Is this a bad installation and is there something wrong with my Samsung heat pump?

360 Posts
15 Users
89 Reactions
18.5 K Views
(@derek-m)
Illustrious Member Member
15282 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4433
 

Posted by: @david999

Also thinking that if the pump initiated a defrost is the room stat shutting the pump down and causing the ice before it defrosts it

I am in the process of compiling a more detail reply, but could you confirm if your heat pump is operating in Weather Compensation (WC) mode or not?

 


   
👍
1
ReplyQuote
(@david999)
Honorable Member Member
1291 kWhs
Joined: 7 months ago
Posts: 282
Topic starter  

@derek-m it was adjusted slightly as far as I’m aware but no idea if it’s activated.  Not sure if this room stat is suitable or if it’s wired like a conventional boiler cycling on and off.


   
ReplyQuote
(@david999)
Honorable Member Member
1291 kWhs
Joined: 7 months ago
Posts: 282
Topic starter  
IMG 2303
IMG 2305
IMG 2304
IMG 2302

   
ReplyQuote
(@david999)
Honorable Member Member
1291 kWhs
Joined: 7 months ago
Posts: 282
Topic starter  

Wiring fairly dodgy as well


   
ReplyQuote
(@derek-m)
Illustrious Member Member
15282 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4433
 

Posted by: @david999

@derek-m mechanical electrical. My good friend has two degrees in pumps and gas turbines but not good on heating systems. 

I read the other post and at the minute my heat pump is cycling because of the room stat and in one position too warm leaving rooms cold and the other way in the cold rooms leaving me too warm.  If it was working like a conventional boiler then it would shut down on the room stat providing it’s positioned in the correct place and cycle on demand.. but I’m hearing that perhaps this shouldn’t happen and the pump should run all the time and confused how I would regulate heat. 

To answer the last question first, the heat pump controller should regulate the Indoor Air Temperature (IAT) using Weather Compensation (WC), which I will explain in more detail later if necessary.

You should have been provided with heat loss calculations for your home, which should detail the room by room heat loss with an Outside Air Temperature (OAT) in the region of -2C or -3C.

To maintain a constant IAT in any given room, it is necessary for the heat emitters to emit the required quantity of thermal energy that will match the heat loss at the present OAT. If the heat loss from a particular room is say 1200W at an IAT of 21C and an OAT of -3C, then for each 1C change in temperature difference between IAT and OAT, the heat loss will change by 50W, so at an OAT of 9C the heat loss will be in the region of 600W.

If the heat emitters are radiators, the quantity of thermal energy that they will emit will primarily be dependent upon the difference between the Average Water Temperature (AWT) within the radiator and the IAT. I always find examples to be of use so consider the following:-

If the above mentioned room has a heat loss of 1200W at an OAT of -3C and contains two radiators with a specified output capacity of 1600W each at the standard DT50, giving a total heating capacity of 3200W, what would be the required AWT to keep the IAT at 21C?

Using the attached spreadsheet it gives an AWT value of 44.51C.

The water coming out of a heat pump, Leaving Water Temperature (LWT), is normally in the region of 5C higher than the water going back to the heat pump, Return Water Temperature (RWT), so the AWT at the radiators would be approximately half way between the two. To produce a AWT of 44.51C would therefore require a LWT of 47C and a RWT of 42C.

By now you are probably thinking what on earth has all this got to do with my heat pump freezing up, some rooms being too warm and others being too cold. A great deal.

I would suggest that you start by obtaining a copy of the relevant installation manual for your system and familiarising yourself with how how to navigate the different menu's within the controller and note the settings of your system, particularly the settings of the WC curve and whether it is enabled or disabled.

Hopefully other Samsung owner's may be able to guide you to the required data.

Once you have established whether your system is in WC mode and its settings then come back with the details.

 


   
👍
2
ReplyQuote
(@david999)
Honorable Member Member
1291 kWhs
Joined: 7 months ago
Posts: 282
Topic starter  

@derek-m there you go.

IMG 2309
IMG 2307
IMG 2308

   
ReplyQuote



(@derek-m)
Illustrious Member Member
15282 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4433
 

@david999

If my understanding is correct your system is operating in WC mode with settings of a LWT of 50C at an OAT of -2C and a LWT of 32C at an OAT of 15C. These values seem reasonable though they may need to be optimised.

