Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
EcoDan Cold Radiators
This is a new system, the ecodan 11.2kw, UFH and radiators. I was running it on fixed flow temperature mode of 40C till my thermostats got installed. When I got my thermostats installed the engineer came back, setup 2 zones, changed it to weather compensation curve. I set the UFH to 20c, a wireless room thermostat set to 20C and all radiators on 5.
Each morning I've got up since the UFH rooms are lovely, reaching 20C and coming off/on as it should. But the radiators are all cold. I checked the panel, the play symbol is showing for the heating, the ASHP symbol is showing, I can hear it running. I got the thermistor readings. It shows a flow of 40 and return of 29 but why are the radiators cold?
I suspect that your system needs to be balanced, since it would appear that the majority of the water flow is going to the UFH.
@derek-m I can understand that, but with thermostats for each UFH room, wouldn't once they reach temperature then turn off and the water flow would be redirected to radiators anyway?
Posted by: @paulrlondon@derek-m I can understand that, but with thermostats for each UFH room, wouldn't once they reach temperature then turn off and the water flow would be redirected to radiators anyway?
I'm afraid that I cannot see your system from where I am sitting, you will need to provide more details of what is operating and what is not. How many water pumps and motorised valves do you have? Where are they located?
@derek-m I have 2x UFH manifolds with 2x heatmisers with 4x motorised valve (ground floor and upper floor). 2x motorised valves on the cylinder, 1x motorised valve per each 1x ufh and 1x heatmiser I have 1 water pump on the rads. The main rad flow pipe is hot. I've gone round all the rads, 3 of them have hot flow pipes, the rest are cold.
Posted by: @paulrlondon@derek-m I have 2x UFH manifolds with 2x heatmisers with 4x motorised valve (ground floor and upper floor). 2x motorised valves on the cylinder, 1x motorised valve per each 1x ufh and 1x heatmiser I have 1 water pump on the rads. The main rad flow pipe is hot. I've gone round all the rads, 3 of them have hot flow pipes, the rest are cold.
On the cold radiators, have you checked that both valves, one at each end, are not fully closed. Has your heating system been correctly balanced?
Are the correct water pumps operating and at what speed? Are the motorised valves open when they need to be?
You could try shutting down your UFH for a short period and see if any radiators get warm.
@derek-m As Derek says, the lockshield and ‘thermostat’ valves both need to be open, if they are now open and those radiators are cold, you one more thing to check and that is that they are full of water and not air. Having checked the valves, try bleeding out any air byt gently opening the bleed valve at the top of the radiator (situated at one end) but have a cloth ready to catch any water spurt; if you hear a lot of hissing… keep going until all the air is released and the water spurts out. If none of these measures help, you have blockages somewhere. If the three are all at one end of the run, this would indicate a blockage between the last warm radiator and the first cold one - likely as not, it will be on the feed rather than the return pipe. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
The flow of 40 and return of 29 is a dT of 11 which is very wide for an Ecodan, they try and hold to 5, if it can't then more heat is being sucked out than it can put back in.
What is the pump speed on your ecodan controller its under the settings menu on the far right labelled pump speed, I find that 3 works for my system but with everything calling for heat the dT will be 6-7C. Its a balance of performance and noise speed 5 is quite loud depending on location of your system.
If some rads are cold and opening the valves on them doesn't help, you could try increasing the Ecodan pump speed on the controller to 5 and see what happens.
As also suggested the pump speed for your radiator circuit may be too slow meaning all the heat is taken by the first rads in the circuit.
Posted by: @paulrlondon@derek-m I have 2x UFH manifolds with 2x heatmisers with 4x motorised valve (ground floor and upper floor). 2x motorised valves on the cylinder, 1x motorised valve per each 1x ufh and 1x heatmiser I have 1 water pump on the rads. The main rad flow pipe is hot. I've gone round all the rads, 3 of them have hot flow pipes, the rest are cold.
Have you resolved your problem? Feedback is always welcome.
