Another ASHP Performance Thread - 13kW Grant Aerona
Hi Everyone
New to the forum - having had a cold week wondering why my Grant Heat Pump isn't keeping the house warm in the cold weather.
My heat pump was installed a year ago and so this is our first winter experience with it. The system seems to have been running well all year but the cold snap in late November and again this week have proved to be somewhat challenging for the heat pump - and we've ended up with several plug in electric heaters on the go and still not managed to keep the house at comfortable temperatures.
I have raised this with our installer who came back in December to do a service and connected up the backup heater in the volumiser (aimed at compensating for the frequent defrost cycles) but we're watching the performance to see what further action might be needed.
I'm quite keen to get a better handle on exactly what's going on so have been reading my manual and checking the settings. I was already quite up to speed on the WC settings and have tinkered with it a few times during the year to try to fine tune things. Following the previous cold snap I had set the Max temperature to 50deg at 3deg outside temperature. However, I have only just discovered how to lookup the flow and return temperatures in the control panel and was a bit surprised to see that it was at 40deg today when the outside temperature was around 0 to 1deg. The return temperature was 36.
I feel like it would be useful to collect a lot more data on how my system is performing to support further analysis - I've seen people posting detailed charts of their heat pump's key parameters and am wondering if and how such data can be collected and downloaded from my Grant Aerona system?
Also, now that I've found the flow and return temperatures I've been calculating the heat output using the flow rate but I wanted to check if I'm reading the flow rate correctly - should I be looking at the top or the bottom of the float? Picture below - is this 29l/min or 37l/min?
I'll follow up with some more details in due course but just wanted to pose those two questions in the first instance to try to get my head around what the situation is. Thanks in advance for any pointers.
Grant Aerona3 13kW
If you remove the insulation from around the flow rate indicator, you should be able to see details of the make and model. Google these details and see what information you can find that should hopefully state how to correctly read the device.
The standard flow regulator which comes with the Grant (and I think yours looks like one), you read from the bottom of the float, so 29l/m if I can see correctly. The base of the float in my regulator is clean. There's seems to be some build-up on yours, or maybe that's just the photo?
In terms of getting data from the Grant, it has an RS485 interface (pins 15 and 16 of the outside unit's PCB) which is enabled by default, and this can be used to read most (if not all) of the parameters detailed within the various Grant guides (at the very least, the 10 numbers displayed in user mode of the remote controller) using the modbus protocol. Although be aware that these figures seem to be less precise than those used by the unit itself (e.g. the Outdoor Air Temperature sent over the interface is only to 1 degree granularity, but the remote controller gives the value to nearest 0.5C - possibly a flaw in the on-board implementation of the interface*). I believe an installation of Home Assistant (there may be others) enables this data to be recorded/displayed, but building your own recording system is a fairly simple task, if you're inclined. Wiring up the interface and getting the other end of the cable to somewhere hospitable is probably the trickiest step.
Have a look at this page, which gives an outline of what's involved.
For my own set-up, I have some external grade network capable wired to the HP, going through to this device which is plugged into a Raspberry Pi sitting in a bedroom cupboard. That just runs a script every minute to pull data from the HP and write it to a database for later analysis/display.
*I wonder if the Homely - or Grant's latest 'smart' - controller receive finer data...
QUESTION for @Rupes - have you found any improvement to performance with the backup heater enabled (I presume only for 'defrost' support), and has this increased/reduced overall energy consumption? (I know this is a 'piece of string' question, as there are so many variables).
Grant Aerona 3 10kW
@mikefl Thanks for the response.
I’ll work on the basis of the 29l/min for now - that does seem the more logical - but I’ll see if the installer can confirm too.
I’m inclined to have a go at setting up a modbus connection and Raspberry Pi arrangement. I think I need some meaningful data to be able to figure out what the problem is.
Regarding the “defrost support” - my installer told me that it was set up to only kick in at outside temperatures of -2 and below when the temperature at the volumiser falls below 50deg - so there should have been some occurences this week but without watching it all the time I’ve no idea if it worked or not hence I need to collect some data. It certainly hasn’t noticably improved anything.
Grant Aerona3 13kW
Been approached by a neighbour who has a newly built home with underfloor heating. His Nibe ASHP system is handling heating fine but when the air temp falls below 5 degrees C his hot water really struggles to get above 35 degrees.
I am no expert but my own Nibe system has never struggled with hot water temp. What are the key things to be checking on his as SMO 20 contoller?
@nibemachawk I'm no expert either and not familiar with the Nibe system. Mine is the opposite problem - no problem heating up water and delivering high flow temperatures required but struggles with the heating. But some thoughts...
