Flow temperature & weather compensation. Impact on efficiency
Having had my heat pump for about 18 months I have gradually got to grips with understanding the controls and functions. I'm sure everyone's experience is different as it depends on so many factors including property efficiency, whether lived in all day, wfh, geographic location and more.
The most simple conclusions I came to are that the setup has best efficiency/cost with: Lowest flow temperature possible which is best managed with weather compensation. This requires a different mindset from my previous Oil central heating experiences! Target room temperatures are mostly around 21deg in main living room and kitchen but much cooler in secondary/less used rooms & bedrooms.
I came across a very useful tool that allows comparison of the impact on SCOP (Seasonal Coefficient of Performance) of different flow temperatures.
In my case using the exact model LG Therma V HM161M.U33
I can see the impact of the flow temperature and added benefit of using weather compensation. I am now using both and see that the flow temp is often as low as 30deg! But the house is reaching and holding the target 21deg without difficulty. The house is very old & generally inefficient but with underfloor heating and modern extension. At night I drop the temp just 1 degree (if more it would take a long time to warm up and/or need higher flow temp)
As can be seen in the screenshot the efficiency is around 375% at 35deg with weather compensation down to 200% at 55deg without weather compensation.
A very graphic and clear view of why flow temp should be as low as possible and weather compensation functionality should be used.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
@tim441 this is really useful info and a great find. Your experience of converting from oil to ASHP mirrors mine. I'm only 3 months into the journey however. My system design temperature was 50degC but I'm finding with climatic compensation on, a maximum of 42degC flow at 0degC ambient and 30degC flow at 20degC ambient is providing efficient operation. I'm using hugely less energy than I was when I had CH and HW from kerosene, hugely less emissions, and saving around 20% on my fuel bills over the most expensive and energy intensive months. As the days draw longer and the weather warms, the ASHP efficiency and solar PV should really start to kick in and save energy.
-
LG Therma V. Software upgrades, AI (weather compensation), SCOP
6 months ago
-
Flow temperature up and down like a yo-yo
8 months ago
-
LG Therma V R32 Monobloc. Setup advice inc flow temperature & weather compensation
1 year ago
-
Daikin EDLA14D3V3 COP is now below 1
1 year ago
-
Ecodan with UFH flow temperature consuming 130kWh per day
2 years ago
- 25 Forums
- 1,513 Topics
- 31.8 K Posts
- 23 Online
- 1,284 Members
Join Us!
Latest Posts
-
-
RE: Delivering a smart and secure electricity system: government consultation
Compared to a poorly executed development and rollout, ...
By ChickenBig , 49 mins ago
-
RE: Ecodan ASHP - How to optimise my set up?
That would seem logical, however do you know if the FTC...
By rhh2348 , 55 mins ago
-
RE: Ecodan - flow rates, sensors, settings
As mentioned above, the one I have 1) has the MITSUBISH...
By rhh2348 , 1 hour ago
-
RE: Additional Battery v Wind Turbine v Ripple
I should add, being an investment, the value of your in...
By Old_Scientist , 8 hours ago
-
RE: Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
Similar thread here
By Johnmo , 17 hours ago
-
RE: VDI 2035 heating water specification
Been looking and it seems a good little project. Ever...
By Johnmo , 2 days ago
-
RE: Do I accept an ASHP and Solar Panel retrofit under the HUG 2 scheme?
Will do. I'm currently waiting for another survey / vis...
By dssr , 2 days ago
-
The company that did the borehole were expecting us to ...
By Johnmo , 2 days ago
-
RE: The Misquote That Ruined the Heating Industry
@abernyte manufacturer training is pretty average. They...
By Mars , 2 days ago
-
-
RE: ECO4 Scheme and EPC ratings
@mellow Thanks. Given there is a scheme requirement to ...
By Old_Scientist , 4 days ago
-
RE: Do I just go with the lowest quote for my heat pump?
@jancold To me its a no-brainer then, a max 40C flow te...
By bontwoody , 4 days ago
-
-
RE: Heat Pump Books Beginners – Bodge Buster & From Zero To Heat Pump Hero
@editor Presumably he had some good weather Compensatio...
By Toodles , 4 days ago
-
RE: New Vaillant 7kW aroTherm ASHP or oil boiler dilemma/decision??
Storage capacity really is dependent on storage tempera...
By Johnmo , 4 days ago
-
RE: HP Cycling, Expected or Undesirable
Just a little update. I ordered a longer shielded twin ...
By bontwoody , 4 days ago
-
RE: Domestic hot water timer doing crazy things on my Grant Aerona3 10kW air source heat pump
Thanks @allyfish for the pics and info. Spoke to the in...
By Mellow , 4 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
It's been a busy day for calls and emails from Aira. I ...
By MikeH , 5 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Hmm. A bit of a nuanced answer, methinks. As I've alr...
By Majordennisbloodnok , 5 days ago
Latest Topics
-
Ecodan - flow rates, sensors, settings
By rhh2348 15 hours ago
-
Replacing mains water with well water
By Johnmo 2 days ago
-
Additional Battery v Wind Turbine v Ripple
By bontwoody 3 days ago
-
By jamespipe 3 days ago
-
VDI 2035 heating water specification
By Johnmo 3 days ago
-
Do I just go with the lowest quote for my heat pump?
By Jancold 5 days ago
-
The Misquote That Ruined the Heating Industry
By Alec Morrow 6 days ago
-
Battery Storage Wiring Gauge Question
By Puff 6 days ago