Daikin Altherma 3 Steady State Operation
New Heat Pump Owner and First Post on the Forum
We had a heat pump installed in September by Octopus Energy. The initial operating settings didn't meet our requirements and I have adjusted the WD curve and changed the control from the Madoka unit, to LWT - WD
The WD curve I have selected is set at:
2 Point Curve
40C Max @ -8C OAT
25C Min @ 15C OAT
Because the Daikin OneEcta app doesn't really show when space heating or water is actually being called for and because I thought it could be useful to indicate and confirm consumption of the new system, I decided to install a Shelley EM and add it into my Home Assistant instance.
I have added an Image of the data screenshot for a 24 Hr Period and also a 2 Hr period, just to give a bit more detail. It isn't quite the sort of operation from the heat pump that I was expecting and I would appreciate any feedback and comments.
I can confirm that the water pump operates for 4 minute cycles with 4 minutes rest until I presume the temperature being sampled drops to the required level it is looking for, whereby it then applies heat for another variable amount of time, again I presume until the water returned reaches another expected threshold temperature and the signal to turn off the heat is applied?
I was expecting something that showed a modulation up and down, not this On / Off display.
Thanks in advance.
Apprentice Retiree
With my limited vision, I may be missing the finer details of your graphs but the ‘timings’ look very ‘mechanical’ as though despite your needs, the pump has a setting based on time rather than needs. I too have a Daikin with the MMI and the Onecta app is of little merit or use to me other than to report an approximation of consumption. Homely presides over the operation of my system so is not a direct comparison by any means but I am attaching a graph from the last 24 hours indicating OAT, IAT and pump cycles in case this is of any assistance. If you look at the list of available data and you notice any that you would like me to include, please ask. I tried to reduce the amount of values on any one chart for clarity - it looks rather busy otherwise!
Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles Thanks for the reply and data. Mine does look very mechanical. I found a setting in the MMI for the Pump and it was as I thought set to "Sampling". I changed this at 14:00 to "Continuous" and have added an extra screenshot below. It has flattened out the sampling cycles between the calls for heat and made it a little easier to see how the heat pulses have variable times of duration. My system is based purely on outside temperature and I presume this is what is affecting the pulse width. I have plans to add external temperature measurement and also flow and return temperature measurement. I just need a little time to get up in to the loft to add the sensors.
My main concern was to try to establish that the Heat pump is working correctly and as the manufacturers, intended. I think I have read that the pump is set to sampling to save costs. I will leave it on continuous for 24 hours to evaluate what happens.
I was very interested in Mars's video regarding heat pump monitoring, with Homely and the other contributors.
Could I take you up on your offer to supply another graph?
Could it include: Inside Temperature, Outside Temperature and Estimated Power Input. (My Shelley device is just a current clamp with mains voltage sensing so it may help me to understand a little better.
Is the Homely device connected to your heat pump via an interface, which it can then access all the heat pump data in real time and adjust the settings of the heat pump to maximise comfort and minimise costs, based on your energy suppliers tariff?
Regards, pj_preston
Apprentice Retiree
@pj_preston The Homely smart controller is connected to the Daikin via the MMI and uses Modbus (they use a D.comm unit to accomplish this). If you read my review on RHH, it describes the control it provides but basically it takes over from the WC settings, compares temperatures OAT and IAT, monitors losses, weather, solar gain etc. and ‘micromanages’ the whole system. From installation, it takes a week or so to ‘learn’ your system and your needs then just gets on with the job. Regards, Toodles (graph as requested attached).
Toodles, he heats his home with cold draughts and cooks his food with magnets.
- 22 Forums
- 2,037 Topics
- 44.4 K Posts
- 33 Online
- 3,250 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
This is where the cold water storage tank was situated;...
By Dwynwen , 7 hours ago
-
RE: Help with understanding my Mitsubishi Ecodan air source heat pump
@majordennisbloodnok, the same thought occurred to me, ...
By Morgan , 7 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
I agree with @mars. My install was not dissimilar. ...
By JamesPa , 7 hours ago
-
RE: Air Source Heat Pump - Side Alley Suitability
Thats probably fair enough. The degree-days calculatio...
By JamesPa , 8 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
That’s interesting, but obviously concerning also…. Do ...
By SUNandAIR , 24 hours ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
Thank you @robs - that very useful data. The issue wa...
By Transparent , 1 day ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
@trebor12345 The Auto function is supposed to adapt au...
By Heatgeek , 2 days ago
-
RE: The Great British Heat Pump Quiz
@allyfish thanks for the feedback and glad it was fun! ...
By Mars , 2 days ago
-
RE: help sizing rads based on room by room heat loss
If its 1988W at DT 50, which is how most radiators are ...
By JamesPa , 2 days ago
-
RE: Career change – entering the world of heating and heat pumps
@editor Mars, thank you. That's along the routes I was ...
By Lakey , 2 days ago
-
@editor thanks Mars, it's a rare occasion I'm looking f...
By big_si , 3 days ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
@ashp-bobba and @jamespa - thank you both for all your ...
By CBrenewable , 3 days ago
-
-
Win one of five "Heat Pumps 101" Courses
Heat pumps are gaining traction in the UK, but between ...
By Mars , 3 days ago
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 4 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 4 days ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 4 days ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 4 days ago