Hitachi Yutaki M efficient operation
Hi everyone. I recently found this forum and i wanted to share my case and ask for input of you knowledgeable people. As the title suggests i have a Hitachi Yutaki m RASM-6NE that is used to heat a two floor 230 sqm house with two separate zones of underfloor heating. I use weather compensation with flow temps ranging from 33 to 41 degrees. Thermostats are set to 20 degrees for both zones. Two water pumps are used for the water flow, one that is integrated in the heat pump unit and a larger one with an output of 40l/m. I have a buffer tank of 200l. The ground floor is more warm in general so the ground demand is often off. I have noticed that the delta t between inflow and outflow is at most times between 1 and zero degrees. I have also noticed the heat pump turning off a few minutes when the set water temp is reached and then back on (i am not able to see the frequency of the cycling) until the room temp is reached. In general the heat pump works for an average of 8 hours day before reaching room temp and going off completely. Since the delta-t is so low i suspect that the number of on/off cycles is high. A reason i believe is causing a low delta-t is the waterflow that is too high. I tried to set the water pump speed to be controlled by the delta-t parameter without much of a difference since i think only the integrated water pump is affected as the external water pump speed is believe is fixed. Is there a way to see the number of on/off cycles?
Posted by: @iraknicIs there a way to see the number of on/off cycles?
I am not familiar with the Hitachi monitoring so someone else will need to answer this. If you can monitor power consumption it will be visible in this though.
More generally, what problem are you trying to solve. Is consumption high/COP low, or something else? It does sound like your heat pump may be trying to deliver a lot more energy than your floor is absorbing.
Can you provide a bit more info eg Capacity of heat pump, house loss
33-14 is quite high for UFH, how were these figures determined.
I am presuming from your description that are heating part time, is this by design (if so why) or because thats what it takes
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hey JamesPa thanks for the reply. The reason for my post is my observation of the low dt and my concerns on the stress that the system undergoes. I have no dedicated consumption meter for the heat pump to know exact consumption or COP. The set flow temp is based on my day to day experience. With the current setting, it takes about 6-8 hours for the air temp to go up by 1 degree and the heat pump shutting down by itself. Anyway the thermostat is turned down by one degree at night to prevent heat pump turning on due to my preference for complete silence (is this a bad practice?). I have wood parquet installed so there is a noticeable heat loss/delay in heat delivery there. Capacity of the heat pump is 17,8 kw. Although i haven' exactly measured house loss i would say that any loss is low as there is a loss of 0,5 degrees at room temp in 12 hours.
i have limited knowledge on the matter hence the questions. Any input from people knowing more, is appreciated
@iraknic Ok
I was hoping 6 was 6kW not 6 tons (an American measure of capacity roughly equal to 3kW). I suspect it's well oversized. What do you know about how it was sized or the house construction/age.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
House is a construction of 2020 with xps insulation and double glazed windows. No clue on sizing. It was decided by the engineers during construction stage
Posted by: @iraknicHouse is a construction of 2020 with xps insulation and double glazed windows. No clue on sizing. It was decided by the engineers during construction stage
That's disappointing. It's way oversized almost without any doubt. 6kW is probably nearer the mark, possibly less.
I will re-read your description and see what I can suggest given the assumption that it's way oversized. Cycling is inevitable even at low outdoor temperatures. You may want to experiment with forcing longish cycling (as a way of preventing short cycling) by having it on for an hour or two then off for an hour or two. If you are really lucky you might be able to operate only during the octopus cosy cheap periods, which would make it very low cost to run. (As I think about this more, designing the schedule around electricity tarrifs feels ever more sensible given the likely scale of oversizing)
I've started a new thread on oversized heat pumps as it's unfortunately common. You may want to follow that also.
I will respond to your specific again later when I have given it some thought.
Are you able to measure the delta t on both primary and secondary (ie the circuit to/from the heat pump and the circuit to/from the emitters)?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@iraknic have you established that you can hear your system? Ours is very much quieter than the old gas fired boiler, no radiator creaking for example. So it wouldn’t be a problem to be on all night.
