I failed to say that the design allows for a 50C flow temperature but since the engineer did some fettling I have not investigated it again.
Posted by: @timatheronwoodI failed to say that the design allows for a 50C flow temperature but since the engineer did some fettling I have not investigated it again.
Oh, you can't beat a good 'fettle'. 😋
I had the unit set to 18 overnight (till 4am) and 19 from then on but this morning at 6am the temperature in the house was down to 17.5C It had not risen beyond that by 10am. At 12 noon the temperature had risen to 18C in the house. I have changed the slope of the "curve" so that it now reaches maximum at 0C instead of -10C. This afternoon the temperature had risen to 18.5C and I have changed the temperatures to 20C in the day and 19 at night to cope with the cold weather.
Could this be due to the unit not meeting the design spec for output temperature. The Daikin literature says that we should be able to get a 65C output. But the most I have ever seen is 45C even thought it is set to 63C.
Any thoughts anyone?
If Homeowners are prepared to provide the information, then maybe a spreadsheet containing the following information would be of most use from the comparison, and highlighting of possible problems, point of view.
Forum Handle: Toodles
Manufacturer: Daikin
Model: EDLA082V3
Type: ASHP
Arrangement: Mono
Area of Country: Berkshire
Home Type: 4 bed semi 1930’s build
Size: Square Metres:95
Insulation Level: Scale of 1 to 10 possibly? 10
Heat Loss Calculation: kW @ Amb. Temp, of: ?C 6.5 kW
Type of Controller: Modulating
Type of Control: Weather Compensation, LWT setting
System Type: Radiators (Mainly new for LT use)
Total Output of Heat Emitters: kW
Buffer Tank or Low Loss Header: LLH
Secondary Pumps: Number or No 1
Solar PV System: Size or No 8.1 kWp
Power Diverter: Yes
Battery System: Size; 13.5 kW/h Tesla Powerwall
Anything else that anyone can think may be useful. Please feel free to rearrange the order. In this milder weather, we are running at 22.5 degrees nominally (we like a warm house!) and are using approx. 0.5 kW/h
For my personal viewing only, bank account details and all necessary passwords and access codes. If I told you, I would have to terminate your existence! Regardsd, Toodles
Toodles, 76 years young and hoping to see 100 and make some ROI on my renewable energy investment!
Perhaps I should add to the above system (sorry, but I failed to be able to edit the entry) based on a Daikin 8 kW ASHP that the domestic hot water heating is handled by a Sunamp Thermino ePV210 heat battery. The reason being, space is at a premium and the MCS guideline for a 4 bedroom house is 210 litres of DHW storage and we just do not have a space for such a tank! The Thermino is considerably smaller and can be accommodated (just!) in our airing cupboard - the insulation is extremely good so the total heat loss in 24 hours is less than 0.75 kW/h, so very little warming is available in the airing cupboard - just the lost heat coming from the unlagged plumbing from the LLH etc. and this helps to provide a background warmth in the cupboard.
I scored 10 myself for insulation as we have double glazing (triple in one room), cavity wall insulation, underfloor insulation from Q-Bot on the ground floor and approx. 40 cm. of loft insulation plus boarding sandwiched in the middle, plus we have approx. 5 cm. thick insulating board with a foil face between all the roof truce work just below the roofing felt. Our EPC rating before installing the Solar PV, battery and then the ASHP was a ‘B’ with notes indicating that Solar PV and / or Heat Pump would improve the rating.
I hope to incorporate an Evergreen Homely smart thermostat system for ASHP control as soon as a compatible device for the Daikin is available. Perhaps I should also mention that the Power Diverter is the Myenergi Eddi with a Harvi and several CT Clamps. We are using the Octopus Energy Agile and Agile Outgoing tariffs for import and export (no James Bond involvement however). 😉 Regards, Toodles
Toodles, 76 years young and hoping to see 100 and make some ROI on my renewable energy investment!
If Homeowners are prepared to provide the information, then maybe a spreadsheet containing the following information would be of most use from the comparison, and highlighting of possible problems, point of view.
