Flow temperature & weather compensation. Impact on efficiency
Having had my heat pump for about 18 months I have gradually got to grips with understanding the controls and functions. I'm sure everyone's experience is different as it depends on so many factors including property efficiency, whether lived in all day, wfh, geographic location and more.
The most simple conclusions I came to are that the setup has best efficiency/cost with: Lowest flow temperature possible which is best managed with weather compensation. This requires a different mindset from my previous Oil central heating experiences! Target room temperatures are mostly around 21deg in main living room and kitchen but much cooler in secondary/less used rooms & bedrooms.
I came across a very useful tool that allows comparison of the impact on SCOP (Seasonal Coefficient of Performance) of different flow temperatures.
In my case using the exact model LG Therma V HM161M.U33
I can see the impact of the flow temperature and added benefit of using weather compensation. I am now using both and see that the flow temp is often as low as 30deg! But the house is reaching and holding the target 21deg without difficulty. The house is very old & generally inefficient but with underfloor heating and modern extension. At night I drop the temp just 1 degree (if more it would take a long time to warm up and/or need higher flow temp)
As can be seen in the screenshot the efficiency is around 375% at 35deg with weather compensation down to 200% at 55deg without weather compensation.
A very graphic and clear view of why flow temp should be as low as possible and weather compensation functionality should be used.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
@tim441 this is really useful info and a great find. Your experience of converting from oil to ASHP mirrors mine. I'm only 3 months into the journey however. My system design temperature was 50degC but I'm finding with climatic compensation on, a maximum of 42degC flow at 0degC ambient and 30degC flow at 20degC ambient is providing efficient operation. I'm using hugely less energy than I was when I had CH and HW from kerosene, hugely less emissions, and saving around 20% on my fuel bills over the most expensive and energy intensive months. As the days draw longer and the weather warms, the ASHP efficiency and solar PV should really start to kick in and save energy.
-
Servicing LG Therma V
4 months ago
-
LG Therma V. Software upgrades, AI (weather compensation), SCOP
10 months ago
-
Flow temperature up and down like a yo-yo
12 months ago
-
LG Therma V R32 Monobloc. Setup advice inc flow temperature & weather compensation
2 years ago
-
Daikin EDLA14D3V3 COP is now below 1
2 years ago
- 21 Forums
- 1,744 Topics
- 37.3 K Posts
- 20 Online
- 2,035 Members
Join Us!
Latest Posts
-
RE: In the Bleak Midwinter... Midea heat pump performance, poor COP and windchill in action
A similar pattern happened again last night and into th...
By cathodeRay , 6 hours ago
-
RE: Do thick walls make for warm houses?
@bontwoody A lot of the reason the u value doesn’t s...
By robl , 7 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
@crimson A raise in flow temperature to 45 deg. C shoul...
By Toodles , 7 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@mikeh, thanks a lot for the video. I found them very i...
By trungdong , 8 hours ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@editor I suspect I need both. We're still trying to ge...
By Odd_Lion , 1 day ago
-
RE: Samsung HP secondary pump wiring
Thanks for the reply. I have asked a couple of days ago...
By Chris-in-Kemnay , 1 day ago
-
RE: New Samsung 12KW Heat Pump Help
@mike-h It has been a few days since we’ve changed t...
By dinhp , 1 day ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Two other things that greatly effect SCOP but havent be...
By bontwoody , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
Hi All We have 2 ASHPs, Solar/Battery system and soon...
By AlanB , 1 day ago
-
@westkent OK , Interesting , Im surprised that Airsourc...
By Alfapat , 1 day ago
-
RE: Post Buffer Tank DUCA Circulating Pump Settings
@potatoman I raised this with Secon, and here's what th...
By Mars , 1 day ago
-
RE: Smart meter installation – seamless or a potential nightmare?
@transparent, now hosted on our site as attached.
By Mars , 2 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
That's actually not too bad, or, to put it another way,...
By cathodeRay , 2 days ago
-
RE: Air source heat pump roll call
Ecodan PUZ-WM85VAA1.7 slimline Stelrad Softline Comp...
By Westkent , 2 days ago
-
RE: Baffled by heat pump size/ choice!
Try reducing the DHW hysteresis setting and schedule th...
By JohnR , 3 days ago
-
RE: Vaillant ASHP Weather Compensation with Octopus Cosy
Your Sensocomfort is the thermostat and it does work as...
By Judith , 3 days ago
-
@raiph I apologise for my incorrect assumption. A PWM p...
By Mike H , 3 days ago
-
RE: Should We Rethink the Name “Heat Pump” for Homeowners?
Not sure you need the "re". Caleferator sounds fine to...
By downfield , 3 days ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
Thanks for this Mars. I've actually found out the issue...
By dnagre , 4 days ago
-
RE: 6 Red Flags to Avoid When Considering a Heat Pump Installation
The ASHP, just like a boiler, can supply water at only ...
By JamesPa , 4 days ago
Latest Topics
-
Samsung HP secondary pump wiring
By Chris-in-Kemnay 2 days ago
-
Post Buffer Tank DUCA Circulating Pump Settings
By Potatoman 2 days ago
-
Baffled by heat pump size/ choice!
By zuluwarrior 5 days ago
-
Vaillant ASHP Weather Compensation with Octopus Cosy
By tom58l 6 days ago
-
By R0y124 6 days ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
By ThunderMink 7 days ago
-
By TheHolyHeatPump 1 week ago
-
Flow temperature- At what point?
By Westkent 1 week ago
-
Excessive performance/system issues with GSHP
By didjerama_uk 1 week ago