14kW Ecodan system installed in a 370sqm new build
Morning all
New member here. I have a 14KW Ecodan system installed in a 370sqm new build (2017). It was pretty poor in terms of efficiency but I have been following all your great suggestions on the forum and I am slowly getting it working much better.
Thanks for all the advice about sticking to weather compensation and also opening up all the actuators and zoned circuits and letting the FTC work it all out for itself.
I now have a couple of questions for your collective wisdom:
- Is the room temperature control (auto adaptation) superior to the weather compensation control option, or do they work in parallel?
- If so, I don't have the wireless thermostat / controller - the FTC5 is in with the cylinder, which is obviously unrepresentative of the house. Should I buy one and would it be relatively easy to self install?
- Is there value in having the wifi adaptor too and then being able to monitor usage via the MELCloud, or is that just a gimmick?
Many thanks
Howard
Posted by: @hjdMorning all
New member here. I have a 14KW Ecodan system installed in a 370sqm new build (2017). It was pretty poor in terms of efficiency but I have been following all your great suggestions on the forum and I am slowly getting it working much better.
Thanks for all the advice about sticking to weather compensation and also opening up all the actuators and zoned circuits and letting the FTC work it all out for itself.
I now have a couple of questions for your collective wisdom:
- Is the room temperature control (auto adaptation) superior to the weather compensation control option, or do they work in parallel?
- If so, I don't have the wireless thermostat / controller - the FTC5 is in with the cylinder, which is obviously unrepresentative of the house. Should I buy one and would it be relatively easy to self install?
- Is there value in having the wifi adaptor too and then being able to monitor usage via the MELCloud, or is that just a gimmick?
Many thanks
Howard
@hjd, the simple answer about auto adaptation is that we (people on the forum) don't know. I assume auto adaptation works in parallel, that is the FTC5/6 changes the flow temp to achieve the room temp set. In a way, that's what I'm doing manually. I have a weather compensation curve that works quite well. I also have thermometers in the house. If I want it hotter/colder, I move the weather compensation curve up/down on the FTC6 screen, check the thermometers and repeat until it's right. E.g if Mrs M goes away for the night I can move the curve down, if my mother in law comes to stay I might move it up; you get the idea.
Mitsubishi claims auto adaptation has some sort of prediction/learning, which might help too.
The easiest way to try might be to move the FTC controller outside the airing cupboard. For me, that would be easy and I'll probably try it. The next cheapest way would be to buy/install a thermistor to detect room temp; they seem to be from £20 or so. The most elegant but expensive solution is the Mitsubushi wireless thermostat. Looking at the manuals, all of these might need some hardware changes (dipswitches and/or wiring to the FTC/5) but nothing too hard.
I'd definitely recommend the wireless transmitter/Melcloud.
Posted by: @hjdMorning all
New member here. I have a 14KW Ecodan system installed in a 370sqm new build (2017). It was pretty poor in terms of efficiency but I have been following all your great suggestions on the forum and I am slowly getting it working much better.
Thanks for all the advice about sticking to weather compensation and also opening up all the actuators and zoned circuits and letting the FTC work it all out for itself.
I now have a couple of questions for your collective wisdom:
- Is the room temperature control (auto adaptation) superior to the weather compensation control option, or do they work in parallel?
- If so, I don't have the wireless thermostat / controller - the FTC5 is in with the cylinder, which is obviously unrepresentative of the house. Should I buy one and would it be relatively easy to self install?
- Is there value in having the wifi adaptor too and then being able to monitor usage via the MELCloud, or is that just a gimmick?
Many thanks
Howard
Hi HJD,
Welcome to the forum,
Weather compensation monitors the ambient air temperature, and varies the water flow temperature, dependent upon the parameters set within the FTC controller. Keeping a home at a reasonably constant internal temperature is a balancing act, as the ambient air temperature falls, the heat loss increases, so to maintain the indoor temperature more heat energy must be put in by increasing the water flow temperature. The reports back from members would indicate that weather compensation works quite well.
