Best base for 6kW Ecodan heat pump external unit
What is everyone's thoughts on installation of a unit on earth/ground - seems to be a few schools of thought, around:
Base materials:
- level poured concrete - either of:
- one base
- two separate bases/'plinths'
- paving slab
- gravel
Beneath unit's feet:
- nothing - feet sit on concrete/slab
- 'flexi foot' (e.g. 600mm longh) with struts
- anti-vibration mounts under each foot
Securing:
- feet bolted directly to concrete/slab
- feet bolted to flexi foot and either of:
- flexi feet sat unsecured on top of concrete/slab/gravel
- flexi feet bolted / strapped to / otherwise secured to concrete/slab
- feet bolted to mounts, mounts bolted to concrete/slab
Mitsubishi installation manual says two concrete plinths with feet bolted directly to them.
It feels to me that two concrete plinths with unit feet secured to rubber and then rubber secured to concrete is best - the thinking with the last part: to avoid any small unit movements which may impact balance / create internal vibrations or cause small pipework vibrations downstream (unless flexi hoses always cancel this out?).
Do people think securing the rubber to the plinths would bring any benefits (even if small), and if so, which way would you go if you were doing a fresh install?
Mitsubishi ecodan PUZ-WM60VAA (6kW) with FTC6; third-party cylinder + pumps; LLH
I would say always always always mount on thick rubber anti-vibration grommets in any domestic setting. You do not want to go through it all to find bzzzzzzzzz through your home. I think the new MIS3005 might give some advice on this when released after the consultation as, presently, anti-vibration mounting is required on installations by MCS but a worrying loop hole is the there is zero guidance on what is appropriate. You could literally put something for the weekend 'twixt the unit and concrete base/wall bracket and could pretend that is the anti-vibration mounting.
Ahh I might be wrong about there being a requirement for AV grommets if the manual says bolt directly to a concrete base. The requirement in MIS3005 is "4.4.4 Anti-vibration pads/mats/mounts and flexible hose connections should be installed according to the manufacturer’s instructions to reduce the effects of vibration on the building structure." This mixes the expectation there should be AV grommets with the requirements in the installers manual, and if no requirement specified then I supposed they are not strictly required under MCS.
Posted by: @eltonI would say always always always mount on thick rubber anti-vibration grommets in any domestic setting. You do not want to go through it all to find bzzzzzzzzz through your home. I think the new MIS3005 might give some advice on this when released after the consultation as, presently, anti-vibration mounting is required on installations by MCS but a worrying loop hole is the there is zero guidance on what is appropriate. You could literally put something for the weekend 'twixt the unit and concrete base/wall bracket and could pretend that is the anti-vibration mounting.
I have found that 'something for the weekend' doesn't actually normally stop 'vibration'. 😋
@rhh2348 here's what we did with our heat pump. We secured our heat pump (weighing around 180kg) by placing four levelled concrete slabs side-by-side for a stable base.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk
Posted by: @eltonI would say always always always mount on thick rubber anti-vibration grommets in any domestic setting.
Can you give an example or two of such items, and explain why those?
You do not want to go through it all to find bzzzzzzzzz through your home.
Indeed - hence the thread question 🙂
Posted by: @eltonAhh I might be wrong about there being a requirement for AV grommets if the manual says bolt directly to a concrete base.
I did think it odd, particularly as my install came with flexi feet! Also, Mitsubishi do list those feet in their accessories.
The requirement in MIS3005 is "4.4.4 Anti-vibration pads/mats/mounts and flexible hose connections should be installed according to the manufacturer’s instructions to reduce the effects of vibration on the building structure." This mixes the expectation there should be AV grommets with the requirements in the installers manual, and if no requirement specified then I supposed they are not strictly required under MCS.
Understood, however I am looking for the optimal approach. What have you done / what would you do again if you did afresh?
Mitsubishi ecodan PUZ-WM60VAA (6kW) with FTC6; third-party cylinder + pumps; LLH
Posted by: @editor@rhh2348 here's what we did with our heat pump. We secured our heat pump (weighing around 180kg) by placing four levelled concrete slabs side-by-side for a stable base.
-- Attachment is not available --
-- Attachment is not available --
Wow!
Are they on earth below?
What's the layers between your ASHP and the slab? (e.g. I think I can see rubber feet under the cabinet / enclosure)
Mitsubishi ecodan PUZ-WM60VAA (6kW) with FTC6; third-party cylinder + pumps; LLH
@rhh2348, yeah on earth below, but the area was very heavily compacted so even trying to burrow them in was quite hard.
