@clairelp finally I can see that you have a volumiser, not buffer setup. So there should be not extra pumps on the system. The pump built into the Daikin is quite strong, I can't see a bypass (but it's hard to tell with the quality of pictures)
This is what they look like, it maybe in the airing cupboard, do you TRVs on every radiator.
Does the noise stop when doing hot water.???
Technical Manager & Professional Installer: Ultimate Renewables
@clairelp I'd expect the primary pipes - which is the ones that connect your heat pump to to the volumiser, to that black and red Esbe valve, and to any manifolds or branching off in your cupboard, to be at least 28mm diameter. From the pictures it looks like they >may< be 22mm? It's hard to tell though.
Apologies - I've forgotten the output of your heat pump..... There's a limit to how many kWhs you can get down each diameter pipe to not go over 0.9 - 1m/s velocity. For 22mm the limit is around 6kW. For 28mm it's more like 10kWh. * Could you please check what the diameter of the pipes going to your volumiser are please? The volumiser is the small gray tank thing in the attic.
Did you then say that each pipe heading off around the house is 10mm? You can get around 1kW down each one of these to not go over 0.9 - 1m/s velocity.
The reason you would want to keep to that velocity limit is it tends to get noisy above it. Also much above 1.5 and it starts to erode the internal of a copper pipe.
As Ken and others thought previously the pipe clips attach the pipe directly to the wood in your attic. An alternative would be to use a clip that goes to the outside of the insulation material. There is a brand called "Primary Pro" that is a favourite with heat pump installers. As you have a cold attic I'd advise consider this a cold space and upgrading the insulation up there - you'll save money in the long run.
Ken's suggestion to check the air vent is a good one too.
*These numbers assume you have glycol in your system, and that the dT of your heat pump is 5. dT means the delta T - it stands for the temperature difference between the hot pipe from the heat pump and the cold one. Delta means "difference" in Latin. As dT increases you can get more and more heat down a pipe within that velocity limit.
Sustainable Groups - Renewable Heating - Co-founder of Firepower. Book a one-to-one consultation to discuss your heating and sustainability here.
Technical Manager & Professional Installer: Ultimate Renewables
Hi, we not had chance to get in the loft to look at the valve yet, difficult to go up in loft making noise when children asleep in the evening.
I did look at pressure gauge in cupboard and it about 1.6.
Friday installers are coming so I will keep you posted. We also have installers msc compliance department checking the install following week. Hoping they will have an answer 🤞🙏
the ashp does have anti freeze valves, with it not been below freezing hoping be okay to keep turning off for a couple of nights.
also looking into sound proofing and insulation for the loft.
Hi,
Installers, have turned down the velocity to I think he said 21-22 and was previously 24. Think he said in the bypass valve. And I sorry can’t remember exactly but I think he said like it around 21 and maybe 24 was making too much noise.
At moment, I don’t think I could hear it and running quieter, it’s only just done so I will test it later when doing hot water and have to wait for a cold night.
🤞
They also did some settings on the frost cycle. They said it shouldn’t be coming on when not cold enough and shouldn’t be constantly going. Said there is two defrost settings one I think he said for the pipes and one for actual pump. They said if changes didn’t help they will contact Daikain, as some setting they can’t change.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 87 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Incidentally this is the sort of thig you can do if you...
By JamesPa , 13 minutes ago
-
RE: Humming sound on new install.
Roof trusses and dry lined ceilings are a massive sound...
By AllyFish , 2 hours ago
-
RE: Midea ASHP – how to set weather compensation
@jamespa is right, typically they are far from linear, ...
By cathodeRay , 3 hours ago
-
Funny story Graham, when I started looking to ...
By DREI , 11 hours ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 15 hours ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 17 hours ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 18 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Yes Octopus only have the £9 a month service plan for t...
By NJT , 19 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
@allyfish Dogs have owners - Cats keep staff. You are o...
By Toodles , 20 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 20 hours ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 1 day ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 2 days ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 2 days ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 3 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 3 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 3 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 3 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
@scalextrix Name plate capacity
By HCas , 3 days ago
-
RE: Solar Thermal DHW and ASHP
I was originally contemplating a solar thermal installa...
By jamespetts , 3 days ago