Daikin Altherma 3M in Buckinghamshire - Snoring Noise
@bridgetjohn Do you mean single- pipe like the link: https://www.buildingservicesindex.co.uk/entry/136545/AEL-Heating-Solutions-Ltd/Single-or-two-pipe-central-heating-system/
Like that?
@cycleneil Hi, yes, that's what I understand. Ours is apparently single pipe and that is what is potentially causing the rushing water noise in the towel rail which links directly off the pipes in the airing cupboard before they disappear into the floorboards and service the rest of the radiators.
@bridgetjohn Oh dear. I’m surprised that the installer didn’t convert to a 2-pipe system as a routine measure, the 1-pipe systems date back to the early days of central heating and never really worked well even then.
Installer has proposed
"We have discussed your system and feel it would help if we separated the heat pump from the existing system by reconfiguring the buffer vessel to a low loss header and installing a secondary pump to the heating system. This will mean we can control the pump speed around the existing system which should in turn reduce the noise issues. "
Any thoughts?
also see above about suspected Single Pipe system. The house was built in the 70's and extended late 70's.
Thanks in advance.
@bridgetjohn that is the solution I have - see Worcestershire ASHP.
The purests would say this adds complexity and reduces efficiency. Which is probably true. Ideally you’d change radiators and reduce flow temperature.
I’m getting SCOP of 3.3 controlled via a Nest. I will change to weather compensation from end of April (after 1year ownership) to compare and hopefully improve SCOP. And my bungalow is warm with no radiator changes
Daikin Altherma 3H HT 12kWh ASHP with Mixergy h/w cylinder; 4kW solar PV with Solic 200 electric diverter; Honda e and Volvo EX30 Ultra Twin Performance electric vehicles with Myenergi Zappi mk1 & Ohme chargers
Update on this. The bathroom towel rail plumbing was re-routed so that stopped that noise. The low loss header added and that reduced the flow noise in the airing cupboard.
apparently if we want to add underfloor heating downstairs we’d have had to do that anyway?
we’ve also added a bit of soundproof board to the adjacent bedroom wall but don’t know if that works yet as heating is off for summer.
just left with very large electricity bill for the two months when first installed with faulty PCB board so we had to use Booster all the time and run on leaving water temp thermostat. Really bad that Daikin supplied faulty kit and didn’t compensate us for the consequences. It’d be like buying a faulty car and getting a huge fuel bill because it was running inefficiency and then refusing to rectify it or compensate.
I don't know if this helps, but you can change the pump limitation parameter to restrict the top end pump speed. It's in Installer Settings, so you'll need to change the user profile to Installer. From there, it's under Installer Settings > Field settings table > 9-0D. Change the value from whatever it is (probably 0) to 4. This will cause the pump speed to run at a maximum of 21lpm on start up. I found the default 30lpm much too loud and found no downsides to dropping this to 21lpm (which is 60%). Since my radiators were happily warm enough at the reduced 11lpm after initial 20 minutes or so, I was fairly sure it'd be fine at 21lpm as well. Sure enough, all rads warm up nicely and maintain their heat. Virtually silent running now.
It's all in the Installer Reference Guide.
- 26 Forums
- 2,391 Topics
- 54.2 K Posts
- 361 Online
- 6,074 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Recommended home battery inverters + regulatory matters - help requested
Both inverters would be limited by the max 16A export t...
By Batpred , 44 minutes ago
-
RE: New Fogstar 15.5kWh upright solution
Of course it is not helpful to frogstar fan club member...
By Batpred , 58 minutes ago
-
RE: Ecodan with FTC7 - True Weather Compensation
@danwright90 I've linked two videos below recorded this...
By Sheriff Fatman , 2 hours ago
-
@steelbadger, I’ve pretty much decided now that there’s...
By Majordennisbloodnok , 2 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
That makes plenty of sense. Perhaps more importantly, O...
By Majordennisbloodnok , 4 hours ago
-
RE: Heat pump not reaching flow temperature
That doesn't make much sense as it should alter the flo...
By JamesPa , 5 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@downfield Likewise we are also retired and want a warm...
By Wally , 6 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
It does but it almost all applies to boiler systems and...
By JamesPa , 7 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
So theres a problem for starters. This means that the ...
By JamesPa , 7 hours ago
-
Daikin Atherma ASHP Cycling 6 Times an Hour?
I have a Daikin Atherma EDLQ07CAV unit and I've come he...
By John Marshall , 9 hours ago
-
RE: Gen 6 Samsung ASHP losing 20C of DHW in 60 min directly after generation
Shouldn’t your temp sensor be in the middle or lowest s...
By EcoBaker , 23 hours ago
-
RE: Insulating a pitched roof with kingspan, has anyone done it?
Thank you everyone for all of the information, it looks...
By TRBob , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@transparent Yep, they didn’t even mention it. When ...
By Papahuhu , 1 day ago
-
Air source heat pump circuit not operational
Hi - need some advice about one circuit on my heating s...
By Plummersknowe , 1 day ago
-
RE: Setback savings - fact or fiction?
They are lovely, and I feel lucky to live in one, but t...
By cathodeRay , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
Worth adding that, for this tariff, the Octopus app has...
By Batpred , 1 day ago
-
RE: APP for remote Daikin ASHP Operation
Thanks, @newhouse87. Understood. I was only asking on...
By Majordennisbloodnok , 1 day ago
-
@mike-patrick A propos, I think my heat pump generates ...
By dr_dongle , 1 day ago
-
RE: Mitsu Zubadan flow temperature issue
Update: The flow temperature has now stabilized at 60C ...
By bontwoody , 1 day ago