[Sticky] Air source heat pump roll call – what heat pump brand and model do you have?
I failed to say that the design allows for a 50C flow temperature but since the engineer did some fettling I have not investigated it again.
Posted by: @timatheronwoodI failed to say that the design allows for a 50C flow temperature but since the engineer did some fettling I have not investigated it again.
Oh, you can't beat a good 'fettle'. 😋
I had the unit set to 18 overnight (till 4am) and 19 from then on but this morning at 6am the temperature in the house was down to 17.5C It had not risen beyond that by 10am. At 12 noon the temperature had risen to 18C in the house. I have changed the slope of the "curve" so that it now reaches maximum at 0C instead of -10C. This afternoon the temperature had risen to 18.5C and I have changed the temperatures to 20C in the day and 19 at night to cope with the cold weather.
Could this be due to the unit not meeting the design spec for output temperature. The Daikin literature says that we should be able to get a 65C output. But the most I have ever seen is 45C even thought it is set to 63C.
Any thoughts anyone?
If Homeowners are prepared to provide the information, then maybe a spreadsheet containing the following information would be of most use from the comparison, and highlighting of possible problems, point of view.
Forum Handle: Toodles
Manufacturer: Daikin
Model: EDLA082V3
Type: ASHP
Arrangement: Mono
Area of Country: Berkshire
Home Type: 4 bed semi 1930’s build
Size: Square Metres:95
Insulation Level: Scale of 1 to 10 possibly? 10
Heat Loss Calculation: kW @ Amb. Temp, of: ?C 6.5 kW
Type of Controller: Modulating
Type of Control: Weather Compensation, LWT setting
System Type: Radiators (Mainly new for LT use)
Total Output of Heat Emitters: kW
Buffer Tank or Low Loss Header: LLH
Secondary Pumps: Number or No 1
Solar PV System: Size or No 8.1 kWp
Power Diverter: Yes
Battery System: Size; 13.5 kW/h Tesla Powerwall
Anything else that anyone can think may be useful. Please feel free to rearrange the order. In this milder weather, we are running at 22.5 degrees nominally (we like a warm house!) and are using approx. 0.5 kW/h
For my personal viewing only, bank account details and all necessary passwords and access codes. If I told you, I would have to terminate your existence! Regardsd, Toodles
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Perhaps I should add to the above system (sorry, but I failed to be able to edit the entry) based on a Daikin 8 kW ASHP that the domestic hot water heating is handled by a Sunamp Thermino ePV210 heat battery. The reason being, space is at a premium and the MCS guideline for a 4 bedroom house is 210 litres of DHW storage and we just do not have a space for such a tank! The Thermino is considerably smaller and can be accommodated (just!) in our airing cupboard - the insulation is extremely good so the total heat loss in 24 hours is less than 0.75 kW/h, so very little warming is available in the airing cupboard - just the lost heat coming from the unlagged plumbing from the LLH etc. and this helps to provide a background warmth in the cupboard.
I scored 10 myself for insulation as we have double glazing (triple in one room), cavity wall insulation, underfloor insulation from Q-Bot on the ground floor and approx. 40 cm. of loft insulation plus boarding sandwiched in the middle, plus we have approx. 5 cm. thick insulating board with a foil face between all the roof truce work just below the roofing felt. Our EPC rating before installing the Solar PV, battery and then the ASHP was a ‘B’ with notes indicating that Solar PV and / or Heat Pump would improve the rating.
I hope to incorporate an Evergreen Homely smart thermostat system for ASHP control as soon as a compatible device for the Daikin is available. Perhaps I should also mention that the Power Diverter is the Myenergi Eddi with a Harvi and several CT Clamps. We are using the Octopus Energy Agile and Agile Outgoing tariffs for import and export (no James Bond involvement however). 😉 Regards, Toodles
Toodles, he heats his home with cold draughts and cooks his food with magnets.
If Homeowners are prepared to provide the information, then maybe a spreadsheet containing the following information would be of most use from the comparison, and highlighting of possible problems, point of view.
