Is your gut better than Math
Every Day is a School Day with an ASHP
Owning an air source heat pump (ASHP) is a constant learning experience. We’ve installed plenty over the years, but only one with a full energy monitoring system.
Normally, we rely on manufacturer data from their various apps and online portals—which, let’s be honest, never quite tell the full story.
Recently, I installed a Vaillant aroTHERM plus 10kW three-phase ASHP at my own home, complete with full monitoring hardware, so I can finally see what’s actually happening with the system. I deliberately went for an oversized unit because—well, my gut told me to. Come summer, we’ll be linking the house to an older building, so at the moment the ASHP is nearly twice the size it could or should be?!
The main house itself is a new build, with 285m² of ground floor space and an additional 15m² mezzanine above the master bedroom. About 50% of the house has ceilings averaging 3…5 metres high, so there’s plenty of air to heat. It’s super-insulated, has high thermal mass, an airtightness of 1.9m3 /(h·m2 ) @ 50Pa and no heat recovery or trickle vents.
yes, no MVHR! I did consider installing an MVHR system, especially since our home is fairly airtight, and recovering up to 80% of the heat from outgoing stale air sounds like a great idea. But every home is different, and how it performs depends on how it’s actually used by its occupants. Instead, we stick with good old-fashioned Stoßlüften (shock ventilation)—turns out, simply opening a window at the right time works brilliantly, especially when combined with the building’s thermal mass! Our windows have always been, and always will be, wide open first thing every morning while the beds are made, and again, probably kept on the night latch every evening. Fresh air, no faff! That said, I wouldn’t recommend this for everyone. In fact, in my day job, I strongly advocate for installing MVHR to maintain good air quality in buildings. It’s an excellent solution for many homes, especially those that are well-sealed and occupied in a way that limits natural ventilation opportunities. But for us? We’ll keep doing what works!
We’ve got underfloor heating (UFH) throughout with 100mm pipe centres buried in 98mm of beautifully polished concrete. This not only provides a fantastic heat store but also makes for a seriously nice-looking floor—because why shouldn’t heating be both efficient and stylish?
The older building we’ll be linking to adds another 80m², with similar U-values. However, it won’t match the airtightness or thermal mass of the main house and will require radiators. This brings the total footprint to 380m², with a calculated heat loss of 6.86
17 W/m² for the main house (17 × 300m²) = 5.1kW
22 W/m² for the older building (22 × 80m²) = 1.76kW
Total heat loss = 6.86kW
So why did I go bigger than necessary? Because my gut said so.
We did all the usual heat loss calculations, Vaillant did theirs, and even our merchant confirmed the numbers. Every bit of logic pointed to a 7kW system being the perfect fit. But despite all that, I went with my instincts and opted for the 10kW unit instead.
I’m always the first to say, “Trust the numbers”—but this time, I didn’t.
The system was installed in December, with the heat monitoring linked on the 17th Jan, meaning we now have nearly a full month of data—aside from the 36-hour blackout courtesy of Storm Éowyn, which apparently decided we didn’t need electricity for a while. That little hiccup aside, the data is starting to paint a very interesting picture of how the system is actually performing.
The initial results, well they looked promising, with the first week averaging a COP of 6.1 with a mean outside temperature of 7°C. Given that this cold wee country averages around 10°C over the year, that’s a very encouraging start.
Over the following three weeks, we’ve seen a 3-4°C drop in outdoor temperatures, in addition to tweaking the system to see how I can achieve the best COP for domestic hot water (DHW). As a result, our overall SCOP (30-day average) is now sitting at 5.3—still respectable, but there’s plenty more experimenting to be done!
So, back to the oversizing…
Today has been the warmest day since installation, and the charts and graphs on Emoncms Heat Pump Monitor make for some interesting reading. In addition to the increase in outdoor temperature, I did two things yesterday:
- Dropped the heat curve from 0.3 to 0.25
- Set the system to Eco Mode
The result? Eco Mode has nearly doubled the DHW COP—but is this purely down to Eco Mode, or is it just the effect of the warmer outdoor temperature? Something to investigate further.
