DHW temp Samsung AE120RXYDEG 12kw ASHP with Gen 6 controller
Had my Samsung ASHP installed start November. They left the DHW temp at 50C and set to go on and off all the time to keep the water at 50C. The tank is huge, I live alone and only use hot water for a shower in the evening so this seemed uneconomical to me.
Following excellent advice on here I've now set a schedule for the DHW to come on for 2 hours in the afternoon and reduced the water temp to 43C. But the DHW still seemed to be way too hot.
I had a look when the DWH was on today and as you can see the set temp is for 43C but the actual temp is over 47C. It still seems to be wanting to heat to 50C it seems to me.
I've looked in the field values and can see no way to set the DHW temp from there (unless I'm missing something).
Any Samsung owners have an idea why the DHW is heating hotter than the set temperature?
@bami it may be to do with the position of the temperature sensor in the tank. If it’s half way down the top of the tank will be hotter than the set temperature due to stratification.
If so do you can drop the temperature further and still have plenty of hot water
although I’ve just noticed the image but it could still be a sensor position issue as hot water will rise even after the heat pump has stopped heating for a time especially if the coil is low down in the tank.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bami lol. I could be wrong 😆
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bami I feel pretty safe then 😁. As a matter of interest where abouts is the coil and the sensor ?
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bami is there a cylinder schematic? Failing that a make and model might be enough to look up.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody The tank is a Kodiak Joule Smart Pre Plumb. Can find no mention of temp sensor anywhere online or in the installation manual. I did find this photo of the coil placement on the Joule.ie website.
@bami check the field setting values #3031 to 3033 for the booster heater (immersion) operation.
#3031 turns it on/off (I have mine set to NOT USE), #3032 sets the delay before it becomes active on a DHW cycle (if you do use it, set this high so the ASHP has sufficient time to try to reach the DHW set point temperature alone), and #3033 sets the overshoot temp (max 4C). This last setting (assuming #3031 is set to use) will allow the DHW tank set point temperature to overshoot by 4C which is what could be happening in your case?
So if #3031 is set to USE, and the delay time in #3032 is short, the immersion will kick in and help the ASHP to achieve the DHW set point temp, and then allow an overshoot of up to 4C as set in #3033.
If this is the issue, setting #3031 to NOT USE should fix it.
Posted by: @bamiFollowing excellent advice on here I've now set a schedule for the DHW to come on for 2 hours in the afternoon and reduced the water temp to 43C. But the DHW still seemed to be way too hot.
2 hours is far too long, and again could be contributing to this issue. It only needs to be long enough to reheat the DHW tank to the set point. Mine typically does this in around 30mins, so I schedule my DHW reheat to start every day at 2pm and schedule it to turn off again after 45mins, as once it's done, I know it's done until tomorrow. Keep an eye on it for a couple days to get a feel for how long it may reasonably take, and then add a bit for good measure just in case the tank is colder than usual.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@bami old scientist has a good call there. I don’t use my Samsung to heat DHW as I have a Mixergy tank so aren’t familiar with the settings.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@old_scientist Thank you so much for this info 🙏🏻 I'm still in the very early stages of getting to grips with it all.
The booster is set to Use and the delay time is 75 mins. Overshoot is 0C.
I've decreased the time the tank heats on the schedule down to 60 mins and will see how that goes. This time is below the delay time of 75 mins for the booster anyway, so the booster even while on shouldn't affect anything. As the overshoot is set to 0C that can't be responsible for heating the water higher than the set point.
- 26 Forums
- 2,323 Topics
- 52.1 K Posts
- 465 Online
- 5,979 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Configuring third party dongle for Ecodan local control
Thanks, @sheriff-fatman. Happy for you to search any po...
By Majordennisbloodnok , 4 minutes ago
-
RE: Electricity price predictions
There is a difference between no longer pursuing Net Ze...
By Transparent , 10 minutes ago
-
Thanks, @cathoderay. I was aware of some changes to ...
By Majordennisbloodnok , 18 minutes ago
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
Sorry but I dont know. There must be something causing...
By JamesPa , 2 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
Are you comparing like for like with similar outside ai...
By Sheriff Fatman , 3 hours ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
It's buried within what has become my ongoing post-inst...
By Sheriff Fatman , 5 hours ago
-
RE: Trying to understand my Nibe F1245
@greenlight Many thanks for the information, it's set m...
By Chris12 , 8 hours ago
-
This is what I answered, I really have no hope: "......
By Batpred , 22 hours ago
-
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@andrewj oh yes they offer Daikin 8kW, they tried to fo...
By AgentGeorge , 24 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@majordennisbloodnok Good point! Just in case anyone re...
By Batpred , 24 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Owners
@sim0n0 It would be very useful if you could tell us...
By trebor12345 , 1 day ago
-
RE: Benefits of an extra horizontal loop for GSHP
A correct sized collector is all you need. Saying this,...
By greenlight , 1 day ago
-
RE: Grant Aerona Short Cycling
@mikefl, thanks for sharing your operating data, very i...
By Steam Powered , 1 day ago
-
-
RE: Here is my heat pump installation with questionable COP in Italy
@jamespa Sorry for the late reply, I apologize for the ...
By materox345 , 1 day ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
@editor Yes BUT that was 3 years ago installed in Janua...
By rob heatpump bob , 2 days ago
-
Thanks for your response. I have UFH downstairs and ...
By GeorgeA , 2 days ago
-
RE: Home energy storage & battery register
2 days uninterruptible power supply (at the moment) wit...
By Batpred , 2 days ago