Advice needed on hybrid system - ASHP not reaching flow temperature
Hi, hope you’re all keeping well.
We had a Mitsubishi 11kw ASHP installed a month or so ago and we struggled to heat our house during the last cold snap we had. We made the decision to install a gas boiler alongside the ASHP to run on the colder days. Looking at the charts the specified flow temp of 50c for space heating has never been reached, it gets to around 45 degrees. The pipe runs are all insulated and i have even increased the compensation curve to the maximum. The flow temp for the hot water seems to reach 60 degrees but it doesn’t on the space heating side. I have attached a diagram of our setup at the moment. Please note that the gas boiler isn’t yet up and running as we are waiting on a sensor from Mitsubishi.
Thanks in advance.
Is it the radiator side of the LLH that's not reaching temperature? Or does the heat pump monitoring show it's not achieving 50degC supply temperature? It clearly can if you're getting 60degC on your hot water, so if the primary side isn't allowing 50degC in heating, I guess some setting or parameter is overriding your climatic curve setting.
But if you're getting 50degC on the primary side and not getting that on the secondary side, the finger of suspicion points at the LLH?
Have you got balanced even flow on primary and secondary sides? Higher flow on the secondary radiator side compared to the primary side will pull return water through the LLH, mix with the higher temperature flow from the ASHP, and cause a lower radiator supply temperature.
If you've not got flow valves on both sides to balance flow, you can do it thermally with some temperature sensors. These are cheap and cheerful, and when cable tied to the copper pipe under insulation will give a reasonable indication of what's what +/-0.5degC or so. https://www.amazon.co.uk/dp/B07TY6HRL4?psc=1&ref=ppx_yo2ov_dt_b_product_details
Thanks for getting back to me ally - I am not sure where the thermistors are which are giving me the readings on the melcloud app.
there doesn’t appear to be any balancing valves installed.
all I know is that the flow temps are showing around 45c on the app despite it been set to 50c on the comp curve. Does the piping layout look ok to you from my diagram?
do you think it could be a setting on the controller somewhere?
worthwhile mentioning that there is a pipe run of around 15m from the ASHP to the llh around 10m of this is outdoors
There is a setting on the Ecodan FTC to limit flow temp. I know because I lowered mine a few days ago. It's in the maintenance menu, Operation Settings, Heating Operation, Flow Temperature Range. In case you don't know, pass key is (probably) 0000 and it'll ask you to shut the system down (which is fine as it will start when you exit).
My flow thermistors are physically just above my (non-Mitsubishi) HW tank. The sensors are attached to the flow and return copper pipes like those on Ally's thermometers and the other end disappears into the FTC.
@parmstar Great, les us know how you get on. Piping on your circuit is simple enough, and with a hybrid bivalent system I can see the LLH being of benefit. I would suggest flow monitoring/setting valves on both primary circuits, one on the ASHP return, one on the boiler return, and one on the secondary flow return. They all need to be in balance. Fired boiler design flow might be lower than ASHP design flow, but I guess you've considered that and how to handle that.
- 22 Forums
- 2,086 Topics
- 46 K Posts
- 32 Online
- 3,377 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness bold choice on the Kronoterm. Nice! Wi...
By Mars , 4 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
It took me more than a few goes as well, plus some help...
By cathodeRay , 20 hours ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@ashp-bobba thank you, and equally so, thank you for ta...
By Mars , 1 day ago
-
@judith good to know… I’ll continue to feed Wattson, an...
By Mars , 2 days ago
-
RE: Vaillant AroTherm Plus 7kW
@jamespa I have a hydronic baseboard heater in the kitc...
By Scalextrix , 2 days ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
@editor great article re accreditation. I note ISO/IEC ...
By Bart , 2 days ago
-
RE: Renewables & Heat Pumps in the News
Here’s a little more technical detail/p>
By Judith , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
I don't (yet), but my PW3 is due to be installed shortl...
By Old_Scientist , 3 days ago
-
RE: MCS and NAPIT complaints process
@chrislay, is your heat pump complaint still unresolved...
By Mars , 3 days ago
-
RE: ASHP Install from hell - help please
@saf1973 I’ve been going through old cases on the forum...
By Mars , 3 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron There's the rub, the database does not list my ...
By AF1 , 4 days ago
-
RE: Commencing on an ASHP Installation Process
Yes, it's "doable" if everything goes to plan, they arr...
By Old_Scientist , 5 days ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 6 days ago
-
RE: DHW SET UP with Samsung gen 5
Thats good news indeed, you are very likely almost ther...
By JamesPa , 6 days ago
-
RE: Plate heat exchanger considerations
As far as I can tell my vented system would have a peak...
By Scalextrix , 6 days ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
There have been a few discussions dotted around (e.g. I...
By Declan90 , 6 days ago