ASHP sizing - value of Heat Transfer Coefficient
@jancold The PCM is heated up by a 3 kW element in the version I have (there are others where a high temperature heat pump can do the same thing instead), the unit itself is very well insulated and loses no more than 0.75 kWh of energy in 24 hours. When hot water is required, it passes through a length of pipework inside the PCM material and is heated to approx. 50- 55 degrees C - then to your tap / shower or whatever. (Rather like a Combi Gas Boiler might supply the hot water) I think if my memory serves that the PCM is heated up to 65 - 70 degrees C. and this is why an HT heat pump is required as an LT can’t raise the temperature to that required. We have a Sunamp supplied regulator on the output so that the water is supplied at 45 degrees C. for safety and comfort.
The energy can be stored in the PCM for days and the unit we have takes approx. 11 kWh of storage; sometimes, we don’t recharge for several days if it is dull (little solar PV) and the Agile price is too high for my Scrooge nature to allow it to run. The control wiring for the Sunamp is connected to a Myenergi Eddi and that indicates ‘Max Temp Reached’ when fully heated and then the control system monitors the temperature of the unit. The system may be a little ‘granular’ though as the LED status indicator shows ‘Full’ then a sort of ‘More than Half full’ , then ‘Half Full’ and then ‘Less than Half’ and finally ‘Empty’ there is also a ‘Mains Connected’ LED that indicates charging or at a standby status. This granularity worries some people a little I gather but I am happy with this as we rarely need more than 25% of the stored energy in a day - and the unit is only a quarter the volume of a conventional DHW tank and does not feature all that pipework that tanks seem to bristle with!
The system is also very unlikely to suffer from Legionella problems as water is not stored in any quantities at dangerous temperatures. As you might have detected, I rather like the system! Having very little space for a conventional tank went a very long way towards our decision to have a box in the airing cupboard and still have some room for the linen! Regards, Toodles.
Toodles, 76 years young and hoping to see 100 and make some ROI on my renewable energy investment!
@jancold To add to what @toodles has said, you can imagine the phase change material as something like candle wax, which will melt before the maximum temperature of the store is reached. A property called the latent heat of fusion means that a lot more energy is needed to raise the temperature between solid and liquid and so this is stored in the liquid material.
I would imagine that the material closest to the coil would solidify initially as it heats the water but might melt again as heat is transferred from the outer volume.
Thermino's are a good idea and small but also a bit pricy and as toodles says need to be heated higher than a cylinder would.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody I might add that the control wiring indicates to Eddi that the temperature required by the PCM closest to the element has reached temperature - at which point, the system stops calling for power. The Eddi is set to (I think) 20 minutes of rest and then it will try again to see if the ‘local to the element’ material has dissipated the energy into the mass of the unit and cooled down sufficient to request more energy to heat the element further. I have observed this happening and noticed the Eddi apply more power after this ‘dissipation’ cycle. Regards, Toodles.
Toodles, 76 years young and hoping to see 100 and make some ROI on my renewable energy investment!
- 25 Forums
- 1,513 Topics
- 31.8 K Posts
- 23 Online
- 1,283 Members
Join Us!
Latest Posts
-
RE: Additional Battery v Wind Turbine v Ripple
I should add, being an investment, the value of your in...
By Old_Scientist , 5 hours ago
-
RE: Ecodan - flow rates, sensors, settings
Achieving an accurate flow measurement is probably the ...
By Derek M , 8 hours ago
-
RE: Ecodan ASHP - How to optimise my set up?
Again, thank you for another thorough post, @derek-m - ...
By rhh2348 , 10 hours ago
-
RE: Delivering a smart and secure electricity system: government consultation
@Transparent.Now that I am represented by a new MP I th...
By IanMK13 , 12 hours ago
-
RE: Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
Similar thread here
By Johnmo , 13 hours ago
-
RE: VDI 2035 heating water specification
Been looking and it seems a good little project. Ever...
By Johnmo , 2 days ago
-
RE: Do I accept an ASHP and Solar Panel retrofit under the HUG 2 scheme?
Will do. I'm currently waiting for another survey / vis...
By dssr , 2 days ago
-
The company that did the borehole were expecting us to ...
By Johnmo , 2 days ago
-
-
RE: The Misquote That Ruined the Heating Industry
@abernyte manufacturer training is pretty average. They...
By Mars , 2 days ago
-
-
RE: ECO4 Scheme and EPC ratings
@mellow Thanks. Given there is a scheme requirement to ...
By Old_Scientist , 3 days ago
-
RE: Do I just go with the lowest quote for my heat pump?
@jancold To me its a no-brainer then, a max 40C flow te...
By bontwoody , 3 days ago
-
-
RE: Heat Pump Books Beginners – Bodge Buster & From Zero To Heat Pump Hero
@editor Presumably he had some good weather Compensatio...
By Toodles , 4 days ago
-
RE: New Vaillant 7kW aroTherm ASHP or oil boiler dilemma/decision??
Storage capacity really is dependent on storage tempera...
By Johnmo , 4 days ago
-
RE: HP Cycling, Expected or Undesirable
Just a little update. I ordered a longer shielded twin ...
By bontwoody , 4 days ago
-
RE: Domestic hot water timer doing crazy things on my Grant Aerona3 10kW air source heat pump
Thanks @allyfish for the pics and info. Spoke to the in...
By Mellow , 4 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
It's been a busy day for calls and emails from Aira. I ...
By MikeH , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Hmm. A bit of a nuanced answer, methinks. As I've alr...
By Majordennisbloodnok , 5 days ago
Latest Topics
-
Ecodan - flow rates, sensors, settings
By rhh2348 11 hours ago
-
Replacing mains water with well water
By Johnmo 2 days ago
-
Additional Battery v Wind Turbine v Ripple
By bontwoody 2 days ago
-
By jamespipe 3 days ago
-
VDI 2035 heating water specification
By Johnmo 3 days ago
-
Do I just go with the lowest quote for my heat pump?
By Jancold 5 days ago
-
The Misquote That Ruined the Heating Industry
By Alec Morrow 6 days ago
-
Battery Storage Wiring Gauge Question
By Puff 6 days ago
Members Online
No online members at the moment