Another interesting—or slightly concerning—occurrence is that the ASHP appears to be switching off or at least cycling for extended periods. Between 2:10 am and 5:10 am this morning, the heat pump was basically off.
Is this a sign that the system is too oversized for the milder weather, or is it simply a normal response to lower heat demand? Will adding the extra 80m² of building help balance things out, will the high thermal mass and system volume just deal with it or have I set myself up for a troublesome time?
Only time will tell whether gut instinct beats maths… but for now, the system is running well, and the learning continues!
I think I would be asking myself ‘ Why is my gut instinct so far out of kilter with the science and the maths!?’ Impressive COP though😉 Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@aaron Welcome to the forum.
With a heat loss of 5.1kW for the main part of the house, I'm not surprised you are seeing cycling as the weather is currently a little milder. My assumption is the heat pump is producing more heat than the property needs at these milder temps, even when modulating down to minimum output. Bringing the additional building online will help in milder weather.
My own heat pump is oversized for our heat loss (we have radiators, not UFH), and we are only able to run constantly at low flow temps when the outside temp reaches ~5C or below, and even then we tend to turn off for a few hours overnight to achieve 18C for sleeping. At the current ~10-12C ambient temps we are seeing, we tend to be on for an hour or so and then off for an hour or two, depending on the hysteresis. As long as the system isn't short cycling (cycling very quickly), I don't think this is overly inefficient compared to constant running.
It's our first winter, but so far my impression is that an oversized heat pump isn't the worst thing in the world and can be operated efficiently. Like you, we are able to achieve good COPs. The last couple days we have got COPs over 5 running 32C flow temps in our radiator system, and have had a worst case daily COP of 3.0 on the coldest day, with the coldest month averaging in the high 3's. If you are achieving COPs of over 5 in winter, I'd be delighted.
EDIT: Not sure about ECO mode on the Vaillant, but I use Samsung's Quiet Mode for DHW runs which limited the output (and hence the noise) to around 70%. This has the effect of ensuring the heat pump is operating in it's most efficient range (i.e, compressor not running flat out), and narrows the dT allowing the heat to transfer into the DHW tank at a slightly lower flow temp. Last summer I ran some tests and found it consistently used less energy each day to reheat the tank than in 'normal' mode.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
Its good to hear that you are pleased with the outcome. I agree with @old_scientist that cycling is to be expected (and is unavoidable) in milder temperatures with a heat pump that has a max output well in excess of the house demand. Its cycling slowly so not really an issue, unless you are uncomfortable with any temperature variations in the house, in which case there are some adjustments that could be made. My 7kW Vaillant is pretty well matched to the house and the onset of cycling is about 11C, which is more or less precisely what one would expect.
The detrimental effects of cycling arent particularly well quantified. At higher flow temperatures such as might be typical with radiators there is a quantifiable detrimental effect on COP (because when the system is running it must do so at a higher temperature than if it were running permanently), but with your very low flow temperatures (resulting presumably from the closely spaced UFH) this is very much less. Soft start compressors mitigate the potential damage to the compressor that was the bogeyman when compressors were fixed speed, so its really a bit unclear overall when you are operating at such low FTs.
Posted by: @aaronThe older building we’ll be linking to adds another 80m², with similar U-values. However, it won’t match the airtightness or thermal mass of the main house and will require radiators. This brings the total footprint to 380m², with a calculated heat loss of 6.86
Im sure you already know that but you will lose the COP advantage of UFH if you end up having to operate your radiators at a higher flow temperature and 'mix down' for the UFH. You may want to give some careful thought to the emitter design/selection (if you havent already/its not too late).
