Is My Midea Heat Pump Inherently Defective?
Posted by: @bobtskutterSwapping the radiator for a fan coil might not give you additional heat output because it's not the radiator that's causing the "restriction".
Absolutely, I am very aware of that! Moving to a fan coil is an (major) aesthetic improvement, but only once I know it will have adequate flow.
I am still trying to think of a way of making a diagnosis ie where is the obstruction, and what is it. I know how to drain the system and so also know it is not a trivial undertaking, and I would prefer to know if possible what I need to fix while it is drained down. I am also not inclined to do it during one of the coldest month's of the year, in case something goes wrong!
Midea 14kW (for now...) ASHP heating both building and DHW
Naturally I was concerned that increasing the energy out (delivered to the house) by opening up the lock shield valves might increase the energy in (used). I now have enough data to be able to plot hourly energy in and mean room temp for hours at a particular OAT for before and after I opened up the valves. I have done this for year to date (note date time axis is categorical, they are just the hours that match the OAT criteria), for mean OATs of 5 (5.0-5.9, normal running) and 2 (2.0-2.9, defrost territory) , and marked when the valves were opened with a down pointing arrow:
Interestingly, no obvious penalty, in fact very possibly (need more data, and there are things I haven't controlled for...) an improvement! In both charts the mean room temp improves a bit (as expected) and in both charts the energy in appears to fall. It's more marked at 5 degrees than 2 degrees OAT, but still present on both charts. Truly heat pumps are a miracle, that surpasseth all understanding...
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayTruly heat pumps are a miracle, that surpasseth all understanding...
I've just remembered...two days after I opened the LSVs I dropped the weather compensation curve 2 degrees, and then 2 days later I dropped it by another 2 degreees.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayI dropped the weather compensation curve
That'll do it 😉
Can you go lower?
Bob
Posted by: @bobtskutterCan you go lower?
Very possibly. The IAT is at the warm end of my preferred range, and it looks like we'll have fairly settled though cool weather here over the next few days so a good time to experiment. Watch this space...
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayTruly heat pumps are a miracle, that surpasseth all understanding...
Somehow that feels like the basis of a motto/strapline.
Without a doubt the combination of the nonlinear response to the main variables, the inherent complexity of the thermal dynamics of houses, contrasted with the extremely simplicity of the thermodynamics on which it is all based, really does make them fascinating beasts.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@cathoderay any updates in this mild spell are you boiling indoors yet?
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
Posted by: @judithany updates in this mild spell are you boiling indoors yet?
Thanks for asking. Yes, the indoor air temperature has certainly been more consistent, a bit higher by a degree or two despite the fact I have lowered the leaving water temperature by a few degrees. The Mark 1 Human Sensor (me) also reports good comfort levels. All in all a success, and I don't think my costs have increased greatly, if at all, the lower LWT appears, as expected, to mean better performance, with COPs at times in the 4-5 range. Sometimes I think we forget how much difference a change in COP can make. For example, a seemingly not very large change, at least in absolute terms, from a COP of 3 to 4.5 means, all other things being equal, including having the same heating load, the unit costs part of my electricity bill falls by one third - where I would have paid £100, I now only pay £66.66, not a trivial saving.
Here's my chart for the last week. On Monday, I restarted the overnight setback (using room stat down to 16 degrees between 2100 and 0300), as I am interested to see how the now all valves open system copes with the recovery period after the setback. Previously it struggled, sometimes taking 12 hours or so to get back to temperature. On Tuesday morning, after a mild night, it recovered well, back to where it should be by 0700. Last night was significantly colder, and the recovery has been a bit slower, but by no means a disaster, despite being in defrost territory. Bear in mind this is partly managed by my auto-adapt script, which adjusts the LWT depending on how far the actual IAT deviates from the desired IAT. At the moment the script is set up to do one degree of LWT change for every degree of actual vs desired IAT deviation, up to a max of 3 degrees eg if desired IAT is 19, actual IAT is 17, deviation is 2 degrees and LWT increases by 2 degrees. These parameters are easily changed, by editing the script and restarting it. I am going to run the system as is for a week, and then see if it needs any tweaking.
Note: subsequent comments here about setback running have now been moved to another thread here.
Midea 14kW (for now...) ASHP heating both building and DHW
- 22 Forums
- 2,096 Topics
- 46.1 K Posts
- 138 Online
- 3,383 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Mitsubishi cycling while on chilled water output
On the buffer tank issue, I use Perplexity more and mor...
By downfield , 40 minutes ago
-
RE: Commencing on an ASHP Installation Process
A system like that seems susceptible to significant amo...
By Majordennisbloodnok , 4 hours ago
-
@jamespa Thanks for the advice - very helpful. I had al...
By abam48 , 1 day ago
-
RE: Weather compensated secondary circuits with Biomass
Hi @andycoo we do an LK 110 standalone weather compensa...
By Sune , 1 day ago
-
RE: Adding battery storage to SolarEdge PV system
@chandykris No need to apologise at all! I forgot to ad...
By Toodles , 2 days ago
-
RE: Say hello and introduce yourself
Yes please do Suggesting a loss in the region...
By JamesPa , 2 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
Can we have some links to those you're considering plea...
By Transparent , 2 days ago
-
As I have reported elsewhere we turned on the cooling o...
By downfield , 3 days ago
-
-
@el3b Hi, sorry to hear that, it is advisable to instal...
By ASHP-BOBBA , 4 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn Out of intrigue, the thread reads as though Ai...
By Sheriff Fatman , 4 days ago
-
RE: Mitsubishi Ecodan Fails to Heat Water despite temperature drop
@m1kegibson If you are able to access the service me...
By HarriUp , 4 days ago
-
RE: When will heat pumps and install prices come down?
... which of course is impossible because the world mov...
By JamesPa , 4 days ago
-
RE: Battery storage to run Heat Pump.
I would be surprised if the battery chemistry is going ...
By Transparent , 5 days ago