Grant Aerona3 13kW Noisy pipes after balancing

16 Posts
6 Users
3 Reactions
270 Views
(@allyfish)
Noble Member Contributor
4175 kWhs
Joined: 2 years ago
Posts: 477
 

Hi @grantmethestrength, looks like your pump setting is on speed 3 in your Grant ASHP, grab the installation manual, read up on circulator pump dip switch settings and drop it to speed 2, circa 3000rpm. You may have to open up some rad lockshields and recheck, but getting a pump speed appropriate to the required flow with a reasonably open circuit is preferable to the pump running flat out against closed valves. The Grant ASHPs are defaulted to speed 3 when supplied, and few installers bother to change that, because throttling the flow on the Grant supplied flow setter/indicator is the lazy, quicker and easier option.


   
ReplyQuote
(@grantmethestrength)
Eminent Member Member
149 kWhs
Joined: 1 month ago
Posts: 20
Topic starter  

Thanks guys, I will open up the valves again and check the dipper switches when I get home tomorrow. Quick follow up question, if the flow has been limited at the ahem new to me flow valve 😜 if I change the pump speed to 2 do I just open the flow valve up to get say 28l/min or just open it as wide as it can go (well until it gets noisy again lol)? Is there a sweet spot?


   
ReplyQuote
Toodles
(@toodles)
Famed Member Contributor
11253 kWhs
Veteran
Joined: 2 years ago
Posts: 1818
 

@grantmethestrength The new to you flow valve is summat I know not of at this stage but, my gut feeling is that if it is in the water circuit, is partially closed and you have noise then, it is well worth noting its’ position then openi9ng it up fully to see what happens. If at this point, everything runs happily still but the noise hasn’t disappeared, then try the heat pump’s pump by reducing the speed a little. little by little improvements will come your way! Regards, Toodles.

Toodles, he heats his home with cold draughts and cooks his food with magnets.


   
👍
1
ReplyQuote
(@allyfish)
Noble Member Contributor
4175 kWhs
Joined: 2 years ago
Posts: 477
 

Posted by: @grantmethestrength

if I change the pump speed to 2 do I just open the flow valve up to get say 28l/min or just open it as wide as it can go (well until it gets noisy again lol)? Is there a sweet spot?

Pretty much, noise is caused by high fluid velocity and turbulence created by restrictions, which is caused by things like nearly closed balance valves, TRVs, etc. Noise is also wasted energy, as is a pump on max speed against partly closed valves which could be on a lower speed setting. Open all the valves up, including the flow setter/indicator, set the primary circulator to an appropriate speed to get the required system velocity, and go from there 🙂


   
👍
1
ReplyQuote
Page 2 / 2



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security