Another ASHP Performance Thread - 13kW Grant Aerona
Hi Everyone
New to the forum - having had a cold week wondering why my Grant Heat Pump isn't keeping the house warm in the cold weather.
My heat pump was installed a year ago and so this is our first winter experience with it. The system seems to have been running well all year but the cold snap in late November and again this week have proved to be somewhat challenging for the heat pump - and we've ended up with several plug in electric heaters on the go and still not managed to keep the house at comfortable temperatures.
I have raised this with our installer who came back in December to do a service and connected up the backup heater in the volumiser (aimed at compensating for the frequent defrost cycles) but we're watching the performance to see what further action might be needed.
I'm quite keen to get a better handle on exactly what's going on so have been reading my manual and checking the settings. I was already quite up to speed on the WC settings and have tinkered with it a few times during the year to try to fine tune things. Following the previous cold snap I had set the Max temperature to 50deg at 3deg outside temperature. However, I have only just discovered how to lookup the flow and return temperatures in the control panel and was a bit surprised to see that it was at 40deg today when the outside temperature was around 0 to 1deg. The return temperature was 36.
I feel like it would be useful to collect a lot more data on how my system is performing to support further analysis - I've seen people posting detailed charts of their heat pump's key parameters and am wondering if and how such data can be collected and downloaded from my Grant Aerona system?
Also, now that I've found the flow and return temperatures I've been calculating the heat output using the flow rate but I wanted to check if I'm reading the flow rate correctly - should I be looking at the top or the bottom of the float? Picture below - is this 29l/min or 37l/min?
I'll follow up with some more details in due course but just wanted to pose those two questions in the first instance to try to get my head around what the situation is. Thanks in advance for any pointers.
Grant Aerona3 13kW
If you remove the insulation from around the flow rate indicator, you should be able to see details of the make and model. Google these details and see what information you can find that should hopefully state how to correctly read the device.
The standard flow regulator which comes with the Grant (and I think yours looks like one), you read from the bottom of the float, so 29l/m if I can see correctly. The base of the float in my regulator is clean. There's seems to be some build-up on yours, or maybe that's just the photo?
In terms of getting data from the Grant, it has an RS485 interface (pins 15 and 16 of the outside unit's PCB) which is enabled by default, and this can be used to read most (if not all) of the parameters detailed within the various Grant guides (at the very least, the 10 numbers displayed in user mode of the remote controller) using the modbus protocol. Although be aware that these figures seem to be less precise than those used by the unit itself (e.g. the Outdoor Air Temperature sent over the interface is only to 1 degree granularity, but the remote controller gives the value to nearest 0.5C - possibly a flaw in the on-board implementation of the interface*). I believe an installation of Home Assistant (there may be others) enables this data to be recorded/displayed, but building your own recording system is a fairly simple task, if you're inclined. Wiring up the interface and getting the other end of the cable to somewhere hospitable is probably the trickiest step.
Have a look at this page, which gives an outline of what's involved.
For my own set-up, I have some external grade network capable wired to the HP, going through to this device which is plugged into a Raspberry Pi sitting in a bedroom cupboard. That just runs a script every minute to pull data from the HP and write it to a database for later analysis/display.
*I wonder if the Homely - or Grant's latest 'smart' - controller receive finer data...
QUESTION for @Rupes - have you found any improvement to performance with the backup heater enabled (I presume only for 'defrost' support), and has this increased/reduced overall energy consumption? (I know this is a 'piece of string' question, as there are so many variables).
Grant Aerona 3 10kW
@mikefl Thanks for the response.
I’ll work on the basis of the 29l/min for now - that does seem the more logical - but I’ll see if the installer can confirm too.
I’m inclined to have a go at setting up a modbus connection and Raspberry Pi arrangement. I think I need some meaningful data to be able to figure out what the problem is.
Regarding the “defrost support” - my installer told me that it was set up to only kick in at outside temperatures of -2 and below when the temperature at the volumiser falls below 50deg - so there should have been some occurences this week but without watching it all the time I’ve no idea if it worked or not hence I need to collect some data. It certainly hasn’t noticably improved anything.
