Antifreeze protection
Hi all,
Just joined (and searched) so forgive me if this has been addressed previously.
Our Mitsubishi Ecodan ASHP has just been serviced by Mitsubishi and they are saying that the level of antifreeze in the system is no longer adequate. They measured it as protection down to -3C. They then set the freeze sat setting to on. Now the pump tends to run mostly all day, when ambient temp is cold enough, and virtually all night. They say this is designed that way. How long before the pump dies? Or am I being neurotic? Not sure I like the noise levels a night though. The obvious alternative is to top up the antifreeze. They quoted to do that but the cost is ENORMOUS. I suspect I could top it up myself but have no idea where to start. Anyone have any experience/expertise with this?
Thanks in advance.
From what I understand you mostly don't need the antifreeze in the pump. When it's cold, it's going to be running so it's not going to get to the point that it freezes. Even if it was off, it's not going to freeze in a couple of hours.
Mitsubishi recommend 25% glycol based antifreeze in the system, which (I think) protects down to -16C. I recently had to remove 3 rads. I asked the supplier if I needed to top up. He said if I topped up with water it would reduce the protection to about -10C. In the end, I bought 5L of heating glycol for £26 from screwfix and my plumbing guy topped it up.
It's a bit fiddly to top up; the easiest way is to drain a radiator, remove a bleed valve and and pour it in. This is a lot easier with a towel rail than a radiator. You could DIY or get a plumber to do it like I did.
To drain and refill the whole system will be expensive as the antifreeze alone will cost hundreds.
I wouldn't risk protection only being to -3C; that will happen and if there is a power cut you might be in trouble.
My freeze stat is set but it only comes occasionally when it's below 5C. I'll have a look at the settings later, not at home now.
@kev-m Thanks for the reply.
I was told by someone that it wasn't good practice to top up these systems via a radiator. No idea if that is correct or not.
Our property was a new build in 2019. The commissioning document states 25% antifreeze added. A year later, at the first service by Mitsubishi, they measured the protection as down to -6C. So my guess is that the 25% originally added was just guess work on behalf of the installer. They did not even mention this after the service, as an issue. I have no idea how much water the system contains but the quote from Mitsubishi specifies 35 litres of antifreeze required for protection down to -13C for installs in England. Plus a ridiculous amount for the labour. Hence the ENORMOUS quote total.
I'd never heard not to add through radiators. Too late now for me!
My freezstat settings are 20C at 5C and my cold weather function is set to -15C. I don't really know what these mean to be honest.
Posted by: @kev-mI'd never heard not to add through radiators. Too late now for me!
My freezstat settings are 20C at 5C and my cold weather function is set to -15C. I don't really know what these mean to be honest.
Hi Kev,
What is the actual description, and where are they in the manual? I may be able decipher what they mean.
When we were looking at your MMSP system, I noticed that it should have been calibrated for an antifreeze mixture of 25%. I have also read in some of the manufacturers manuals that their internal energy measurement systems do not work if antifreeze has been added to the system. When they say do not work, I think that if you set the parameter to indicate that antifreeze has been added, it does not produce any data because it knows that it will be incorrect.
@derek-m, they are on p35 of the FTC6 manual.
My flow meter has a sticker on it saying "25% glycol" so the installer at least aware that it needs to be set up that way. Whether it is, is a different story.
Posted by: @kev-m@derek-m, they are on p35 of the FTC6 manual.
My flow meter has a sticker on it saying "25% glycol" so the installer at least aware that it needs to be set up that way. Whether it is, is a different story.
Hi Kev,
I think that the sticker means that the flowmeter was calibrated with a 25% glycol mixture, so should give accurate readings provided that your system contains a 25% glycol mixture.
This is a very interesting subject, and when it comes to heat pumps, the experts are yet again divided.
Our system, for the record, has glycol in it which GES were insistent on. Heat pump purists (guys like RED) will tell you that a properly designed and installed system has no requirement for antifreeze or glycol.
Derek, however, has a great point – what happens if the power goes off after a storm and it's -5C outside and you don't get your power back for 2-3 days (over over 10 days like some households after storm Arwen).
Interesting subject and conversation.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @editorThis is a very interesting subject, and when it comes to heat pumps, the experts are yet again divided.
Our system, for the record, has glycol in it which GES were insistent on. Heat pump purists (guys like RED) will tell you that a properly designed and installed system has no requirement for antifreeze or glycol.
Derek, however, has a great point – what happens if the power goes off after a storm and it's -5C outside and you don't get your power back for 2-3 days (over over 10 days like some households after storm Arwen).
Interesting subject and conversation.
To which Derek do you refer?
@editor I should imagine that damage to your property from lack of heating would be covered by your insurance as its "storm damage" in that scenario. I am sure they might try to argue differently, however if the power goes down it doesn't matter what heating system you have - your pumps wont be working so they would all potentially suffer the same fate.
Posted by: @batalto@editor I should imagine that damage to your property from lack of heating would be covered by your insurance as its "storm damage" in that scenario. I am sure they might try to argue differently, however if the power goes down it doesn't matter what heating system you have - your pumps wont be working so they would all potentially suffer the same fate.
Hmm, If I were an insurance assessor and the ASHP I was inspecting froze and broke because it hadn't been filled to the correct spec, I might recommend not paying out.
- 22 Forums
- 2,084 Topics
- 46 K Posts
- 25 Online
- 3,377 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
@judith good to know… I’ll continue to feed Wattson, an...
By Mars , 8 hours ago
-
RE: Vaillant AroTherm Plus 7kW
@jamespa I have a hydronic baseboard heater in the kitc...
By Scalextrix , 14 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
I think that QR code is to download the app SmartHome o...
By cathodeRay , 20 hours ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
@editor great article re accreditation. I note ISO/IEC ...
By Bart , 23 hours ago
-
RE: Renewables & Heat Pumps in the News
Here’s a little more technical detail/p>
By Judith , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
I don't (yet), but my PW3 is due to be installed shortl...
By Old_Scientist , 2 days ago
-
RE: MCS and NAPIT complaints process
@chrislay, is your heat pump complaint still unresolved...
By Mars , 2 days ago
-
RE: ASHP Install from hell - help please
@saf1973 I’ve been going through old cases on the forum...
By Mars , 2 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron There's the rub, the database does not list my ...
By AF1 , 2 days ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@editor excellent news, congratulations and well deserv...
By ASHP-BOBBA , 2 days ago
-
RE: Commencing on an ASHP Installation Process
Yes, it's "doable" if everything goes to plan, they arr...
By Old_Scientist , 4 days ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 4 days ago
-
RE: DHW SET UP with Samsung gen 5
Thats good news indeed, you are very likely almost ther...
By JamesPa , 4 days ago
-
RE: Plate heat exchanger considerations
As far as I can tell my vented system would have a peak...
By Scalextrix , 5 days ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
There have been a few discussions dotted around (e.g. I...
By Declan90 , 5 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having made some enquiries locally I have found a compa...
By Morgan , 5 days ago