Forum Handle: @FJJ
Manufacturer: Grant
Model: HPID10R32
Type: ASHP
Arrangement: Mono
Area of Country: Warwickshire
Home Type: 3 bed detached 1970's
Size: Square Metres: 100
Insulation Level: Scale of 1 to 10 possibly? 7
Heat Loss Calculation: kW @ Amb. Temp, of: -1.1C 6.8 kW
Type of Controller: Modulating
Type of Control: Weather Compensation
System Type: Radiators (5K3, 3K2, 1K1 Stelrad compact)
Total Output of Heat Emitters: not known
Buffer Tank or Low Loss Header: LLH
Secondary Pumps: Number 1
Solar PV System: Size or No 8 kW
Power Diverter: Yes
Battery System: Size; 10Kw Solaredge Powerbank
Forum Handle: MikeFl
Manufacturer: Grant
Model: Aerona HPID10R32
Type: ASHP
Arrangement: Mono
Area of Country: Cumbria
Home Type: Dormer Bungalow
Size: Square Metres: 148
Insulation Level: 7? (Loft/eaves insulation topped up with 30mm+; Room in Roof insulation is less
Heat Loss Calculation: 9-10kW @ Amb. Temp, of: 10C (this is my calculation - hope the installer has a better one)
Type of Controller: Two zones (up/down) controlled by room thermostats, with TRVs on all but two radiators
Type of Control: Fixed flow temperate at installation, possibly.
System Type: Radiators
Total Output of Heat Emitters: K2 *3, K3 * 4, K1 * 1
Buffer Tank or Low Loss Header: Grant volumiser / LLH
Secondary Pumps: 1(Grundfos ups3 15-50)
Solar PV System: No
Power Diverter: No
Battery System: No
Water cylinder is a FlowCyl Slimline 170L (FCHPS2170) with 24kW heating coil installed.
Grant Aerona 3 10kW
Forum Handle: Madrajin
Manufacturer: Vaillant
Model: Arotherm Plus 7kw, UniTower plus, sensoComfort
Type: ASHP
Arrangement: Monoblock, high temp I think.
Area of Country: General Location
Home Type: House solid wall construction, built 1763 (uniTower located in outhouse)
Size: Square Metres: 126m2
Insulation Level: Scale of 1 to 10 possibly? Listed as energy mark D when I bought it
Heat Loss Calculation: kW @ Amb. Temp, of: ?C
Type of Controller: unknown (sensoComfort), EveThermo TRV
Type of Control: Adaptive, Weather Compensation, Flow Temperature, Room Temperature
System Type: Radiators unchanged, mostly double.
Total Output of Heat Emitters: ? kW
Buffer Tank or Low Loss Header: No
Secondary Pumps: No
Solar PV System: No
Power Diverter: No
Battery System: No
Forum Handle: GC61
Manufacturer: Viessmann
Model: Vitocal 151-A
Type: ASHP
Arrangement: Mono
Area of Country: Ireland
Home Type: 2-Storey detached
Size: 180 sqm
Insulation Level: 8
Heat Loss Calculation: 1.63
Type of Controller: Viessmann Vitotrol 300-E
Type of Control: Weather Compensation / Flow Temperature / Room Temperature
System Type: UFH and radiators
Total Output of Heat Emitters:
Buffer Tank or Low Loss Header:
Secondary Pumps:
Solar PV System: 4.2KW
Power Diverter: No
Battery System: No
Forum Handle: @dougmlancs
Manufacturer: Panasonic
Model: Aquarea L (R290)
Type: ASHP
Arrangement: Split with hydraulic connection
Area of Country: Lancashire
Home Type: Semi-detached house
Size: Square Metres: 110
Insulation Level: CWI, DG + 300mm loft
Heat Loss Calculation: 7.1kW @ Amb. Temp, of: -3C
Type of Controller: Modulating, no 3rd party thermostats, TRV’s set in bedrooms otherwise all open full
Type of Control: Weather Compensation
System Type: Radiators
Buffer Tank or Low Loss Header: No
Secondary Pumps: No
Solar PV System: 4.44 kW
Power Diverter: No
Battery System: 9.5kWh Givenergy battery
Smart Tech Specialist with Octopus Energy Services (all views my own). 4.4kW PV with 9.5kWh Givenergy battery. 9kW Panasonic Aquarea L ASHP
Forum Handle: @ajdunlop
Manufacturer: Mitsubishi
Model: Ecodan R32 8.5kW (PUZ-WM85VAA)
Type: ASHP
Arrangement: Mono