In terms of what to look out for - my controller clearly shows on the display if it is working to produce heating or hot water. It is set up such that it will only do one or the other at any one time - due to the higher heating needs of the hot water. In addition to the symbols showing on the controller - I can see which zone valve is open (they have LEDs on them in my system). I have three zone valves: radiators, underfloor heating and hot water. Again, when the hot water is being heated, it can be clearly seen that the other two valves are closed. I guess if the system was trying to do both heating and hot water at the same time then it's likely it would struggle to heat up the water sufficiently.
Grant Aerona3 13kW
So, thanks to the suggestion from @mikefl I am now up and running with Home Assistant and a wired connection from my heat pump into an old laptop. Setup was easier than I anticipated in the end.
First chart output here…
I have drawn a few interim conclusions:
- The HP is not performing well at outdoor temperatures below about 3-4deg.
- The HP is not achieving the weather compensation curve at these low temperatures.
- DT seems to be fairly static at 4deg.
- Flow rate is static at about 33l/min (fixed pump speed) although seems to have increased a bit today somehow.
- The heat pump is outputting about 9.5-10kW.
So, given that the house is too cold af these temperatures, how can I access the additional 3kW of rated capacity that my heat pump is supposed to have? Why is it not using this to deliver the higher heat requirement that the WC curve and thermostats are demanding?
Grant Aerona3 13kW
Your conclusions (1) and (2) are probably valid, and common for most ASHPs it seems - the defrost cycles nobble performance, as although they only take 5 minutes to happen, it takes about 20 minutes for performance to recover. If that's happening every 40 minutes, your performance is half what it could be.
DT of 4 is around what I get; obviously varies based on internal temp, and LWT, and is generally wider whilst things are "getting up to speed".
Possibly to get your hands on that 3kW you need to adjust other parameters - I know it can operate in a purely "help with defrost" mode or as "help with heating" (altho obviously that's at a COP of 1 at best). The LLH installation guide (attached)
gives Grant's suggestion for values, so maybe you need to be more aggressive on the temp for turning on? Including Outdoor Air Temp on your graphs to see if it's triggered - although I'm unsure if the value for 'Current Consumption (01 03)' will include the 3Kw from the LLH.
Another thing, less easy to check is how well balanced flows are either side of the LLH. These need to be roughly the same, which can be tricky to achieve when you probably only have 3 to 5 options for flow rate on the secondary side. I've tried to balance mine using temp sensors on the 4 flow/return pipes either side of the LLH, to get something like equal deltaT (and hence about equal flows, given energy must be the same). Unbalanced flows can mean you're recycling return water on one side or another (various topics about this elsewhere on the forum).
Grant Aerona 3 10kW
-
New Installation - Grant Aerona 3 + 210L Hot Water Cylinder
12 months ago
-
Grant Aerona 3 Help programing
1 year ago
- 22 Forums
- 2,032 Topics
- 44.3 K Posts
- 25 Online
- 3,237 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 2 hours ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
Welcome to the forums. It’s clear that you’ve taken t...
By Mars , 3 hours ago
-
RE: help sizing rads based on room by room heat loss
By JamesPa , 3 hours ago
-
Hi Thanks for the reply, the walls are being constru...
By Fingers , 5 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15 I'm no plumber so please don't take this as ...
By dnagre , 6 hours ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 10 hours ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 10 hours ago
-
The Rise and Fall of Europe’s Most Generous Green Subsidy
This story came to my attention thanks to Graham Hendra...
By Mars , 10 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 10 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
From the Full SAP Report: Space heating requirements:...
By trebor12345 , 10 hours ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 14 hours ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 17 hours ago
-
RE: How hard and expensive would it be to change panel and add battery?
@transparent It is a setting that Octopus make via the ...
By Toodles , 17 hours ago
-
RE: Performance of Heat Pumps in Mild Weather
@heatgeek The flow rate isnt controlled by Mitsub...
By RobS , 20 hours ago
-
RE: Say hello and introduce yourself
I might put a couple of speakers in the ceiling if fund...
By Fingers , 1 day ago
-
RE: Bathroom Radiator replacement
@rob-nezard can you please offer your professional advi...
By Mars , 2 days ago
-
-
RE: Questions on my Hitachi Yutaki SCombi Heat Pump
OK, thats good and low. With low flow temperatures lik...
By JamesPa , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa “They are all equal but, some are more equal t...
By Toodles , 2 days ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
@cliffhanger Mine has a 'space heating off' setting! O...
By JamesPa , 3 days ago