Ah, that does make some sense....which is why I'm also getting installers back to put the outside temp monitor Outside! Currently in loft so doesn't accurately show outside temp.
This sounds like the job was not quite as promised. Will pester installers tomorrow to get resolutions!
Posted by: @ajbevsterAh, that does make some sense....which is why I'm also getting installers back to put the outside temp monitor Outside! Currently in loft so doesn't accurately show outside temp.
You are kidding me surely.
No?
In which case it's the first time I have heard this particular abomination, I will bear that in mind when asking others about their systems!
Pure weather compensation, without any influence at all from room temperature measurement, works very well for many, including me. I turned off completely the built in 'room compensation' function on my controller, which is an overlay to the WC, and the internal temperature is more stable as a result. Some houses, eg ones which are poorly insulated or have high solar gain, may need additional tweaks but in all cases the starting point is weather compensation.
In some European countries it's been mandatory for two decades on boilers and heat pumps, sadly we didn't follow suit and as a result many of our houses are less comfortable and we have paid about 10% more for our heating. Sheer madness but that's how it is. Now we are paying the price with the need to relearn everything we thought we knew about heating systems!
It doesn't help that the User interface for WC is rubbish on most controllers. I will have to look up the ideal one. Vaillant have come closer than most to cracking a sensible interface to WC, presumably because they also sell boilers in countries where WC is mandatory.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Sadly not kidding...
Would you suggest I disconnect my thermostat and just let the ashp run by itself? It looks like wc is enabled...
Managed to find the wc screen and it's set to 1.5 with summer/winter heating limit 21c and room influence 50%....
Same as the manual...does this mean if I just ignore the thermostat it should be more efficient being on constantly?
Anyone want to give advice as to what to set the wc to? 1.5 seems high.....I'm thinking try out .75?
@ajbevster, one thing I’ve learned with weather compensation is to start low and adjust gradually. I’d recommend starting at 0.50 and letting it run for at least 24 hours, keeping track of the outdoor temperature during that time. It’s best to do this over 3–4 days of consistent weather if possible. If it’s too cold inside, increase it to 0.75. Every house is different, so it’s hard to predict exactly, but that’s a good starting point in my opinion.
Are you sure it’s the outdoor sensor that’s in the loft?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor sadly yes, I'm 100% sure. So it's throwing the system out by about 10 degrees.
I will be getting it moved ASAP! Can't believe they fit the control box in the loft also! Not best pleased.
I think with the logic ideal it says 1.5 for 50 @ 0. So I'm thinking looking at the wc curve for this probably 1 might be best but will start low and work way up. Thanks so much for the support.
Should I also set room influence to 0?
@Ajbevster If the OAT is reading 10C high then it might be possible to offset this by setting the target house temperature as 10C high until the OAT sensor is moved (and make sure it gets put on the shady side of the building). The heat put into the building by using weather compensation is based on the difference between inside and outside temperatures.
Posted by: @ajbevster! Can't believe they fit the control box in the loft also! Not best pleased.
I would insist they move that too
Posted by: @ajbevsterWould you suggest I disconnect my thermostat and just let the ashp run by itself? It looks like wc is enabled...
Ideally yes at least initially. However the ashp may be configured to require a contact closure in the thermostat as a call for heat. If so you would also either need to reconfigure the ashp to ignore or wire the contacts together to simulate continuously closed. That's why I suggest turning the station to max as it has the same effect without having to change any settings or wiring.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa thanks James. Good plan! Managed to adjust the curve to about 1 to compensate for the indoor outdoor sensor...kept the thermostat on max and seems to have solved the cycling inefficiency.
Regarding noise, plumber has said sounds like air in system and they will come back to fix.
Sensor and control box should be moved this week. Fingers crossed. When the electrician comes back I'll get him to disconnect the thermostat and make sure the ashp is set up to work without only using wc.
Thanks so much for the help. It's already making a big difference and starting not to panic as much. Hopefully can avoid bankruptcy this month...
@ajbevster I received the following message from Ideal pertaining to your sensor: "You can simulate an outdoor temperature in the installer menu as a temporary measure until the installer returns. Removing the outdoor sensor now will only generate a fault code as the PCB has already recognised one has been fitted."
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor I did find that in the manual and feel confident enough to give this a go. Can't be worse than it currently. The heat pump must be so confused recording intake temperatures of 0 degrees and the outdoor temp saying its 9 degrees. Thanks again for the support. Feeling much more at peace now.
@ajbevster this makes me want to scream, that ideal heat pump is the simplest heat pump on the market to install. Its a lovely unit. I have one at home, its amazing. Ideal tech will assist you, they offer the best support of all the manufacturers.
give them a ring and they will guide you by video call how to fix it temporarily. then get the installer back in.
It doesn't matter how simple the installation or the unit is there is always an installer who can balls it up.
good luck.
Heat pump builder
-
Avoid the Heat Pump Villain: Why Low-Loss Headers and Buffers Can Sabotage Your Heat Pump's Efficiency
1 week ago
-
Massive Electricity Cost for Running My Air Source Heat Pump
5 months ago
-
hum/whine from Wilo circulation pump
7 months ago
-
Samsung 5kW R32 Monobloc Gen 6 ASHP
7 months ago
-
L9 error with Mitsubishi ecodan heat pump
9 months ago
Currently viewing this topic 2 guests.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 45 Online
- 5,736 Members
Podcast Picks
Latest Posts
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I couldn't agree more with this. Whilst I still have a...
By JamesPa , 2 minutes ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
I am about to get my Mitsubishi 14kW Zubadan serviced b...
By downfield , 8 minutes ago
-
RE: Who’s Caved and Switched the Heating On Already?
Central heating still switched off and will be until Oc...
By AllyFish , 43 minutes ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
I think the problem you are having comes down almost en...
By JamesPa , 1 hour ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 1 hour ago
-
RE: Midea ASHP – how to set weather compensation
I think it is a bug in the code, it comes on even when ...
By cathodeRay , 16 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 17 hours ago
-
RE: Buffers, hot water and cooling
@jamespa Your reasonably close! Especially with warmer ...
By dgclimatecontrol , 19 hours ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 1 day ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 2 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 2 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 2 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
@scalextrix Name plate capacity
By HCas , 2 days ago
-
RE: Solar Thermal DHW and ASHP
I was originally contemplating a solar thermal installa...
By jamespetts , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
My system installed in July 2024 has produced 6.4mWh in...
By jamespetts , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@judith thanks for your suggestions. Starting from col...
By GrahamF , 3 days ago
-
RE: Inventor (Midea) Heat Pump short cycling advice
I switched to "fan coil mode" to be able to set water t...
By immunity , 3 days ago
-
RE: DESNZ doing a survey which asks the right questions!
Without a survey their only source of data is probably ...
By JamesPa , 3 days ago