Posted by: @ajbevster@jamespa once again thank you for the advice last week. I'm keen to move away from the evo thermostat and receiver. Can I just disconnect the receiver from the heat pump (isolating everything) and i assume it will then work purely on wc? I'm tempted to buy the halo air for future tweaking but struggling to see it's major value other than looking pretty and slightly easier to adjust temp inside property.
Is your unit the R290 or the R32 model
I dont know the specific wiring of the Ideal heat pumps but I think what you say is very probably the case. The R32 manual suggests that either the Halo or a call for heat (normally from a thermostat) is needed. I havent yet looked at the R290 manual. Thus in either case need to do one of
1. Change an installer setting to tell it that there is no external thermostat
2. Wire together the contacts to which the thermostat is currently connected on the heat pump/wiring centre so that there is a continual call for heat
Otherwise the heat pump will be expecting a call for heat but wont get it.
The latter is more or less bound to work unless they have done something really weird (unlikely) and can be simulated first of all (to check) by setting the thermostat as high as it will go.
Halo looks quite nice but as you say no obvious major value add unless it produces statistics or enables operation from the internet (if that is useful to you).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I went for the ideal halo air controller as I can sell on the evohome to cover costs. Wiring is very straight forward pretty much straight swap apart from a couple of wires moving in control box.
Last question, do I need to have the control box on my landing or shall I leave it in the loft as I will be able to control the majority of the heat pumps settings from the halo air....
In two minds.
Last, last question, what is the most efficient way to run the hot water heating system...continually top up or heat twice a day?
Posted by: @ajbevsterLast question, do I need to have the control box on my landing or shall I leave it in the loft as I will be able to control the majority of the heat pumps settings from the halo air....
If the halo has an inbuilt temp sensor (which I imagine it does, but check) then you can leave the control unit in the loft.
Posted by: @ajbevsterLast, last question, what is the most efficient way to run the hot water heating system...continually top up or heat twice a day?
The latter, or even once per day if you have enough capacity in your DHW tank. There is probably not a lot of difference however!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@grahamh I took the plunge and git the ideal halo air controller. My current settings are w/c 0.8 with 50% room influence. Only challenge I'm finding is how much to have the controller impact the wc. It's a 10kw logic monobloc and cycling between 1-2 an hour. Flow rate runs about 28l/m. Target temp is 22c (wife likes it warm) with setback at 20c overnight. Hot water set at 46c. Does anyone understand how the halo impacts the wc as I know it's intuitive...I just don't understand how it works together. Maybe I should set room influence lower whilst the system settles and I find the right wc.
The flow and return always seem a little too similar...currently 36 to 33 return.
Basically, what in asking is, for the most efficiently run ashp what settings should u be looking for with a 10kw pump? What should target flow rate be, flow temp and return temp. How many cycles should I be aiming for over 24 hours. Is there anything else I'm missing?
- @jamespa any advice on best setting for hot water...like schedule 2 hours long? Everything the halo air says is to leave the hot water demand on constant for most efficient running but it doesn't feel right...we will never use the 300ltr hot water plus 72ltr buffer. Plus I thought that's what the buffer was for so you didn't have to constantly keep the tank hot water high...I feel like I'm nearly there but not quite getting the best out the system. Should I just go for pure weather comp with scheduled hot water and see how it goes? Kwh averaging 50 a day but has been as low as 30. What's funny is the heat pump says its only using 21kwh a day but I know our normal use is around 10, so any idea where the remaining 20kwh might be being used?
Personally I would start with pure WC and hot water scheduled once or twice per day 1-2 hrs depending on your consumption. If you schedule once per day you might need to adjust the dhw hysterisis down from the default to make sure it always reheats.
Once that's working well you can tweak, or not as you choose. I'm running on pure WC and dhw once per day for 1.5 hrs (hysterisis 3C) but we don't use my dhw.
As to consumption, where do the various figures you quote come from? I assume your meter and your heat pump. To answer the question suggest you plot over a couple of weeks to give more insight, then it might be possible to tell. Spot readings are almost impossible to interpret due to various sources of noise.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
What's funny is the heat pump says its only using 21kwh a day but I know our normal use is around 10, so any idea where the remaining 20kwh might be being used?
I have a Logic Air 4kW heat pump and the CoP numbers reported are a work of fiction. It has been installed since November and the Halo Air is reporting a SCOP of 9.87. The main controller unit reports a different figure (though still wrong AFAICT). I complained to an Ideal engineer when he visited and he fobbed me off saying that all manufacturers' reporting is like that. I have installed my own custom monitoring now to get sensible data out of it.
The flow and return always seem a little too similar...currently 36 to 33 return.
