Controversial opinions - pure weather compensation, buffer tank, heat loss, oversized heat pumps
Posted by: @transparentThat's it!
Emitters on a roll.
Now why didn't I think of that? 😜
Available (and indeed standard) in Italy I am told (by an Italian). Radiators are assembled onsite from small, standard, sections that plug together (and presumably seal!) into the length required.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa It is all about design choices. In my view heating at extreme low end temperatures is a small minority of overall heating which might not even occur some years. I choice to match a more efficient, smaller heat pump to 15C OAT to eliminate cycling and provide a wood-burner in the lounge coupled with a thermostat. At low temperatures, the wood-burner would be activated and the large lounge load from HP would be switched off by the thermostat, allowing the HP to concentrate its heat on the rest of the house.
The major mistake I made is mixing radiators in bedrooms with UFH which complicates things enormously. In hindsight I should have implemented UFH throughout regardless, whereby WC would be a breeze. There is still the problem at low temperatures due to HP modulation range but I solved that one. I am a believer in designing from the 15C OAT end. I also believe in 2 heat pumps, one for UFH and one for DHW.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
Posted by: @jamespaIm cant see why two compressors in the same heat pump falls foul of the rules.
Because there isn't one on the MCS Approved list.
This list can be bizarre and overly pedantic at times.
For example, installations of rooftop PV panels must use 65mm screws to attach the brackets to rafters.
I fell foul of that because there's 50mm of insulation and a 22mm counter-batten on top of my rafters!
When I handed the installer a box of 140mm stainless steel screws, he said that was 'non-compliant'.
We arrived at a compromise which allowed him to produce the MCS certification...
... and you'll appreciate why I won't explain more here on an open forum 😉
I like the idea of a double-compressor heat pump.
But as I'm based not far from the workshops where Newcomen and Trevithick pioneered Cornish steam-engine designs, I favour a more innovative approach.
There should be two impellers on the same shaft, whereby the energy still remaining from the first stage can be fed to the second.
Ie, this mirrors the compound engine, whereby dual pressure expansion cylinders greatly increased the efficiency of early steam engines.
Save energy... recycle electrons!
Posted by: @heatgeek@jamespa It is all about design choices. In my view heating at extreme low end temperatures is a small minority of overall heating which might not even occur some years. I choice to match a more efficient, smaller heat pump to 15C OAT to eliminate cycling and provide a wood-burner in the lounge coupled with a thermostat. At low temperatures, the wood-burner would be activated and the large lounge load from HP would be switched off by the thermostat, allowing the HP to concentrate its heat on the rest of the house.
As it happens I wouldn't disagree, but if it can in fact eliminate cycling then it wont meet the requirements of the BUS grant to be capable of heating the house 100%, at least not with a 3:1 modulation ratio.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I agree. That is where the design choices come in. You have to design within the constraints imposed on you, realistic or not.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
Posted by: @transparentPosted by: @jamespaIm cant see why two compressors in the same heat pump falls foul of the rules.
Because there isn't one on the MCS Approved list.
There is, the Mitsubishi R290 8kW has a 6kW inverter and a 2kW fixed in the outside unit. The 2kW is only used when more output than the 6kW can produce is needed. As a result it can modulate to less that 25% of its badged max output.
Makes a lot of sense to me. I wonder how much adding a second fixed output compressor adds to cost, I would guess very little.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Quoted performance figures @35C flow, -7C OAT = 8.2kW and @25C flow, 15C OAT = 2.1kW. Quite something. Other output models as well.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
Posted by: @heatgeek@jamespa Quoted performance figures @35C flow, -7C OAT = 8.2kW and @25C flow, 15C OAT = 2.1kW. Quite something. Other output models as well.
Nice!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@sunandair This new Ecodan validates your argument about following WC closely for maximum efficiency. You can now set your design flow and radiator size at 15C and turn down the top end accordingly. However, the WC facility is linear which is fine for UFH. It appears that there are no radiator compatible curves. There is a mid-point setting so you can produce a simple triangle. Nevertheless, it will do me fine as it meets the 25% criterion and all-UFH is the only way to go if you are rational. As @jamespa rightly said in my view, if you want air to air heating, use fan coils, not radiators.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 209 Online
- 3,393 Members
Join Us!
Latest Posts
-
RE: Location of hot water isolation valve on cylinder
@transparent Thank you so much and very helpful. Earlie...
By rossowheels , 8 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@toodles Indeed. On a tariff such as IOF where import a...
By Old_Scientist , 8 hours ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
It does indeed look like that, @skyefarmer. There is ...
By Majordennisbloodnok , 15 hours ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 1 day ago
-
@editor @bart Hi, I can see a few problems with your in...
By Brendon Uys , 1 day ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 2 days ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 3 days ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 3 days ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 3 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 3 days ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 4 days ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 4 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 4 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 5 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 5 days ago
Members Online
No online members at the moment