From the pictures on your first post it appears that the DHW outlet and secondary return inlet are piped straight up into your ceiling space, no doubt that pipework then runs horizontally and then upwards to your taps / bath / showers upstairs.
I am not a plumber, nor a heating engineer, but I have recently had a similar piped system installed and I can see that I can have a 300l cylinder cool itself due to syphoning in a day, without any hot water drawn off for household use.
If you have your system programmed to maintain a certain temperature in the cylinder, or one or two times programs a day, you will be unnecessarily cooling the cylinder continuously with the secondary return which then needs to be reheated.
If you want to test this, ensure the DHW return pump is turned off and then close one of pump valves. Yes, you will have to wait longer for hot water at the outlets during the test, but I think you will find that your cylinder doesn't take as much energy.
@aceshigh @colin I isolated the secondary return at the weekend and today the DHW has not had to recharge following yesterday's anti legionnela cycle. The temperature has remained above 50 degrees even though we've both had showers. It does take marginally longer to get hot water, but I prefer this if we're saving energy. So this is a positive sign. I wonder if this issue has impacted the ASHP performance for the heating. We had our DHW on constant and can imagine it would need to keep cutting in to recharge the DHW. When it did this perhaps the flow temp for heating dropped, incurring greater consumption to get back to desired temperature. Something to monitor but positive signs. I just wanted to say many thanks to you both for taking the time to help me. It is greatly appreciated. Thank you.
@aceshigh Do you know if it is possible to plumb in a secondary return so it does not syphon? It might be nice to circulate on demand at particular times of day (which is what the pump with attached timer is supposed to do, but it didn't ever need the pump. A motorised control zone perhaps?
@colin it sounds like we have similar setups and houses (minus 2 children). What is your current daily electricity kwh usage for the house? I'm looking for a comparison because ours is still 6 kwh without any ASHP usage. I don't think we have several tvs on standby, two fridge freezers and a lot of Philips hue devices on standby. Not sure if 6 kwh is good or bad...
@webcmg Glad you're making progress and happy to help. The screenshots shows my usage including approx 2kwh per day for hot water. That includes everything, oven, hob, Fridge freezer, computers, TVs, Starlink internet, Unifi PoE network, outdoor Pirs, alarm, garage door.
When the ASHP, oven, TVs etc are off, there's a baseload of approx 270 watts which is about 6.5 units per day.
Our daily electricity consumption is normally around 6kW to 8kW, and this does not include DHW heating. Because we have a solar PV system, the water gets heated by Sun power and at the moment we only need to draw 2kW to 3 kW from the grid each day.
In Winter we run the gas boiler, which provides heating and hot water, with a little help from the solar PV on sunny days. From Spring through to Autumn the vast majority of DHW is heated by the Sun.
@webcmg Below is a screenshot of my DHW heating in Feb. I'd only just installed the Vaillant Internet gateway & Home Assistant, I hadn't fully optimised things yet plus had a higher temperature set. DHW Consumption was averaging 3kwh per day. Being in an exposed area of Scotland it's also probably a little less efficient.
@derek-m Hi Derek, I thought the same when I first saw it but I just put it down to bad user interface design 🤭 . The yield figure at the bottom is the total overall for the heat pump (excluding DHW) since it was first commissioned, not for February.
-
Surface mount or bury primaries for heat pump installation?
1 day ago
-
UFH and ASHPs
1 month ago
-
Installing your own ASHP - DIY
2 months ago
-
ASHP install contract and BUS grant money
4 months ago
-
Savings - using Weather Compensation & Time of Use Tariffs
4 months ago
Currently viewing this topic 1 guest.
- 22 Forums
- 2,097 Topics
- 46.2 K Posts
- 49 Online
- 3,385 Members
Join Us!
Latest Posts
-
RE: Weather compensated secondary circuits with Biomass
@sune thanks for the LK link, looks like a possible opt...
By AndyCoo , 9 hours ago
-
RE: Heat pump solutions and/or installer recommendations for France
No idea, but Google-Fu leads me to Bon chan...
By Scalextrix , 11 hours ago
-
If you are thinking of heating on the immersion conside...
By JamesPa , 22 hours ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness, I think your best bet would be using ...
By Aventus Eco , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles all depends on asking the right questions! And...
By Tim441 , 1 day ago
-
RE: Mitsubishi cycling while on chilled water output
I absolutely wouldn't remove the buffer altogether, I'd...
By JamesPa , 2 days ago
-
RE: Commencing on an ASHP Installation Process
I received confirmation this morning that my Greener Ho...
By Sheriff Fatman , 2 days ago
-
@jamespa Thanks for the advice - very helpful. I had al...
By abam48 , 3 days ago
-
RE: Adding battery storage to SolarEdge PV system
@chandykris No need to apologise at all! I forgot to ad...
By Toodles , 4 days ago
-
RE: Say hello and introduce yourself
Yes please do Suggesting a loss in the region...
By JamesPa , 4 days ago
-
As I have reported elsewhere we turned on the cooling o...
By downfield , 5 days ago
-
-
@el3b Hi, sorry to hear that, it is advisable to instal...
By ASHP-BOBBA , 5 days ago