Effect of buffer tank or volumiser on heat pump system
Posted by: @davidalgarveApologies for re-introducing this topic. I was persuaded by contributers on this forum, that I should remove the second CH pump and change the function of the buffer tank to use it as a volumiser.
I have forgotten how it was suggested that I should use the four connections on the tank in this configuration.
Existing connections are LHS: Top - From ASHP; Bottom - Return to ASHP RHS Top- To CH: Bottom - Return from CH
I think that you will find that the best location for a volumiser is in the return pipework to the heat pump.
It has also become apparent that some buffer tanks are directional, so have a look around the casing for any direction arrows.
The LHS bottom - return to ASHP pipe should be left as is. The LHS top - from ASHP pipe should be disconnected from the buffer tank and also the RHS top - to CH pipe should also be disconnected. A connection pipe should be used to connect these two pipes together, so that the flow from the ASHP goes directly to the heating system, bypassing the buffer tank. The remaining pipe connected to the RHS bottom - return from CH should be disconnect from its present position and connected to the LHS top. The two pipe connections that will now be without pipes will need to be plugged.
Once completed the water flow should be from the heat pump, direct to the heat emitters, with the return from the heat emitters going into the LHS top of the volumiser, then out of the LHS bottom connection back to the heat pump.
Thank you very much for reminding me, Derek. My installer of choice, here in Portugal, is rather sceptical so I have to be persuasive. I am attaching a photo of my tank and you will see that re-directing the CH return to the top left hand may be rather difficult. Is there any real difference if the CH return is connected to the top right? It seems to me to be almost advantageous for the flow to be across the tank in addition to top to bottom but I am in new territory here.
The other pipe from the 3 way valve goes vertically to my DHW tank.
Incidentally, there is no evidence that this Cordivari tank is directional
If the flow through the buffer tank is not directional then it should be possible to connect the CH return to the top RHS connection rather than the top LHS.
I forgot to mention that it will also be necessary to remove the secondary water pump and replace it with a connecting length of pipe.
Many thanks Derek. That is what I will suggest and hope to report back in due course.
- 21 Forums
- 1,964 Topics
- 42.6 K Posts
- 40 Online
- 2,278 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: What is the best strategy for operating a very oversized heat pump?
This whole discussion highlights just how much of a mes...
By Mars , 4 minutes ago
-
Hi I'm new to the forum. I've just had the latest G...
By cliffhanger , 6 minutes ago
-
RE: NIBE F2040 12 kW heat pump and 100 liter buffer tank
@cheshirejohn thanks for the update and for sharing. I’...
By Mars , 27 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@jamespa @bontwoodyHeat loss calculations found and att...
By BAMi , 2 hours ago
-
RE: Setback savings - fact or fiction?
Here's the same plot, less the R squared values, done q...
By cathodeRay , 3 hours ago
-
RE: SolarPV tables / online calculator
We've only had our solar since last June, but so far fo...
By Old_Scientist , 3 hours ago
-
@robs useful thread! Thanks for sharing - Octopus are c...
By big_si , 3 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 5 hours ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 6 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 7 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 9 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 11 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 1 day ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 1 day ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 2 days ago
Latest Topics
-
By cliffhanger 6 minutes ago
-
Heat Pump Sizing & Installation Costs
By Mars 13 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 14 hours ago
-
SolarPV tables / online calculator
By MichelleC 21 hours ago