Had my Samsung ASHP installed start November. They left the DHW temp at 50C and set to go on and off all the time to keep the water at 50C. The tank is huge, I live alone and only use hot water for a shower in the evening so this seemed uneconomical to me.
Following excellent advice on here I've now set a schedule for the DHW to come on for 2 hours in the afternoon and reduced the water temp to 43C. But the DHW still seemed to be way too hot.
I had a look when the DWH was on today and as you can see the set temp is for 43C but the actual temp is over 47C. It still seems to be wanting to heat to 50C it seems to me.
I've looked in the field values and can see no way to set the DHW temp from there (unless I'm missing something).
Any Samsung owners have an idea why the DHW is heating hotter than the set temperature?
@bami it may be to do with the position of the temperature sensor in the tank. If it’s half way down the top of the tank will be hotter than the set temperature due to stratification.
If so do you can drop the temperature further and still have plenty of hot water
although I’ve just noticed the image but it could still be a sensor position issue as hot water will rise even after the heat pump has stopped heating for a time especially if the coil is low down in the tank.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bami lol. I could be wrong 😆
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bami I feel pretty safe then 😁. As a matter of interest where abouts is the coil and the sensor ?
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bami is there a cylinder schematic? Failing that a make and model might be enough to look up.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody The tank is a Kodiak Joule Smart Pre Plumb. Can find no mention of temp sensor anywhere online or in the installation manual. I did find this photo of the coil placement on the Joule.ie website.
@bami check the field setting values #3031 to 3033 for the booster heater (immersion) operation.
#3031 turns it on/off (I have mine set to NOT USE), #3032 sets the delay before it becomes active on a DHW cycle (if you do use it, set this high so the ASHP has sufficient time to try to reach the DHW set point temperature alone), and #3033 sets the overshoot temp (max 4C). This last setting (assuming #3031 is set to use) will allow the DHW tank set point temperature to overshoot by 4C which is what could be happening in your case?
So if #3031 is set to USE, and the delay time in #3032 is short, the immersion will kick in and help the ASHP to achieve the DHW set point temp, and then allow an overshoot of up to 4C as set in #3033.
If this is the issue, setting #3031 to NOT USE should fix it.
Posted by: @bamiFollowing excellent advice on here I've now set a schedule for the DHW to come on for 2 hours in the afternoon and reduced the water temp to 43C. But the DHW still seemed to be way too hot.
2 hours is far too long, and again could be contributing to this issue. It only needs to be long enough to reheat the DHW tank to the set point. Mine typically does this in around 30mins, so I schedule my DHW reheat to start every day at 2pm and schedule it to turn off again after 45mins, as once it's done, I know it's done until tomorrow. Keep an eye on it for a couple days to get a feel for how long it may reasonably take, and then add a bit for good measure just in case the tank is colder than usual.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@bami old scientist has a good call there. I don’t use my Samsung to heat DHW as I have a Mixergy tank so aren’t familiar with the settings.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@old_scientist Thank you so much for this info 🙏🏻 I'm still in the very early stages of getting to grips with it all.
The booster is set to Use and the delay time is 75 mins. Overshoot is 0C.
I've decreased the time the tank heats on the schedule down to 60 mins and will see how that goes. This time is below the delay time of 75 mins for the booster anyway, so the booster even while on shouldn't affect anything. As the overshoot is set to 0C that can't be responsible for heating the water higher than the set point.
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 74 Online
- 5,662 Members
Podcast Picks
Latest Posts
-
@bontwoody me too. I've contacted Heat Geek today, and ...
By Mars , 1 hour ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 2 hours ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 16 hours ago
-
RE: Does anyone have experience of a smart water meter?
Yes, I was aware the “smart” part is the same tech used...
By Majordennisbloodnok , 16 hours ago
-
RE: Mitsu Wireless Controller and MelCloud
Well it has now become obvious that the installation of...
By DavidAlgarve , 1 day ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@heat-pump-newbie as I suspected. I measure/monitor my ...
By Old_Scientist , 2 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 3 days ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 3 days ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 4 days ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 4 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 5 days ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 6 days ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 6 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 6 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 1 week ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 1 week ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 1 week ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 1 week ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 1 week ago