Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan thoughts please: QUHZ-W40VA takes longer than I would like to revert back to heat mode following a DHW cycle
Welcome to the forums @barry-the-bear
Your experience does seem a bit unusual, but I noticed that the unit in question is a 4kW Ecodan QUHZ. What makes this model stand out is that it uses CO2 (R744) as its refrigerant, which is quite different from other Ecodan models that use traditional refrigerants like R32. While I’m not a refrigerant specialist, CO2-based systems tend to operate differently, especially with regard to temperature management.
One key aspect is that CO2 systems generally prefer lower return temperatures, and this can impact the delta T. With a CO2 system like the QUHZ, a delta T of around 30°C isn’t uncommon, which can explain why you’re noticing specific temperature behaviours. It’s possible that the system is designed to prioritise certain flow temperatures during mode changes (for example, between heating and defrost) to optimise refrigerant performance.
It might be that when the unit switches modes, it needs to hit a specific flow temperature - like the 32°C you’ve observed - before resuming normal operation. This is likely tied to the system’s internal logic for efficiently managing CO2 refrigerant, which behaves differently compared to more common refrigerants.
It could be helpful to have a chat with a Mitsubishi support to get some insight into how the QUHZ manages these transitions. They should be able to explain the logic behind the temperature regulation more clearly.
Let us know.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Thank you for your welcome and reply.
You are right that the QUHZ use CO2 (R744) refrigerant. CO2 does have special properties and may operate more efficiently closer to its critical point (31°C), but I have no idea if that plays a role in the delay transitioning from DHW mode to heating mode - and I'm not sure Mitsubishi do either or at least it's not something they've bothered to explain to me. I have talked to them several times, but not once was the refrigerant mentioned.
About the specific (transitional) UFH flow temperature, there seems nothing special about 32C. That's just what it was on the day. What seems to matter is that the post DHW flow temperature matches the required UFH flow temperature. If I fixed the UFH flow at 40C for example the UFH would start fairly promptly, at 38C it take a little longer and so on. The UFH delta T is typically around 7C.
Cheers!
So I suppose the real question is you house cooling down to much or are temps ok?
How is the circulation pump operated on all the time?
The house isn't cooling while for heat mode - the fabric of the house and the MVHR and so on ensures that doesn't happen, but that doesn't mean it isn't desirable to have a shorter delay. The pump doesn't run all of the time.
Posted by: @barry-the-bearThe pump doesn't run all of the time.
That may be your issue. You have hot water sitting in, I assume is an insulated pipe, so it will not cool quickly. If your pump runs when ever there is a demand for heat, the hot water in the pipe is flushed away when the diverter valve moves to heating system and cools really quickly.
The other issue could be if you have mixer valve on the UFH, it will just recycle 90% of its return water and only let a small amount of hot water through. So you see an issue, but in reality you UFH is getting hot water.
Today even without having to do DHW heating, my ASHP compressor went off 8 hrs ago, water is just circulating, sensing the return temp, if it needs the compressor to start it will.
I don't know if you are right or not!. I am sure though that the UFH doesn't receive any hot water until QUHZ sends it and UFH pump, housed in the packaged thermal store won't run until the flow temperature reduces to the required level. My thought was that the rapid cooling from minute 11 to 15 ideally should continue a little longer.
- 27 Forums
- 2,768 Topics
- 65.2 K Posts
- 912 Online
- 7,169 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Why are ASHP installs so expensive?
@rob-of-york Another good question. Until now most ...
By JamesPa , 5 minutes ago
-
Thanks @jamespa The gas fire is definitely not an ess...
By Rob of York , 53 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
My guess is that if you do nothing, Octopus will contin...
By Old_Scientist , 5 hours ago
-
RE: Starting Our Heat Pump Journey: 1962 build 3 bed detached house
@ian-s I would encourage you to have a conversation ...
By Rob of York , 5 hours ago
-
RE: Is it the house or the equipment?
Thanks @jamespa The last hard to fix draughts in the...
By springswood , 7 hours ago
-
RE: Missing flow temperature in Heat Geek proposal
I suspect it's a deliberate decisi...
By JamesPa , 8 hours ago
-
RE: Vaillant Arotherm – Using Heating
@l8again Mine is typically using 11w including the i...
By Batpred , 9 hours ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
If you have a flowmeter and two temperature probes, the...
By bobflux , 17 hours ago
-
RE: Siting of the external sensor on a heatpump
@jamespa Absolutely. Even if the same mistake was mad...
By Batpred , 1 day ago
-
-
RE: Recommendations in Ely (Cambs) area for Full setup checks on Nibe HP setup for House.
In fairness all heating has cost a lot to run in recent...
By JamesPa , 2 days ago
-
RE: Navigating the World of Refrigerants In Heat Pumps: A Guide for Homeowners
Indeed we are invvestigating AC at present and are havi...
By Toodles , 3 days ago
-
RE: Daikin ESPAltherma and Home Assistant installation
It's laziness lol The PV system is very chatty, meter...
By bobflux , 4 days ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
R (The R Project for Statistical Computing, I use it wi...
By cathodeRay , 4 days ago