Interesting you mention that you’re surprised most installers don’t set up their curve like this, any heat pump supplied from freedom over the years that GH was in charge, would have been setup with a pretty reasonable curve of 37@15, 50@0 and with external thermostat control.
I always thought that was a bit of a cop out from a design perspective, but having looked at most heat pump controllers on the market I’ve come to the same conclusion as GH did, they’re awful things to use as a thermostat 🤣.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
It is a cop out and as I say upthread will incur a penalty of 3-6% or more if it's more than a a couple of degrees out. However installers don't wast to return to site and setting up the perfect wc curve is iterative, so if running cost isn't critical it's an approach that has attractions. I'm not advocating it, just recognising it.
Why 37 at 15 incidentally, that's almost obviously too high in most cases, leading to a further penalty. Is this so that radiators always feel warm to avoid callouts?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa yes… it’s what I run at too. Keeps the wife happy.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
I just ran the numbers through my WC simulator. This calculates, based on Ecodan R32 data, the efficiency gain from various WC curves relative to fixed temperature operation, based on an OAT pattern representative of southern England. If we take your 50;0, 37;15 case and assume that this is 5C higher above the ideal' WC curve until it reaches the floor at 37C, then the curve gives a 10% improvement on fixed temperature operation, as opposed to 20% if the WC curve is set up properly. So you can either look at that as a 12.5% penalty relative to optimum, or as a halving of the benefit of WC.
Most of the penalty is due to the curve being above the optimum value not the ('lizzie ') floor. So one good approach would be to set it up initially this way and (during the coldest season) gradually reduce the cold end until it didn't quite heat the house, then turn it up by a degree.
As I say I'm not advocating this method, only recognising it.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I should have added more flesh to my post but I was on my phone - We actually set the top end of the curve to the design flow temp, 45 degrees in my case (so 47.5 flow). The bottom end of the curve was also chosen as we have fan coils in some rooms/areas (kitchen, hallway, bathroom), and no-one wants to stand under cold air...
I also figured that lifting from 15 degrees ambient to 37.5 is hardly much work that I wasn't going to sweat the details. Also handy to have the rads deliver some heat on the odd occasion that it's 18 degrees outside and raining and the wife wants the heat on. Handy to be able to deliver some heat into the property in that case. I almost thought about switching to a fixed flow temp of 45 during the summer for this precise reason, but haven't needed to yet.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
I did a couple of days testing running weather comp and a fixed flow temperature with thermostat control on similar average temperature days, one being 8.7 and the other 9.0. Very little difference in target flow temp.
Fixed flow temp (to simulate a slightly elevated flow temperature), compressor cutoff was 30.8, WC obviously varied between 29.1 and 29.2. But the starting temp was the biggest variable. WC never started the compressor until return temp had dropped to 21.6 degs, while the fixed with thermostat could be as high as 25 degs.
Fixed and thermostat
Space heating CoP 4.8
kWh used over 24hrs 6.8kWh
WC
Space heat CoP 5.4
kWh used over 24 hrs 4.6
You will see from the image the difference in run duration and frequency of starts. The one with plenty of starts is the thermostat.
CoP is generally made up of two components at a fixed outside temperature. Flow temperature and dT, the wider the dT the better the CoP.
The rest was not definitive as the temp varied over the day. But a 30% reduced kWh used was quite a suprise, when comparing WC to using the thermostat. Think that must be down to the the increased shorter duration cycling and less higher quality heat being delivered
The image below is the day I implemented the change in strategy to the left straight WC to the right thermostat control. The off period is some solar gain switching off the heat pump.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
-
My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
1 month ago
-
My British Gas – Heat Force ASHP Installation: A Frustrating Experience
5 months ago
-
Low shower pressure after ASHP retrofit
5 months ago
-
What is Wrong with our Heat Pump Installation?
10 months ago
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 71 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 53 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
Something else... that works for some people... LG ha...
By Tim441 , 59 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
OMG, the attached schematics (even with incorrect room ...
By BAMi , 2 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 2 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 3 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 3 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 4 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 15 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 18 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 19 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 22 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 23 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 24 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 3 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 4 hours ago
-
SolarPV tables / online calculator
By MichelleC 11 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 23 hours ago
-
By Toodles 2 days ago