Ecodan 8.5kW ASHP - 320L DHW Tank
Hello
I have a Ecodan 8.5kW ASHP with a 320L Water Tank. I have tried to set the water to heat for 120 minutes at 2.30am and it does reaching the target temp of 49 degrees. Wife had a shower at 6.30am (5-7 Minutes) and then I went for a shower at 7.30 and these was only luke warm water. Heated water again on demand and went for a shower. Tank temp showed 48 degrees after an hour. After dinner at 7pm we were washing the dishes and half way through we ran out of hot water.
Re-circulating pump was switch off a few days ago but this has made no difference.
What could be the cause of this. Im sure 320L should last for a day and im sure it should do more then a shower and washing up.
Currently running the ASHP to heat after a temp drop of 10 degrees so it heats as soon as we go for a shower.
I notice as soon as the shower turned on the temp drops within minutes on the hourly chart on the MELCloud App.
I have the same problem
i heat at night on cheap tariff but one shower and temp drop from 48 to 18
I suppose that the first thing would be to quantify how much electrical energy is being used during the DHW heating cycle, since this should provide a measure of how much thermal energy is being supplied.
If the electrical energy usage is low, then check the position of the temperature sensor fitted in the side of the hot water cylinder, also ensure that the sensor is making good thermal contact inside the sensor pocket.
If electrical energy usage is high, you will need to discover where the thermal energy is going.
Do you have a anti-stratification pump on your hot water cylinder? If so, is it running whilst the cylinder is being heated?
Where is your mains water supply pipe connected to the hot water cylinder? When you draw off hot water from the cylinder the outlet pipe should be at the top of the cylinder, with the mains supply being located near the base. Is this correct?
@derek-m attached a screen shot of what happens when someone goes for a shower. Takes about an 1 hour and 15 minutes to heat the tank on average from the heat pump. Not sure how much energy was used.
We have a Temp sensor in the lower part of the tank. There is only one place for this to go in. Goes in all the way and seems to be reading correctly.
Hot water comes out the top pipe and the cold water plus if on the recirculated water goes in the bottom of the cylinder.
The fact that the temperature sensor is located in the bottom section of the tank will be the reason why the reading plummets. There should still be plenty of hot water in the rest of the tank.
@ambaz79 You can query Melcloud under Energy Usage and specify just one day and see pie charts of the energy consumed and generated for heating and hot water. It only gives figures for consumed energy, though there are ways to see other figures using MelCloud in a browser window. 75 mins seems a reasonable time to complete a reheat, especially on a large tank.
Unless it is an optical distortion you seem to have a portion of the tank above the hot water draw, the hottest water you can never use! Try putting your hand on the various pipes entering the tank and see how warm they are - you have a number of uninsulated pieces of copper connected. A couple of hours after the HW cycle has finished you would hope those flow and return pipes would be cool as they are uninsulated but if they are still warm then this might show they are conducting heat back out of the tank.
Possibly check the cold supply pipe too, though in this case I wonder about the effect of the recirculation loop that joins it. Even though you are not now actively pumping the hot water round, which will destratify the tank and make it all increasingly (decreasingly?) tepid, it is still a loop through which the hot water within could cool and sink into the bottom of the tank drawing more hot water out of the top. I am not certain but I think the pump will still allow water to flow through even when it is not actively pumping.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Turns out my son was going for a shower for over 20 minutes after school. This was emptying the tank. I've kept the Circulating Pump off and might just remove it. I've set the tank to warn once at night and once in the day. Also districts my sons shower to less than 10 minutes. Not sure this is being fully followed though! We are getting through 24 hours with just 2 cylinder head ups. Thanks for all your help on this.
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 290 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Setback savings - fact or fiction?
No need to create a new thread, @sheriff-fatman. You do...
By Majordennisbloodnok , 37 minutes ago
-
RE: Power outages and storms: A surprisingly good DNO experience
Well done to Scottish Power for doing a good job. Well ...
By Majordennisbloodnok , 1 hour ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
Fair point. The highest frequency of defrosts I'd seen...
By Sheriff Fatman , 2 hours ago
-
RE: Heatpunk Floor plan issues
It's usually the complete opposite... seldom that Safar...
By Mars , 2 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@mike-patrick interesting update - thanks.I've been thr...
By Tim441 , 3 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I remember reading in some inverters. They mandate a se...
By Batpred , 4 hours ago
-
RE: Fan is clipping ice build up from the front of unit.
@majordennisbloodnok I’ll not go there thanks! Toodles.
By Toodles , 5 hours ago
-
RE: Running from backup generaor in powercut?
@majordennisbloodnok Back in the 80’ or 90’ we had a te...
By Toodles , 5 hours ago
-
RE: Running my new Nibe ASHP efficiently
I'm new to the forum. Did you get a reply to this last ...
By Mike @ Camelot , 7 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@grantmethestrength MCS requirements for DHW capacity h...
By Toodles , 7 hours ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
Great to hear! I just figured this out a day or tw...
By anotherdaveuk , 8 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk I'm observing my own system at low temperatures ...
By dr_dongle , 13 hours ago
-
RE: Free Ecoheat Heat Pump Install
@deltona Yes older houses are problematic like that, bu...
By bontwoody , 1 day ago
-
RE: Radiator sizing sanity check
As I mentioned early on the cost of supplying and fitti...
By JamesPa , 1 day ago
-
RE: Electricity price predictions
Great point, one of the key ones in my chat with Octopu...
By Batpred , 2 days ago
-
RE: New Fogstar 15.5kWh upright solution
Let me point out that there are many Chinese suppliers ...
By Transparent , 2 days ago
-
RE: Weather compensation- why you should use it
@majordennisbloodnok — The Two Ronnies Mastermind sketc...
By cathodeRay , 2 days ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 2 days ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 2 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
In the diagram below, I describe my understanding of th...
By Batpred , 2 days ago