Posted by: @aaronid consider installing an MVHR system, especially since our home is fairly airtight, and recovering up to 80% of the heat from outgoing stale air sounds like a great idea. But every home is different, and how it performs depends on how it’s actually used by its occupants. Instead, we stick with good old-fashioned Stoßlüften (shock ventilation)—turns out, simply opening a window at the right time works brilliantly, especially when combined with the building’s thermal mass! Our windows have always been, and always will be, wide open first thing every morning while the beds are made, and again, probably kept on the night latch every evening. Fresh air, no faff!
There is a reason why windows are deigned to open! One air change per day is well below the recommended value of typically 0.5ACH but as you say the effect on energy is nothing like as much as one would imagine, because it is just that, one air change per day, perhaps 2, as opposed to 12 from 0.5ACH. With MVHR 0.5ACH is equivalent to perhaps 2-3 air changes per day in terms of energy loss, so about the same. Obviously you have some natural infiltration on top, but if the house isnt getting mouldy, damp or musty I can see nothing wrong with the low tech solution personally!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I wonder if those charts could be redrawn to make the LWT and RWT trends easier to read? Was the system in eco mode during the night when it was cycling? Can you add compressor speed to the chart?
A heat pump works by condensing the refrigerant against the water flowing through the heating. As the RETURN water temperature increases, the compressor discharge pressure must increase otherwise the refrigerant will not condense. This is why the COP usually goes down as the LEAVING water temperature goes up, because the return water temperature also goes up. However, if you have a house with a huge thermal mass (lots of concrete underfloor heating) the return water temperature doesn't go up very much, because all the energy is removed from the water. So houses with huge thermal mass and underfloor heating should be able to get very high COP, at least upto the point where the slab is "fully charged".
Anyway...assuming its the RETURN water temperature which sets compressor power and therefore COP, you would get the best efficiency at the lowest return water temperature. It looks to me like eco mode is trying to limit the return water temperature.
I would say engineering is about knowing the theory of how the system should work and then adjusting the design based on what you know actually happens. I strongly suspect this system is benefiting from the oversized compressor not being run flat out, but it will cycle at low power demands. My opinion would be to have two heat pumps, so you could achieve very low power outputs from 1 pump, and high outputs from 2 pumps.
Regards
Bob
Posted by: @bobtskutterMy opinion would be to have two heat pumps, so you could achieve very low power outputs from 1 pump, and high outputs from 2 pumps.
The Mitsubishi R29O pump has 2 compressors to achieve exactly that. Sofaik the only domestic one so far to do this
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa we will design the emitters/radiators to suit the same flow temperature. If this can't be achieved with radiators or they take up too much space we will consider in ceiling heating.
Posted by: @old_scientistEDIT: Not sure about ECO mode on the Vaillant, but I use Samsung's Quiet Mode for DHW runs which limited the output (and hence the noise) to around 70%. This has the effect of ensuring the heat pump is operating in it's most efficient range (i.e, compressor not running flat out), and narrows the dT allowing the heat to transfer into the DHW tank at a slightly lower flow temp. Last summer I ran some tests and found it consistently used less energy each day to reheat the tank than in 'normal' mode.
That is interesting, I read an article recently advising against the use of "Quiet Mode" for heating, it is only for use when the heat pump is in cooling mode in the summer. This is so the pump does not create too much noise during a warm night.
How long and to what temperature does your set up operate to?
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss, deltaT = 8 degrees
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
4.1Kw Solar Panel Array
34Kwh GivEnergy Stackable Battery System
Posted by: @technogeekPosted by: @old_scientistEDIT: Not sure about ECO mode on the Vaillant, but I use Samsung's Quiet Mode for DHW runs which limited the output (and hence the noise) to around 70%. This has the effect of ensuring the heat pump is operating in it's most efficient range (i.e, compressor not running flat out), and narrows the dT allowing the heat to transfer into the DHW tank at a slightly lower flow temp. Last summer I ran some tests and found it consistently used less energy each day to reheat the tank than in 'normal' mode.
That is interesting, I read an article recently advising against the use of "Quiet Mode" for heating, it is only for use when the heat pump is in cooling mode in the summer. This is so the pump does not create too much noise during a warm night.
