Ecodan 8.5kW ASHP - 320L DHW Tank
Hello
I have a Ecodan 8.5kW ASHP with a 320L Water Tank. I have tried to set the water to heat for 120 minutes at 2.30am and it does reaching the target temp of 49 degrees. Wife had a shower at 6.30am (5-7 Minutes) and then I went for a shower at 7.30 and these was only luke warm water. Heated water again on demand and went for a shower. Tank temp showed 48 degrees after an hour. After dinner at 7pm we were washing the dishes and half way through we ran out of hot water.
Re-circulating pump was switch off a few days ago but this has made no difference.
What could be the cause of this. Im sure 320L should last for a day and im sure it should do more then a shower and washing up.
Currently running the ASHP to heat after a temp drop of 10 degrees so it heats as soon as we go for a shower.
I notice as soon as the shower turned on the temp drops within minutes on the hourly chart on the MELCloud App.
I have the same problem
i heat at night on cheap tariff but one shower and temp drop from 48 to 18
I suppose that the first thing would be to quantify how much electrical energy is being used during the DHW heating cycle, since this should provide a measure of how much thermal energy is being supplied.
If the electrical energy usage is low, then check the position of the temperature sensor fitted in the side of the hot water cylinder, also ensure that the sensor is making good thermal contact inside the sensor pocket.
If electrical energy usage is high, you will need to discover where the thermal energy is going.
Do you have a anti-stratification pump on your hot water cylinder? If so, is it running whilst the cylinder is being heated?
Where is your mains water supply pipe connected to the hot water cylinder? When you draw off hot water from the cylinder the outlet pipe should be at the top of the cylinder, with the mains supply being located near the base. Is this correct?
@derek-m attached a screen shot of what happens when someone goes for a shower. Takes about an 1 hour and 15 minutes to heat the tank on average from the heat pump. Not sure how much energy was used.
We have a Temp sensor in the lower part of the tank. There is only one place for this to go in. Goes in all the way and seems to be reading correctly.
Hot water comes out the top pipe and the cold water plus if on the recirculated water goes in the bottom of the cylinder.
The fact that the temperature sensor is located in the bottom section of the tank will be the reason why the reading plummets. There should still be plenty of hot water in the rest of the tank.
@ambaz79 You can query Melcloud under Energy Usage and specify just one day and see pie charts of the energy consumed and generated for heating and hot water. It only gives figures for consumed energy, though there are ways to see other figures using MelCloud in a browser window. 75 mins seems a reasonable time to complete a reheat, especially on a large tank.
Unless it is an optical distortion you seem to have a portion of the tank above the hot water draw, the hottest water you can never use! Try putting your hand on the various pipes entering the tank and see how warm they are - you have a number of uninsulated pieces of copper connected. A couple of hours after the HW cycle has finished you would hope those flow and return pipes would be cool as they are uninsulated but if they are still warm then this might show they are conducting heat back out of the tank.
Possibly check the cold supply pipe too, though in this case I wonder about the effect of the recirculation loop that joins it. Even though you are not now actively pumping the hot water round, which will destratify the tank and make it all increasingly (decreasingly?) tepid, it is still a loop through which the hot water within could cool and sink into the bottom of the tank drawing more hot water out of the top. I am not certain but I think the pump will still allow water to flow through even when it is not actively pumping.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Turns out my son was going for a shower for over 20 minutes after school. This was emptying the tank. I've kept the Circulating Pump off and might just remove it. I've set the tank to warn once at night and once in the day. Also districts my sons shower to less than 10 minutes. Not sure this is being fully followed though! We are getting through 24 hours with just 2 cylinder head ups. Thanks for all your help on this.
- 25 Forums
- 1,434 Topics
- 30.1 K Posts
- 28 Online
- 1,218 Members
Join Us!
Latest Posts
-
RE: Insulation of flow and return Heat Pump piping
@dr_dongle From your figures, this suggests the heat lo...
By Toodles , 14 mins ago
-
RE: Incorrect Billing of Customers with a Smart Meter
I agree @derek-m but as I wrote earlier, I don't (yet)...
By Transparent , 56 mins ago
-
It is certainly possible, using a modbus connection. If...
By cathodeRay , 11 hours ago
-
RE: Home energy storage & battery register
1 x Seplos 14.3kWh (Seplos box from Alibaba, battery ce...
By KoRWraith , 21 hours ago
-
I did another reconnection/ reconfiguration session wit...
By Abernyte , 1 day ago
-
RE: Recommended ASHP installers in Hampshire
@benson After my initial enquiries with Octopus, we had...
By Toodles , 1 day ago
-
RE: Air source heat pump roll call
To help bolster the rather small number of NIBE owners ...
By Steve D , 1 day ago
-
RE: A beginner's journey into DIY home energy storage - no solar!
@editor All good here! I'm happy to say that the system...
By KoRWraith , 2 days ago
-
RE: Say hello and introduce yourself
@fse_bec welcome to the forums, and it’s very generous ...
By Mars , 2 days ago
-
RE: Meter Readings - What are theses meters telling me?
@transparent Hi, I am the landlord of the property, we ...
By Potatoman , 2 days ago
-
RE: Octopus (the grid) is my battery
@andris My ‘Best Effort’ so far was on 4th. June 2023 w...
By Toodles , 2 days ago
-
Save the Energy Save the World using Daikin Altherma 3 operation mode and schedules settings.
Hello Everyone. Our Daikin Altherma 3 was set to Dome...
By Mevl , 2 days ago
-
RE: Have Octopus Energy discovered a way to Narnia?
Oh dear. Always winter never Christmas?
By Davesoa , 2 days ago
-
RE: Bivalent oil boiler system to work alongside ground or water source heat pump
I can provide a lot of detail on LED lighting. But no...
By Transparent , 3 days ago
-
RE: Making best use of Agile with a battery and ASHP
I try to ovoid doing that...
By Majordennisbloodnok , 3 days ago
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
@kenbone no need for what kenbone regarding the 100watt...
By David999 , 5 days ago
-
RE: Bivalent (or even trivalent!) system design options for a new GSHP installation
For your interest @algienon this is what happens when a...
By Transparent , 5 days ago
-
RE: Rising Damp – Production Recommendation
Yet another topic I'm not an expert in. Nonetheless, th...
By Majordennisbloodnok , 5 days ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@editor yes, the more I read the forum posts the more I...
By sjn , 5 days ago
-
RE: Observations on my Ecodan's estimates of energy consumed and delivered
As it is possible for the FTC to be powered from a sepa...
By HarriUp , 6 days ago
Latest Topics
-
Incorrect Billing of Customers with a Smart Meter
By KoRWraith 2 days ago
-
Home energy storage & battery register
By Mars 2 days ago
-
Meter Readings - What are theses meters telling me?
By Potatoman 3 days ago
-
Have Octopus Energy discovered a way to Narnia?
By Davesoa 3 days ago
-
Making best use of Agile with a battery and ASHP
By jamesw 4 days ago
-
By Toodles 6 days ago
-
By Blaine_t 6 days ago
-
Insulation of flow and return Heat Pump piping
By Toodles 6 days ago
-
Rising Damp – Production Recommendation
By Mars 6 days ago