ASHP + two cylinders - possible?
Hi All,
I will be having an ASHP fitted this year. We are a family of four who occasionally host one or two guests. There's not a lot of space available for a cylinder (we can squeeze in a 200 litre one), and I was wondering if it might be possible to combine a conventional cylinder that supplies all the bathrooms, with a Heat Geek Mini-Store in the kitchen to supply kitchen sink, hot-feed dishwasher and washing machine, and downstairs w.c.. The mini-store and hot water cylinder would be installed on the same ground-floor level as the heat-pump, which would hopefully make pipework straightforward and I'm hoping it would just be a matter of a suitably-configured controller and valves to make this setup work.
At the moment I'm thinking of going with a Mitsubishi Ecodan heat pump but if going with another brand would help to make this work then I'd be willing to consider that.
Thanks for reading and any thoughts gratefully received!
Posted by: @dr-hAt the moment I'm thinking of going with a Mitsubishi Ecodan heat pump but if going with another brand would help to make this work then I'd be willing to consider that.
The brand will usually be recommended by the installer as they'll be working (specialising) in certain brands. If you want to email me your location, I can connect you with reputable installers in your area: editor@renewableheatinghub.co.uk
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @dr-hHi All,
I will be having an ASHP fitted this year. We are a family of four who occasionally host one or two guests. There's not a lot of space available for a cylinder (we can squeeze in a 200 litre one), and I was wondering if it might be possible to combine a conventional cylinder that supplies all the bathrooms, with a Heat Geek Mini-Store in the kitchen to supply kitchen sink, hot-feed dishwasher and washing machine, and downstairs w.c.. The mini-store and hot water cylinder would be installed on the same ground-floor level as the heat-pump, which would hopefully make pipework straightforward and I'm hoping it would just be a matter of a suitably-configured controller and valves to make this setup work.
At the moment I'm thinking of going with a Mitsubishi Ecodan heat pump but if going with another brand would help to make this work then I'd be willing to consider that.
Thanks for reading and any thoughts gratefully received!
I cant see any fundamental reason not to have two cylinders and Im not sure that one needs to be a mini store (but it could be).
The challenge, as you identify, will be with the plumbing and control particularly the latter. Heat pumps like to 'control' dhw cylinders, and by default allow for one. Some heat pumps, I believe, think of a cylinder as just another 'zone' and so they might easily cope with more than 1. Legionella cycles might also confuse. I would suggest that this detail should be worked out in advance to avoid nasty surprises and equally nasty kludges at install time. Its clearly not impossible, but might require a bit more ingenuity than some installers can cope with.
That said are you sure 200l isnt enough. If you heat 200l to 55C you get ~300l of water at 40C. 55 is a bit higher than the fairly normal 48, but not so far out as to be silly. Sometimes simplicity is better. Obviously it depends on your needs, if all 4 take 10 minute showers at 20l/s in quick succession, neither will suffice.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Thanks for the response. The ministore idea was motivated by the particularly restricted space available for the second cylinder, although I am sure control setup would be much simpler with two conventional cylinders. One thing I'm particularly unclear on is why the pipework for traditional cylinders seems so very complicated relative to a ministore, and whether volumisers are required.
In terms of whether 200 litres is enough - I'm just used to having a combi boiler and never running out of hot water! Although, I guess in terms of the kitchen hot water usage, it would be fairly easy to time-shift the vast majority of the hot water usage so it has negligible impact on availability of hot water for showers/baths.
Posted by: @dr-hOne thing I'm particularly unclear on is why the pipework for traditional cylinders seems so very complicated relative to a ministore,
The only real difference (in terms of complexity of pipework) is the pressure release drain required on a traditional cylinder because of the possibility of explosion. This can be a pain or can be easy.
Posted by: @dr-hwhether volumisers are required.
That's a separate question, depends on the volume of water in your central heating system in relation to the requirements of the heat pump.
