Antifreeze protection
Hi all,
Just joined (and searched) so forgive me if this has been addressed previously.
Our Mitsubishi Ecodan ASHP has just been serviced by Mitsubishi and they are saying that the level of antifreeze in the system is no longer adequate. They measured it as protection down to -3C. They then set the freeze sat setting to on. Now the pump tends to run mostly all day, when ambient temp is cold enough, and virtually all night. They say this is designed that way. How long before the pump dies? Or am I being neurotic? Not sure I like the noise levels a night though. The obvious alternative is to top up the antifreeze. They quoted to do that but the cost is ENORMOUS. I suspect I could top it up myself but have no idea where to start. Anyone have any experience/expertise with this?
Thanks in advance.
From what I understand you mostly don't need the antifreeze in the pump. When it's cold, it's going to be running so it's not going to get to the point that it freezes. Even if it was off, it's not going to freeze in a couple of hours.
Mitsubishi recommend 25% glycol based antifreeze in the system, which (I think) protects down to -16C. I recently had to remove 3 rads. I asked the supplier if I needed to top up. He said if I topped up with water it would reduce the protection to about -10C. In the end, I bought 5L of heating glycol for £26 from screwfix and my plumbing guy topped it up.
It's a bit fiddly to top up; the easiest way is to drain a radiator, remove a bleed valve and and pour it in. This is a lot easier with a towel rail than a radiator. You could DIY or get a plumber to do it like I did.
To drain and refill the whole system will be expensive as the antifreeze alone will cost hundreds.
I wouldn't risk protection only being to -3C; that will happen and if there is a power cut you might be in trouble.
My freeze stat is set but it only comes occasionally when it's below 5C. I'll have a look at the settings later, not at home now.
@kev-m Thanks for the reply.
I was told by someone that it wasn't good practice to top up these systems via a radiator. No idea if that is correct or not.
Our property was a new build in 2019. The commissioning document states 25% antifreeze added. A year later, at the first service by Mitsubishi, they measured the protection as down to -6C. So my guess is that the 25% originally added was just guess work on behalf of the installer. They did not even mention this after the service, as an issue. I have no idea how much water the system contains but the quote from Mitsubishi specifies 35 litres of antifreeze required for protection down to -13C for installs in England. Plus a ridiculous amount for the labour. Hence the ENORMOUS quote total.
I'd never heard not to add through radiators. Too late now for me!
My freezstat settings are 20C at 5C and my cold weather function is set to -15C. I don't really know what these mean to be honest.
Posted by: @kev-mI'd never heard not to add through radiators. Too late now for me!
My freezstat settings are 20C at 5C and my cold weather function is set to -15C. I don't really know what these mean to be honest.
Hi Kev,
What is the actual description, and where are they in the manual? I may be able decipher what they mean.
When we were looking at your MMSP system, I noticed that it should have been calibrated for an antifreeze mixture of 25%. I have also read in some of the manufacturers manuals that their internal energy measurement systems do not work if antifreeze has been added to the system. When they say do not work, I think that if you set the parameter to indicate that antifreeze has been added, it does not produce any data because it knows that it will be incorrect.
@derek-m, they are on p35 of the FTC6 manual.
My flow meter has a sticker on it saying "25% glycol" so the installer at least aware that it needs to be set up that way. Whether it is, is a different story.
Posted by: @kev-m@derek-m, they are on p35 of the FTC6 manual.
My flow meter has a sticker on it saying "25% glycol" so the installer at least aware that it needs to be set up that way. Whether it is, is a different story.
Hi Kev,
I think that the sticker means that the flowmeter was calibrated with a 25% glycol mixture, so should give accurate readings provided that your system contains a 25% glycol mixture.
This is a very interesting subject, and when it comes to heat pumps, the experts are yet again divided.
Our system, for the record, has glycol in it which GES were insistent on. Heat pump purists (guys like RED) will tell you that a properly designed and installed system has no requirement for antifreeze or glycol.
Derek, however, has a great point – what happens if the power goes off after a storm and it's -5C outside and you don't get your power back for 2-3 days (over over 10 days like some households after storm Arwen).
Interesting subject and conversation.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @editorThis is a very interesting subject, and when it comes to heat pumps, the experts are yet again divided.
Our system, for the record, has glycol in it which GES were insistent on. Heat pump purists (guys like RED) will tell you that a properly designed and installed system has no requirement for antifreeze or glycol.
Derek, however, has a great point – what happens if the power goes off after a storm and it's -5C outside and you don't get your power back for 2-3 days (over over 10 days like some households after storm Arwen).
Interesting subject and conversation.
To which Derek do you refer?
@editor I should imagine that damage to your property from lack of heating would be covered by your insurance as its "storm damage" in that scenario. I am sure they might try to argue differently, however if the power goes down it doesn't matter what heating system you have - your pumps wont be working so they would all potentially suffer the same fate.
Posted by: @batalto@editor I should imagine that damage to your property from lack of heating would be covered by your insurance as its "storm damage" in that scenario. I am sure they might try to argue differently, however if the power goes down it doesn't matter what heating system you have - your pumps wont be working so they would all potentially suffer the same fate.
Hmm, If I were an insurance assessor and the ASHP I was inspecting froze and broke because it hadn't been filled to the correct spec, I might recommend not paying out.
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 56 Online
- 2,277 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 2 hours ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 2 hours ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami I think if the heat loss documentation matches a ...
By bontwoody , 2 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa I'm afraid that's over my head but if anyon...
By IRMartini , 3 hours ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 3 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 3 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 5 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 7 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 9 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 21 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 24 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 9 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 10 hours ago
-
SolarPV tables / online calculator
By MichelleC 17 hours ago
-
By Toodles 2 days ago