Forum Handle: @FJJ
Manufacturer: Grant
Model: HPID10R32
Type: ASHP
Arrangement: Mono
Area of Country: Warwickshire
Home Type: 3 bed detached 1970's
Size: Square Metres: 100
Insulation Level: Scale of 1 to 10 possibly? 7
Heat Loss Calculation: kW @ Amb. Temp, of: -1.1C 6.8 kW
Type of Controller: Modulating
Type of Control: Weather Compensation
System Type: Radiators (5K3, 3K2, 1K1 Stelrad compact)
Total Output of Heat Emitters: not known
Buffer Tank or Low Loss Header: LLH
Secondary Pumps: Number 1
Solar PV System: Size or No 8 kW
Power Diverter: Yes
Battery System: Size; 10Kw Solaredge Powerbank
Forum Handle: MikeFl
Manufacturer: Grant
Model: Aerona HPID10R32
Type: ASHP
Arrangement: Mono
Area of Country: Cumbria
Home Type: Dormer Bungalow
Size: Square Metres: 148
Insulation Level: 7? (Loft/eaves insulation topped up with 30mm+; Room in Roof insulation is less
Heat Loss Calculation: 9-10kW @ Amb. Temp, of: 10C (this is my calculation - hope the installer has a better one)
Type of Controller: Two zones (up/down) controlled by room thermostats, with TRVs on all but two radiators
Type of Control: Fixed flow temperate at installation, possibly.
System Type: Radiators
Total Output of Heat Emitters: K2 *3, K3 * 4, K1 * 1
Buffer Tank or Low Loss Header: Grant volumiser / LLH
Secondary Pumps: 1(Grundfos ups3 15-50)
Solar PV System: No
Power Diverter: No
Battery System: No
Water cylinder is a FlowCyl Slimline 170L (FCHPS2170) with 24kW heating coil installed.
Grant Aerona 3 10kW
Forum Handle: Madrajin
Manufacturer: Vaillant
Model: Arotherm Plus 7kw, UniTower plus, sensoComfort
Type: ASHP
Arrangement: Monoblock, high temp I think.
Area of Country: General Location
Home Type: House solid wall construction, built 1763 (uniTower located in outhouse)
Size: Square Metres: 126m2
Insulation Level: Scale of 1 to 10 possibly? Listed as energy mark D when I bought it
Heat Loss Calculation: kW @ Amb. Temp, of: ?C
Type of Controller: unknown (sensoComfort), EveThermo TRV
Type of Control: Adaptive, Weather Compensation, Flow Temperature, Room Temperature
System Type: Radiators unchanged, mostly double.
Total Output of Heat Emitters: ? kW
Buffer Tank or Low Loss Header: No
Secondary Pumps: No
Solar PV System: No
Power Diverter: No
Battery System: No
Forum Handle: GC61
Manufacturer: Viessmann
Model: Vitocal 151-A
Type: ASHP
Arrangement: Mono
Area of Country: Ireland
Home Type: 2-Storey detached
Size: 180 sqm
Insulation Level: 8
Heat Loss Calculation: 1.63
Type of Controller: Viessmann Vitotrol 300-E
Type of Control: Weather Compensation / Flow Temperature / Room Temperature
System Type: UFH and radiators
Total Output of Heat Emitters:
Buffer Tank or Low Loss Header:
Secondary Pumps:
Solar PV System: 4.2KW
Power Diverter: No
Battery System: No
Forum Handle: @dougmlancs
Manufacturer: Panasonic
Model: Aquarea L (R290)
Type: ASHP
Arrangement: Split with hydraulic connection
Area of Country: Lancashire
Home Type: Semi-detached house
Size: Square Metres: 110
Insulation Level: CWI, DG + 300mm loft
Heat Loss Calculation: 7.1kW @ Amb. Temp, of: -3C
Type of Controller: Modulating, no 3rd party thermostats, TRV’s set in bedrooms otherwise all open full
Type of Control: Weather Compensation
System Type: Radiators
Buffer Tank or Low Loss Header: No
Secondary Pumps: No
Solar PV System: 4.44 kW
Power Diverter: No
Battery System: 9.5kWh Givenergy battery
4.4kW PV with 9.5kWh Givenergy battery. 9kW Panasonic Aquarea L ASHP
Forum Handle: @ajdunlop
Manufacturer: Mitsubishi
Model: Ecodan R32 8.5kW (PUZ-WM85VAA)
Type: ASHP
Arrangement: Mono
Area of Country: West Yorkshire, England
Home Type: End Terrace House
Size: Square Metres: 170m2
Insulation Level: 6/10 (Attic very well insulated, some main rooms with IWI, others not insulated yet and suspended floors not insulated yet)
Heat Loss Calculation: 7.54kW @ Amb. Temp, of: -2C (Self calculated using Heat Engineer)
Type of Controller: Ecodan FTC6 Main controller in Hallway, Smart TRVs on most Rads (set to limit overheating)
Type of Control: For 1st winter probably a mix of Weather Compensation and use of Ecodan's Auto Adaptive taking room temperature from main controller
System Type: Radiators (mix of very old P1, less old P2 and some newer K2)
Total Output of Heat Emitters: 9.863kW (@45C flow temp)
Buffer Tank or Low Loss Header: No
Secondary Pumps: No
Solar PV System: 4.4 kW (12x JA Solar 370W Panels evenly E-W Split, Inverter Fox ESS Hybrid H1-3.7-E)
Power Diverter: Yes (Soon to be installed Eddi, hopefully wired to use immersion at low overproduction and the ASHP for high overproduction)
Battery System: 5.8 kW (Fox ESS Cube CM2900 + CS2900)
Forum Handle: Crustydoodle
Manufacturer: Mitsubishi
Model: Ecodan R32 11.2kW
Type: ASHP
Arrangement: Mono
Area of Country: South East
Home Type: Detached House
Size: Square Metres: ~190
Insulation Level: Scale of 1 to 10 possibly? High
Heat Loss Calculation: 9.7 kW @ Amb. Temp, of: -2.39C
Type of Controller: FTC6 + Neomiser Thermostats in every room (11 zones)
Type of Control: Room temp I think; HW set to 50DegC and reheats when 10 below
System Type: UFH.
