Is this a bad installation and is there something wrong with my Samsung heat pump?
Posted by: @david999Also thinking that if the pump initiated a defrost is the room stat shutting the pump down and causing the ice before it defrosts it
I am in the process of compiling a more detail reply, but could you confirm if your heat pump is operating in Weather Compensation (WC) mode or not?
@derek-m it was adjusted slightly as far as I’m aware but no idea if it’s activated. Not sure if this room stat is suitable or if it’s wired like a conventional boiler cycling on and off.
Posted by: @david999@derek-m mechanical electrical. My good friend has two degrees in pumps and gas turbines but not good on heating systems.
I read the other post and at the minute my heat pump is cycling because of the room stat and in one position too warm leaving rooms cold and the other way in the cold rooms leaving me too warm. If it was working like a conventional boiler then it would shut down on the room stat providing it’s positioned in the correct place and cycle on demand.. but I’m hearing that perhaps this shouldn’t happen and the pump should run all the time and confused how I would regulate heat.
To answer the last question first, the heat pump controller should regulate the Indoor Air Temperature (IAT) using Weather Compensation (WC), which I will explain in more detail later if necessary.
You should have been provided with heat loss calculations for your home, which should detail the room by room heat loss with an Outside Air Temperature (OAT) in the region of -2C or -3C.
To maintain a constant IAT in any given room, it is necessary for the heat emitters to emit the required quantity of thermal energy that will match the heat loss at the present OAT. If the heat loss from a particular room is say 1200W at an IAT of 21C and an OAT of -3C, then for each 1C change in temperature difference between IAT and OAT, the heat loss will change by 50W, so at an OAT of 9C the heat loss will be in the region of 600W.
If the heat emitters are radiators, the quantity of thermal energy that they will emit will primarily be dependent upon the difference between the Average Water Temperature (AWT) within the radiator and the IAT. I always find examples to be of use so consider the following:-
If the above mentioned room has a heat loss of 1200W at an OAT of -3C and contains two radiators with a specified output capacity of 1600W each at the standard DT50, giving a total heating capacity of 3200W, what would be the required AWT to keep the IAT at 21C?
Using the attached spreadsheet it gives an AWT value of 44.51C.
The water coming out of a heat pump, Leaving Water Temperature (LWT), is normally in the region of 5C higher than the water going back to the heat pump, Return Water Temperature (RWT), so the AWT at the radiators would be approximately half way between the two. To produce a AWT of 44.51C would therefore require a LWT of 47C and a RWT of 42C.
By now you are probably thinking what on earth has all this got to do with my heat pump freezing up, some rooms being too warm and others being too cold. A great deal.
I would suggest that you start by obtaining a copy of the relevant installation manual for your system and familiarising yourself with how how to navigate the different menu's within the controller and note the settings of your system, particularly the settings of the WC curve and whether it is enabled or disabled.
Hopefully other Samsung owner's may be able to guide you to the required data.
Once you have established whether your system is in WC mode and its settings then come back with the details.
If my understanding is correct your system is operating in WC mode with settings of a LWT of 50C at an OAT of -2C and a LWT of 32C at an OAT of 15C. These values seem reasonable though they may need to be optimised.
I would therefore suggest that at a convenient time you open all the TRV's fully, except for used bedrooms and allow all the room temperatures to stabilise. Any room thermostats should also be set to a temperature of 1C or 2C above the desired value to ensure that the heat pump is operating as much as possible. Also check that the lockshield valves on the radiators are also fully open.
Find out which room has the lowest temperature and if necessary adjust the WC settings to raise or lower the LWT to bring this room temperature to the desired value.
Starting at the warmest room, gradually close the lockshield valves on any radiators to lower the IAT to the desired value. Note, this is not a 5 minute job and could potentially take hours or even days to achieve. Once the temperature in the warmest room has been balanced carryout the same procedure in the next warmest room, and so on and so forth.
Adjusting lockshield valves in one room may affect water flowrates in other rooms so it may be necessary to repeat the balancing process.
Once balancing of the radiators has been accomplished the optimisation of the WC curve can then be completed if necessary.
If after completing the above the heat pump is still suffering severe icing then come back for further help and advice.
There's a wider issue we ought to consider @david999 - how do we impart this knowledge into the wider population of GB (incl the professionals who aren't achieving satisfactory installations)?
We're not suffering from a lack of willingness to move towards eco-friendly technologies.
But every inefficient heat-pump installation has long-term negative outcomes on friends, family and work-colleagues who hear about it.
Dept Energy thinks the significant issue is a lack of MCS approved installers who can apply the £7500 grant under the Boiler Upgrade Scheme.
So they are promoting a 3-day course to transform existing plumbers and electricians into Heat-Pump Installers.
They get £500 off the £700 course-fee and can then self-certify their work within the Building Regulations' Competent Persons Scheme.
Do you have an opinion on that strategy?
