ASHP and how it should run and potential kw consumption?
Hi there,
I have a 10kw Vaillant arotherm plus, had it since Oct so fairly new to the game.
I have a slightly complicated system as the upstairs is radiators, the downstairs is UFH but mixed one large area is screed based UFH and the rest is wunda board with pipes in it, very hard to balance it all.
The main thing I am trying to find out is the expected behaviour of how the heat pump should run and expected kw consumption.
As odd as it may sound the UFH I can run on an extremely low heat curve where the target flow temp sits around 29-33c and the downstairs is very comfortable, will reach 22c and the consumption at 10c is like 1kw and 0c is 2.1kw
This is not so great for the radiators although the temperature upstairs is not bad, likely from the heat rising from downstairs, however if I try to run the upstairs radiators at a normal temp so say a flow temp of 35-40c the electric consumption is around 3.2kw to 4kw
Is this really normal, as thats a hell of alot of kw consumption if I have it running like this thru the day, I understand setup etc makes a difference, but I just wondered what is normal for for a 10kw ASHP to consume, maybe this is normal I have no idea right now.
13.6kw Solar, 27kw Battery, 10kw Heat Pump and EV Car
I have an 8.5kw heat pump and its currently running at 36C and pulling 2kw so not miles away from yours, when it runs at 45C its will pull 3.5kw, there is a big consumption penalty for high flow temps.
I've got a 7kW Arotherm Plus which is currently using 1133W with a 31C flow temp and -2C outside. This is with a 0.5 heat curve setting and target room temperature of 20.5C (actual temp 20.1C). I don't have any UFH but had many of the radiators upsized when I had the heat pump installed. The bedrooms are plenty warm enough (I've fitted smart TRVs help the rooms get a bit cooler at night). 1970s 4-bed detached house with cavities insulated, double glazing, etc.
Posted by: @jeegneshThis is not so great for the radiators although the temperature upstairs is not bad, likely from the heat rising from downstairs, however if I try to run the upstairs radiators at a normal temp so say a flow temp of 35-40c the electric consumption is around 3.2kw to 4kw
Is this really normal, as thats a hell of alot of kw consumption if I have it running like this thru the day, I understand setup etc makes a difference, but I just wondered what is normal for for a 10kw ASHP to consume, maybe this is normal I have no idea right now.
Like any heating system the consumption will depend on outside temperature. At the design minimum temperature you need to deliver roughly twice as much energy to the house as you do at the typical temperature during the heating season. So if you need to deliver 10kW at whatever your design temp is (eg -2 in south east England), much of the time you need to deliver only 5kW or less
Unlike other heating systems, with an ashp the COP (heat to house/electricity consumption) varies strongly with outside temperature). At your design outside temperature the COP is likely 3 or less, so the consumption will around be 10/3 = 3.3kW. At a more typical outside temperature your COP should be more like 4.5 so your consumption will be much lower, around 1-1.5 kW.
Unfortunately a mix of rads and ufh generally means that the heat pump has to run at the higher flow temperature (= poorer COP) needed by the rads. Essentially you lose the COP benefits of ufh if you also have radiators, unless they are sized for the ft of the ufh. I picked the COP figures above assuming rads and a ft at the design temp of 45 or thereabouts.
It's not really valid to give a typical consumption for a 10kW heat pump because the consumption depends on the house loss not the heat pump capacity. They should, in principle, be fairly close but it's by no means unknown for heat pumps to be significantly oversized, by much as a factor of 2. From your figures it sounds like yours may be correctly sized, but without knowing your house loss we don't really know. What does the heat pump claim the cop is (look in myvaillant if you have it))?
Hope that helps.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
So according the design info,
Heat Loss: 9.99kw @ -2c
Target: 440% efficiency at 40oC max flow temperature.
I’ve not been running nowhere near the 40c as it scares the hell out of me (kw cost), but I would like to be able to run closer to that
Heating COP from app:
Nov - 4.9
Dec - 4.0
Today probably been the coldest day so far temp ranged 3c to 0c and app COP is at 3.6
13.6kw Solar, 27kw Battery, 10kw Heat Pump and EV Car
Posted by: @jeegneshSo according the design info,
Heat Loss: 9.99kw @ -2c
Target: 440% efficiency at 40oC max flow temperature.
I’ve not been running nowhere near the 40c as it scares the hell out of me (kw cost), but I would like to be able to run closer to that
Heating COP from app:
Nov - 4.9
Dec - 4.0
Today probably been the coldest day so far temp ranged 3c to 0c and app COP is at 3.6
Those cops sounds pretty close to what I see (7kW house, 7kW Arotherm). My energy delivered is currently tracking fairly close to what my measured gas consumption was.
Taking these together and with a bit of electric tarrif manipulation (I've signed up for eon next drive which gives 7cheap hours overnight, I also have an EV) I reckon that means its going to be a little little cheaper than gas over a season. If I didn't have an EV then the OVO heat pump tarrif 15p for everything used by your heat pump) would easily bring it in cheaper than gas.
