The thermostat is set at 21.5 degrees and the house is being held at 21 and has been for over 24 hours.
Good morning Batalto,
Very useful data.
As a check, try increasing your thermostat setpoint to say 23C and see if the indoor temperature increases. If it does then your system is not fully operating on weather compensation.
You could try make the slope of your weather compensation shallower, by changing the left hand end to 50C @ -10C.
Don't change the slope immediately, increase the thermostat setting and wait several hours or more to see the effect.
@kev-m actually I used LESS power. You can see from below the details of the days.
And of course as soon as I said it, I was wrong. My heating got the house to 21.5, so I've adjusted the weather curve down a tiny bit from 25@20, to 25@18. I'll wait to see the impact. Also yesterday I adjusted the hot water from 55 to 53 and that seems to be fine as well. Its not perfect as ambient is an average of the whole day - It could have been a cold night and a warm day and still average 13 vs 13 all day. However for my needs its close enough to be interesting.
@derek-m It doesnt matter what I set the thermostat to. Originally I had it on 22, but moved it to 21.5 to prevent a boiling house if the experiment went totally wrong. So far my nest app says the heating was being called for "23.5 hours" yesterday. It is showing 21 steady in the house downstairs. I've left upstairs on normal thermostat as its so warm up there anyway its not really ever on. When it does come on, it warms up pretty quickly.
Checked the filter today and it was pretty much totally clean - so I think the gunk is now cleaned out. The system is basically silent now as well, whereas before it made a high pitched noise in the main return pipe. I assume this was just a restricted flow issue.
House seems to be totally fine today, however the temps seem to creep up in the day. Now evening has come it's back to holding at 21. Not sure what to do as it seems to be a solar gain issue. However it wasn't a major issue as it was only 0.5° above target. A stated I've adjusted my curve a little bit. I'll be leaving it alone for the next few days and seeing the impact. However any tweaks will be around the edges.
Current setting 50°@-3° and 25°@18°
room temperature hit 21.5 again today, so trimmed the weather comp at the bottom end a little. Its not exactly sunny, so solar gain should be negligible today. Now the house is up to temperature it'll be interesting to see how it holds. slowly slowly dialling in. Just need a cold snap to see how we are really getting on
we're a tiny bit cooler indoors today on the same flow temps. I think it's because it's damps and misty. Not enough to worry about though. Like you say, this is too easy, we need some proper winter weather.
Ran through the night with a COP of 4.2 - Lost some heat downstairs though, the temperature dropped to 20. So I've adjusted my curve 1 degree upwards; 25 @ 17
Posted by: @bataltoRan through the night with a COP of 4.2 - Lost some heat downstairs though, the temperature dropped to 20. So I've adjusted my curve 1 degree upwards; 25 @ 17
Good morning Batalto,
The wind speed was higher last night in our area, and I have noticed that it appears to have added about 5C to the required water flow temperature.
@derek-m there is a bit of cycling on the system due to the super mild weather (ambient was 13 overnight). However its very wet today, so interesting to see how we get on. The house is well up to temperature now.
@kev-m It'll be a mix of hot water (for the showers), my wife's hair dryer, washing machine going on etc. This measures power in 5 min intervals, so its prone to being a bit spikey. You think 2/3kw for hot water being heated plus a 2kw hair drier and you're getting up there. Interestingly I am still running on battery, so my power is still 5p/kw
SOC = State of charge e.g. %
- 26 Forums
- 2,238 Topics
- 49.8 K Posts
- 250 Online
- 5,900 Members
Join Us!
Podcast Picks
Latest Posts
-
Thanks! My consumer unit collection is ready with the W...
By Batpred , 45 minutes ago
-
RE: DESNZ doing a survey which asks the right questions!
@jamespa but is MCS capable of knowing the difference b...
By Judith , 8 hours ago
-
RE: Solar inverters - where does the energy go when clipping?
Since the combination of fitting plus scaffolding makes...
By Judith , 9 hours ago
-
RE: Designing my house system with a mix of air to air and air to water
@jamespa Cheers James, it's great reading. In quite a f...
By pipebaron , 9 hours ago
-
RE: PV Panels on roof in Conservation Area
If there is any way you can determine daily oil consump...
By JamesPa , 9 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@editor The Good: How efficient have you fou...
By wreckguru , 10 hours ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
Good plan and pretty much what I did in the end (there ...
By JamesPa , 11 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
attached is prelagged in case indicates anything. &nb...
By Crimson , 13 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
The more we learn about about an ASHP potentially repla...
By colinc , 13 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Via the cloud and via the online, similar data is shown...
By Batpred , 16 hours ago
-
@old_scientist yes. No E911 error. Very odd. Thanks for...
By bontwoody , 18 hours ago
-
RE: Incorrect Billing of Customers with a Smart Meter
How odd @korwraith - that functionality being offered ...
By Transparent , 19 hours ago
-
RE: Master & Slave Zones/Setback
Re outdoor probes can be added from the ones attached t...
By bretix , 23 hours ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
Thanks for sharing this, it is clearly disappointing, B...
By Batpred , 1 day ago
-
I'm seriously considering an air to air A2A multi-split...
By springswood , 2 days ago
-
RE: Effect of Mitsu PAR WT60 Wireless Controller
@sunandair We were not present to do a tidy changeover ...
By DavidAlgarve , 2 days ago
-
I’m frankly amazed you think anything I have posted on ...
By Majordennisbloodnok , 2 days ago
-
RE: Replacing knackered oil boiler with Samsung ASHP - Perthshire
Thanks for your full reply @mike-h. It certainly cleare...
By DowallyDrifter , 2 days ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
I don't seem to have a mixer valve. Just pressure regul...
By Jancold , 2 days ago