I would therefore suggest that at a convenient time you open all the TRV's fully, except for used bedrooms and allow all the room temperatures to stabilise. Any room thermostats should also be set to a temperature of 1C or 2C above the desired value to ensure that the heat pump is operating as much as possible. Also check that the lockshield valves on the radiators are also fully open.

Find out which room has the lowest temperature and if necessary adjust the WC settings to raise or lower the LWT to bring this room temperature to the desired value.

Starting at the warmest room, gradually close the lockshield valves on any radiators to lower the IAT to the desired value. Note, this is not a 5 minute job and could potentially take hours or even days to achieve. Once the temperature in the warmest room has been balanced carryout the same procedure in the next warmest room, and so on and so forth.

Adjusting lockshield valves in one room may affect water flowrates in other rooms so it may be necessary to repeat the balancing process.

Once balancing of the radiators has been accomplished the optimisation of the WC curve can then be completed if necessary.

If after completing the above the heat pump is still suffering severe icing then come back for further help and advice.

 


   
👍
2
ReplyQuote
(@david999)
Honorable Member Member
1291 kWhs
Joined: 7 months ago
Posts: 282
Topic starter  

@derek-m a huge thanks for all the advice, it’s been so helpful and given me quite a lot to think about and some direction.  You guy’s are priceless 👍


   
👍
1
ReplyQuote
Transparent
(@transparent)
Famed Member Moderator
10146 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 1708
 

There's a wider issue we ought to consider @david999 - how do we impart this knowledge into the wider population of GB (incl the professionals who aren't achieving satisfactory installations)?

We're not suffering from a lack of willingness to move towards eco-friendly technologies.
But every inefficient heat-pump installation has long-term negative outcomes on friends, family and work-colleagues who hear about it.

HP InstallsGraph

Dept Energy thinks the significant issue is a lack of MCS approved installers who can apply the £7500 grant under the Boiler Upgrade Scheme.
So they are promoting a 3-day course to transform existing plumbers and electricians into Heat-Pump Installers.
They get £500 off the £700 course-fee and can then self-certify their work within the Building Regulations' Competent Persons Scheme.

Do you have an opinion on that strategy?

 

This post was modified 6 months ago by Transparent

Save energy... recycle electrons!


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
20631 kWhs
Veteran
Joined: 4 years ago
Posts: 2613
 

@david999 could you please post some photos of your plant room where your conrtrols, distribution pumps, valves, etc. are located so we can see the pipework and if there’s any zoning?

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Follow our sustainability journey at My Home Farm:https://kirstenandmars.com


   
ReplyQuote
(@david999)
Honorable Member Member
1291 kWhs
Joined: 7 months ago
Posts: 282
Topic starter  

@editor I wasn’t going to trouble you guys again you have been so kind and felt I was being a nuisance.

i have attached the photos you requested.  I was under the house again really to have a better look at that pipe work as it looks fairly untidy. I noticed no manifolds and feed and return pipes are hard to fathom. I checked in the house to see if there was consistency regarding flow and some feed through the thermostat valves and others through the lock valves. Had it been me I would have fitted manafolds and at least connected all the feeds first so no crossovers. I need to take more photos and try to figure what’s what underneath.  So depressing. The stuff in the plant room is too complicated for me and I think for the installers as well.

IMG 2359
IMG 2361
IMG 2360
IMG 2366
IMG 2364
IMG 2362
IMG 2363
IMG 2365

 


   
👍
1
ReplyQuote
(@guthrie)
Estimable Member Member
631 kWhs
Joined: 11 months ago
Posts: 60
 

That is ridiculous.  So you have the hot water tank, a buffer tank, a red and a white tank and a big white one as well.  For comparison, our installation just has the hot water tank and the small red and white ones, basically for expansion of water and adding more if necessary.  Not to mention the pipes everywhere and do I see two water pumps?

It looks like your Samsung controller is in a cupboard?  I believe you can put them out in the room and use the room temp to control the heat pump, which would be better than leaving it in a cupboard.


   
👍
1
ReplyQuote