Daikin Altherma 3 Steady State Operation
New Heat Pump Owner and First Post on the Forum
We had a heat pump installed in September by Octopus Energy. The initial operating settings didn't meet our requirements and I have adjusted the WD curve and changed the control from the Madoka unit, to LWT - WD
The WD curve I have selected is set at:
2 Point Curve
40C Max @ -8C OAT
25C Min @ 15C OAT
Because the Daikin OneEcta app doesn't really show when space heating or water is actually being called for and because I thought it could be useful to indicate and confirm consumption of the new system, I decided to install a Shelley EM and add it into my Home Assistant instance.
I have added an Image of the data screenshot for a 24 Hr Period and also a 2 Hr period, just to give a bit more detail. It isn't quite the sort of operation from the heat pump that I was expecting and I would appreciate any feedback and comments.
I can confirm that the water pump operates for 4 minute cycles with 4 minutes rest until I presume the temperature being sampled drops to the required level it is looking for, whereby it then applies heat for another variable amount of time, again I presume until the water returned reaches another expected threshold temperature and the signal to turn off the heat is applied?
I was expecting something that showed a modulation up and down, not this On / Off display.
Thanks in advance.
Apprentice Retiree
With my limited vision, I may be missing the finer details of your graphs but the ‘timings’ look very ‘mechanical’ as though despite your needs, the pump has a setting based on time rather than needs. I too have a Daikin with the MMI and the Onecta app is of little merit or use to me other than to report an approximation of consumption. Homely presides over the operation of my system so is not a direct comparison by any means but I am attaching a graph from the last 24 hours indicating OAT, IAT and pump cycles in case this is of any assistance. If you look at the list of available data and you notice any that you would like me to include, please ask. I tried to reduce the amount of values on any one chart for clarity - it looks rather busy otherwise!
Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles Thanks for the reply and data. Mine does look very mechanical. I found a setting in the MMI for the Pump and it was as I thought set to "Sampling". I changed this at 14:00 to "Continuous" and have added an extra screenshot below. It has flattened out the sampling cycles between the calls for heat and made it a little easier to see how the heat pulses have variable times of duration. My system is based purely on outside temperature and I presume this is what is affecting the pulse width. I have plans to add external temperature measurement and also flow and return temperature measurement. I just need a little time to get up in to the loft to add the sensors.
My main concern was to try to establish that the Heat pump is working correctly and as the manufacturers, intended. I think I have read that the pump is set to sampling to save costs. I will leave it on continuous for 24 hours to evaluate what happens.
I was very interested in Mars's video regarding heat pump monitoring, with Homely and the other contributors.
Could I take you up on your offer to supply another graph?
Could it include: Inside Temperature, Outside Temperature and Estimated Power Input. (My Shelley device is just a current clamp with mains voltage sensing so it may help me to understand a little better.
Is the Homely device connected to your heat pump via an interface, which it can then access all the heat pump data in real time and adjust the settings of the heat pump to maximise comfort and minimise costs, based on your energy suppliers tariff?
Regards, pj_preston
Apprentice Retiree
@pj_preston The Homely smart controller is connected to the Daikin via the MMI and uses Modbus (they use a D.comm unit to accomplish this). If you read my review on RHH, it describes the control it provides but basically it takes over from the WC settings, compares temperatures OAT and IAT, monitors losses, weather, solar gain etc. and ‘micromanages’ the whole system. From installation, it takes a week or so to ‘learn’ your system and your needs then just gets on with the job. Regards, Toodles (graph as requested attached).
Toodles, he heats his home with cold draughts and cooks his food with magnets.
- 22 Forums
- 2,058 Topics
- 44.9 K Posts
- 37 Online
- 3,309 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
Nah. Not really you're not - I can see right through yo...
By Majordennisbloodnok , 10 minutes ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@heatgeek this is for an additional buffer vessel, used...
By Damon Blakemore , 15 minutes ago
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
This is indeed welcome news. In addition the new legi...
By JamesPa , 7 hours ago
-
RE: Is your heat pump insured?
@benson fairly typical of some insurers.
By KevinPotts , 18 hours ago
-
RE: Rate the quality of your heat pump design and installation
Yes the HP is running weather compensation and I’ve lef...
By Davesoa , 1 day ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
OK, so when the HP comes on it becomes obvious.It's on ...
By tdudgeon , 2 days ago
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
@johnmo I think we’ve been trudging through the same...
By SUNandAIR , 2 days ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 3 days ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 3 days ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 3 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 3 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 4 days ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Hopefully iv done the right thing today by signing up t...
By Westkent , 4 days ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 4 days ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 4 days ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
The useful bit is the bit that specifies the heat loss ...
By JamesPa , 4 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 4 days ago
-
@editor thanks Mars that’s the same table I found in th...
By Gary , 5 days ago
-
RE: Tariff and charging strategy advice please
They haven't asked me to prove that I have an EV (I do)...
By JamesPa , 5 days ago