Advice needed on inefficient Samsung ASHP installation
Interesting you mention that you’re surprised most installers don’t set up their curve like this, any heat pump supplied from freedom over the years that GH was in charge, would have been setup with a pretty reasonable curve of 37@15, 50@0 and with external thermostat control.
I always thought that was a bit of a cop out from a design perspective, but having looked at most heat pump controllers on the market I’ve come to the same conclusion as GH did, they’re awful things to use as a thermostat 🤣.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
It is a cop out and as I say upthread will incur a penalty of 3-6% or more if it's more than a a couple of degrees out. However installers don't wast to return to site and setting up the perfect wc curve is iterative, so if running cost isn't critical it's an approach that has attractions. I'm not advocating it, just recognising it.
Why 37 at 15 incidentally, that's almost obviously too high in most cases, leading to a further penalty. Is this so that radiators always feel warm to avoid callouts?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa yes… it’s what I run at too. Keeps the wife happy.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
I just ran the numbers through my WC simulator. This calculates, based on Ecodan R32 data, the efficiency gain from various WC curves relative to fixed temperature operation, based on an OAT pattern representative of southern England. If we take your 50;0, 37;15 case and assume that this is 5C higher above the ideal' WC curve until it reaches the floor at 37C, then the curve gives a 10% improvement on fixed temperature operation, as opposed to 20% if the WC curve is set up properly. So you can either look at that as a 12.5% penalty relative to optimum, or as a halving of the benefit of WC.
Most of the penalty is due to the curve being above the optimum value not the ('lizzie ') floor. So one good approach would be to set it up initially this way and (during the coldest season) gradually reduce the cold end until it didn't quite heat the house, then turn it up by a degree.
As I say I'm not advocating this method, only recognising it.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I should have added more flesh to my post but I was on my phone - We actually set the top end of the curve to the design flow temp, 45 degrees in my case (so 47.5 flow). The bottom end of the curve was also chosen as we have fan coils in some rooms/areas (kitchen, hallway, bathroom), and no-one wants to stand under cold air...
I also figured that lifting from 15 degrees ambient to 37.5 is hardly much work that I wasn't going to sweat the details. Also handy to have the rads deliver some heat on the odd occasion that it's 18 degrees outside and raining and the wife wants the heat on. Handy to be able to deliver some heat into the property in that case. I almost thought about switching to a fixed flow temp of 45 during the summer for this precise reason, but haven't needed to yet.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
I did a couple of days testing running weather comp and a fixed flow temperature with thermostat control on similar average temperature days, one being 8.7 and the other 9.0. Very little difference in target flow temp.
Fixed flow temp (to simulate a slightly elevated flow temperature), compressor cutoff was 30.8, WC obviously varied between 29.1 and 29.2. But the starting temp was the biggest variable. WC never started the compressor until return temp had dropped to 21.6 degs, while the fixed with thermostat could be as high as 25 degs.
Fixed and thermostat
Space heating CoP 4.8
kWh used over 24hrs 6.8kWh
WC
Space heat CoP 5.4
kWh used over 24 hrs 4.6
You will see from the image the difference in run duration and frequency of starts. The one with plenty of starts is the thermostat.
CoP is generally made up of two components at a fixed outside temperature. Flow temperature and dT, the wider the dT the better the CoP.
The rest was not definitive as the temp varied over the day. But a 30% reduced kWh used was quite a suprise, when comparing WC to using the thermostat. Think that must be down to the the increased shorter duration cycling and less higher quality heat being delivered
The image below is the day I implemented the change in strategy to the left straight WC to the right thermostat control. The off period is some solar gain switching off the heat pump.
-
Yes, the "zoning with ASHP" topic again...
3 months ago
-
My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
6 months ago
-
My British Gas – Heat Force ASHP Installation: A Frustrating Experience
10 months ago
-
Low shower pressure after ASHP retrofit
10 months ago
-
What is Wrong with our Heat Pump Installation?
1 year ago
Currently viewing this topic 2 guests.
- 26 Forums
- 2,114 Topics
- 46.4 K Posts
- 156 Online
- 3,410 Members
Latest Posts
-
RE: The good, the bad and the not that great – my heat pump installation
Said I would pop back with a update. Only Mr Jesus h...
By Burtis , 11 hours ago
-
RE: No-code, plug-and-play monitoring for your heat pump
@cathoderay i will have to take a look at that, tbh as ...
By Grantmethestrength , 12 hours ago
-
RE: Buffers, hot water and cooling
Thats presumably heat pump DT, what about radiator DT a...
By JamesPa , 12 hours ago
-
RE: Benefits of an extra horizontal loop for GSHP
I have no direct knowledge of GSHP ground loops but it ...
By Abernyte , 20 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Exactly the same here. We now have 13.5kWh ...
By Old_Scientist , 22 hours ago
-
Compressor and Evaporator Stratification
I have had a few issues with my Hitachi spilt heatpump ...
By trebor12345 , 23 hours ago
-
RE: Wood burner with ASHP - direct air?
This depends on the size of your wood burner and size/t...
By Lucia , 2 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn It's a not a buffer it's a volumiser which is ...
By Lucia , 2 days ago
-
RE: Is your heat pump insured?
To make things clear, lots of insurance companies cover...
By Lucia , 2 days ago
-
RE: Boxt Heat Pump Installation Experience
@adrian any updates since installation? How is it perfo...
By Ashfp , 2 days ago
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 3 days ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 3 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 6 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 6 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 6 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 6 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 1 week ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 1 week ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 1 week ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 1 week ago