Mitsubishi ecodan 11kW ridiculously expensive running costs. Help!

24 Posts
4 Users
0 Reactions
6,412 Views
(@parmstar)
Estimable Member Member
274 kWhs
Joined: 2 years ago
Posts: 51
Topic starter  

The heat pump is a

PUZ-WM112VAA

controller is shown on the pic and itโ€™s a 3rd party joule 300l cylinderย 

9C4AE3EE B3B0 4171 AABA 44AD4FE34941

ย 


   
ReplyQuote
(@hughf)
Noble Member Member
3009 kWhs
Joined: 3 years ago
Posts: 487
 

Is the controller in the hallway or in the cylinder cupboard?

and Iโ€™m asking for photos so I can map out the plumbing layoutโ€ฆ. It saves me asking you โ€˜do you have a buffer, do you have a plate heat exchanger, do you have a llh, is your primary pump pwm controllerโ€™ etcโ€ฆ

Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.

My wifeโ€™s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.


   
ReplyQuote
(@parmstar)
Estimable Member Member
274 kWhs
Joined: 2 years ago
Posts: 51
Topic starter  

Thanks Hugh- the cylinder is located in airing cupboard with the main controls and the thermostat is located in the hallway. The ASHP is on the side of the house with the flow and return pipes running up the side of the house in to the loft where the rest of the install is located. See pics. I hope that helps

33291957 075D 4838 AB97 B60088A80AA8
F7E08F4B EA9B 484D 8E8D DB736C792B9D
D2C7DBF4 EBD8 4C4E A83D E85F590B296A
E7147A5F A74C 4F86 94DE 03AFCE63434B
75B58F91 A456 4124 8846 12207C03F717

ย 


   
ReplyQuote
(@hughf)
Noble Member Member
3009 kWhs
Joined: 3 years ago
Posts: 487
 
79307B3E B835 4259 A0B0 F61E944F3577

How many cables go to this pump? It will either be one, or two.

With the ecodan controller located in the airing cupboard, your system is installed like a boiler, with the ecodan controller having no input on the flow temperature and the thermostat controlling the secondary pump.

Unless you have a Mitsubishi wireless thermostat in your hallway? What brand of thermostat do you have?

Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.

My wifeโ€™s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.


   
ReplyQuote
(@parmstar)
Estimable Member Member
274 kWhs
Joined: 2 years ago
Posts: 51
Topic starter  

@hughf its a ecodan wireless remote controller and reciever - PAR-WT50R-E / PAR-WR51R-E

There is just one cable going to that pumpย 


   
ReplyQuote
(@hughf)
Noble Member Member
3009 kWhs
Joined: 3 years ago
Posts: 487
 

Ok, so the primary pump is not pwm controlled so the heat pump isnโ€™t able to modulate itโ€™s flow. Not the end of the world but certainly not the most efficient way of doing things.

Are you running the ecodan controller in auto adaption mode or standard weather compensation?

Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.

My wifeโ€™s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.


   
ReplyQuote



(@parmstar)
Estimable Member Member
274 kWhs
Joined: 2 years ago
Posts: 51
Topic starter  

@hughf standard weather compensation. I am just on the phone to Mitsubishi technical now and sent them a screen shot of my usage chart through my solar app. They are slightly concerned and he has gone to speak to his colleague..... got me even more worried now! Will post an update shortly. (Usage chart attached for your perusal)

IMG 1478

   
ReplyQuote
(@parmstar)
Estimable Member Member
274 kWhs
Joined: 2 years ago
Posts: 51
Topic starter  

They said it's fine to cycle like that as its on the hour - he thought it was cycling a lot more. It was not until I zoomed in he confirmed that it is ok like that.


   
ReplyQuote
(@hughf)
Noble Member Member
3009 kWhs
Joined: 3 years ago
Posts: 487
 

Cycling looks fine to me, not too short. Itโ€™s bubbling along at 6.5kW ish, all night. Heat loss is very good for something thatโ€™s 400 square meters. Weโ€™re at 6.7kW heat loss at -3/21 and weโ€™re only at 100 square meters.

ย 

Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.

My wifeโ€™s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.


   
ReplyQuote
(@batalto)
Famed Member Member
3655 kWhs
Joined: 4 years ago
Posts: 1091
 

Given your house size, I'd personally whip out that low loss header as well. Cant see flow rates being an issue in 400m2 of floor space.

12kW Midea ASHP - 8.4kw solar - 29kWh batteries
262m2 house in Hampshire
Current weather compensation: 47@-2 and 31@17
My current performance can be found - HERE
Heat pump calculator spreadsheet - HERE


   
ReplyQuote
(@kev-m)
Famed Member Member
5606 kWhs
Joined: 4 years ago
Posts: 1276
 

Posted by: @parmstar

@hughf standard weather compensation. I am just on the phone to Mitsubishi technical now and sent them a screen shot of my usage chart through my solar app. They are slightly concerned and he has gone to speak to his colleague..... got me even more worried now! Will post an update shortly. (Usage chart attached for your perusal)

IMG 1478

This is more likely to be defrosting.ย  (The term cycling is usually used where the ASHP can't modulate down low enough where the load is low) My Ecodan energy looks very similar at the moment and it's definitely defrosting every 60-80 minutes as I can see it on my monitoring.ย  All normal in these conditions.ย  You can see the flow plummet and a tiny blip in the ambient (assmued because of where the sensor is).

ย 

chart (1)

ย 


   
ReplyQuote
(@hughf)
Noble Member Member
3009 kWhs
Joined: 3 years ago
Posts: 487
 

Posted by: @batalto

Given your house size, I'd personally whip out that low loss header as well. Cant see flow rates being an issue in 400m2 of floor space.

Agreed, going direct would bring a benefit on efficiency. Can the ecodan drive a pwm primary pump? I havenโ€™t checked the wiring diagrams .

ย 

Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.

My wifeโ€™s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.


   
ReplyQuote



Page 2 / 2



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but itโ€™s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

โœ… Pre-Installation Planning
โœ… Post-Installation Troubleshooting
โœ… Performance Optimisation
โœ… Complaint Support (Manufacturer & Installer)

๐Ÿ‘‰ Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security