From the pictures on your first post it appears that the DHW outlet and secondary return inlet are piped straight up into your ceiling space, no doubt that pipework then runs horizontally and then upwards to your taps / bath / showers upstairs.
I am not a plumber, nor a heating engineer, but I have recently had a similar piped system installed and I can see that I can have a 300l cylinder cool itself due to syphoning in a day, without any hot water drawn off for household use.
If you have your system programmed to maintain a certain temperature in the cylinder, or one or two times programs a day, you will be unnecessarily cooling the cylinder continuously with the secondary return which then needs to be reheated.
If you want to test this, ensure the DHW return pump is turned off and then close one of pump valves. Yes, you will have to wait longer for hot water at the outlets during the test, but I think you will find that your cylinder doesn't take as much energy.
@aceshigh @colin I isolated the secondary return at the weekend and today the DHW has not had to recharge following yesterday's anti legionnela cycle. The temperature has remained above 50 degrees even though we've both had showers. It does take marginally longer to get hot water, but I prefer this if we're saving energy. So this is a positive sign. I wonder if this issue has impacted the ASHP performance for the heating. We had our DHW on constant and can imagine it would need to keep cutting in to recharge the DHW. When it did this perhaps the flow temp for heating dropped, incurring greater consumption to get back to desired temperature. Something to monitor but positive signs. I just wanted to say many thanks to you both for taking the time to help me. It is greatly appreciated. Thank you.
@aceshigh Do you know if it is possible to plumb in a secondary return so it does not syphon? It might be nice to circulate on demand at particular times of day (which is what the pump with attached timer is supposed to do, but it didn't ever need the pump. A motorised control zone perhaps?
@colin it sounds like we have similar setups and houses (minus 2 children). What is your current daily electricity kwh usage for the house? I'm looking for a comparison because ours is still 6 kwh without any ASHP usage. I don't think we have several tvs on standby, two fridge freezers and a lot of Philips hue devices on standby. Not sure if 6 kwh is good or bad...
@webcmg Glad you're making progress and happy to help. The screenshots shows my usage including approx 2kwh per day for hot water. That includes everything, oven, hob, Fridge freezer, computers, TVs, Starlink internet, Unifi PoE network, outdoor Pirs, alarm, garage door.
When the ASHP, oven, TVs etc are off, there's a baseload of approx 270 watts which is about 6.5 units per day.
Our daily electricity consumption is normally around 6kW to 8kW, and this does not include DHW heating. Because we have a solar PV system, the water gets heated by Sun power and at the moment we only need to draw 2kW to 3 kW from the grid each day.
In Winter we run the gas boiler, which provides heating and hot water, with a little help from the solar PV on sunny days. From Spring through to Autumn the vast majority of DHW is heated by the Sun.
@webcmg Below is a screenshot of my DHW heating in Feb. I'd only just installed the Vaillant Internet gateway & Home Assistant, I hadn't fully optimised things yet plus had a higher temperature set. DHW Consumption was averaging 3kwh per day. Being in an exposed area of Scotland it's also probably a little less efficient.
@derek-m Hi Derek, I thought the same when I first saw it but I just put it down to bad user interface design 🤭 . The yield figure at the bottom is the total overall for the heat pump (excluding DHW) since it was first commissioned, not for February.
-
Rodents! A word of warning for heat pump owners
2 weeks ago
-
Surface mount or bury primaries for heat pump installation?
2 months ago
-
UFH and ASHPs
4 months ago
-
Installing your own ASHP - DIY
5 months ago
-
ASHP install contract and BUS grant money
6 months ago
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 34 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Help me keep the faith with my air source heat pump installation
Does your heat pump have a Silent/Quiet mode? Some he...
By Tim441 , 42 minutes ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Quite, yes it's a disaster waiting to happen and just e...
By Scalextrix , 52 minutes ago
-
I agree with @jamespa. If you are not using the tank ...
By Old_Scientist , 4 hours ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 18 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 21 hours ago
-
I didn't want to say that, bus since you have said it n...
By JamesPa , 21 hours ago
-
RE: Midea ASHP – how to set weather compensation
Mostly, I think, but with some caveats. I set the TI...
By cathodeRay , 24 hours ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 2 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 2 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 2 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
@allyfish Dogs have owners - Cats keep staff. You are o...
By Toodles , 2 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 2 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 2 days ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 3 days ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 3 days ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 4 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 4 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 4 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 4 days ago