If your temperature only drops by 0.5C in 12 hours then you could easily choose to heat in just smaller set periods.(as James suggested).
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
@judith i can't hear the heatpump but i can hear the external waterpump. Maybe i can try increasing the flow temp, reducing the flow rate manually through the manifolds and have the heatpump working for smaller periods. Is it generally preferable to have the heatpump turning on once or twice daily to get water temp to 38c from 10c or having it run continuously depending on thermostat temps?
@jamespa only able to measure delta t on primary circuit. If anyone with knowledge on hitachi heatpumps can suggest a way to see number of cycles, it would be great. I can remember reading somewhere that the particular model is rated for 200sqm spaces
Posted by: @iraknic. I can remember reading somewhere that the particular model is rated for 200sqm spaces
That will be the water pump capacity not the heat pump capacity, which is dependent on the house loss.
The water pump may be on longer than the heat pump. However from what you know, roughly how frequently is it cycling and for how long on and off at what outside temperature. Have you got any monitoring equipment at all for temperature or electrical power. Could you put a mobile phone on record next to the pump and record the on off noises for an hour or two
Do you have an internet/WiFi interface on the pump, without this the monitoring options will be pretty limited.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa i was able to watch a 20 minute operation. In a 12c outside temp, the heat pump cycled off 2 times for 3 minutes at a time. When it cycled on it did not exceed 30% capacity. There is a setting for a minimum off and on time to reduce cycling. If i force it to stay on for longer how it will be able to stay within water temp limits? On the other hand if i force it to stay off for longer wouldn't it operate harder to get back to temp each time it cycles on?
Posted by: @iraknic@judith i can't hear the heatpump but i can hear the external waterpump. Maybe i can try increasing the flow temp, reducing the flow rate manually through the manifolds and have the heatpump working for smaller periods. Is it generally preferable to have the heatpump turning on once or twice daily to get water temp to 38c from 10c or having it run continuously depending on thermostat temps?
it’s much more efficient to run a heat pump continuously but for everyone in the end it’s about money. So if you were able to run only on the cosy cheap 8hrs or economy 7 then despite the efficiency being lower your costs would be too.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
- 22 Forums
- 2,031 Topics
- 44.2 K Posts
- 52 Online
- 3,236 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: help sizing rads based on room by room heat loss
The output of a rad is proportional to DT to the power ...
By JamesPa , 37 minutes ago
-
RE: Agile: average import cost vs other tariffs?
@toodles Thank you for sharing that. I note you have a...
By Old_Scientist , 55 minutes ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15 just wondering did you eventually find the o...
By SUNandAIR , 1 hour ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 4 hours ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 4 hours ago
-
The Rise and Fall of Europe’s Most Generous Green Subsidy
This story came to my attention thanks to Graham Hendra...
By Mars , 4 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 4 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
From the Full SAP Report: Space heating requirements:...
By trebor12345 , 4 hours ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 8 hours ago
-
I'm just trying to imagine this construction approach @...
By Transparent , 10 hours ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 11 hours ago
-
RE: How hard and expensive would it be to change panel and add battery?
@transparent It is a setting that Octopus make via the ...
By Toodles , 11 hours ago
-
RE: Performance of Heat Pumps in Mild Weather
@heatgeek The flow rate isnt controlled by Mitsub...
By RobS , 14 hours ago
-
RE: Say hello and introduce yourself
I might put a couple of speakers in the ceiling if fund...
By Fingers , 24 hours ago
-
RE: Bathroom Radiator replacement
@rob-nezard can you please offer your professional advi...
By Mars , 1 day ago
-
-
RE: Questions on my Hitachi Yutaki SCombi Heat Pump
OK, thats good and low. With low flow temperatures lik...
By JamesPa , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa “They are all equal but, some are more equal t...
By Toodles , 2 days ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
@cliffhanger Mine has a 'space heating off' setting! O...
By JamesPa , 2 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
Is this something you are thinking of doing? Or has thi...
By Cliff-Arnold , 3 days ago