How does your energy delivered (as a function of outdoor temp) compared to your previous (if you know the latter)? Unless there is a big disparity then I can't see what you have to worry about, unless of course your previous fuel consumption scared you too (which is if course possible, but that's just the cost of energy!).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
If I take out what the water heating from the gas, then I would say yes the generated kw is about right from previous, I also have an EV and play with the tariffs which is really what saves the day in terms of cost. So far its def cheaper than my gas bill and we are in the worst months right now, so there is hope 🙂
Couple of things I am interested in knowing
1 - what water pressure do you keep it at, mine is sitting on 1.4 bar
2 - From cool 24/25c how long does it take to ramp up to the flow temp say of 35/40c?
I noticed overnight the call was for 42c flow temp, but after 2 hours it only reached 36/37c then it ramped down onto my lower setting, it seems to love sitting on 30/31c calls for higher seems to take forever and not sure it ever reaches its target - I have not been brave enough to keep higher flow temp for more than 2 hours.
13.6kw Solar, 27kw Battery, 10kw Heat Pump and EV Car
Posted by: @jeegneshCouple of things I am interested in knowing
1 - what water pressure do you keep it at, mine is sitting on 1.4 bar
2 - From cool 24/25c how long does it take to ramp up to the flow temp say of 35/40c?
Vaillant's specs indicate an operating pressure between 0.5 and 2.5 bar for the 10kW Arotherm Plus https://professional.vaillant.co.uk/for-installers/products/arotherm-plus-air-source-heat-pump-10kw-146562.html. Inconsistently, the specs for my 7kW unit say 0.5 to 3.0 bar.
The time to ramp up the flow temperature depends on both system volume and the temperature in the building. If you've let the floor slab cool down then it will need a lot of kWh to warm it up again and that will suck the heat out of the circulating water. You may find it more efficient overall to let the heat pump run for more hours a fairly low temperature sufficient to keep the temperature of the concrete close to constant.
Yes I am finding that running it long and low is the better outcome also more comfortable throughout.
with regards the water pressure what’s the positive or negative of it being higher or lower considering there such a range from the manual?
13.6kw Solar, 27kw Battery, 10kw Heat Pump and EV Car
Posted by: @jeegnesh1 - what water pressure do you keep it at, mine is sitting on 1.4 bar
abut 1.5 bar, but I dont think it matters much unless you have a very tall house (it merely needs to be sufficient to ensure that negative pressure doesnt occur anywhere in the plumbing, there is nothing 'ashp' about this at all the same occurs in any unvented CH system)
Posted by: @jeegnesh2 - From cool 24/25c how long does it take to ramp up to the flow temp say of 35/40c?
Here is a shot of some defrost cycles today. You can see wat the FT does. Obviously this is with the house already warm. If the house were cold it would take several hours.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Thanks, I'm away at the minute so cannot get to my HA flow temp graphs, but I have it it running on a more constant basis, and I get this feeling that it never really reaches the target flow temp, I will post some graphs on my return likely Wednesday just to get views on if this is the expectation.
I for sure know that 440% efficiency at 40c at -2 is more like 290/300%
13.6kw Solar, 27kw Battery, 10kw Heat Pump and EV Car
I think that conditions over the last couple of days are about the worst possible - cold but very wet = lots of defrost. I too am interested in what others see, mine is defrosting more than once per hour (but in fairness is just about keeping up). I suspect defrost behaviour might vary quite considerably depending on
- Available (central heating) system volume
- Whether the heat pump is oversized or right sized (this is a case where oversizing probably brings benefits)
- The specific heat pump model and how sophisticated its defrost routines are
I may start a thread!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 22 Forums
- 2,036 Topics
- 44.4 K Posts
- 38 Online
- 3,250 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: In the middle of an ASHP installation - a few questions (and issues)
Thank you @robs - that very useful data. The issue wa...
By Transparent , 2 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@sunandair don't seem to have this outside either ...
By Phoenix15 , 3 hours ago
-
RE: Air Source Heat Pump - Side Alley Suitability
All sounds sensible to me and to be clear, the idea of ...
By JamesPa , 4 hours ago
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
@editor Attached images of external insulation. Think...
By Dwynwen , 8 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
@trebor12345 The Auto function is supposed to adapt au...
By Heatgeek , 22 hours ago
-
RE: The Great British Heat Pump Quiz
@allyfish thanks for the feedback and glad it was fun! ...
By Mars , 1 day ago
-
RE: help sizing rads based on room by room heat loss
If its 1988W at DT 50, which is how most radiators are ...
By JamesPa , 1 day ago
-
RE: Career change – entering the world of heating and heat pumps
@editor Mars, thank you. That's along the routes I was ...
By Lakey , 1 day ago
-
@editor thanks Mars, it's a rare occasion I'm looking f...
By big_si , 2 days ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
@ashp-bobba and @jamespa - thank you both for all your ...
By CBrenewable , 2 days ago
-
-
Win one of five "Heat Pumps 101" Courses
Heat pumps are gaining traction in the UK, but between ...
By Mars , 2 days ago
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 3 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 3 days ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 3 days ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 3 days ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 3 days ago
-
RE: How hard and expensive would it be to change panel and add battery?
@transparent It is a setting that Octopus make via the ...
By Toodles , 3 days ago