Effect of buffer tank or volumiser on heat pump system
Posted by: @davidalgarveApologies for re-introducing this topic. I was persuaded by contributers on this forum, that I should remove the second CH pump and change the function of the buffer tank to use it as a volumiser.
I have forgotten how it was suggested that I should use the four connections on the tank in this configuration.
Existing connections are LHS: Top - From ASHP; Bottom - Return to ASHP RHS Top- To CH: Bottom - Return from CH
I think that you will find that the best location for a volumiser is in the return pipework to the heat pump.
It has also become apparent that some buffer tanks are directional, so have a look around the casing for any direction arrows.
The LHS bottom - return to ASHP pipe should be left as is. The LHS top - from ASHP pipe should be disconnected from the buffer tank and also the RHS top - to CH pipe should also be disconnected. A connection pipe should be used to connect these two pipes together, so that the flow from the ASHP goes directly to the heating system, bypassing the buffer tank. The remaining pipe connected to the RHS bottom - return from CH should be disconnect from its present position and connected to the LHS top. The two pipe connections that will now be without pipes will need to be plugged.
Once completed the water flow should be from the heat pump, direct to the heat emitters, with the return from the heat emitters going into the LHS top of the volumiser, then out of the LHS bottom connection back to the heat pump.
Thank you very much for reminding me, Derek. My installer of choice, here in Portugal, is rather sceptical so I have to be persuasive. I am attaching a photo of my tank and you will see that re-directing the CH return to the top left hand may be rather difficult. Is there any real difference if the CH return is connected to the top right? It seems to me to be almost advantageous for the flow to be across the tank in addition to top to bottom but I am in new territory here.
The other pipe from the 3 way valve goes vertically to my DHW tank.
Incidentally, there is no evidence that this Cordivari tank is directional
If the flow through the buffer tank is not directional then it should be possible to connect the CH return to the top RHS connection rather than the top LHS.
I forgot to mention that it will also be necessary to remove the secondary water pump and replace it with a connecting length of pipe.
Many thanks Derek. That is what I will suggest and hope to report back in due course.
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 30 Online
- 5,662 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Rodents! A word of warning for heat pump owners
@tim441 Or as they didn’t quite say in the space travel...
By Toodles , 1 hour ago
-
RE: Mitsu Wireless Controller and MelCloud
Update: I have found that the contractor had changed on...
By DavidAlgarve , 13 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@editor Hi Mars, We have just installed a Grant Aerona...
By GrahamF , 14 hours ago
-
RE: Sanity check please. Battery storage and inverter sizing.
There are MCS guidelines about how close to the edge/ri...
By Old_Scientist , 17 hours ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
I estimated our usage on the following basis. The mos...
By Old_Scientist , 18 hours ago
-
RE: Why so many sigenergi installer recommendations?
It’s a really simple answer, GivEnergy. Installers ...
By SAEnergy , 22 hours ago
-
@editor Something changed in this last 12 months, they ...
By ASHP-BOBBA , 2 days ago
-
RE: Ecodan & MelCloud scheduling
I put the above question to Mitsu UK at the sme time as...
By DavidAlgarve , 2 days ago
-
Thanks for the heat geek info. I've fitted my own heat ...
By bontwoody , 3 days ago
-
RE: Does anyone have experience of a smart water meter?
Just to give a sense of scale, I've used the CCW water ...
By Majordennisbloodnok , 3 days ago
-
RE: Powerwall 3 or Myenergi or something else?
We have a Tesla Powerwall 3, recently installed, so I m...
By Old_Scientist , 4 days ago
-
RE: Mitsubishi PAR-WT60R-E Wireless Controller installation
@morgan They have been paired once but it was thought b...
By DavidAlgarve , 5 days ago
-
RE: Isolating the system for a planned power cut
A great many ground-mounted local substation transforme...
By Transparent , 5 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 6 days ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 6 days ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 7 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 1 week ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 1 week ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 1 week ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 1 week ago