Ecodan 8.5kW ASHP - 320L DHW Tank
Hello
I have a Ecodan 8.5kW ASHP with a 320L Water Tank. I have tried to set the water to heat for 120 minutes at 2.30am and it does reaching the target temp of 49 degrees. Wife had a shower at 6.30am (5-7 Minutes) and then I went for a shower at 7.30 and these was only luke warm water. Heated water again on demand and went for a shower. Tank temp showed 48 degrees after an hour. After dinner at 7pm we were washing the dishes and half way through we ran out of hot water. Â
Re-circulating pump was switch off a few days ago but this has made no difference.Â
What could be the cause of this. Im sure 320L should last for a day and im sure it should do more then a shower and washing up.Â
Currently running the ASHP to heat after a temp drop of 10 degrees so it heats as soon as we go for a shower.Â
I notice as soon as the shower turned on the temp drops within minutes on the hourly chart on the MELCloud App.Â
I have the same problem
Â
i heat at night on cheap tariff but one shower and temp drop from 48 to 18
I suppose that the first thing would be to quantify how much electrical energy is being used during the DHW heating cycle, since this should provide a measure of how much thermal energy is being supplied.
If the electrical energy usage is low, then check the position of the temperature sensor fitted in the side of the hot water cylinder, also ensure that the sensor is making good thermal contact inside the sensor pocket.
If electrical energy usage is high, you will need to discover where the thermal energy is going.
Do you have a anti-stratification pump on your hot water cylinder? If so, is it running whilst the cylinder is being heated?
Where is your mains water supply pipe connected to the hot water cylinder? When you draw off hot water from the cylinder the outlet pipe should be at the top of the cylinder, with the mains supply being located near the base. Is this correct?
@derek-m attached a screen shot of what happens when someone goes for a shower. Takes about an 1 hour and 15 minutes to heat the tank on average from the heat pump. Not sure how much energy was used.
We have a Temp sensor in the lower part of the tank. There is only one place for this to go in. Goes in all the way and seems to be reading correctly.Â
Hot water comes out the top pipe and the cold water plus if on the recirculated water goes in the bottom of the cylinder.
Â
Â
Â
Â
Â
The fact that the temperature sensor is located in the bottom section of the tank will be the reason why the reading plummets. There should still be plenty of hot water in the rest of the tank.
@ambaz79 You can query Melcloud under Energy Usage and specify just one day and see pie charts of the energy consumed and generated for heating and hot water. It only gives figures for consumed energy, though there are ways to see other figures using MelCloud in a browser window. 75 mins seems a reasonable time to complete a reheat, especially on a large tank.
Unless it is an optical distortion you seem to have a portion of the tank above the hot water draw, the hottest water you can never use! Try putting your hand on the various pipes entering the tank and see how warm they are - you have a number of uninsulated pieces of copper connected. A couple of hours after the HW cycle has finished you would hope those flow and return pipes would be cool as they are uninsulated but if they are still warm then this might show they are conducting heat back out of the tank.
Possibly check the cold supply pipe too, though in this case I wonder about the effect of the recirculation loop that joins it. Even though you are not now actively pumping the hot water round, which will destratify the tank and make it all increasingly (decreasingly?) tepid, it is still a loop through which the hot water within could cool and sink into the bottom of the tank drawing more hot water out of the top. I am not certain but I think the pump will still allow water to flow through even when it is not actively pumping.
Â
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Turns out my son was going for a shower for over 20 minutes after school. This was emptying the tank. I've kept the Circulating Pump off and might just remove it. I've set the tank to warn once at night and once in the day. Also districts my sons shower to less than 10 minutes. Not sure this is being fully followed though! We are getting through 24 hours with just 2 cylinder head ups. Thanks for all your help on this.Â
- 22 Forums
- 2,082 Topics
- 45.7 K Posts
- 17 Online
- 3,370 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron will it bring the rating up in a property with G...
By AF1 , 2 hours ago
-
RE: To relocate or add extra PV panels..advice required
The situation you are currently experiencing is represe...
By apollogrid , 6 hours ago
-
RE: DHW SET UP with Samsung gen 5
no it’s not it just a search of user manuals , being ca...
By Alfapat , 13 hours ago
-
RE: I don't need any heating in the summer. How do I turn my Samsung heat pump off?
SmartThings indeed allows remote control over the heat ...
By HCas , 14 hours ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
@jamespa I have not had a heat calc yet that is below 4...
By ASHP-BOBBA , 15 hours ago
-
RE: Remaining hot water/hot water flow meter
@lakey Hi, I had a quick read through and wanted to see...
By ASHP-BOBBA , 17 hours ago
-
@bart Which county are you in? Kent by any chance? S...
By ASHP-BOBBA , 19 hours ago
-
RE: I worry I've messed my Samsung settings up somehow
@ecobaker I missed this, sorry So 3031 was set to...
By Joshua , 20 hours ago
-
RE: Flow Rate & Low Loss Headers
It sounds like you have thought about this a lot and ev...
By JamesPa , 20 hours ago
-
RE: Forum updates, announcements & issues
@old_scientist thank you, and thank you to @Morgan for ...
By Mars , 22 hours ago
-
RE: Say hello and introduce yourself
I am a UK based product manager for an energy storage s...
By shawnlee , 1 day ago
-
RE: Thinking of ripping our my IVT Greenline HT Plus C model and replacing with a gas boiler.
That's great and in principle I wouldn't disagree, but ...
By JamesPa , 2 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Mitsubishi 8.5 kW Ecodan Standalone (PUZ-WM85VAA)
By Nell , 2 days ago
-
-
RE: Jokes and fun posts about heat pumps and renewables
This is the plan to get our next heat pump installed an...
By Mars , 3 days ago
-
Thanks! That is most useful. I've had a look at the Mid...
By benson , 3 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
I found that Homely blog a few days ago and was tempted...
By cathodeRay , 3 days ago
-
RE: Home energy storage & battery register
I love that! Unfortunately there doesn't appear curr...
By JamesPa , 4 days ago