Advice needed on hybrid system - ASHP not reaching flow temperature
Hi, hope you’re all keeping well.
We had a Mitsubishi 11kw ASHP installed a month or so ago and we struggled to heat our house during the last cold snap we had. We made the decision to install a gas boiler alongside the ASHP to run on the colder days. Looking at the charts the specified flow temp of 50c for space heating has never been reached, it gets to around 45 degrees. The pipe runs are all insulated and i have even increased the compensation curve to the maximum. The flow temp for the hot water seems to reach 60 degrees but it doesn’t on the space heating side. I have attached a diagram of our setup at the moment. Please note that the gas boiler isn’t yet up and running as we are waiting on a sensor from Mitsubishi.
Thanks in advance.
Is it the radiator side of the LLH that's not reaching temperature? Or does the heat pump monitoring show it's not achieving 50degC supply temperature? It clearly can if you're getting 60degC on your hot water, so if the primary side isn't allowing 50degC in heating, I guess some setting or parameter is overriding your climatic curve setting.
But if you're getting 50degC on the primary side and not getting that on the secondary side, the finger of suspicion points at the LLH?
Have you got balanced even flow on primary and secondary sides? Higher flow on the secondary radiator side compared to the primary side will pull return water through the LLH, mix with the higher temperature flow from the ASHP, and cause a lower radiator supply temperature.
If you've not got flow valves on both sides to balance flow, you can do it thermally with some temperature sensors. These are cheap and cheerful, and when cable tied to the copper pipe under insulation will give a reasonable indication of what's what +/-0.5degC or so. https://www.amazon.co.uk/dp/B07TY6HRL4?psc=1&ref=ppx_yo2ov_dt_b_product_details
Thanks for getting back to me ally - I am not sure where the thermistors are which are giving me the readings on the melcloud app.
there doesn’t appear to be any balancing valves installed.
all I know is that the flow temps are showing around 45c on the app despite it been set to 50c on the comp curve. Does the piping layout look ok to you from my diagram?
do you think it could be a setting on the controller somewhere?
worthwhile mentioning that there is a pipe run of around 15m from the ASHP to the llh around 10m of this is outdoors
There is a setting on the Ecodan FTC to limit flow temp. I know because I lowered mine a few days ago. It's in the maintenance menu, Operation Settings, Heating Operation, Flow Temperature Range. In case you don't know, pass key is (probably) 0000 and it'll ask you to shut the system down (which is fine as it will start when you exit).
My flow thermistors are physically just above my (non-Mitsubishi) HW tank. The sensors are attached to the flow and return copper pipes like those on Ally's thermometers and the other end disappears into the FTC.
@parmstar Great, les us know how you get on. Piping on your circuit is simple enough, and with a hybrid bivalent system I can see the LLH being of benefit. I would suggest flow monitoring/setting valves on both primary circuits, one on the ASHP return, one on the boiler return, and one on the secondary flow return. They all need to be in balance. Fired boiler design flow might be lower than ASHP design flow, but I guess you've considered that and how to handle that.
- 26 Forums
- 2,356 Topics
- 53.4 K Posts
- 412 Online
- 6,017 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@andrewj Seeing they deleted both threads with the pict...
By HarrisonC , 5 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@mars I think your commentary is very fair and balanc...
By JamesPa , 6 hours ago
-
RE: External pipework insulation
That's great advice @transparent... thank you. @david...
By Mars , 6 hours ago
-
RE: Advice on internal circulation pump noise
Thanks @mikefl - I'll maybe have a look at the lock-shi...
By jtg , 8 hours ago
-
RE: Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
@toodles interesting suggestion, thanks. I will try to...
By GrahamF , 8 hours ago
-
RE: Mitsubishi Ecodan Auto Adaption trial to stop cycling.
The interval you talk of, i think, will be 60min for an...
By F1p , 12 hours ago
-
RE: Electricity price predictions
Does anyone have a current graphic, visual or breakdown...
By Mars , 15 hours ago
-
Agree with @majordennisbloodnok on the setbacks. We hav...
By ChandyKris , 1 day ago
-
RE: New Fogstar 15.5kWh upright solution
It is a matter of luck. 2ith Fogstar "instructions", to...
By Batpred , 1 day ago
-
RE: Speedcomfort radiator fans
@deltona the way the links were added broke the page. A...
By Mars , 1 day ago
-
RE: Setback savings - fact or fiction?
I agree! Even more so if we get an answer! But the chal...
By cathodeRay , 1 day ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
This has been delayed from what I believe to be this ye...
By dgclimatecontrol , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
this is why I provided current flow temperatures in the...
By ksim , 2 days ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
There's many homes that would be quite a disruption for...
By dgclimatecontrol , 2 days ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@rhh2348 ...maybe this option is what you want? Alter...
By benson , 2 days ago
-
RE: Free Ecoheat Heat Pump Install
@old_scientist This does make the unit smaller as the b...
By dgclimatecontrol , 2 days ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
@old_scientist hiya mate, did you ever get to the botto...
By 9jwr9 , 2 days ago
-
RE: Configuring third party dongle for Ecodan local control
@majordennisbloodnok I think the HPDHD diagnosis may be...
By Sheriff Fatman , 2 days ago