How is water flow controlled in a heat pump system?
Comming from a +20 years old heatpump installation where the flow of the water flow is fixed I am trying to understand how the water flow is controlled in modern modulation ASHP.
I am looking at the simple installation of floor heating, no thermostats in the house, floor heating always on, no water buffer....
When the heatpump modulates because heat demand drops because of higher outside temperature.
- do HP keep the water flow constant (and this changing the delta temperature over the inflow-return)
- do HP change the flow so delta temperature over the inflow-return stays constant..
Or what do heatpump (of the circulation pump) control and how?
And is there a best solution for efficiency?
Walter
The short answer as always is it depends, different models do it differently. Mitsubishi is constant flow rate so as the heat pump modulates down you will see changes in delta T. Other manufacturers modulate the circulation pump flow rate and try to target dT5.
Is there an inherently better way to do it for efficiency, I don't believe so as just different sides of the mass flow equation in my opinion unless you want get into the watts a circulation pump uses.
Thanks for the feedback!
How does Mitsubishi control the flow rate? Is that the pump that does measure the rate or the Heatpump that measures and controls the pump power? And how is the pump power controlled?
(Sorry for the questions; I have a hard time finding that info on the installation guides).
I indeed think my question goes back to how different manufacturers implement their controls and I guess it goes together how they manage the modulation of the heatpump.
Thinking about it: Lowest water side temperature is best... So that would mean high water flow, meaning there would be no need to modulate the circulation pump down...
Maybe only when there is no heat demand from the house.
Opening the question how manufacturers would organize the modulation of the heatpump...
Posted by: @wvtienen1How does Mitsubishi control the flow rate? Is that the pump that does measure the rate or the Heatpump that measures and controls the pump power? And how is the pump power controlled?
There is a flow meter that measures the flow rate and can be accessed on the heatpump controller, the pump speed/power can be set from the heat pump controller to an arbitrary value (1-5), you can then check the flow rate that each of these values achieves.
@gary and how does Mitsubishi control the pump? Is there stearing signal going to the pump (pwm?) or ...?
Sorry fore the detailed question. In think I need to read about circulation pump controls...
@wvtienen1 Yes its controlled by a signal to the pump, if I change the value on the heatpump controller I can hear the pump speed up or slow down and I can see an increased or decreased flow rate on the controller.
- 22 Forums
- 2,084 Topics
- 46 K Posts
- 18 Online
- 3,378 Members
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
Mitsubishi Ecodan Fails to Heat Water despite temperature drop
My daughter has recently moved into a new flat where wa...
By m1kegibson , 22 minutes ago
-
@editor Mars if you have any recommendations for down s...
By abam48 , 12 hours ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness HI, The rules is a best practise, the ...
By ASHP-BOBBA , 15 hours ago
-
RE: Vaillant AroTherm Plus 7kW
@scalextrix if your under unit heater is like our Myson...
By Judith , 17 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@cathoderay how did you get a script to run for that- d...
By benson , 18 hours ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@ashp-bobba thank you, and equally so, thank you for ta...
By Mars , 2 days ago
-
@judith good to know… I’ll continue to feed Wattson, an...
By Mars , 3 days ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
@editor great article re accreditation. I note ISO/IEC ...
By Bart , 3 days ago
-
RE: Renewables & Heat Pumps in the News
Here’s a little more technical detail/p>
By Judith , 4 days ago
-
RE: Who's your electricity provider and what's your tariff?
I don't (yet), but my PW3 is due to be installed shortl...
By Old_Scientist , 4 days ago
-
RE: MCS and NAPIT complaints process
@chrislay, is your heat pump complaint still unresolved...
By Mars , 4 days ago
-
RE: ASHP Install from hell - help please
@saf1973 I’ve been going through old cases on the forum...
By Mars , 4 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron There's the rub, the database does not list my ...
By AF1 , 5 days ago
-
RE: Commencing on an ASHP Installation Process
Yes, it's "doable" if everything goes to plan, they arr...
By Old_Scientist , 6 days ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 7 days ago
-
RE: DHW SET UP with Samsung gen 5
Thats good news indeed, you are very likely almost ther...
By JamesPa , 7 days ago