Posted by: @davewPosted by: @gotaashp
As an aside - this installer video has the case off at 29:30, no mention of an internal pump whilst discussing the internal gubbings.
@gotaashp, @derekm
I have a total package ecodan 8.5kw pump and packaged cylinder and I have three pumps pre plumbed by mitsubishi on the indoor unit....looking at the schematic for my system (See page 5) it shows the 3 pumps , one for the DHW, one on the primary heat pump return and one on the heating circuit (not sure how this works I think it is something to do with the magical hydraulic separation in the low loss header.....however I think this confirms the heat pump has no internal pump.
I am still not sure which of the two heating pump I have been adjusting using the FTC setting but I am down to 1 (currently showing 11l/min) and everything seems okay but still only achieving DT of 3.
Still trying 24 HR trials on AA with tweaks and getting 3.2 to 3.4 cops... today's test is no setbacks and 20c set point.
Still running repetitive with one cycle per hour.
Hope this helps
You are indeed correct that the Ecodan does not have an internal water pump. My bad. 🙄
So I must assume that when you change the pump speed on the controller it is varying the speed of, probably, the return pump, which must therefore be wired to the controller.
What I fail to understand, is why you are having to manually change the speed of the water pump, if the speed is being controlled from the controller? Why does the controller not vary the speed automatically to control the DeltaT?
Edit.
The only other way to increase the COP would probably be to reduce the LWT, but I would also suggest checking that the temperature sensors are actually installed correctly, are making good thermal contact with the pipework, and are adequately insulated.
Posted by: @derek-mPosted by: @davewPosted by: @gotaashp
As an aside - this installer video has the case off at 29:30, no mention of an internal pump whilst discussing the internal gubbings.
@gotaashp, @derekm
I have a total package ecodan 8.5kw pump and packaged cylinder and I have three pumps pre plumbed by mitsubishi on the indoor unit....looking at the schematic for my system (See page 5) it shows the 3 pumps , one for the DHW, one on the primary heat pump return and one on the heating circuit (not sure how this works I think it is something to do with the magical hydraulic separation in the low loss header.....however I think this confirms the heat pump has no internal pump.
I am still not sure which of the two heating pump I have been adjusting using the FTC setting but I am down to 1 (currently showing 11l/min) and everything seems okay but still only achieving DT of 3.
Still trying 24 HR trials on AA with tweaks and getting 3.2 to 3.4 cops... today's test is no setbacks and 20c set point.
Still running repetitive with one cycle per hour.
Hope this helps
You are indeed correct that the Ecodan does not have an internal water pump. My bad. 🙄
So I must assume that when you change the pump speed on the controller it is varying the speed of, probably, the return pump, which must therefore be wired to the controller.
What I fail to understand, is why you are having to manually change the speed of the water pump, if the speed is being controlled from the controller? Why does the controller not vary the speed automatically to control the DeltaT?
Edit.
The only other way to increase the COP would probably be to reduce the LWT, but I would also suggest checking that the temperature sensors are actually installed correctly, are making good thermal contact with the pipework, and are adequately insulated.
Think I’ll claim the no pump in the heat pump thingy 😉😂😂
Davew have you tried a DT check while your system is in DHW mode? That will be a shorter return loop to the heat pump and so may give you a higher delta T. That should also switch off one of the other pumps… I’m guessing the CH return pump will de activated.
Edit- I know this isn’t a solution in itself but it may explain where heat exchange is poorer.
Also. The Mitsubishi pre plumbed cylinder assemblies are the only ones guaranteed to have ftc linked speed control. If an installer assembles their own pipework they may install different pumps with manual adjustment. Availability has been cited as a reason!?
Also endorse what Derek Said about checking the thermistor placement and contact is good. Make sure they are on the Primary Flow and Return and not on the CH flow and return.
Our story so far
we’ve got our daily COP up to 3.75, 3.4, 3.73, 3.72, 3.67, 3.58, 3.72 for the past 7 days. This is taken from our daily consumption update on screen.
Our Problem area is : Reporting graphs.. Not sure how good MELCloud is? What’s the best-simplest-low cost system people are using?
morning. an update....
i have WC curve set to 45 @ -3c, 25 @19c. before I went to bed last night I offset the LFT by -3c on the FTC panel, so not to have it so warm during the night. WRT was showing 20c.
at 8am this morn, WRT was still showing 20c. (it hasn't fluctuated hardly at all from this since I started WC (72 hrs ago)). interestingly, because of the lower outside temps the LFT was at 40 and the RFT was at 36, so a DT of 4 - the best I have seen it since observation started 3 days ago. this suggests that I can achieve a better DT with higher LFTs but struggles with lower (~32) LFTs (DT2). any thoughts why this might be?
