@william1066 I do not usually use the ESBE valves. This is the one I usually use and they are available for next day delivery.

https://www.jtmplumbing.co.uk/central-heating-controls-valves-c436/belimo-valves-actuators-c1014/belimo-valves-c408/belimo-3-port-zone-valve-with-240v-actuator-powered-open-powered-close-p26349

 

The valves you have, in reality, from tests I have run, bear no resemblance to the actual KV value.

A flow rate of 30 L/min seams a bit high, and will as you see, be costly to run, It is better to run the system on Delta T, if the heat pump cannot do it, Grundfoss Magna3 will do it for you.

 

Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.


   
👍
1
ReplyQuote
cathodeRay
(@cathoderay)
Famed Member Moderator
Joined: 3 years ago
Posts: 2092
 

I get the fact that Honeywell valves act as partial blockages and so throttle the system, but aren't they the standard fit item? Isn't this another example of most of the heat pump industry not really knowing what it is doing? I wonder how many installation don't have Honeywell (or Honeywell clone) valves? 

Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
(@heacol)
Noble Member Contributor
Joined: 4 years ago
Posts: 408
 

@cathoderay "Isn't this another example of most of the heat pump industry not really knowing what it is doing? I wonder how many installation don't have Honeywell (or Honeywell clone) valves? "

 

Correct, very few installations do not have them. Heat pumps need high flow, and restricting the flow costs money.

Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.


   
ReplyQuote



(@william1066)
Reputable Member Member
Joined: 3 years ago
Posts: 206
 

@heacol Thanks for the link.  I already have a Grundfos Magna 3 [25-100].  I think I have a dodgy manual flow meter as well (seems to go down to 22mm in the middle despite being 1inch BSP on each end) then of course I have the zone valves.

In terms of delta T.  At -2 deg, the heat loss is a phenomenal 15kW.  Now we just put on another layer right now, and live with 15deg temp inside, but if I wanted to deliver for that heat loss, I need 30 litres per minute at delta T of 7.

Let me see what ripping out the zone valves and the mechanical flow rate meter does. (replacing with what you suggested)


   
ReplyQuote
(@alec-morrow)
Honorable Member Contributor
Joined: 4 years ago
Posts: 216
 

A heat pump needs to be installed a certain way, as do condensing boilers to optimise them.

Prosaic understanding of heating (turning on and off, end user management etc) generally holds back the U.K. in its transition to heat pumps.

At the root of the issue are U.K. regulations, which are not sympathetic to, or understanding of, these design principles  or the technology. Seeing this from afar exporters to the U.K.  throw up their arms in despair and pursue volume sales. That means not upsetting the apple cart of buyers who are so far deep in the forest , they can not see the wood from the trees. After all lecturing to your buyers won’t favours sales. For this reason manufactures “dumb down” their schematics to accommodate U.K. understanding, Some manufacturers remove from market their more sophisticated products.  And training, technical help and information sharing is minimised to what’s necessary to sell. The installer provides a useful “get out of jail card”.

Its not helped by NVQs, CIbse, British Gas and other large players being unaware of the changes needed, both in plant and understanding.

The change needed is actually quite daunting, but that’s because we in the U.K. will always be quick to say why a change won’t work, well before asking how the change can improve things, and what need’s to be done to effect the change and make life  better.

Professional installer


   
👍
2
ReplyQuote
(@william1066)
Reputable Member Member
Joined: 3 years ago
Posts: 206
 

@heacol What I am learning is how to understand the numbers.  There is a big difference between getting 8.6 m3per hour with a 1 bar pressure drop (which is 10mh2o) and 17 m3per hour with a .7 mh20 pressure drop.  If my maths is correct, a diverting valve has about 30 times less resistance than a zone valve [likely for a specific flow rate of course, more work needed here on my part].  Pretty important to understand the maths here, as I am slowly finding out.

On my 25-100 pump I really have a 10 mh20 "budget" to play with (at most).  There is no water pump in the heat pump.

At least I have something to do this weekend 🙂


   
ReplyQuote
(@scrchngwsl)
Reputable Member Member
Joined: 3 years ago
Posts: 91
 

Regarding the Honeywell valves, I have this one installed:

IMG 20230117 105403

Should I ask for it to be replaced with a different one? If so what should I tell/ask for from my installer? They're coming tomorrow to look at a very noisy pump so I want to discuss this at the same time.

ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh


   
ReplyQuote
(@alec-morrow)
Honorable Member Contributor
Joined: 4 years ago
Posts: 216
 

noisey pump is an issue!

 

 

Professional installer


   
👍
1
ReplyQuote
(@william1066)
Reputable Member Member
Joined: 3 years ago
Posts: 206
 

@scrchngwsl That is a good question, one I am trying to work out for myself.  Ideally you need to know your target flow rate to start.  This simple number is not so easy to get as it is likely to be variable, and ideally set by the heat pump controller and depend on a number of factors.

Assuming you have a flow rate range that will be required for the majority of the time.  I guess you can then look ats the spec sheet of the zone valve vs the full bore diverting valve and do some maths on cost, some experiments on noise etc, look at your pump head spec etc. 

A non trivial exercise which I need to undertake, and which could take some time.  As a diy'er I tend to save time by doing rough calculations and over spec, not ideal, but one way to approach it.  That is what I did with my pump and actually it turned to be only just big enough.  I calculated 6.5 mh2o, it seems the pump needs close to 10mh2o pressure to get to 30 litres per min.  And this is a bit too noisy for me right now, so I am looking at options (including moving the pump outside the house)


   
👍
1
ReplyQuote



(@william1066)
Reputable Member Member
Joined: 3 years ago
Posts: 206
 

Here is one spec sheet I found.  They are not for my valves, but the below are two different sizes of the V8043.  You can see the impact at my target flow rate for the smaller one is quite significant, but even for the bigger one, at my flow rate of 30 l/s I lose 0.7mh2o. 

image
image

   
ReplyQuote
(@william1066)
Reputable Member Member
Joined: 3 years ago
Posts: 206
 

I am going to say that my maths is probably not correct here [earlier post that said 30x].  Will come back following some more thought.  A quick look suggests diverting valve about 3 times less resistance not 30, but I need to spend a bit more time comparing things that are equivalent.  Don't won't to panic anyone as a result of some low quality thought processes.


   
ReplyQuote
cathodeRay
(@cathoderay)
Famed Member Moderator
Joined: 3 years ago
Posts: 2092
 

Posted by: @william1066

Ideally you need to know your target flow rate to start.  This simple number is not so easy to get as it is likely to be variable, and ideally set by the heat pump controller and depend on a number of factors.

This page has a useful calculator at the bottom, and even caters for systems with added glycol as well as just water. In fact the whole page is rather useful:

https://heatpumps.co.uk/technical/pressure-drops-flow-rates/

Midea 14kW (for now...) ASHP heating both building and DHW


   