Total Output of Heat Emitters: Unsure - something says 19kW heat demand
Buffer Tank or Low Loss Header: None
Secondary Pumps: Not sure
Solar PV System: No
Power Diverter: No
Battery System: No
- 25 Forums
- 1,513 Topics
- 31.8 K Posts
- 21 Online
- 1,283 Members
Join Us!
Latest Posts
-
RE: Additional Battery v Wind Turbine v Ripple
I should add, being an investment, the value of your in...
By Old_Scientist , 5 hours ago
-
RE: Ecodan - flow rates, sensors, settings
Achieving an accurate flow measurement is probably the ...
By Derek M , 8 hours ago
-
RE: Ecodan ASHP - How to optimise my set up?
Again, thank you for another thorough post, @derek-m - ...
By rhh2348 , 10 hours ago
-
RE: Delivering a smart and secure electricity system: government consultation
@Transparent.Now that I am represented by a new MP I th...
By IanMK13 , 12 hours ago
-
RE: Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
Similar thread here
By Johnmo , 13 hours ago
-
RE: VDI 2035 heating water specification
Been looking and it seems a good little project. Ever...
By Johnmo , 2 days ago
-
RE: Do I accept an ASHP and Solar Panel retrofit under the HUG 2 scheme?
Will do. I'm currently waiting for another survey / vis...
By dssr , 2 days ago
-
The company that did the borehole were expecting us to ...
By Johnmo , 2 days ago
-
-
RE: The Misquote That Ruined the Heating Industry
@abernyte manufacturer training is pretty average. They...
By Mars , 2 days ago
-
-
RE: ECO4 Scheme and EPC ratings
@mellow Thanks. Given there is a scheme requirement to ...
By Old_Scientist , 3 days ago
-
RE: Do I just go with the lowest quote for my heat pump?
@jancold To me its a no-brainer then, a max 40C flow te...
By bontwoody , 3 days ago
-
-
RE: Heat Pump Books Beginners – Bodge Buster & From Zero To Heat Pump Hero
@editor Presumably he had some good weather Compensatio...
By Toodles , 4 days ago
-
RE: New Vaillant 7kW aroTherm ASHP or oil boiler dilemma/decision??
Storage capacity really is dependent on storage tempera...
By Johnmo , 4 days ago
-
RE: HP Cycling, Expected or Undesirable
Just a little update. I ordered a longer shielded twin ...
By bontwoody , 4 days ago
-
RE: Domestic hot water timer doing crazy things on my Grant Aerona3 10kW air source heat pump
Thanks @allyfish for the pics and info. Spoke to the in...
By Mellow , 4 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
It's been a busy day for calls and emails from Aira. I ...
By MikeH , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Hmm. A bit of a nuanced answer, methinks. As I've alr...
By Majordennisbloodnok , 4 days ago
Latest Topics
-
Ecodan - flow rates, sensors, settings
By rhh2348 11 hours ago
-
Replacing mains water with well water
By Johnmo 2 days ago
-
Additional Battery v Wind Turbine v Ripple
By bontwoody 2 days ago
-
By jamespipe 3 days ago
-
VDI 2035 heating water specification
By Johnmo 3 days ago
-
Do I just go with the lowest quote for my heat pump?
By Jancold 5 days ago
-
The Misquote That Ruined the Heating Industry
By Alec Morrow 6 days ago
-
Battery Storage Wiring Gauge Question
By Puff 6 days ago
Members Online
No online members at the moment