Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @bobtskutterAre the pipes to living room radiator in a concrete floor? Do they have insulation? You're probably loosing heat into the slab.
You might want to set your pump back to CC3 just to see if makes any difference.
Yes they are in a concrete floor. I think they were covered in Denso tape for corrosion protection, not sure about insulation. It was a long time ago...
I did check the living room rad after opening all the lock shields when I was still on CC3, it was cold then as well.
I do have an infrared camera and thought it might be possible to find out something using it. It confirms the rad itself is as the same temperature as its surroundings, with just a barely detectable bit of warmth in the feed (~20 degrees). The penultimate rad on the way to the living room rad is interesting. You can see it's supply pipes in the floor, coming in from the left, but nothing going out on the right towards the living room:
This suggests some sort of blockage to me, but of course there is no clue as to where it is. The pin on the TRV (the head is off) moves freely but I wonder if you can get rogue one where the pin moves but the actual shut off bit doesn't. Or whether the same thing can happen with lock shields, appear to be open but the are not.
The radiator circuit had a very thorough power flush at installation time (Feb 2022), partly because even back then the living room rad was cool.
@judith - yes, Bob's help has been invaluable - thanks Bob!
I installed the pipes myself (1986?) and all I remember is the Kango and the dust! I'm pretty sure I didn't do anything silly but I can't remember about the insulation. I thought I had some photos taken at the time, but if I do have some, I don't know where they are!
See also the above about no heat getting beyond the penultimate rad. If heat was getting lost to the slab, I think I might see some heat past the penultimate rad when then fizzles out.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayThe pin on the TRV (the head is off) moves freely but I wonder if you can get rogue one where the pin moves but the actual shut off bit doesn't
Yes. If the pin feels sprung then no problem. If it moves freely then the closing piece (not sure what it's called) may be stuck. A few sharp taps with a hammer directly opposite the outlet to the rad usually frees it. Standard procedure at the beginning of the season!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaIf the pin feels sprung then no problem.
Moves freely but definitely against a spring with increasing resistance as it is pushed down, not flapping in the breeze freely.
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay you're very welcome.
If your living room radiator got warm when you had the system balanced with the lock shield valves pinched in then the pipework is probably not blocked, at least not completely.
It's likely the long(ish) run of narrow (15mm) pipe is creating too much flow restriction. The flow path through a 15mm TRV is a narrow orifice about 4 or 5mm. If you can change the TRV for a simple lock shield valve it might improve things (but that's not going to be an easy job).
My in-laws once had their single pipe "solid fuel type" heating system power flushed and TRV's fitted. Most of the radiators stopped working because of the narrow flow path through the TRV's (single pipe systems have almost driving force to get the water into the radiators, it's all done by convection). I swapped several TRV's for basic lock shield valves to improve the system.
It's not impossible that a T-piece on the branch to the living room radiator is partially blocked. That could direct the flow away from the branch to the living room. You would have to disconnect the living room radiator and vent water from each valve (TRV and lockshield) to clear each branch. (Had to do that at the in-laws as well).
Bob
Posted by: @bobtskutterIf your living room radiator got warm when you had the system balanced with the lock shield valves pinched in then the pipework is probably not blocked, at least not completely.
It did get warmer, but never as warm as the other radiators. I agree the evidence points to a partial restriction, significant enough to reduce flow in normal running to the point where effectively no heat arrives at the radiator. It is about 9 metres each way, and as I think I mentioned has more than its fair share of 90 degree elbows where the pipe work travels round from the old radiator wall to the new radiator wall.
Posted by: @bobtskutterThe flow path through a 15mm TRV is a narrow orifice about 4 or 5mm. If you can change the TRV for a simple lock shield valve it might improve things (but that's not going to be an easy job).
That is a very tight orifice! Being so small, it must also be vulnerable to blockage, though I have to say I think my system despite it's age is fairly clean (the water that came out when I bled the rad yesterday was clear). It might be worth cycling the TRV through its full range a few times, and then applying @jamespa's light touch tap with a hammer. Changing the valve will be a big job, full system drain down as the radiator is on the ground floor.
That said, I have never been happy with the aesthetics of the radiator. It is a large K3 taking up about half of an inside wall, in a room with limited wall space. It dominates that part of the room. It 'had' to go on that wall as the adjacent wall (where the old rad was) was not big enough to take a properly sized K3. The upshot of all this is I have for a while been mulling over finding a large enough vertical 'designer' radiator than can go where the old rad was, but when I have looked, all I have found is ludicrously priced designs that look like they have fallen off a space ship, and still don't have enough output. A low ceiling is another constraint. The room's calculated heat loss is 1700W, and at heat pump temperatures that means a big radiator.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayand then applying @jamespa's light touch tap with a hammer. Changing the valve will be a big job, full system drain down as the radiator is on the ground floor.