What should target flow rate be, flow temp and return temp.
The manual says that the design flow rate for the 10kW model is 28.7 l/m so it sounds like your flow rate is correct. The heat pump uses a fixed flow rate which means the heat pump will control the difference between flow and return temp by modulating the compressor. If the difference gets too small, it will turn off the compressor for a bit. I wouldn't worry about these numbers too much, just tweak the w/c curve until it is achieving your desired temperature.
How many cycles should I be aiming for over 24 hours.
There are two kinds of cycles:
1) The room temperature exceeds some threshold and stops the heating demand. With the Halo Air controller, I think the limit is the set point + 1 degree. This limit only exists if you have room influence enabled. If you set the w/c curve correctly this kind of cycling should never or rarely happen.
2) There is still a heating demand from the controller but the compressor turns off because the flow temp is too close to the return temp because it can't modulate low enough. This kind of cycling depends on how well sized the heat pump is to your house and I don't think there is too much you can do about it. The Ideal engineer told me that up to 3 cycles per hour is acceptable in his opinion.
Is there anything else I'm missing?
If you have an idea of how much heat in kWh your house needs, you could try to estimate whether your heat pump electricity usage is in the right ballpark.
@jamespa so I've tweaked to heat once a day during the midday as we have solar and only tend to use hot water later on in the day. My only issue I'm finding is the system doesn't seem to recognise the correct hot water temperature. Whenever I look at the hot water temp it is normally completely off. See attached. It's meant to be set for 46c but ranges from reading 24 to 60.....could the dhw thermistor be connected in the wrong place?
I know it's not 35 c as it's really hot out the tap
Posted by: @ajbevster..could the dhw thermistor be connected in the wrong place?
Yes, or not properly pushed into the pocket on the side of the cylinder.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
If it's fully pushed in yes, better if it also had some tape over the hole to ensure that circulating air didn't cool down the sensor.
You could take it out and test it! There maybe a loose connection somewhere.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
-
British Gas Heat Pump Installation Complaint
2 months ago
-
Heating Turned Off but Radiators Still Warm
2 months ago
-
Samsung Heat pump with Yonos Pico circulating pump running all the time
2 months ago
-
Samsung 5kW R32 Monobloc Gen 6 ASHP
3 months ago
-
Avoid the Heat Pump Villain: Why Low-Loss Headers and Buffers Can Sabotage Your Heat Pump's Efficiency
4 months ago
Currently viewing this topic 2 guests.
- 26 Forums
- 2,356 Topics
- 53.4 K Posts
- 310 Online
- 6,017 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@andrewj Seeing they deleted both threads with the pict...
By HarrisonC , 7 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@mars I think your commentary is very fair and balanc...
By JamesPa , 8 hours ago
-
RE: External pipework insulation
That's great advice @transparent... thank you. @david...
By Mars , 8 hours ago
-
RE: Advice on internal circulation pump noise
Thanks @mikefl - I'll maybe have a look at the lock-shi...
By jtg , 9 hours ago
-
RE: Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
@toodles interesting suggestion, thanks. I will try to...
By GrahamF , 10 hours ago
-
RE: Mitsubishi Ecodan Auto Adaption trial to stop cycling.
The interval you talk of, i think, will be 60min for an...
By F1p , 13 hours ago
-
RE: Electricity price predictions
Does anyone have a current graphic, visual or breakdown...
By Mars , 17 hours ago
-
Agree with @majordennisbloodnok on the setbacks. We hav...
By ChandyKris , 1 day ago
-
RE: New Fogstar 15.5kWh upright solution
It is a matter of luck. 2ith Fogstar "instructions", to...
By Batpred , 1 day ago
-
RE: Speedcomfort radiator fans
@deltona the way the links were added broke the page. A...
By Mars , 1 day ago
-
RE: Setback savings - fact or fiction?
I agree! Even more so if we get an answer! But the chal...
By cathodeRay , 1 day ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
This has been delayed from what I believe to be this ye...
By dgclimatecontrol , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
this is why I provided current flow temperatures in the...
By ksim , 2 days ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
There's many homes that would be quite a disruption for...
By dgclimatecontrol , 2 days ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@rhh2348 ...maybe this option is what you want? Alter...
By benson , 2 days ago
-
RE: Free Ecoheat Heat Pump Install
@old_scientist This does make the unit smaller as the b...
By dgclimatecontrol , 2 days ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
@old_scientist hiya mate, did you ever get to the botto...
By 9jwr9 , 2 days ago
-
RE: Configuring third party dongle for Ecodan local control
@majordennisbloodnok I think the HPDHD diagnosis may be...
By Sheriff Fatman , 2 days ago