Issue with Samsung A2W Heat Pump - Water Outlet Temperature
Dear Community
Today - It was 0.4°C outdoors, but the Water Output Temperature was regulated to 34°C. Based on the Water Law configuration, it should start at 35°C.
I assume there is some setting that prevents the unit from allowing more than 35°C for Floor heating.
I do not have a Samsung so I'm just speculating until someone more useful comes along.
Just using the numbers you've provided it seems like you're getting 8.4kW from the unit (DT * flow rate * SHC). I wonder if the flow temp won't go any higher because you're right at the limit of the unit's power. Samsungs have external pumps, right? Is that set to full power or is it controlled by the heat pump via PWM? I would have thought in any case that higher flow rate and lower temps is better for efficiency reasons anyway.
-
Sudden drop in COP
3 weeks ago
-
Samsung E911 intermittent issue
7 months ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
9 months ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
1 year ago
-
Any installer recommendations for Samsung ASHP?
1 year ago
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 25 Online
- 5,662 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Mitsu Wireless Controller and MelCloud
Update: I have found that the contractor had changed on...
By DavidAlgarve , 11 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@editor Hi Mars, We have just installed a Grant Aerona...
By GrahamF , 12 hours ago
-
RE: Sanity check please. Battery storage and inverter sizing.
There are MCS guidelines about how close to the edge/ri...
By Old_Scientist , 15 hours ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
I estimated our usage on the following basis. The mos...
By Old_Scientist , 16 hours ago
-
RE: Rodents! A word of warning for heat pump owners
ChatGPT comments: Yes – u...
By Tim441 , 18 hours ago
-
RE: Why so many sigenergi installer recommendations?
It’s a really simple answer, GivEnergy. Installers ...
By SAEnergy , 20 hours ago
-
@editor Something changed in this last 12 months, they ...
By ASHP-BOBBA , 2 days ago
-
RE: Ecodan & MelCloud scheduling
I put the above question to Mitsu UK at the sme time as...
By DavidAlgarve , 2 days ago
-
Thanks for the heat geek info. I've fitted my own heat ...
By bontwoody , 3 days ago
-
RE: Does anyone have experience of a smart water meter?
Just to give a sense of scale, I've used the CCW water ...
By Majordennisbloodnok , 3 days ago
-
RE: Powerwall 3 or Myenergi or something else?
We have a Tesla Powerwall 3, recently installed, so I m...
By Old_Scientist , 4 days ago
-
RE: Mitsubishi PAR-WT60R-E Wireless Controller installation
@morgan They have been paired once but it was thought b...
By DavidAlgarve , 5 days ago
-
RE: Isolating the system for a planned power cut
A great many ground-mounted local substation transforme...
By Transparent , 5 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 6 days ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 6 days ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 6 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 1 week ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 1 week ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 1 week ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 1 week ago