The thermostat is set at 21.5 degrees and the house is being held at 21 and has been for over 24 hours.
Good morning Batalto,
Very useful data.
As a check, try increasing your thermostat setpoint to say 23C and see if the indoor temperature increases. If it does then your system is not fully operating on weather compensation.
You could try make the slope of your weather compensation shallower, by changing the left hand end to 50C @ -10C.
Don't change the slope immediately, increase the thermostat setting and wait several hours or more to see the effect.
@kev-m actually I used LESS power. You can see from below the details of the days.
And of course as soon as I said it, I was wrong. My heating got the house to 21.5, so I've adjusted the weather curve down a tiny bit from 25@20, to 25@18. I'll wait to see the impact. Also yesterday I adjusted the hot water from 55 to 53 and that seems to be fine as well. Its not perfect as ambient is an average of the whole day - It could have been a cold night and a warm day and still average 13 vs 13 all day. However for my needs its close enough to be interesting.
@derek-m It doesnt matter what I set the thermostat to. Originally I had it on 22, but moved it to 21.5 to prevent a boiling house if the experiment went totally wrong. So far my nest app says the heating was being called for "23.5 hours" yesterday. It is showing 21 steady in the house downstairs. I've left upstairs on normal thermostat as its so warm up there anyway its not really ever on. When it does come on, it warms up pretty quickly.
Checked the filter today and it was pretty much totally clean - so I think the gunk is now cleaned out. The system is basically silent now as well, whereas before it made a high pitched noise in the main return pipe. I assume this was just a restricted flow issue.
House seems to be totally fine today, however the temps seem to creep up in the day. Now evening has come it's back to holding at 21. Not sure what to do as it seems to be a solar gain issue. However it wasn't a major issue as it was only 0.5° above target. A stated I've adjusted my curve a little bit. I'll be leaving it alone for the next few days and seeing the impact. However any tweaks will be around the edges.
Current setting 50°@-3° and 25°@18°
room temperature hit 21.5 again today, so trimmed the weather comp at the bottom end a little. Its not exactly sunny, so solar gain should be negligible today. Now the house is up to temperature it'll be interesting to see how it holds. slowly slowly dialling in. Just need a cold snap to see how we are really getting on
we're a tiny bit cooler indoors today on the same flow temps. I think it's because it's damps and misty. Not enough to worry about though. Like you say, this is too easy, we need some proper winter weather.
Ran through the night with a COP of 4.2 - Lost some heat downstairs though, the temperature dropped to 20. So I've adjusted my curve 1 degree upwards; 25 @ 17
Posted by: @bataltoRan through the night with a COP of 4.2 - Lost some heat downstairs though, the temperature dropped to 20. So I've adjusted my curve 1 degree upwards; 25 @ 17
Good morning Batalto,
The wind speed was higher last night in our area, and I have noticed that it appears to have added about 5C to the required water flow temperature.
@derek-m there is a bit of cycling on the system due to the super mild weather (ambient was 13 overnight). However its very wet today, so interesting to see how we get on. The house is well up to temperature now.
@kev-m It'll be a mix of hot water (for the showers), my wife's hair dryer, washing machine going on etc. This measures power in 5 min intervals, so its prone to being a bit spikey. You think 2/3kw for hot water being heated plus a 2kw hair drier and you're getting up there. Interestingly I am still running on battery, so my power is still 5p/kw
SOC = State of charge e.g. %
- 22 Forums
- 2,089 Topics
- 45.9 K Posts
- 29 Online
- 3,375 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
Im sure you are right. Running costs are tiny and just...
By JamesPa , 4 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
I don't (yet), but my PW3 is due to be installed shortl...
By Old_Scientist , 4 hours ago
-
RE: MCS and NAPIT complaints process
@chrislay, is your heat pump complaint still unresolved...
By Mars , 8 hours ago
-
RE: ASHP Install from hell - help please
@saf1973 I’ve been going through old cases on the forum...
By Mars , 9 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@benson I have gone down the Home Assistant and wavesha...
By Grantmethestrength , 19 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron There's the rub, the database does not list my ...
By AF1 , 21 hours ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@editor excellent news, congratulations and well deserv...
By ASHP-BOBBA , 22 hours ago
-
RE: Vaillant AroTherm Plus 7kW
Depends on the flow temperature; the Czech data sheet i...
By JamesPa , 1 day ago
-
RE: Renewables & Heat Pumps in the News
Thanks @lucia I look forward to some technical facts as...
By Judith , 1 day ago
-
RE: Commencing on an ASHP Installation Process
Yes, it's "doable" if everything goes to plan, they arr...
By Old_Scientist , 2 days ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 3 days ago
-
@ashp-bobba ‘Wattson, how many grammes of Co2 are you r...
By Toodles , 3 days ago
-
RE: DHW SET UP with Samsung gen 5
Thats good news indeed, you are very likely almost ther...
By JamesPa , 3 days ago
-
RE: Plate heat exchanger considerations
As far as I can tell my vented system would have a peak...
By Scalextrix , 3 days ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
There have been a few discussions dotted around (e.g. I...
By Declan90 , 3 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having made some enquiries locally I have found a compa...
By Morgan , 3 days ago