Ecodan 8.5kW ASHP - 320L DHW Tank
Hello
I have a Ecodan 8.5kW ASHP with a 320L Water Tank. I have tried to set the water to heat for 120 minutes at 2.30am and it does reaching the target temp of 49 degrees. Wife had a shower at 6.30am (5-7 Minutes) and then I went for a shower at 7.30 and these was only luke warm water. Heated water again on demand and went for a shower. Tank temp showed 48 degrees after an hour. After dinner at 7pm we were washing the dishes and half way through we ran out of hot water.
Re-circulating pump was switch off a few days ago but this has made no difference.
What could be the cause of this. Im sure 320L should last for a day and im sure it should do more then a shower and washing up.
Currently running the ASHP to heat after a temp drop of 10 degrees so it heats as soon as we go for a shower.
I notice as soon as the shower turned on the temp drops within minutes on the hourly chart on the MELCloud App.
I have the same problem
i heat at night on cheap tariff but one shower and temp drop from 48 to 18
I suppose that the first thing would be to quantify how much electrical energy is being used during the DHW heating cycle, since this should provide a measure of how much thermal energy is being supplied.
If the electrical energy usage is low, then check the position of the temperature sensor fitted in the side of the hot water cylinder, also ensure that the sensor is making good thermal contact inside the sensor pocket.
If electrical energy usage is high, you will need to discover where the thermal energy is going.
Do you have a anti-stratification pump on your hot water cylinder? If so, is it running whilst the cylinder is being heated?
Where is your mains water supply pipe connected to the hot water cylinder? When you draw off hot water from the cylinder the outlet pipe should be at the top of the cylinder, with the mains supply being located near the base. Is this correct?
@derek-m attached a screen shot of what happens when someone goes for a shower. Takes about an 1 hour and 15 minutes to heat the tank on average from the heat pump. Not sure how much energy was used.
We have a Temp sensor in the lower part of the tank. There is only one place for this to go in. Goes in all the way and seems to be reading correctly.
Hot water comes out the top pipe and the cold water plus if on the recirculated water goes in the bottom of the cylinder.
The fact that the temperature sensor is located in the bottom section of the tank will be the reason why the reading plummets. There should still be plenty of hot water in the rest of the tank.
@ambaz79 You can query Melcloud under Energy Usage and specify just one day and see pie charts of the energy consumed and generated for heating and hot water. It only gives figures for consumed energy, though there are ways to see other figures using MelCloud in a browser window. 75 mins seems a reasonable time to complete a reheat, especially on a large tank.
Unless it is an optical distortion you seem to have a portion of the tank above the hot water draw, the hottest water you can never use! Try putting your hand on the various pipes entering the tank and see how warm they are - you have a number of uninsulated pieces of copper connected. A couple of hours after the HW cycle has finished you would hope those flow and return pipes would be cool as they are uninsulated but if they are still warm then this might show they are conducting heat back out of the tank.
Possibly check the cold supply pipe too, though in this case I wonder about the effect of the recirculation loop that joins it. Even though you are not now actively pumping the hot water round, which will destratify the tank and make it all increasingly (decreasingly?) tepid, it is still a loop through which the hot water within could cool and sink into the bottom of the tank drawing more hot water out of the top. I am not certain but I think the pump will still allow water to flow through even when it is not actively pumping.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Turns out my son was going for a shower for over 20 minutes after school. This was emptying the tank. I've kept the Circulating Pump off and might just remove it. I've set the tank to warn once at night and once in the day. Also districts my sons shower to less than 10 minutes. Not sure this is being fully followed though! We are getting through 24 hours with just 2 cylinder head ups. Thanks for all your help on this.
- 26 Forums
- 2,221 Topics
- 49.3 K Posts
- 197 Online
- 5,881 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Should Our Water Circulation Pump Be Configured to Run All The Time?
ive got a similar issue with my Vaillant. when it was o...
By AdamK , 6 hours ago
-
RE: Twin 10kw Grant Aerona Volumiser Tanks using lots of power
@adam Hi just jumped on this thread as I too have 2 10k...
By bretix , 7 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
on a facebook thread someone has comented to the effect...
By AdamK , 7 hours ago
-
The timing of training and inference are very applicati...
By wully , 9 hours ago
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
Wanted to add an update. As I am running HomeAssistan...
By bubuontheweb , 10 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
You are correct you dont need the second pump if there ...
By JamesPa , 10 hours ago
-
RE: New Fogstar 15.5kWh upright solution
From my experience with inverters from different Far Ea...
By Transparent , 11 hours ago
-
@bontwoody Thank goodness you are ‘back on-line’ so to ...
By Toodles , 12 hours ago
-
RE: Automation options to maximuse efficiency & ToU tariffs
@majordennisbloodnok Seems reasonable. It would be m...
By Batpred , 12 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas OK Thanks. Will do.
By bontwoody , 15 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
@transparent Thank you for a very comprehensive, tim...
By Batpred , 17 hours ago
-
RE: Isolating the system for a planned power cut
@transparent 😊 I may have lost you there.. I ...
By Batpred , 18 hours ago
-
RE: How good is the app support for your heat pump?
We have a Grant Aerona 290 15.5kW heat pump with their ...
By GrahamF , 19 hours ago
-
-
RE: Low COP and unevenly heated rooms with 12kW Samsung AE120MXTPEH / AE260TNWTEH
Where is the noise coming from. If its the pump then p...
By JamesPa , 22 hours ago
-
The Mars and Richard Kitchen Show
Just stopping by to say: 1) Mars I'm so sorry that yo...
By Lucia , 1 day ago
-
RE: Electricity price predictions
Without getting too much into politics, given that the ...
By Batpred , 2 days ago
-
UK Consumer Law Reality Check (for anyone dealing with ...
By DREI , 2 days ago
-
@dgclimatecontrol Thanks... this was resolved back in M...
By Sandman1600 , 2 days ago
-
Electrical is the only way forward.. But until we get...
By Batpred , 2 days ago