How long and to what temperature does your set up operate to?
You could be correct (I'd love to see a link if you can find the article). My Samsung unit does weird things (does not behave as expected) if I use quiet mode when space heating is in operation. When running with weather compensation, the LWT does not stay at the set point, but continues to rise, so there is a bug there (or as you suggest, this is just not it's intended usage). I do not use Quiet Mode when space heating for this reason.
However, during a DHW run, where the LWT does just continually rise until the DHW tank set temp is reached and it switches off, activating Quiet Mode has the effect of limiting input/output/compressor speed? (I'm not sure what it actually limits). If quiet mode were not activated, when reheating the DHW from 30-45C, I would typically see the input power gradually rise over the 20-30min run, starting at around 2kW and maybe peaking at 4.7kW. The LWT may finish at around 9C above the DHW tank set point of 45C (so maybe 54C).
If I turn on Quiet Mode, the peak power draw is limited to around 3.3kW, and the difference between the final LWT and DHW tank set point is lower, with LWT finishing 6-7C above the set point (LWT 51-52C, DHW tank 45C). The run takes slightly longer but uses less energy input overall, and obviously we are not having to heat the LWT as high. I also benefit from longer runs at lower power, as more of the power used is covered by my 3.6kW solar array in summer.
This also has the added advantage that the system is not running flat out annoying the neighbours for 20-30mins at 4am.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss, deltaT = 8 degrees
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
4.1Kw Solar Panel Array
34Kwh GivEnergy Stackable Battery System
I don't believe your approach is purely gut-feel.
You've used knowledge/experience to build in some features which allow you greater flexibility to control the heating efficiency.
Posted by: @aaronWe’ve got underfloor heating (UFH) throughout with 100mm pipe centres buried in 98mm of beautifully polished concrete.
Somewhere you've picked up the concept that pipe-spacing makes a difference when embedding them in a concrete pad.
You've also decided to use several interpersed pipe-loops within the same concrete slab.
That allows you to turn off a loop if you wanted to lengthen the heating-time.
Equally you can turn on loops if you wish to increase the total volume of fluid in the system.
Those two actions will affect the amount of Heat-Pump cycling.
The vast majority of the respondents arriving here on the RHH Forum are lacking this sort of background knowledge.
They don't know enough to query the proposed solution being offered by an installer.
By the time they get here, we are often the "last gasp" port of call in a dispute with the installer due to the very high electricity bills they now have.
Informing the public about the underlying concepts is an important part of our role,
either through this forum or talking with friends & neighbours.
Save energy... recycle electrons!
-
Is Your 6kW Air Source Heat Pump Really a 6kW?
10 months ago
-
Oversized Daikin 9kw
11 months ago
-
Trickle vents v mechanical ventilation
3 years ago
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 847 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Daikin Altherma 3 LT compressor longevity question
This mess is intriguing: I wonder if this represent...
By bobflux , 41 minutes ago
-
RE: Say hello and introduce yourself
Hi. I'm Mike. Thank you for letting me join. My partn...
By Fretless6 , 2 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 5 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
ASHPs do have a minimum compressor speed. The minimum h...
By bobflux , 12 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 12 hours ago
-
RE: Tell us about your Solar (PV) setup
Location: near Lyon, France 12kWp on the roof, 2x Sol...
By bobflux , 13 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 15 hours ago
-
What matters for flow and pressure drop is internal dia...
By bobflux , 16 hours ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 18 hours ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 22 hours ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 2 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 3 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
Yes... I went through this particular headache and ende...
By bobflux , 4 days ago
-
O-oh! Let's take this as an opportunity to 'pass the ...
By Transparent , 4 days ago
-
RE: Homely setup on daikin heat pump
@craigh I refer to our somewhat elevated temperature of...
By Toodles , 4 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
My turn, this describes the future installation, only t...
By bobflux , 4 days ago