buffer/volumizer cupboard space eater, do i need one?
Posted by: @sunandair@heacol I’ve also herd that a volumiser can help with short cycling.
I wondered if short cycling would be reduced if it was caused by mild outdoor ambient circa 10c and a corresponding low flow temperatures and possibly insufficient radiator capacity at low flow temperatures…. Can you use a volumiser as a replacement for increased radiator capacity to reduce cycling? Eg. Flow temps down to 30c and rad capacity sized for 50c at -3c might not be large enough… as an example.
or is this just a red herring?
As you say, short cycling can occur during milder ambient conditions where the flow temps are reduced and the radiators/emitters then cannot dissipate the heat that is being produced. This causes the return temperature to rise (as the heat cannot be effectively dissipated into the property) thus narrowing the dT between flow and return. When this happens, the heat pump can cycle off to allow the water to cool and maintain a more optimal dT (somewhere in the controller logic the heat pump decides when dT drop below a certain value, the heat pump should cycle off).
Having a volumiser is not going to change the above fundamentals, as unlike a radiator it cannot dissipate heat (it's well insulated so it is reasonable to assume near zero heat loss relative to a radiator or other emitter). Consider it as simply a well lagged fat pipe, so there is more volume of water in the system. It may take longer to reach the initial point of cycling as there is initially more water to heat, so at best it may extent the periods between cycling (so short cycling now becomes longer cycling). Extending this premise, if the system volume were infinitely large, the return temperature would never rise to the point where the dT narrows to cause cycling, so there is a point of diminishing returns and as long as the system volume is large enough, then short cycling shouldn't be an issue. I do not know what this point is, but I have heard recommendations of having a system volume that is 3-4 times the recommended minimum system volume.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
Posted by: @old_scientistWhen this happens, the heat pump can cycle off to allow the water to cool and maintain a more optimal dT (somewhere in the controller logic the heat pump decides when dT drop below a certain value, the heat pump should cycle off).
Not sure this is precisely what happens or how the control loop works. What I observe on plots I have seen (including mine) is that the flow temperature rises above the set point (because the heat pump is putting in more heat than the radiators are emitting). Eventually the flow temperature exceeds the target + allowable hysteresis, at which point the heat pump will shut down. You could in fact restore deltaT by simply slowing down the water pump, but the flow temperature will still rise above the target value because the heat pump is putting in more heat than the radiators are emitting.
Posted by: @old_scientistHaving a volumiser is not going to change the above fundamentals, as unlike a radiator it cannot dissipate heat (it's well insulated so it is reasonable to assume near zero heat loss relative to a radiator or other emitter). Consider it as simply a well lagged fat pipe, so there is more volume of water in the system. It may take longer to reach the initial point of cycling as there is initially more water to heat, so at best it may extent the periods between cycling (so short cycling now becomes longer cycling)
Agreed, particularly with the sentence in brackets. A volumiser changes the period of the cycling but not the on/off ratio.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaNot sure this is precisely what happens or how the control loop works. What I observe on plots I have seen (including mine) is that the flow temperature rises above the set point (because the heat pump is putting in more heat than the radiators are emitting).
Here might be a case in point James.
Here are 2 hourly charts showing flow and return. These are supposed to be operating at fixed flow 34C and 35C respectively. They both have a little burst of temperature before closing down for around 4 minutes. I’ve always assumed this was a deliberate duty cycle function to bridge the shutdown temp drop… but it’s just a guess. There is no thermostat controlling, it’s just fixed flow. The room temp is close to 21 with an ambient of around4C last night and 9C for this afternoons chart
This 24 hour indoor/outdoor temp chart covers both hourly graphs above.
- 26 Forums
- 2,342 Topics
- 53 K Posts
- 294 Online
- 6,000 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
…otherwise known as “hive got news for you”. And don’...
By Majordennisbloodnok , 4 hours ago
-
RE: Configuring third party dongle for Ecodan local control
Logically, I'll fall into that category so the natural ...
By Sheriff Fatman , 5 hours ago
-
RE: Controlling Daikin Altherma via P1P2 and Home Assistant
I haven’t got a Daikin but I have been having some fun ...
By Majordennisbloodnok , 5 hours ago
-
RE: Setback savings - fact or fiction?
@robs — thanks again for your detailed comments. Some r...
By cathodeRay , 7 hours ago
-
RE: Free Ecoheat Heat Pump Install
I don't mind thread drift, it's how conversation natura...
By Deltona , 9 hours ago
-
RE: A Smarter Smart Controller from Homely?
@papahuhu I hope you get a swift resolution. Regards, T...
By Toodles , 11 hours ago
-
RE: Poll for Time of Use, tariffs, technology
That’s fine by me too Major, I feel it is a sad reflect...
By Toodles , 12 hours ago
-
Bingo. Sometimes a judiciously placed size 10 bovver bo...
By Majordennisbloodnok , 13 hours ago
-
RE: Mitsubishi Ecodan 11.2kW heat pump with low COP
@ciocoiu-alexandru I can't provide the same level of di...
By Sheriff Fatman , 13 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Recently had my follow up with octopus for the vibratio...
By swwils , 14 hours ago
-
The three technical issues I'm considering are: BMS...
By Transparent , 15 hours ago
-
RE: LiFePO4 lithium battery fires and explosions
@transparent Your post may fit better in th...
By Batpred , 15 hours ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
@jamespawhite, if you could be bothered, you could also...
By Mars , 17 hours ago
-
RE: Commencing on an ASHP Installation Process
I've got a bit of time to draft something today, so the...
By Sheriff Fatman , 1 day ago
-
RE: Help with heat pump sizing
@amin I dont think materially relative to t...
By JamesPa , 1 day ago
-
@majordennisbloodnok I have decided to take the plunge....
By TechnoGeek , 1 day ago
-
RE: Different dT on each radiator?
I cant sorry. Its based on some calculations I did fro...
By JamesPa , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@simonf thats interesting as I’ve noticed my flow and r...
By AdamK , 3 days ago