@bontwoody scop of 3.2 is certainly achievable, but not very easily on a retrofit unless you design for 45 degree flow, maximum. With octopus (for example) designing for 50 (nothing wrong with that), I expect we’ll see quite a few systems running at 3-3.5 ish.
It isn’t as clear cut as it seems…. And yes I probably was generalising massively with my statement.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@bontwoody Togfather, my Daikin is basically based on WC as seen by the Homely controller; here is a graph of OAT for the last week working at 22.5 degrees C throughout the whole house. (Yes, we like it warm) with a COP of 2.64; the temperature has ranged from 6 degrees to -4 degrees during this time. When we have perhaps 6 -8 degrees, the COP is over 4. Regards, Toodles.
Toodles, 76 years young and hoping to see 100 and make some ROI on my renewable energy investment!
@togfather so unfortunately we have heard a lot of cases of Eco4 installs using several methods that are bad practice for ASHP installation, all at the same time.
can see a flow rate of 10 l/min in your pictures. That could be part of the problem as thats way too low to move 11kw, at the DeltaT (DT means difference in temperatures between warm to the radiators and cold coming back) needed by a heat pump system (DT5). 10 litres a minute only moves 11kw if the DT is 15. DT15 is not going to work on a heat pump. So the effect is that if the DT stays at 5, you're only moving 3.5kw, which is almost certainly not enough to heat your house in freezing weather, which is (at least partly) why you're cold.
So you need to get the flow rate up: Can you post photos of your system, what circulation pumps do you have and what setting are they on?
the fact your're only moving 3.5kw and its still costing you loads suggests as others have said that a backup resistance heater (basically a 3kw immersion built into the heatpump as a BACKUP - not for permanent use) may be running all the time
@ other daikin users on here - can someone please advise the OP of config parameters for WC, and how to check if the resistance backup heater is running and configure it not to?
do you have TRV's on your radiators? If yes, please open them all up to 5 , or remove them. you also mentioned multiple zones - please make sure both zones are always on - are they controlled by the external stats? if so, set that stat higher than the current temperature. But those can wait as I think the flow rate and backup heater (see above) are the first priority.
Do you understand what weather compensation is? This controls the setpoint for the water in your heating system according to how cold it is. The colder it is outside, the warmer the heating water, and vice versa. This is absolutely essential for an efficient system. It appear your system is not configured in this mode.
can you just get your installer to come back? tell him what you've said here, your house is way too cold, its costing you lots of money - clearly, they haven't set it up properly.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@hughf Ok Hugh, thanks for the explanation. Flow temperature certainly is a big factor. Personally I wouldnt advise anyone to go for 50C flow.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@iancalderbank Good spot on the flow rate Ian!
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Togfather, if you wish to try using Weather Compensation and are unsure of how to start, may I suggest that you tap the left hand button dial on the MMI and scroll to user profile and tap the button then select ‘Installer’ by tapping in the code 5678 - this should then give you access to all the settings menus? You should now be able to scroll to Main Zone, select, then scroll down to Weather Dependant, select, then you will have the ‘curve’ displayed ready to set. Adam from Heat Geek made a You Tube presentation about setting up WC which I’ll go away and find and post the link shortly. Regards, Toodles.
Toodles, 76 years young and hoping to see 100 and make some ROI on my renewable energy investment!
Togfather, I have the Heat Geek link for you:
I mentioned using the user profile setting of installer as I can’t recall how much access the default setting access allows on each menu; I don’t wish to alter any settings on mine as Homely might smack my wrists for interfering! 😉 Have Fun and I hope this warms you up and lowers your bills!
Toodles, 76 years young and hoping to see 100 and make some ROI on my renewable energy investment!
@iancalderbank I did complain and got the installer back, together with a Daikin sales engineer. They both said that I should not use the WC setpoint sytem, as it would cost me more money. They also said the system wasa set up correctly, with no mention of a backup heater.
Both were very courteous and friendly, but I am sceptical because the installer is giving Daikin a lot of ECO4 business, who therefore has no motive to be impartial or in favour of me.
So, I now have two questions.
Should I turn of the backup heater, and if so, how do I do that?
What settings should I use for the WC setpoint to experiment?