Grant Aerona3 13kW
Been approached by a neighbour who has a newly built home with underfloor heating. His Nibe ASHP system is handling heating fine but when the air temp falls below 5 degrees C his hot water really struggles to get above 35 degrees.
I am no expert but my own Nibe system has never struggled with hot water temp. What are the key things to be checking on his as SMO 20 contoller?
@nibemachawk I'm no expert either and not familiar with the Nibe system. Mine is the opposite problem - no problem heating up water and delivering high flow temperatures required but struggles with the heating. But some thoughts...
In terms of what to look out for - my controller clearly shows on the display if it is working to produce heating or hot water. It is set up such that it will only do one or the other at any one time - due to the higher heating needs of the hot water. In addition to the symbols showing on the controller - I can see which zone valve is open (they have LEDs on them in my system). I have three zone valves: radiators, underfloor heating and hot water. Again, when the hot water is being heated, it can be clearly seen that the other two valves are closed. I guess if the system was trying to do both heating and hot water at the same time then it's likely it would struggle to heat up the water sufficiently.
Grant Aerona3 13kW
So, thanks to the suggestion from @mikefl I am now up and running with Home Assistant and a wired connection from my heat pump into an old laptop. Setup was easier than I anticipated in the end.
First chart output here…
I have drawn a few interim conclusions:
- The HP is not performing well at outdoor temperatures below about 3-4deg.
- The HP is not achieving the weather compensation curve at these low temperatures.
- DT seems to be fairly static at 4deg.
- Flow rate is static at about 33l/min (fixed pump speed) although seems to have increased a bit today somehow.
- The heat pump is outputting about 9.5-10kW.
So, given that the house is too cold af these temperatures, how can I access the additional 3kW of rated capacity that my heat pump is supposed to have? Why is it not using this to deliver the higher heat requirement that the WC curve and thermostats are demanding?
Grant Aerona3 13kW
Your conclusions (1) and (2) are probably valid, and common for most ASHPs it seems - the defrost cycles nobble performance, as although they only take 5 minutes to happen, it takes about 20 minutes for performance to recover. If that's happening every 40 minutes, your performance is half what it could be.
DT of 4 is around what I get; obviously varies based on internal temp, and LWT, and is generally wider whilst things are "getting up to speed".
Possibly to get your hands on that 3kW you need to adjust other parameters - I know it can operate in a purely "help with defrost" mode or as "help with heating" (altho obviously that's at a COP of 1 at best). The LLH installation guide (attached)
gives Grant's suggestion for values, so maybe you need to be more aggressive on the temp for turning on? Including Outdoor Air Temp on your graphs to see if it's triggered - although I'm unsure if the value for 'Current Consumption (01 03)' will include the 3Kw from the LLH.
Another thing, less easy to check is how well balanced flows are either side of the LLH. These need to be roughly the same, which can be tricky to achieve when you probably only have 3 to 5 options for flow rate on the secondary side. I've tried to balance mine using temp sensors on the 4 flow/return pipes either side of the LLH, to get something like equal deltaT (and hence about equal flows, given energy must be the same). Unbalanced flows can mean you're recycling return water on one side or another (various topics about this elsewhere on the forum).
Grant Aerona 3 10kW
-
New Installation - Grant Aerona 3 + 210L Hot Water Cylinder
1 year ago
-
Grant Aerona 3 Help programing
2 years ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 39 Online
- 5,662 Members
Podcast Picks
Latest Posts
-
RE: Does anyone have experience of a smart water meter?
Sorry, @transparent, but I disagree. Legislation brough...
By Majordennisbloodnok , 11 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 17 hours ago
-
@bontwoody me too. I've contacted Heat Geek today, and ...
By Mars , 21 hours ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 22 hours ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 2 days ago
-
RE: Mitsu Wireless Controller and MelCloud
Well it has now become obvious that the installation of...
By DavidAlgarve , 2 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 3 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 4 days ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 4 days ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 5 days ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 5 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 6 days ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 7 days ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 7 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 7 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 1 week ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 1 week ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 1 week ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 1 week ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 1 week ago