Effect of buffer tank or volumiser on heat pump system
Posted by: @davidalgarveApologies for re-introducing this topic. I was persuaded by contributers on this forum, that I should remove the second CH pump and change the function of the buffer tank to use it as a volumiser.
I have forgotten how it was suggested that I should use the four connections on the tank in this configuration.
Existing connections are LHS: Top - From ASHP; Bottom - Return to ASHP RHS Top- To CH: Bottom - Return from CH
I think that you will find that the best location for a volumiser is in the return pipework to the heat pump.
It has also become apparent that some buffer tanks are directional, so have a look around the casing for any direction arrows.
The LHS bottom - return to ASHP pipe should be left as is. The LHS top - from ASHP pipe should be disconnected from the buffer tank and also the RHS top - to CH pipe should also be disconnected. A connection pipe should be used to connect these two pipes together, so that the flow from the ASHP goes directly to the heating system, bypassing the buffer tank. The remaining pipe connected to the RHS bottom - return from CH should be disconnect from its present position and connected to the LHS top. The two pipe connections that will now be without pipes will need to be plugged.
Once completed the water flow should be from the heat pump, direct to the heat emitters, with the return from the heat emitters going into the LHS top of the volumiser, then out of the LHS bottom connection back to the heat pump.
Thank you very much for reminding me, Derek. My installer of choice, here in Portugal, is rather sceptical so I have to be persuasive. I am attaching a photo of my tank and you will see that re-directing the CH return to the top left hand may be rather difficult. Is there any real difference if the CH return is connected to the top right? It seems to me to be almost advantageous for the flow to be across the tank in addition to top to bottom but I am in new territory here.
The other pipe from the 3 way valve goes vertically to my DHW tank.
Incidentally, there is no evidence that this Cordivari tank is directional
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 16kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
If the flow through the buffer tank is not directional then it should be possible to connect the CH return to the top RHS connection rather than the top LHS.
I forgot to mention that it will also be necessary to remove the secondary water pump and replace it with a connecting length of pipe.
Many thanks Derek. That is what I will suggest and hope to report back in due course.
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 16kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
- 26 Forums
- 2,356 Topics
- 53.4 K Posts
- 216 Online
- 6,017 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Electricity price predictions
Ben Watts posted on LinkedIn that he had updated this w...
By Judith , 1 hour ago
-
RE: The good, the bad and the not that great – my heat pump installation
Small update, Emailed and Spoke to Midea UK and they ...
By Burtis , 2 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@bash Octopus does charge for the admin. The process al...
By Batpred , 2 hours ago
-
RE: External pipework insulation
@transparent HI all The products you mention are ver...
By David Smith , 2 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Issues still under investigation by Solis... Fogstar ...
By Batpred , 2 hours ago
-
RE: Who's your electricity provider and what's your tariff?
I agree, the consumer is not being properly represented...
By Batpred , 2 hours ago
-
RE: Controlling Daikin Altherma via P1P2 and Home Assistant
@weoleyric, apologies for the delay in response. Give...
By Majordennisbloodnok , 4 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@harrisonc wow. That’s going to get the rumour mill gr...
By AndrewJ , 6 hours ago
-
RE: Advice on internal circulation pump noise
Thanks @mikefl - I'll maybe have a look at the lock-shi...
By jtg , 19 hours ago
-
RE: Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
@toodles interesting suggestion, thanks. I will try to...
By GrahamF , 19 hours ago
-
RE: Mitsubishi Ecodan Auto Adaption trial to stop cycling.
The interval you talk of, i think, will be 60min for an...
By F1p , 23 hours ago
-
Agree with @majordennisbloodnok on the setbacks. We hav...
By ChandyKris , 2 days ago
-
RE: Speedcomfort radiator fans
@deltona the way the links were added broke the page. A...
By Mars , 2 days ago
-
RE: Setback savings - fact or fiction?
I agree! Even more so if we get an answer! But the chal...
By cathodeRay , 2 days ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
This has been delayed from what I believe to be this ye...
By dgclimatecontrol , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
this is why I provided current flow temperatures in the...
By ksim , 2 days ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
There's many homes that would be quite a disruption for...
By dgclimatecontrol , 2 days ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@rhh2348 ...maybe this option is what you want? Alter...
By benson , 2 days ago
-
RE: Free Ecoheat Heat Pump Install
@old_scientist This does make the unit smaller as the b...
By dgclimatecontrol , 2 days ago