Just to say you do need a firm tap (occasionally several), just opposite the inlet to the radiator. Hit it about as hard as you dare. Sometimes this partially frees it and you need to 'work' the pin to free it completely. Your flow and return are reversed I think which may mean that the water pressure is working against you.
Posted by: @cathoderayIt is a large K3 taking up about half of an inside wall, in a room with limited wall space.
I potentially had that problem for one of my rads in a living room. FWIW I ended up with a Mitsubishi fancoil. Expensive (~550) and you can hear the fan, but its no more disturbing than the fridge which is in the same room and not at all tonal, just white noise. Looks very smart and neat, (they are Italian and it shows IMHO).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa - I'm not convinced the valve is jammed shut (the pin has the expected spring resistance), more that it is blocked, the idea being that rattling it by tapping it might free a blockage if there is one.
I hadn't thought of using a fan coil in the living room, certainly worth looking into.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @bobtskutter@jamespa please can you share the details of the fan coil you used.
Thanks
Bob
Mitsubishi iLife 2 slim. https://www.saturnsales.co.uk/I-Life2-Slim-DLMV-170-ATS2-Fan-Assisted-Radiator.html
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa - thanks. It looks like the larger version will just fit where the old radiator was, and the max output at heat pump flow temps is 2.11kW, more than enough for the room (1700W). I may need to check the flow rate though! City Plumbing Supplies do the larger one for £505.44 inc VAT and delivery, with the possibility of discounts.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayI may need to check the flow rate though!
Shouldn't be a problem, in common with many fancoils it has a very short pipe with lots of fins on, not a long pipe. That means it doesn't add much to system volume or resistance.
At full output expect to hear the fan quite distinctly (but not annoyingly, at least not to me). Mine rarely goes up to full speed.
One thing to watch is that it shuts down when the FT < 30C. So far this hasn't been a problem, but at the end of the season it might be as I might end up operating at a FT just a bit under. This setting isn't adjustable, but Im guessing a resistor in series (or parallel as appropriate) with the sensor might fool it into thinking the FT is just a bit higher than it is. I might have to make it switchable summer/winter if I use the unit for cooling, which I just may. That said the room where it is has another radiator and gets lots of solar gain, so it might not matter when we get to that point in the season where Im still heating but at a low FT.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
The flow restriction to your living room radiator is likely to be the pipes and valves. Swapping the radiator for a fan coil might not give you additional heat output because it's not the radiator that's causing the "restriction". If you're considering swapping the radiator for a fan coil you're probably also considering removing the TRV and installing a full flow valve. Why not try removing the TRV and installing a full flow valve to see if it makes any difference. It might save you £500.
Bob
- 27 Forums
- 2,541 Topics
- 59.2 K Posts
- 315 Online
- 6,822 Members
Join Us!
Worth Watching
Latest Posts
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Thanks for such a comprehensive response!!! ...
By errmm , 1 hour ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Indeed we don’t! Much though I wish to be loy...
By Toodles , 4 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Thanks, that’s a fair point and I agree th...
By Eliuccio , 5 hours ago
-
As a full price electricity user (nae smart meter signa...
By Abernyte , 10 hours ago
-
Aerotherm 12+12kw cascade huge power utilisation
Looking for a little bit of advice. new inst...
By Hamish_mckay , 10 hours ago
-
Daikin high temperature heat pump
Hello, I have a DAIKIN ERSQ 016AAV1 16KW. I have a BRC2...
By gajolos , 11 hours ago
-
RE: Setback savings - fact or fiction?
I changed the pump power to the actual value to see if ...
By RobS , 12 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
@majordennisbloodnok Thanks I hope it helps someone. St...
By antonical , 1 day ago
-
RE: NIBE Heat Pump Warranty: What's an Adequate Engineer Attendance Time?
Totally agree. However the manufacturers know that fe...
By JamesPa , 1 day ago
-
-
RE: The law of unintended consequences....
Oh Thank you Major, I was just beginning to wonder wher...
By Toodles , 1 day ago
-
RE: Forum updates, announcements & issues
I know that the notifications are being delivered now w...
By Mars , 1 day ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli I have sent a direct message with the financial ...
By ChandyKris , 1 day ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Does it disappear when the heat pump is off? What abou...
By JamesPa , 1 day ago
-
RE: Fitting heat pump plumbing and pipes in advance?
Great tips, thanks. The PEX/Al/PEX option sounds much m...
By Jonatan , 2 days ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Those control valves on the UFH manifold could be an is...
By Travellingwave , 2 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 2 days ago
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 2 days ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 2 days ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 2 days ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 2 days ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 2 days ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 3 days ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 3 days ago