Ok , thanks , but I thought that was the purpose of adjusting them , to get them where they need to be , especially same room size an temperature. Yes they do seem to be very sensitive at lower perameters IDE: nearly closed. Patience for me is required !
I will have a look at Heat Geek , thank you.
@alfapat Adjusting an LSV to provide a temperature setting is probably the start of a road to frustration and madness; as the name suggests, it is to balance the relative output compared with all others. Opening up one valve will to some extent, affect the available supply to all the others. (Hence the need to rough balance all the emitters first), then the ‘fun’ starts as each subsequent mini tweak should take you closer to the goal.
You will know if you are getting close as all the rooms will be equally in need of less or more heat from the source. If one stands out as not warm enough or too warm compared to the rest, then further tweaking may be required.
Once all the emitters are balanced, any change in the heat output of the boiler / heat pump will be equally reflected by all emitters (as long as one of those pesky TRV’s hasn’t poked its’ nose in of course!) The beauty of balancing the system is that the only adjustment day to day is then carried out by the system’s controller when it adjusts the heat source to hold your required comfort level. In the long term, just keep the adjustable spanner and a screwdriver to release the cover over the LSV if you decide that a particular valve requires a ‘nadgers’ adjustment to finesse your requirements. I have the great advantage of being retired and a nerd of the first oder - it all helps! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
HaHa , Im retired too and also have a need to be too fussy. I have read the Heat Geek so understand a little more , whatever my valves are , they are at least are all the same . I must say the adjustable spanner is a pain , some keys are ordered meantime .
The first radiator From the pump missing out two at least on full throttle , is or has been more consistant on temp , sorry I didnt say that , Flow is what I searching for . If I count the turns from being shut I will make them all the same , Is that a better plan ? ....Then fine fettle.
Thanks!
And as a post script: When you commence the balancing exercise, you will be running around the radiators checking which is heating up the quickest (i.e., hogging the supply) and this where you start the job of restricting the flow by closing the LSV a little. I am going to go a stage further here and suggest that to save some time, you might like to close that valve completely, then open it up 1.5 turns as the throttling adjustment is nearly always in the last half turn or so from the closed position.
My first round of adjustments were at the end of a very mild February 2023 and so approximate settings only were used until the late Autumn of ‘23 arrived then I was able to continue to tweak in earnest. It helps if you are able start with cool radiators and ascertain perhaps the two or three biggest hoggers of the heat.
Assuming the system was calculated for heat loss of each room and the specified emitters are the correct capacity, then the apparent warmth from each emitter will be similar when balanced - thus room temperatures will also be similar. The science is not perfect but as long as the emitters are not underspecified, the tweaking of the LSV’s will allow you to achieve the comfort levels you seek. We like the same temperature in all rooms and areas except the bedroom at night and we have pretty well achieved this with the help of our Homely controller. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @alfapatOk , thanks , but I thought that was the purpose of adjusting them , to get them where they need to be , especially same room size an temperature. Yes they do seem to be very sensitive at lower perameters IDE: nearly closed. Patience for me is required !
I will have a look at Heat Geek , thank you.
Perhaps I didn't make myself clear. Let's make up a scenario and see if we can do better.
Suppose you want all rooms at 20C. Your rads are successfully balanced when all rooms are at the same temperature, whatever it is (subject to the condition that at least one is fully open).
Once you have achieved this there is no point further adjusting the rads. Just adjust the ft.
Actually this is a good place to start whatever outcome you want. You can tweak your individual rads up or down from this point in the.rooms that you don't want at 20.
Unfortunately patience is required as you say.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@alfapat I would think starting froma common 1.5 turns open would be a good start - unless there is an emitter at the end of the run that might suffer as a result. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles Do you think that the Rads I have in the large rooms , Kitchen and bathrooms should also be throttled down as in Balance and all be the same parameters despite there being a need for more heat.
What do you mean by an Emitter at the end of a run, please. When you say an Emitterr is that another word for a Radiator.Posted by: @toodles@alfapat I would think starting froma common 1.5 turns open would be a good start - unless there is an emitter at the end of the run that might suffer as a result. Regards, Toodles.
By way what do you suggest I do with two Rads on Frost setting , they are in a conservartory which is not heated.
Just adjust the ft.?Posted by: @jamespaPosted by: @alfapatOk , thanks , but I thought that was the purpose of adjusting them , to get them where they need to be , especially same room size an temperature. Yes they do seem to be very sensitive at lower perameters IDE: nearly closed. Patience for me is required !
I will have a look at Heat Geek , thank you.
Perhaps I didn't make myself clear. Let's make up a scenario and see if we can do better.
Suppose you want all rooms at 20C. Your rads are successfully balanced when all rooms are at the same temperature, whatever it is (subject to the condition that at least one is fully open).
Once you have achieved this there is no point further adjusting the rads. Just adjust the ft.
Actually this is a good place to start whatever outcome you want. You can tweak your individual rads up or down from this point in the.rooms that you don't want at 20.
Unfortunately patience is required as you say.
Also do I keep one fully open as it was in Hallway please.
@alfapat Start by throttling down the first to heat up, then the next to heat up…. ALL the emitters / radiators should be regarded as components of one system - this includes any and all emitters normally required to protect an area from frost.
The frost protection is going to be provided by a TRV I imagine as it is only at low temperatures that such emitters will be required to contribute heat. For setting up (balancing the emitters / radiators) those ‘frost protection’ TRV’s should be left fully open and not closed to the snow flake symbol position until after all balancing is complete. This may have some influence on the other emitters but I imagine they are not going to be opening / closing all the time so their influence should be minimal I think. Regards and Have Fun! Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@alfapat Remember Pat, as the outside temperature varies, so does your flow temperature. If you are not getting to room temperature today when its warmer, maybe you need to raise the lower end of the water law settings.
@Jamespa Do you mean the temperature of the radiator rather than the room James? I suppose if the radiator is correctly sized, the outcome is the room at the right temperature.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody@Jamespa Do you mean the temperature of the radiator rather than the room James? I suppose if the radiator is correctly sized, the outcome is the room at the right temperature
I mean the room. I'm assuming that there is spread in radiator sizing in reality!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 64 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: What is the best strategy for operating a very oversized heat pump?
It makes sense, although shows a complete lack of thoug...
By JamesPa , 9 seconds ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 3 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
No need for apologies, just cautioning about getting to...
By JamesPa , 20 minutes ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 22 minutes ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 2 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 4 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 6 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 7 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 18 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 21 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 22 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 6 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 7 hours ago
-
SolarPV tables / online calculator
By MichelleC 14 hours ago
-
By Toodles 2 days ago