Posted by: @dr-hIn terms of whether 200 litres is enough - I'm just used to having a combi boiler and never running out of hot water! Although, I guess in terms of the kitchen hot water usage, it would be fairly easy to time-shift the vast majority of the hot water usage so it has negligible impact on availability of hot water for showers/baths.
showers/baths are the main determinant of the requirement for many households. Kitchen appliances are usually cold fill, so its only washing up that uses DHW in the kitchen.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @dr-hOne thing I'm particularly unclear on is why the pipework for traditional cylinders seems so very complicated relative to a ministore,
The only real difference (in terms of complexity of pipework) is the pressure release drain required on a traditional cylinder because of the possibility of explosion. This can be a pain or can be easy.
👍
Posted by: @jamespaPosted by: @dr-hwhether volumisers are required.
That's a separate question, depends on the volume of water in your central heating system in relation to the requirements of the heat pump.
Ah, OK, so it's nothing to do with the cylinder? It's just that I feel like I've always seen a little white or red cylinder installed next to the big DHW cylinder so assumed they kind of went together, but I guess it's just that the install location of the DHW is usually also the best place for a volumiser to go, if required.
Posted by: @jamespaPosted by: @dr-hIn terms of whether 200 litres is enough - I'm just used to having a combi boiler and never running out of hot water! Although, I guess in terms of the kitchen hot water usage, it would be fairly easy to time-shift the vast majority of the hot water usage so it has negligible impact on availability of hot water for showers/baths.
showers/baths are the main determinant of the requirement for many households. Kitchen appliances are usually cold fill, so its only washing up that uses DHW in the kitchen.
I'll be using hot-fill washing machine and dishwasher. Better to get the water for those heated by the heat pump than with electric coils in the machines.
Posted by: @dr-h@jamespa I'll be using hot-fill washing machine and dishwasher. Better to get the water for those heated by the heat pump than with electric coils in the machines.
Fair enough, I didn't know that they existed any more. Can I ask who produces such things?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I've actually made an assumption on the washing-machine front, but I know that many Bosch dishwashers can be programmed for hot-fill (they only have one fill supply pipe, which is by default expecting cold water)
Please note I edited my previous post above after you replied to it.
Thanks for your help.
Posted by: @dr-h@jamespa I've actually made an assumption on the washing-machine front, but I know that many Bosch dishwashers can be programmed for hot-fill (they only have one fill supply pipe, which is by default expecting cold water)
Please note I edited my previous post above after you replied to it.
Thanks for your help.
I didnt know that about dishwashers - Im off to check the instructions to mine, thanks for the tip-off.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I was told some years back that ‘cold fill only’ was now the preferred option (obviously a cost saver for the manufacturers says the cynic in me) as splashing hot water onto greasy plates would ‘bake on’ the residue rather than rinse it away. In addition, they reckon it is better to start from cool and heat the water gradually to avoid thermal shock. That’s the manufacturer’s story anyway. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @dr-hAh, OK, so it's nothing to do with the cylinder? It's just that I feel like I've always seen a little white or red cylinder installed next to the big DHW cylinder so assumed they kind of went together, but I guess it's just that the install location of the DHW is usually also the best place for a volumiser to go, if required.
That is not a volumiser that's an expansion vessel. You need one in each pressurised heated system, so one for the central heating (red) and one for the dhw (white)
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@toodles hmmm. I think the "thermal shock" thing has got to be cobblers surely? For the Bosch, it says the hot feed should be between 40 and 60 °C. I'm not convinced that spraying an item that's at room temperature with water that's 60 °C is going to cause a thermal shock problem.
I have assumed that even with a hot feed, that the dishwasher does (or can) heat the water further.
@jamespa, examples of Bosch machines that will accept a hot feed are the SMS6ZCW10G and SMS4EMW06G. See the bottom of Page 36 on the respective user manuals. And here is a washing machine with hot fill: https://ebac.com/washing-machines/e-care-8kg-hot-fill
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 49 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
OMG, the attached schematics (even with incorrect room ...
By BAMi , 40 minutes ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 1 hour ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 1 hour ago
-
What is the best strategy for operating a very oversized heat pump?
As the title really. There are at least three live thr...
By JamesPa , 2 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 2 hours ago
-
Heat Pump Sizing & Installation Costs
I’m doing some research for an upcoming article and pod...
By Mars , 2 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 3 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 14 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 17 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 18 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 20 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 21 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 23 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 2 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 3 hours ago
-
SolarPV tables / online calculator
By MichelleC 10 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 22 hours ago
-
By Toodles 2 days ago