So I bled the radiators, I switched my programme back to fixed flow 40C and within 12 hours all radiators were hot again. So there's no blockages. I have then since discovered separate issues which may impact things, actuators on manifolds were not tight so they weren't actually turning UFH rooms off and on as they reached temp, so in effect stealing heat. That may have been the problem, the ASHP unable to keep up with the constant heat demand from UFH during the cold snap where we were at 0C. But it's only a theory. I'm going to leave my programme on fixed flow 40C for the next 0C spell which I think is tomorrow night and see if the radiators stay warm. If they do ill go back to weather compensation and try tweaking that, otherwise im concerned my ASHP just isn't able to deliver enough heat for the whole system.
@paulrlondon this sounds to me very much like a flow balancing issue, as the others are suggesting. Its not an "ASHP can't deliver enough heat" issue . get the flow balancing right your house will be warm and your ASHP will be as efficient as it can be.
Posted by: @paulrlondonI switched my programme back to fixed flow 40C and within 12 hours all radiators were hot again.
its should take a few 10's of minutes at most, to feel warmth in all the emitters , in a balanced system.
Hypothesis, based on your two described behaviours:
1. By running at the higher fix flow temp, you are using the UFH's actuators as a "non-ideal" means of flow balancing i.e. eventually the UFH zone will close down because its hot enough, and then (and only then) does the flow want to go to the radiator zone. flow flip-flops between the two. Not ideal, but keeps you warm.
2. in weather compensation mode with the lower flow temperature, the UFH zone may never shut down as its always wanting "just a bit more" heat, it takes all the flow, nothing left for the radiators.
running in fixed WT mode keeps your house warm so a valid workaround for now, but it will cost you lots more to run, so there are three possible solutions to investigate:
- increase the radiator pump speed. this might be enough to get the flow to to round the radiators at the same time as the UFH is active.
- If some radiators are hot and others are not, partially close the lockshield valves on the ones that warm up first / most quickly, until the cold one gets some warmth. This is a trial and error process. Keep notes of how many turns you do, you will forget.
- BEST OPTION: Consult with your installer about how the UFH circuit and the radiator circuit have been balanced so that they both get their fair amount of flow. If they say they didn't do this, ask them to do so and remind them that balancing is part of the proper commissioning of any heating system.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
- 27 Forums
- 2,539 Topics
- 59.1 K Posts
- 394 Online
- 6,818 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Balancing is a long process and its possible to mess th...
By JamesPa , 3 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 4 hours ago
-
Thanks everyone for the help, Havenwise now diasbled. q...
By Boycey , 6 hours ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli Depending on whether you can get an EV tariff, I...
By ChandyKris , 7 hours ago
-
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 8 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@technogeek I think you are correct, but, it didn’t inf...
By Papahuhu , 8 hours ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 9 hours ago
-
@Mars at the time of writing heating oil is £1.28 / ltr...
By TechnoGeek , 9 hours ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 12 hours ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 12 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
The setup for this is a Samsung Modbus card. Connected ...
By antonical , 14 hours ago
-
RE: Forum updates, announcements & issues
@davidalgarve, if the emails are more than roughly a mo...
By Mars , 14 hours ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 14 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Sorry to hear that but I'm not surprised TBH. Stratifi...
By JamesPa , 15 hours ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 1 day ago
-
RE: Setback savings - fact or fiction?
The answer was in two parts in my reply, the second par...
By RobS , 1 day ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 1 day ago
-
Ecodan control return to Melpump from Havenwise trial. settings check
Hi, Just got control back after being on the hav...
By Boycey , 1 day ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
I wonder if heat pump manufacturers will tone these sit...
By JamesPa , 1 day ago
-
RE: Who’s Caved and Switched the Heating On Already?
@editor yesterday we used 12kW of electricity for heat,...
By Judith , 2 days ago
-
RE: Rate the quality of your heat pump design and installation
Loss assessments can be a very serious case of GIGO. I...
By JamesPa , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@jamespa Just bizarre. This is our data. I really don't...
By antonical , 2 days ago
-
RE: Mitsubishi Ecodan 11.2kW review
I think you said its an 11.2kW model and your house is ...
By JamesPa , 2 days ago