12kW Samsung gen 6 short cycling
Posted by: @craig1980A quick update on my system.Â
I'm running at a COP of around 3.3-3.4 at around 3 degrees outside temp including water heating for an hour at midnight. I'm still messing with settings so hopefully this will increase. Once the cold weather arrives the COP definitely drops.Â
LWT at around 28-29 degrees and WC is on.Â
Derek got to the bottom of the issue. I was running the WC settings incorrectly. There are 3 options which run the pump in different ways whilst WC is on and one of those tells the pumps to turn off after 7 mins then back on. That's why it was short cycling.Â
I still need to contact Samsung and I'll let them know about this thread. My Teva out sensor is showing -50 so I may need a new sensor there. I've checked the outside heat pump and it is all plugged in properly. I'll reply on here with any updates.Â
Craig (@craig1980) would you be kind enough to provide @iantelescope with details of the changes that you made to the controller settings to stop the short cycling.Â
Â
Hi Derek,
Many thanks for the data.
I have tried the Samsung Field bits 2091 Options 1 to 4Â on several occasions.
I too found the field bit 2091 option 4 was suspiciously near to my original 8 minute Cycle time.
Samsung field bit 2091, Water Pump 3 subroutine :
1) Delay for 3 minutes
2) OFF for 7 minutes .
3) ON for 3 minutes.
4) OFF for 7 minutes.
However, I, and the French Samsung Engineer tried all of these settings , multiple times, without any great effect.
The pulsing briefly increases the water temperature, and cycle time during the water cycle .
I Do currently use Water Pump 3 given the 2 C thermostat Hysteresis and the slight resultingincrease in cycle time caused by the extra, mid cycle, Motor pulse.
I have , however tried setting Field bit 2091 , Water Pump 2 subroutine again. given that many other parameters, and settings have changed in the interim.
Samsung field bit 2091, Water Pump 2 subroutine has however a 1 C Hysteresis.
Many thanks to you and Craig.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 61 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 2 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I doubt it, many 'improvements' are quite the opposite....
By cathodeRay , 4 hours ago
-
RE: Electricity price predictions
@julianc Expressed as a flow diagram, I suspect one wou...
By Toodles , 5 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
@jamespa The dormitories at my boarding school (in Exet...
By Toodles , 5 hours ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 20 hours ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 21 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 23 hours ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 1 day ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Referring to the problem of rooms with diff...
By Tasos , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 1 day ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 2 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 3 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 3 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 4 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 4 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 4 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 4 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 4 days ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 5 days ago