Advice needed on inefficient Samsung ASHP installation
Interesting you mention that you’re surprised most installers don’t set up their curve like this, any heat pump supplied from freedom over the years that GH was in charge, would have been setup with a pretty reasonable curve of 37@15, 50@0 and with external thermostat control.
I always thought that was a bit of a cop out from a design perspective, but having looked at most heat pump controllers on the market I’ve come to the same conclusion as GH did, they’re awful things to use as a thermostat 🤣.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
It is a cop out and as I say upthread will incur a penalty of 3-6% or more if it's more than a a couple of degrees out. However installers don't wast to return to site and setting up the perfect wc curve is iterative, so if running cost isn't critical it's an approach that has attractions. I'm not advocating it, just recognising it.
Why 37 at 15 incidentally, that's almost obviously too high in most cases, leading to a further penalty. Is this so that radiators always feel warm to avoid callouts?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa yes… it’s what I run at too. Keeps the wife happy.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
I just ran the numbers through my WC simulator. This calculates, based on Ecodan R32 data, the efficiency gain from various WC curves relative to fixed temperature operation, based on an OAT pattern representative of southern England. If we take your 50;0, 37;15 case and assume that this is 5C higher above the ideal' WC curve until it reaches the floor at 37C, then the curve gives a 10% improvement on fixed temperature operation, as opposed to 20% if the WC curve is set up properly. So you can either look at that as a 12.5% penalty relative to optimum, or as a halving of the benefit of WC.
Most of the penalty is due to the curve being above the optimum value not the ('lizzie ') floor. So one good approach would be to set it up initially this way and (during the coldest season) gradually reduce the cold end until it didn't quite heat the house, then turn it up by a degree.
As I say I'm not advocating this method, only recognising it.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I should have added more flesh to my post but I was on my phone - We actually set the top end of the curve to the design flow temp, 45 degrees in my case (so 47.5 flow). The bottom end of the curve was also chosen as we have fan coils in some rooms/areas (kitchen, hallway, bathroom), and no-one wants to stand under cold air...
I also figured that lifting from 15 degrees ambient to 37.5 is hardly much work that I wasn't going to sweat the details. Also handy to have the rads deliver some heat on the odd occasion that it's 18 degrees outside and raining and the wife wants the heat on. Handy to be able to deliver some heat into the property in that case. I almost thought about switching to a fixed flow temp of 45 during the summer for this precise reason, but haven't needed to yet.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
I did a couple of days testing running weather comp and a fixed flow temperature with thermostat control on similar average temperature days, one being 8.7 and the other 9.0. Very little difference in target flow temp.
Fixed flow temp (to simulate a slightly elevated flow temperature), compressor cutoff was 30.8, WC obviously varied between 29.1 and 29.2. But the starting temp was the biggest variable. WC never started the compressor until return temp had dropped to 21.6 degs, while the fixed with thermostat could be as high as 25 degs.
Fixed and thermostat
Space heating CoP 4.8
kWh used over 24hrs 6.8kWh
WC
Space heat CoP 5.4
kWh used over 24 hrs 4.6
You will see from the image the difference in run duration and frequency of starts. The one with plenty of starts is the thermostat.
CoP is generally made up of two components at a fixed outside temperature. Flow temperature and dT, the wider the dT the better the CoP.
The rest was not definitive as the temp varied over the day. But a 30% reduced kWh used was quite a suprise, when comparing WC to using the thermostat. Think that must be down to the the increased shorter duration cycling and less higher quality heat being delivered
The image below is the day I implemented the change in strategy to the left straight WC to the right thermostat control. The off period is some solar gain switching off the heat pump.
-
Yes, the "zoning with ASHP" topic again...
4 months ago
-
My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
8 months ago
-
My British Gas – Heat Force ASHP Installation: A Frustrating Experience
11 months ago
-
Low shower pressure after ASHP retrofit
12 months ago
-
What is Wrong with our Heat Pump Installation?
1 year ago
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 26 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
@cliffhanger - seriously though, I have no idea. What I...
By cathodeRay , 2 hours ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 2 hours ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 4 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 7 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 9 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 10 hours ago
-
@jamespa Ours is a Daikin EDLA03 8 kW and the Delta T =...
By Toodles , 11 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
Day one is done. The system’s been fully flushed and ...
By Mars , 1 day ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 1 day ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 1 day ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 1 day ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 1 day ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 2 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 2 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 2 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 4 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 5 days ago