Issue with Samsung A2W Heat Pump - Water Outlet Temperature
Dear Community
Today - It was 0.4°C outdoors, but the Water Output Temperature was regulated to 34°C. Based on the Water Law configuration, it should start at 35°C.
I assume there is some setting that prevents the unit from allowing more than 35°C for Floor heating.
I do not have a Samsung so I'm just speculating until someone more useful comes along.
Just using the numbers you've provided it seems like you're getting 8.4kW from the unit (DT * flow rate * SHC). I wonder if the flow temp won't go any higher because you're right at the limit of the unit's power. Samsungs have external pumps, right? Is that set to full power or is it controlled by the heat pump via PWM? I would have thought in any case that higher flow rate and lower temps is better for efficiency reasons anyway.
- 24 Forums
- 1,419 Topics
- 29.8 K Posts
- 48 Online
- 1,205 Members
Join Us!
Latest Posts
-
RE: Bivalent (or even trivalent!) system design options for a new GSHP installation
@transparent You are a bright spark aren’t you?!
By Toodles , 2 hours ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
That could be the case, depending on where the triple r...
By AllyFish , 2 hours ago
-
RE: No-code, plug-and-play monitoring for your heat pump
Thanks for highlighting this product, @editor. It's an ...
By Majordennisbloodnok , 3 hours ago
-
RE: Ecodan software update. Real or scam?
@Morgan then that looks legit to me, because the people...
By Mars , 3 hours ago
-
RE: Say hello and introduce yourself
@irmartini Oh! That’s a great shame.😳 Toodles.
By Toodles , 3 hours ago
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
@david999 On the subject of isolation after the battery...
By HughF , 9 hours ago
-
RE: New Fogstar 15.5kWh upright solution
@robl I've added the screens. Li-Bms screen is accur...
By GGW , 19 hours ago
-
RE: SCOP and seasonal variations
I’ve had a long chat with Aaron from Homely Technical S...
By Toodles , 23 hours ago
-
RE: Gas Combi to ASHP - Making sense of survey results and proposal.
Many thanks to everyone who has helped with advice and ...
By IRMartini , 1 day ago
-
RE: What is Wrong with our Heat Pump Installation?
With BESS the ASHP is best. Charge battery for free fro...
By AllyFish , 1 day ago
-
@hubb84 Try looking at powerflushassociation.com. They ...
By Toodles , 2 days ago
-
Central heating inhibitor with ASHPs
Have you seen the Heat Geek article and video?
By ChickenBig , 2 days ago
-
RE: Advice on potential HW Cylinder size
@jwilliams89 I would imagine that the MCS would insist ...
By bontwoody , 2 days ago
-
RE: Creating a second zone on Mitsubishi Ecodan ASHP
Had another go at this, the morning. With SW2-7 ON it ...
By BryanB , 2 days ago
-
RE: Samsung ASHP scheduling help
@morh Your post was music to my ears! I am getting a ...
By Elgreco69 , 3 days ago
-
RE: Issues with Vaillant connectivity via the MyCONNECT gateway
@drew-pa I have given up on the app - right now it is s...
By dr_dongle , 3 days ago
-
RE: ASHP Advice: High Temperature vs. Low Temperature Heat Pump For Microbore
Hi - we have a Daikin 16kW HT ASHP installed which was ...
By Marzipan71 , 3 days ago
-
RE: Question about Ecodan's Room Autoadapt mode
@gary Thanks. I'm emboldened to give it a go!
By afarmery , 4 days ago
-
RE: My ASHP is not performing as well as I’d hoped: COP just over 2
@toodles No. But I wasn't forced there either and The K...
By Morgan , 4 days ago
-
RE: Viessmann Vitocal 250-A in the UK
We have a 10Kw Viessmann 200A it SCOP is currently 5.2,...
By MikeF , 4 days ago
Latest Topics
-
Ecodan software update. Real or scam?
By Morgan 5 hours ago
-
Noise problems with newly installed Samsung 8kW ASHP
By Lokisam 2 days ago
-
Central heating inhibitor with ASHPs
By IRMartini 2 days ago
-
Advice on potential HW Cylinder size
By JWilliams89 3 days ago
-
By Graeme 4 days ago
-
Interesting heat pumps installations
By Mars 7 days ago