The heat demand and internal temperature can be affected by other factors, such as solar gain, wind chill, rain effect and human activity, all of which can increase or reduce the heat demand. So, even if the slope of the weather compensation curve has been fully optimised, there will still be variations in the indoor temperature away from the desired level.
Auto adaptation measures not only the outdoor air temperature, but also the indoor air temperature, and acts to fine tune the temperature control to maintain the indoor temperature closer to the setpoint. So if the indoor air temperature were to start to increase due to solar gain or human activity, then auto adaptation would slightly reduce the water flow temperature, to try to counteract the temperature rise. Conversely, a falling indoor air temperature due to wind chill and/or rain effect, would slightly increase the water flow temperature.
Weather compensation with auto adaptation, will therefore maintain the indoor air temperature closer to the desired setpoint, and I do believe it will allow the indoor temperature setpoint to be adjusted, as with a standard thermostat.
Posted by: @hjdMorning all
New member here. I have a 14KW Ecodan system installed in a 370sqm new build (2017). It was pretty poor in terms of efficiency but I have been following all your great suggestions on the forum and I am slowly getting it working much better.
Thanks for all the advice about sticking to weather compensation and also opening up all the actuators and zoned circuits and letting the FTC work it all out for itself.
I now have a couple of questions for your collective wisdom:
- Is the room temperature control (auto adaptation) superior to the weather compensation control option, or do they work in parallel?
- If so, I don't have the wireless thermostat / controller - the FTC5 is in with the cylinder, which is obviously unrepresentative of the house. Should I buy one and would it be relatively easy to self install?
- Is there value in having the wifi adaptor too and then being able to monitor usage via the MELCloud, or is that just a gimmick?
Many thanks
Howard
If you're happy to keep the indoor temp set at a constant value throughout the day/night, weather compensation alone seems to be more than up to the job.
It's also the easiest solution as you don't have to add anything to the system.
Try it for a month and see how you get on with it.
Just curious but you have a 14kw ASHP in 370m2? It must be a very highly insulated property indeed...that does seem to my amateur eye a possibly undersized pump for what is a very large house. We have a 16kw in a 210m2 house and it copes well but I have no doubt it would be on pretty much permanently if fitted to a significantly larger property. You must have some fairly large electric bills I assume...
@siko Good question. We didn't specify it so not entirely sure who did the calcs. That said, for 7-8 months a year it only has to deal with hot water. For the remaining 4/5 it is dealing with heating as well. In recent weeks - and it has been fairly mild - we have been running at about 10-12KWh per day on heating. Not sure if that is good or bad really!
That seems really good, I must admit I don't know what the separate usage is for ours but we are very heavy users of electric and our total usage (water, heat, light, power etc etc) was 843kwh in Oct, probably on track for 1000+ in Nov. So we average prob 30 kwh a day for everything...again I don't know if that is good or not, but compared to before the ASHP came our bills are only marginally higher.....so far!
Posted by: @hjd@siko Good question. We didn't specify it so not entirely sure who did the calcs. That said, for 7-8 months a year it only has to deal with hot water. For the remaining 4/5 it is dealing with heating as well. In recent weeks - and it has been fairly mild - we have been running at about 10-12KWh per day on heating. Not sure if that is good or bad really!
Hi Howard,
12kWh for a large property is very good. Do you have any heat loss calculations for your property? Where is your location?
Have you considered a solar PV system to both help power your ASHP or help provide hot water from Spring through to Autumn?
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 72 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@jamespa cannot find loss calculation. When they get i...
By BAMi , 12 minutes ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 54 minutes ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 3 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
Something else... that works for some people... LG ha...
By Tim441 , 3 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 4 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 5 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 5 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 6 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 17 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 20 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 21 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 24 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 5 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 6 hours ago
-
SolarPV tables / online calculator
By MichelleC 13 hours ago
-
By Toodles 2 days ago