Thanks @bridgetjohn. So from those pics I'm fairly certain you've got a non-Daikin thermostat which is controlling the operation. You have a fixed leaving water temperature (ie the radiator water) of 60 deg C. That looks to me like a classic case of it being set up like a gas boiler !!Â
With Derek's invaluable help I've set mine up like a heat pump - so my radiator water varies with the outside temp. It was 12 deg C when I took these pics and the system set the radiator water at 29 deg. The pump ran on tick-over all day long and kept the house at a steady 21/22 deg. All was silent ! As the outside cools the system will increase the radiator water temp. @Derek-m will advise some numbers...
Incidentally your leaving water hadn't reached 60 deg, which is a push (possibly even impossible!) for your heat pump. The little blue arrowhead on the circle indicates where 60 would be and the end of the blue curve indicates what the temperature actually is.Â
@heat-pump-newbie thank you. You are right - we have a honeywell thermostat control which is clicking it on and off as the heat drops / increases.
And yes it seems to want to "fire up" like a gas boiler - blast round the pipes and make a noise and then settle down.
Posted by: @bridgetjohn@heat-pump-newbie thank you. You are right - we have a honeywell thermostat control which is clicking it on and off as the heat drops / increases.
And yes it seems to want to "fire up" like a gas boiler - blast round the pipes and make a noise and then settle down.
Hi Bridget,
Thanks to Newbie's guidance you have discovered that your system has been set with a fixed water flow temperature setting of 60C, which is about the worst possible setting that could have been made. 😡Â
I would strongly recommend that you change your system to weather dependent (WD) control, with the following initial settings water flow temperature (WFT) 45C at outdoor air temperature of -5C and WFT of 20C at outdoor air temperature of 18C.
Newbie, would you be kind enough to guide Bridget through the adjustment process. 😎Â
As the name suggests I am new to this but here goes:
Go to Main > Setpoint mode > and left dial to highlight in blue 'WD heating fixed cooling' Press left dial to select.
**Derek - my system's not set up for cooling so is different here **
Then dial down to highlight 'Heating WD curve', press to select. Can you take a photo of that and post it here please !! Then we'll see what's next... I'm assuming there will be a default curve already there??
Posted by: @heat-pump-newbieAs the name suggests I am new to this but here goes:
Go to Main > Setpoint mode > and left dial to highlight in blue 'WD heating fixed cooling' Press left dial to select.
**Derek - my system's not set up for cooling so is different here **
Then dial down to highlight 'Heating WD curve', press to select. Can you take a photo of that and post it here please !! Then we'll see what's next... I'm assuming there will be a default curve already there??
Hi Newbie,
Thank you for helping. Because I don't have access to a Daikin controller and the manual is not that clear, I thought that you would be of greatest help to Bridget. I hope that you don't mind.
As far as cooling is concerned, you don't really want it to operate unless you have fan coil units within your system. Passing cold water through radiators will probably lead to puddles of water on the floor.
Posted by: @heat-pump-newbiemaybe its shouldn't be set up with that option ?
Hi Newbie,
If it is possible I would suggest disabling the cooling option. If not then set the parameters such that it will never operate.
Maybe then @bridgetjohn keep scrolling on the Setpoint Mode screen and select Weather Dependant if that is an option..
@derek-m actually this description from Daikin says it's heating only ! Not sure the commissioning procedure was followed very well !Â
From reading the various manuals it would appear that the operation of the controllers is fairly standard, though some settings may be excluded if the necessary equipment has not been installed.
If you could explain to Bridget, step by step, how you set up weather compensation on your system that would be very useful.
Bridget, make a note of the parameter settings prior to making any changes, so that you can always reverse any changes.
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 25 Online
- 5,662 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Powerwall 3 or Myenergi or something else?
We have a Tesla Powerwall 3, recently installed, so I m...
By Old_Scientist , 1 hour ago
-
@majordennisbloodnok The drying out of air shouldn't ha...
By dgclimatecontrol , 1 hour ago
-
RE: Does anyone have experience of a smart water meter?
Thanks, @technogeek. So far as I can make out, whilst...
By Majordennisbloodnok , 22 hours ago
-
RE: Mitsubishi PAR-WT60R-E Wireless Controller installation
@morgan They have been paired once but it was thought b...
By DavidAlgarve , 24 hours ago
-
RE: Isolating the system for a planned power cut
A great many ground-mounted local substation transforme...
By Transparent , 24 hours ago
-
@bontwoody From what I’ve learned the hard way: 1) T...
By DREI , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 2 days ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 2 days ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 3 days ago
-
RE: Mitsu Wireless Controller and MelCloud
Well it has now become obvious that the installation of...
By DavidAlgarve , 3 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 5 days ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 5 days ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 6 days ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 6 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 1 week ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 1 week ago
-
RE: How much am I ‘saving’?
@old_scientist like for like comparisons are almost imp...
By Tim441 , 1 week ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 1 week ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 1 week ago