Save energy... recycle electrons!
@david999 could you please post some photos of your plant room where your conrtrols, distribution pumps, valves, etc. are located so we can see the pipework and if there’s any zoning?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Follow our sustainability journey at My Home Farm:https://kirstenandmars.com
@editor I wasn’t going to trouble you guys again you have been so kind and felt I was being a nuisance.
i have attached the photos you requested. I was under the house again really to have a better look at that pipe work as it looks fairly untidy. I noticed no manifolds and feed and return pipes are hard to fathom. I checked in the house to see if there was consistency regarding flow and some feed through the thermostat valves and others through the lock valves. Had it been me I would have fitted manafolds and at least connected all the feeds first so no crossovers. I need to take more photos and try to figure what’s what underneath. So depressing. The stuff in the plant room is too complicated for me and I think for the installers as well.
That is ridiculous. So you have the hot water tank, a buffer tank, a red and a white tank and a big white one as well. For comparison, our installation just has the hot water tank and the small red and white ones, basically for expansion of water and adding more if necessary. Not to mention the pipes everywhere and do I see two water pumps?
It looks like your Samsung controller is in a cupboard? I believe you can put them out in the room and use the room temp to control the heat pump, which would be better than leaving it in a cupboard.
- 25 Forums
- 1,615 Topics
- 34.8 K Posts
- 71 Online
- 1,887 Members
Join Us!
Latest Posts
-
RE: Interesting new product for woodburners - Recoheat
It’s not the most polished design in the world. We don’...
By Mars , 3 hours ago
-
RE: alternative to Homely - HavenWise. Anyone used it?
@editor I'll watch with interest. My LG ashp does not h...
By Tim441 , 3 hours ago
-
RE: Has anyone seen this problem before? Huge anticycling times
I’m sorry - I thought I had replied but I don’t see it!...
By cg360 , 5 hours ago
-
RE: Which liquid is used in the central heating loop?
@trbob Ah! Now, what you are referring to (R32) is the ...
By Toodles , 5 hours ago
-
RE: Will heat pump heat hot water without increasing the temp in my home?
Thankfully I do have a electricity smart meter thing so...
By Ellyse , 6 hours ago
-
RE: How to Solve Mould and Mildew Issues in Renovated Properties
MEV - Mechanical Extract Ventilation. A central extract...
By Johnmo , 7 hours ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
Thanks all. To cover all the points and advice: 1. Pa...
By benson , 8 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Update from our Aira install. We've just had an enginee...
By MikeH , 10 hours ago
-
RE: Calculating inverter size to match battery size
Erm... yes, but that's bad practice. As GB moves towa...
By Transparent , 12 hours ago
-
RE: Ecodan - flow rates, sensors, settings
I am assuming you are aware of the FTC(6, I think) pump...
By rhh2348 , 17 hours ago
-
RE: Determining correct flow rate for a heat pump
Assume so too. I think my pipes are at 150mm centres,...
By rhh2348 , 17 hours ago
-
RE: Midea ASHP – how to set weather compensation
Many thanks @mphb and @cathoderay. Didn't expect so qui...
By iWolf , 19 hours ago
-
RE: British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
@jancold My day 1 of install over. It started at 7 wi...
By Lucia , 1 day ago
-
RE: Undersized Vaillant ASHP and abandoned by installer
Ps to the above. The requirements on the heat pum...
By JamesPa , 1 day ago
-
The greenhouse tomatoes have ,as usual, done well but t...
By Jancold , 1 day ago
-
RE: Locational electricity pricing
@transparent Phew! ok have skim read despite hectic d...
By Lucia , 1 day ago
-
'If you are not part of the problem there's good money ...
By AllyFish , 2 days ago
-
RE: Suitability of 45C flow temp with existing pipework
I've ordered a cheap borescope online and I'm going to ...
By Alex_N , 3 days ago
-
RE: Agile: average import cost vs other tariffs?
@tim441 Last year I ‘netted’ about £400 that way so I h...
By Toodles , 4 days ago
-
RE: Gas Combi to ASHP - Making sense of survey results and proposal.
@irmartini I think that @editor might sympathise with t...
By Toodles , 4 days ago
Latest Topics
-
Which liquid is used in the central heating loop?
By TRBob 10 hours ago
-
Interesting new product for woodburners - Recoheat
By Tim441 11 hours ago
-
alternative to Homely - HavenWise. Anyone used it?
By Tim441 11 hours ago
-
Calculating inverter size to match battery size
By Homonid 2 days ago
-
Agile: average import cost vs other tariffs?
By Tim441 4 days ago
-
Suitability of 45C flow temp with existing pipework
By Alex_N 4 days ago
-
Setback for Vaillant Arotherm Plus
By JWilliams89 4 days ago
-
By Toodles 5 days ago
-
By Jeff 5 days ago
Members Online
No online members at the moment