Best wishes. Tog 🙂
@togfather Togfather, the settings as advised by Adam Heat Geek will be a good starting point - you can tweak them later if required. I know nothing of the 3 kW heater settings as my pump doesn’t have one but I suspect it is within the Installer Settings for which you will need the user profile - code 5678 to access. When you enter the installer settings area, you will find many options and there should be one for back up heater (or some such name) did your installer leave you with a manual for the Daikin? This is fairly heavy going in places but is detailed and may assist in the settings. Regards, Toodles.
Toodles, 76 years young and hoping to see 100 and make some ROI on my renewable energy investment!
@togfather Go and check whether the back up heater is running. See attached pictures. You need to go to the actuators menu.
@togfather They said using Weather Compensation would cost you more money to run? This just gets better! 😆 I am gobsmacked by what these installers seem to get away with.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
-
Daikin COP / energy used measurement from MMI
1 month ago
-
Do I need a bigger volumizer: 8kW Daikin Altherma R32 LT split
2 months ago
-
Dedicated heat meter and HP heat meter discrepency
1 year ago
-
Daikin Altherma LT R32 - poor SCOP and breaking heat exchangers!
1 year ago
-
Heating Turned Off but Radiators Still Warm
1 year ago
- 25 Forums
- 1,439 Topics
- 30.2 K Posts
- 28 Online
- 1,225 Members
Join Us!
Latest Posts
-
RE: Incorrect Billing of Customers with a Smart Meter
It seems someone else stumbled upon the same issue earl...
By KoRWraith , 9 hours ago
-
Share Your Experiences with Heat Pump Manufacturer Support
Have you ever reached out to your air source heat pump ...
By Mars , 10 hours ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
@ivanopinion Octopus have told me they will have a Cosy...
By Davesoa , 17 hours ago
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
@ant87 thanks for that.
By David999 , 17 hours ago
-
RE: No-code, plug-and-play monitoring for your heat pump
But if you compare what was predicted with what happene...
By Majordennisbloodnok , 18 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
I might change my mind again, but I'm currently unlikel...
By IvanOpinion , 22 hours ago
-
RE: Samsung ASHP scheduling help
@elgreco69 worth reading the GitHub here as that will a...
By morh , 1 day ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@toodles Thanks for the explanation I get it now as I h...
By Jancold , 1 day ago
-
RE: Questions about yearly heat pump maintenance
For the installer, I believe servicing and maintenance ...
By Majordennisbloodnok , 1 day ago
-
RE: Rate the quality of your heat pump design and installation
@retrorich It is very worrying that any of this should ...
By Toodles , 2 days ago
-
RE: Spacing for roof fixing bolts ?
There is another consideration...but alas this doesn't ...
By Transparent , 2 days ago
-
RE: Air source heat pumps and noise
Yes, but when they go wrong things get really sticky. D...
By Majordennisbloodnok , 2 days ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
Hi, Bit of an update. I bought a decibel meter and moni...
By Lokisam , 2 days ago
-
RE: Are You Getting the Most Out of Your Renewable Energy?
As I mentioned, there are going to be some follow-up ar...
By Majordennisbloodnok , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Now, I know that this may be a little simplistic and pe...
By Toodles , 3 days ago
-
-
RE: Save the Energy Save the World using Daikin Altherma 3 operation mode and schedules settings.
Hello Mevl, I won't be able to answer all your question...
By HCas , 3 days ago
-
I have been watching, with interest, the rebuild and re...
By iantelescope , 3 days ago
-
RE: Making best use of Agile with a battery and ASHP
On the subject of automating battery charging schedules...
By jamesw , 3 days ago
-
Safety update; RCBOs supplying inverters or storage batteries
BEAMA have issued a safety update (March 2024) regardin...
By Transparent , 4 days ago
Heat Pump Humour
Latest Topics
-
Share Your Experiences with Heat Pump Manufacturer Support
By Mars 10 hours ago
-
Spacing for roof fixing bolts ?
By heat-pump-newbie 4 days ago
-
ASHP sizing - value of Heat Transfer Coefficient
By jamesw 5 days ago
-
Incorrect Billing of Customers with a Smart Meter
By KoRWraith 1 week ago
-
Home energy storage & battery register
By Mars 1 week ago
-
Meter Readings - What are theses meters telling me?
By Potatoman 1 week ago
-
Have Octopus Energy discovered a way to Narnia?
By Davesoa 1 week ago