Not a huge gap bewteen the ASHP and the slab. It's running now and I'm out tomorrow but I can measure on Wednesday. It is standing in rubber feet. There is zero vibration noise from this unit. It's rock solid.
Base drawing from our manufacturer.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk
Posted by: @editorIt is standing in rubber feet. There is zero vibration noise from this unit. It's rock solid.
Niiice. Which feet did you go for and (how) are they secured to the slabs and enclosure / unit?
Mitsubishi ecodan PUZ-WM60VAA (6kW) with FTC6; third-party cylinder + pumps; LLH
@rhh2348 it's the way the heat pump arrived. It was literally taken off a truck, wheeled to the slabs and placed there. It's designed to stand (it's taller than me, and I'm over 6-foot), so no option of wall mounting. Because of it's tall design it's very well balanced, and even when running full tilt, it never reverberates or shakes. Prior to hearing form other homeowners we never even knew that reverberations were a "thing" when it came to heat pumps.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk
Posted by: @editoryeah on earth below, but the area was very heavily compacted so even trying to burrow them in was quite hard.
This comment has me thinking whether adding concrete/slabs may introduce the possibility of vibrations, when some flexi feet (to raise off ground) on level compacted earth (maybe even sat within a 10mm recess with small drain channel out) may do the job as well if not better...
Mitsubishi ecodan PUZ-WM60VAA (6kW) with FTC6; third-party cylinder + pumps; LLH
- 25 Forums
- 1,513 Topics
- 31.8 K Posts
- 27 Online
- 1,283 Members
Join Us!
Latest Posts
-
RE: Additional Battery v Wind Turbine v Ripple
I should add, being an investment, the value of your in...
By Old_Scientist , 4 hours ago
-
RE: Ecodan - flow rates, sensors, settings
Achieving an accurate flow measurement is probably the ...
By Derek M , 8 hours ago
-
RE: Ecodan ASHP - How to optimise my set up?
Again, thank you for another thorough post, @derek-m - ...
By rhh2348 , 10 hours ago
-
RE: Delivering a smart and secure electricity system: government consultation
@Transparent.Now that I am represented by a new MP I th...
By IanMK13 , 12 hours ago
-
RE: Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
Similar thread here
By Johnmo , 12 hours ago
-
RE: VDI 2035 heating water specification
Been looking and it seems a good little project. Ever...
By Johnmo , 1 day ago
-
RE: Do I accept an ASHP and Solar Panel retrofit under the HUG 2 scheme?
Will do. I'm currently waiting for another survey / vis...
By dssr , 2 days ago
-
The company that did the borehole were expecting us to ...
By Johnmo , 2 days ago
-
-
RE: The Misquote That Ruined the Heating Industry
@abernyte manufacturer training is pretty average. They...
By Mars , 2 days ago
-
-
RE: ECO4 Scheme and EPC ratings
@mellow Thanks. Given there is a scheme requirement to ...
By Old_Scientist , 3 days ago
-
RE: Do I just go with the lowest quote for my heat pump?
@jancold To me its a no-brainer then, a max 40C flow te...
By bontwoody , 3 days ago
-
-
RE: Heat Pump Books Beginners – Bodge Buster & From Zero To Heat Pump Hero
@editor Presumably he had some good weather Compensatio...
By Toodles , 4 days ago
-
RE: New Vaillant 7kW aroTherm ASHP or oil boiler dilemma/decision??
Storage capacity really is dependent on storage tempera...
By Johnmo , 4 days ago
-
RE: HP Cycling, Expected or Undesirable
Just a little update. I ordered a longer shielded twin ...
By bontwoody , 4 days ago
-
RE: Domestic hot water timer doing crazy things on my Grant Aerona3 10kW air source heat pump
Thanks @allyfish for the pics and info. Spoke to the in...
By Mellow , 4 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
It's been a busy day for calls and emails from Aira. I ...
By MikeH , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Hmm. A bit of a nuanced answer, methinks. As I've alr...
By Majordennisbloodnok , 4 days ago
Latest Topics
-
Ecodan - flow rates, sensors, settings
By rhh2348 10 hours ago
-
Replacing mains water with well water
By Johnmo 2 days ago
-
Additional Battery v Wind Turbine v Ripple
By bontwoody 2 days ago
-
By jamespipe 3 days ago
-
VDI 2035 heating water specification
By Johnmo 3 days ago
-
Do I just go with the lowest quote for my heat pump?
By Jancold 5 days ago
-
The Misquote That Ruined the Heating Industry
By Alec Morrow 5 days ago
-
Battery Storage Wiring Gauge Question
By Puff 6 days ago
Members Online
No online members at the moment