You can test this further by simply switching off those radiators completely.
Then check what temperature you get in the bedrooms.

It's difficult to sleep in a room that's above 14°C at night

 

Save energy... recycle electrons!


   
👍
1
ReplyQuote



(@chandykris)
Estimable Member Member
567 kWhs
Joined: 8 months ago
Posts: 61
Topic starter  

@transparent As it was a retrofit, changing 10 mm microbore to bigger pipes was out of question. Changing pipework for a three storey house would have been prohibitively expensive. Having said that, the maximum heat that can flow to this radiator on 10 mm microbore (as per HeatGeek calculations) is still way higher than the heat loss of the room. If I remember, 10 mm microbore at DT7 is about 1.6 kW and the heat loss of this room is about 1.2 kW. So, don't think microbore is the problem. Unless, I have understood it incorrectly.

My DIY skills are rather limited, so if turning down TRVs upstairs helps with the downstairs room, I will ask the installer to balance properly with the lockshield valves.

I did raise the point about bedroom design temperature being high at 21 degrees, but then the design engineer said this is MCS standard. Having said that, it does feel really toasty in the bedrooms now, so maybe turn down a notch. The dog will appreciate that definitely!!

16 * 435 watts PV
6.6 kWh Growatt battery
1 EV - Mercedes EQB
6 kW Aira Heat Pump


   
ReplyQuote
(@jamespa)
Famed Member Moderator
10711 kWhs
Veteran
Joined: 2 years ago
Posts: 2018
 

Posted by: @chandykris

My DIY skills are rather limited, so if turning down TRVs upstairs helps with the downstairs room, I will ask the installer to balance properly with the lockshield valves.

I did raise the point about bedroom design temperature being high at 21 degrees, but then the design engineer said this is MCS standard. Having said that, it does feel really toasty in the bedrooms now, so maybe turn down a notch. The dog will appreciate that definitely!!

MCS spec for bedrooms is actually 18C.

Its quite difficult for an installer to balance radiators properly because it takes a long time.  If you post a picture of one of your lockshield valves we can tell you what to do, you will most likely need a 7 or 8mm spanner (or an adjustable spanner.  Normally its as simple as popping off the plastic cap then using the spanner on the spindle projecting out of the top.  Often the easiest way to start if dirst to turn it off fully, then to turn it up a turn, and work from there making small changes and leaving for a few hours each time.

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
1
ReplyQuote
(@chandykris)
Estimable Member Member
567 kWhs
Joined: 8 months ago
Posts: 61
Topic starter  

@jamespa Few others on the forum mentioned about the 18 degrees too. But, the design engineer didn't budge. I wonder whether that's to keep the existing towel rail radiators in the bathrooms as-is.

I have done exactly like you have mentioned, pop the white cap off and turned the valve anticlockwise until it's fully open.The temperature has gone up slightly around 18 degrees now. I assume it will take a few hours to settle, as I have turned down the TRVs in the bedrooms and my study to four from five. It has dropped a little bit down upstairs by 0.5 degrees and is steady now. I will speak to Aira on Monday and see whether they can do anything remotely like the flow rate before making further changes.

This post was modified 1 month ago 2 times by ChandyKris

16 * 435 watts PV
6.6 kWh Growatt battery
1 EV - Mercedes EQB
6 kW Aira Heat Pump


   
ReplyQuote
(@jamespa)
Famed Member Moderator
10711 kWhs
Veteran
Joined: 2 years ago
Posts: 2018
 

Posted by: @chandykris

Few others on the forum mentioned about the 18 degrees too. But, the design engineer didn't budge.

 

designer is talking rubbish.  See page 14 of this document 

Posted by: @chandykris

I have done exactly like you have mentioned, pop the white cap off and turned the valve anticlockwise until it's fully open.The temperature has gone up slightly around 18 degrees now. I assume it will take a few hours to settle, as I have turned down the TRVs in the bedrooms and my study to four from five. It has dropped a little bit down upstairs by 0.5 degrees and is steady now. I will speak to Aira on Monday and see whether they can do anything remotely like the flow rate before making further changes.

It sounds like its moving in the right direction.  TRVs may not have the same effect as lockshields since they will switch on and off rather than presenting a static turned down position.  4 out of 5 is really still high so my guess is you will either need to turn it down quite a lot more to get from 21 to 18 (if thats your desired temp) or resort to the LSVs.  As an alternative if you have got the static 'decorators caps' for the TRVs, unscrewing the head and replacing it with one of these is an option giving you fine control but acting like an LSV.

 

Unfortunately trial and error is the name of the game here, until flow balancing valves designed for heat pumps become commonplace, which currently they are not.

 

 

This post was modified 1 month ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
1
ReplyQuote
(@chandykris)
Estimable Member Member
567 kWhs
Joined: 8 months ago
Posts: 61
Topic starter  

Looks like this issue is now resolved. Aira installed a K3 radiator, with 20% more output, and now the temperature is holding steady around 19.5 degrees in the open plan living kitchen dining room. Given the decent solar gain in that room and heat from cooking, this room is now perfect. The cold snap next week will be a good test, but pretty confident that it should hold up even in sub zero temperatures.

16 * 435 watts PV
6.6 kWh Growatt battery
1 EV - Mercedes EQB
6 kW Aira Heat Pump


   
👍
3
ReplyQuote
Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

Members Online

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security