Derek - I haven't tried your suggested trial yet or checked the temp sensors. I'm not sure what I'm looking for but I'll figure it out 🙂
EDIT: also wanted to ask, how are you calculating your COP? is this number readily available on the MELCLOUD app? (something I don't have).
Posted by: @si-filloalso wanted to ask, how are you calculating your COP?
I’m sure MELCloud works it out once you’re familiar with it.
The quickest way I’ve been using is off the FTC main screen. Press the right menu button and you should get 4 rows of options. The right one is the daily consumption and generation rate. This is updated daily at 11.59pm and gives you a running total for the current month. I then subtract yesterday’s number from todays total to give me the last 24 hours stat.
to work out the cop divide the big number by the small number.
example :
total generated 206kwh
total consumed 56kwh
206 / 56 = 3.68 COP
@sunandair ah, thank you. I had seen this numbers but didn't realise it was a cumulative (monthly) number. So yesterday I had COP of 2.64. current month...2.52. could be better I feel.
I had a look at temp sensors on flow/return pipes. Contacts look ok, but no insulation as Derek suggested should be present. Do I need to lag them with something?
You can drill down further on those energy figures, but they only go as granular as monthly. For daily you'll have to do as @SUNandAIR suggests (subtract the number from the day before). Have a watch of the video below.
Mitsubishi Electric Ecodan FTC5 - Using energy monitoring - YouTube
If you go to melcloud and click on reports tab then select energy usage.....set the start and end dates for period you want ...for a single day use both dates the same....it gives a pie chart showing total consumed and below that a bar chart for consumed and delivered...you can deselect the hot water by clicking on the orange bit under the bar charts if you want just heating consumption.
All said on my melcloud it does not show cop which I would have thought was very easy to do but as you said it's just delivered/ consumed.
You can of course look back to any date or period this way.
Posted by: @sunandairAlso. The Mitsubishi pre plumbed cylinder assemblies are the only ones guaranteed to have ftc linked speed control. If an installer assembles their own pipework they may install different pumps with manual adjustment. Availability has been cited as a reason!?
Ah-ha that makes a lot of sense. Ours isn't pre-plumbed and like @si-fillo we don't have a large number of rads with long runs - so likely the installer deems a fixed flow rate sufficient (and it seems to be tbh) so no need for any speed control. Thanks
Posted by: @davew
I will investigate tomorrow and finally determine what is happening and report back.
Hi Dave,
Thank you so much for the feedback, not everyone provides it, which makes ensuring that we are supplying correct, meaningful, help and advice more difficult.
It is also helpful for future forum readers to see that the problems were actually correctly identified and resolved.
- 22 Forums
- 2,068 Topics
- 45.3 K Posts
- 51 Online
- 3,341 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Kensa GSHP finally installed - now to start the optimisation process
Just had a quick scan of the manual and should be weath...
By Johnmo , 11 hours ago
-
RE: Potentially more choice including air to air heat pump grants
Hi all, I agree, the consultation documents are alway...
By madbilly , 11 hours ago
-
RE: Commencing on an ASHP Installation Process
I think those are pretty much the standard figures that...
By JamesPa , 18 hours ago
-
RE: Load Compensation and Weather Compensation
I think that maybe what the adia thermal system does, b...
By JamesPa , 18 hours ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
@old_scientist @profzarkov thanks to you both for the v...
By Grahamh-uk , 19 hours ago
-
RE: Nibe F2040 periodic warm water increase fails
@tribol here's an official reply from NIBE on your case...
By Mars , 21 hours ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
Hi guys, let’s keep this thread focused and constructiv...
By Mars , 23 hours ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
@ecodan-efficiency On the other hand, the fact that the...
By Richard24738 , 2 days ago
-
RE: How accurate was your heat loss survey?
@scalextrix for our house 1950s detached the air leakag...
By Judith , 2 days ago
-
-
RE: Air Changes per Hour - ACH and the MCS requirement
@matwin If you plan to commission one it might b...
By JamesPa , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
In a similar vein, this recent spell of sustained good ...
By Majordennisbloodnok , 3 days ago
-
RE: Home energy storage & battery register
By the end of next month... 8 kW PV + Tesla Powerwall...
By Algienon , 3 days ago
-
RE: Various different approaches to battery storage.
I thought I'd share my story/journey and experiences he...
By Old_Scientist , 3 days ago
-
RE: Renewables & Heat Pumps in the News
Here on the Forum we're going to need to be increasingl...
By Transparent , 4 days ago
-
What I Wish I Knew Before Installing a Heat Pump
I’m putting together the next Homeowners Q&A episod...
By Mars , 4 days ago
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
In Scotland they still follow the MCS rules, so the noi...
By Johnmo , 4 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@johnmo and @benson Thanks! I was aware there was a p...
By MarcT , 4 days ago
-
RE: Is your heat pump insured?
My insurer just asks the question: "Is your home heated...
By AndrewJ , 5 days ago