12kW Samsung gen 6 short cycling
Posted by: @craig1980A quick update on my system.Â
I'm running at a COP of around 3.3-3.4 at around 3 degrees outside temp including water heating for an hour at midnight. I'm still messing with settings so hopefully this will increase. Once the cold weather arrives the COP definitely drops.Â
LWT at around 28-29 degrees and WC is on.Â
Derek got to the bottom of the issue. I was running the WC settings incorrectly. There are 3 options which run the pump in different ways whilst WC is on and one of those tells the pumps to turn off after 7 mins then back on. That's why it was short cycling.Â
I still need to contact Samsung and I'll let them know about this thread. My Teva out sensor is showing -50 so I may need a new sensor there. I've checked the outside heat pump and it is all plugged in properly. I'll reply on here with any updates.Â
Craig (@craig1980) would you be kind enough to provide @iantelescope with details of the changes that you made to the controller settings to stop the short cycling.Â
Â
Hi Derek,
Many thanks for the data.
I have tried the Samsung Field bits 2091 Options 1 to 4Â on several occasions.
I too found the field bit 2091 option 4 was suspiciously near to my original 8 minute Cycle time.
Samsung field bit 2091, Water Pump 3 subroutine :
1) Delay for 3 minutes
2) OFF for 7 minutes .
3) ON for 3 minutes.
4) OFF for 7 minutes.
However, I, and the French Samsung Engineer tried all of these settings , multiple times, without any great effect.
The pulsing briefly increases the water temperature, and cycle time during the water cycle .
I Do currently use Water Pump 3 given the 2 C thermostat Hysteresis and the slight resultingincrease in cycle time caused by the extra, mid cycle, Motor pulse.
I have , however tried setting Field bit 2091 , Water Pump 2 subroutine again. given that many other parameters, and settings have changed in the interim.
Samsung field bit 2091, Water Pump 2 subroutine has however a 1 C Hysteresis.
Many thanks to you and Craig.
- 26 Forums
- 2,102 Topics
- 46.2 K Posts
- 87 Online
- 3,388 Members
Join Us!
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
Thanks @toodles for the update. My PW3 is due to be i...
By Old_Scientist , 1 hour ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 2 hours ago
-
@editor @bart Hi, I can see a few problems with your in...
By Brendon Uys , 5 hours ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
Well at least that solves the mystery of where the exce...
By JamesPa , 7 hours ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 7 hours ago
-
RE: Location of hot water isolation valve on cylinder
@rossowheels if you isolate the water supply in it will...
By ASHP-BOBBA , 24 hours ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 1 day ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 1 day ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 2 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 2 days ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 2 days ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 3 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 3 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 3 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 3 days ago