Antifreeze protection

45 Posts
15 Users
27 Likes
9,854 Views
(@scratchyman)
Eminent Member Member
11 kWhs
Joined: 2 years ago
Posts: 7
Topic starter  

Hi all,

Just joined (and searched) so forgive me if this has been addressed previously.

Our Mitsubishi Ecodan ASHP has just been serviced by Mitsubishi and they are saying that the level of antifreeze in the system is no longer adequate. They measured it as protection down to -3C. They then set the freeze sat setting to on. Now the pump tends to run mostly all day, when ambient temp is cold enough, and virtually all night. They say this is designed that way. How long before the pump dies? Or am I being neurotic? Not sure I like the noise levels a night though. The obvious alternative is to top up the antifreeze. They quoted to do that but the cost is ENORMOUS. I suspect I could top it up myself but have no idea where to start. Anyone have any experience/expertise with this?

Thanks in advance.

 


   
Quote
(@batalto)
Famed Member Member
3655 kWhs
Joined: 3 years ago
Posts: 1091
 

From what I understand you mostly don't need the antifreeze in the pump. When it's cold, it's going to be running so it's not going to get to the point that it freezes. Even if it was off, it's not going to freeze in a couple of hours.

12kW Midea ASHP - 8.4kw solar - 29kWh batteries
262m2 house in Hampshire
Current weather compensation: 47@-2 and 31@17
My current performance can be found - HERE
Heat pump calculator spreadsheet - HERE


   
ReplyQuote
(@kev-m)
Famed Member Moderator
5561 kWhs
Joined: 3 years ago
Posts: 1299
 

Mitsubishi recommend 25% glycol based antifreeze in the system, which (I think) protects down to -16C.  I recently had to remove 3 rads.  I asked the supplier if I needed to top up. He said if I topped up with water it would reduce the protection to about -10C. In the end, I bought 5L of heating glycol for £26 from screwfix and my plumbing guy topped it up.   

It's a bit fiddly to top up; the easiest way is to drain a radiator, remove a bleed valve and  and pour it in.  This is a lot easier with a towel rail than a radiator.  You could DIY or get a plumber to do it like I did.  

To drain and refill the whole system will be expensive as the antifreeze alone will cost hundreds. 

I wouldn't risk protection only being to -3C; that will happen and if there is a power cut you might be in trouble. 

My freeze stat is set but it only comes occasionally when it's below 5C.  I'll have a look at the settings later, not at home now.


   
ReplyQuote



(@scratchyman)
Eminent Member Member
11 kWhs
Joined: 2 years ago
Posts: 7
Topic starter  

@kev-m Thanks for the reply.

I was told by someone that it wasn't good practice to top up these systems via a radiator. No idea if that is correct or not.

Our property was a new build in 2019. The commissioning document states 25% antifreeze added. A year later, at the first service by Mitsubishi, they measured the protection as down to -6C. So my guess is that the 25% originally added was just guess work on behalf of the installer. They did not even mention this after the service, as an issue. I have no idea how much water the system contains but the quote from Mitsubishi specifies 35 litres of antifreeze required for protection down to -13C for installs in England. Plus a ridiculous amount for the labour. Hence the ENORMOUS quote total. 


   
ReplyQuote
(@kev-m)
Famed Member Moderator
5561 kWhs
Joined: 3 years ago
Posts: 1299
 

@scratchyman 

I'd never heard not to add through radiators.  Too late now for me! 

My freezstat settings are 20C at 5C and my cold weather function is set to -15C.  I don't really know what these mean to be honest.


   
ReplyQuote
(@derek-m)
Illustrious Member Moderator
13648 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4158
 
Posted by: @kev-m

@scratchyman 

I'd never heard not to add through radiators.  Too late now for me! 

My freezstat settings are 20C at 5C and my cold weather function is set to -15C.  I don't really know what these mean to be honest.

Hi Kev,

What is the actual description, and where are they in the manual? I may be able decipher what they mean.

When we were looking at your MMSP system, I noticed that it should have been calibrated for an antifreeze mixture of 25%. I have also read in some of the manufacturers manuals that their internal energy measurement systems do not work if antifreeze has been added to the system. When they say do not work, I think that if you set the parameter to indicate that antifreeze has been added, it does not produce any data because it knows that it will be incorrect.


   
ReplyQuote
(@kev-m)
Famed Member Moderator
5561 kWhs
Joined: 3 years ago
Posts: 1299
 

@derek-m, they are on p35 of the FTC6 manual.

My flow meter has a sticker on it saying "25% glycol" so the installer at least aware that it needs to be set up that way. Whether it is, is a different story.

 


   
ReplyQuote
(@derek-m)
Illustrious Member Moderator
13648 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4158
 
Posted by: @kev-m

@derek-m, they are on p35 of the FTC6 manual.

My flow meter has a sticker on it saying "25% glycol" so the installer at least aware that it needs to be set up that way. Whether it is, is a different story.

 

Hi Kev,

I think that the sticker means that the flowmeter was calibrated with a 25% glycol mixture, so should give accurate readings provided that your system contains a 25% glycol mixture.


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
16750 kWhs
Veteran
Joined: 3 years ago
Posts: 2316
 

This is a very interesting subject, and when it comes to heat pumps, the experts are yet again divided.

Our system, for the record, has glycol in it which GES were insistent on. Heat pump purists (guys like RED) will tell you that a properly designed and installed system has no requirement for antifreeze or glycol.

Derek, however, has a great point – what happens if the power goes off after a storm and it's -5C outside and you don't get your power back for 2-3 days (over over 10 days like some households after storm Arwen). 

Interesting subject and conversation. 

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU

Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk


   
ReplyQuote



(@derek-m)
Illustrious Member Moderator
13648 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4158
 
Posted by: @editor

This is a very interesting subject, and when it comes to heat pumps, the experts are yet again divided.

Our system, for the record, has glycol in it which GES were insistent on. Heat pump purists (guys like RED) will tell you that a properly designed and installed system has no requirement for antifreeze or glycol.

Derek, however, has a great point – what happens if the power goes off after a storm and it's -5C outside and you don't get your power back for 2-3 days (over over 10 days like some households after storm Arwen). 

Interesting subject and conversation. 

To which Derek do you refer?


   
Mars and Mars reacted
ReplyQuote
(@batalto)
Famed Member Member
3655 kWhs
Joined: 3 years ago
Posts: 1091
 

@editor I should imagine that damage to your property from lack of heating would be covered by your insurance as its "storm damage" in that scenario. I am sure they might try to argue differently, however if the power goes down it doesn't matter what heating system you have - your pumps wont be working so they would all potentially suffer the same fate.

12kW Midea ASHP - 8.4kw solar - 29kWh batteries
262m2 house in Hampshire
Current weather compensation: 47@-2 and 31@17
My current performance can be found - HERE
Heat pump calculator spreadsheet - HERE


   
Mars and Mars reacted
ReplyQuote
(@kev-m)
Famed Member Moderator
5561 kWhs
Joined: 3 years ago
Posts: 1299
 
Posted by: @batalto

@editor I should imagine that damage to your property from lack of heating would be covered by your insurance as its "storm damage" in that scenario. I am sure they might try to argue differently, however if the power goes down it doesn't matter what heating system you have - your pumps wont be working so they would all potentially suffer the same fate.

Hmm, If I were an insurance assessor and the ASHP I was inspecting froze and broke because it hadn't been filled to the correct spec, I might recommend not paying out. 

 

This post was modified 2 years ago by Kev M

   
ReplyQuote