Area of Country: West Yorkshire, England
Home Type: End Terrace House
Size: Square Metres: 170m2
Insulation Level: 6/10 (Attic very well insulated, some main rooms with IWI, others not insulated yet and suspended floors not insulated yet)
Heat Loss Calculation: 7.54kW @ Amb. Temp, of: -2C (Self calculated using Heat Engineer)
Type of Controller: Ecodan FTC6 Main controller in Hallway, Smart TRVs on most Rads (set to limit overheating)
Type of Control: For 1st winter probably a mix of Weather Compensation and use of Ecodan's Auto Adaptive taking room temperature from main controller
System Type: Radiators (mix of very old P1, less old P2 and some newer K2)
Total Output of Heat Emitters: 9.863kW (@45C flow temp)
Buffer Tank or Low Loss Header: No
Secondary Pumps: No
Solar PV System: 4.4 kW (12x JA Solar 370W Panels evenly E-W Split, Inverter Fox ESS Hybrid H1-3.7-E)
Power Diverter: Yes (Soon to be installed Eddi, hopefully wired to use immersion at low overproduction and the ASHP for high overproduction)
Battery System: 5.8 kW (Fox ESS Cube CM2900 + CS2900)
Forum Handle: Crustydoodle
Manufacturer: Mitsubishi
Model: Ecodan R32 11.2kW
Type: ASHP
Arrangement: Mono
Area of Country: South East
Home Type: Detached House
Size: Square Metres: ~190
Insulation Level: Scale of 1 to 10 possibly? High
Heat Loss Calculation: 9.7 kW @ Amb. Temp, of: -2.39C
Type of Controller: FTC6 + Neomiser Thermostats in every room (11 zones)
Type of Control: Room temp I think; HW set to 50DegC and reheats when 10 below
System Type: UFH.
Total Output of Heat Emitters: Unsure - something says 19kW heat demand
Buffer Tank or Low Loss Header: None
Secondary Pumps: Not sure
Solar PV System: No
Power Diverter: No
Battery System: No
- 22 Forums
- 2,036 Topics
- 44.4 K Posts
- 25 Online
- 3,239 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
@dwynwen welcome back… and glad to hear you made it thr...
By Mars , 9 hours ago
-
RE: Air Source Heat Pump - Side Alley Suitability
@ad3628 I’ve seen loads of heat pumps successfully inst...
By Mars , 9 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
@trebor12345 The Auto function is supposed to adapt au...
By Heatgeek , 12 hours ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
@jamespa they didn't provide any contract, or design pr...
By benson , 14 hours ago
-
RE: The Great British Heat Pump Quiz
@allyfish thanks for the feedback and glad it was fun! ...
By Mars , 17 hours ago
-
RE: help sizing rads based on room by room heat loss
If its 1988W at DT 50, which is how most radiators are ...
By JamesPa , 22 hours ago
-
RE: Career change – entering the world of heating and heat pumps
@editor Mars, thank you. That's along the routes I was ...
By Lakey , 22 hours ago
-
@editor thanks Mars, it's a rare occasion I'm looking f...
By big_si , 1 day ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
@ashp-bobba and @jamespa - thank you both for all your ...
By CBrenewable , 1 day ago
-
-
Win one of five "Heat Pumps 101" Courses
Heat pumps are gaining traction in the UK, but between ...
By Mars , 2 days ago
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 2 days ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15 I'm no plumber so please don't take this as ...
By dnagre , 2 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 3 days ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 3 days ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 3 days ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 3 days ago
-
RE: How hard and expensive would it be to change panel and add battery?
@transparent It is a setting that Octopus make via the ...
By Toodles , 3 days ago