I've just watched the outside temp on the display for the whole 8 min run. It starts at 6.6 degrees then by around 4 mins it's dropped to 6.3 degrees then in the last minute or so it climbs back to 6.6 where it cuts out for 20 seconds but starts again when still on 6.6.Â
I'm looking for something changing, during the 20 second period, from the heat pump switching off, to it restarting.
Correct me if I am wrong, that your heat pump runs for 8 minutes or so, switches off for 20 seconds, then runs for a further 8 minutes or so, etc. etc.
A further thing that I find quite surprising is how low are the temperatures of your radiators, your home must be very well insulated.
The next test to try would be to change the controller mode from WC to a fixed LWT of say 35C, and see what effect this has on how your heat pump operates, and what changes occur to the radiator temperatures and room temperatures.
Yes, that's correct. 8 mins on, 20 seconds off then 8 on ad infinitum. There is no change in the outside temp during the 20 seconds.Â
I'm not sure if it's that great on insulation. Cavity wall beads, loft insulation, large double glazed windows but heating sits at 18-18.5 all day. Heat pump is on 24-7.Â
Posted by: @craig1980Yes, that's correct. 8 mins on, 20 seconds off then 8 on ad infinitum. There is no change in the outside temp during the 20 seconds.Â
I'm not sure if it's that great on insulation. Cavity wall beads, loft insulation, large double glazed windows but heating sits at 18-18.5 all day. Heat pump is on 24-7.Â
The temperatures measured on your radiators would indicate that there is very little heat energy being transferred into your home.
Â
Try pulling up the 'Indoor Zone Status Information' as shown on page 18 in the manual shown below.
Thanks,
Now try monitoring the 'Master Indoor Zone Information', particularly as the 20 second off period ends and the heat pump restarts.
- 26 Forums
- 2,208 Topics
- 48.7 K Posts
- 47 Online
- 5,868 Members
Join Us!
Podcast Picks
Latest Posts
-
Automation options to maximuse efficiency & ToU tariffs
I started a conversation with ChatGPT. What automation...
By Tim441 , 24 minutes ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@davidnolan22 I genuinely do not know the answer, unles...
By ASHP-BOBBA , 5 hours ago
-
RE: Renewables & Heat Pumps in the News
@transparent my reading of the report P28 (and probably...
By Judith , 6 hours ago
-
RE: 4 Year Ongoing Heat Pump Battle With Poor Heat Pump Installation
@jamespa Oh, I know some that are good and some not so....
By ASHP-BOBBA , 6 hours ago
-
RE: Samsung Heat pump with Yonos Pico circulating pump running all the time
I don't know how many pumps you have but I guess it's o...
By JamesPa , 7 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
That's just human nature unfortunately, not special to ...
By JamesPa , 7 hours ago
-
RE: Octopus tariffs - a quick comparison
Absolutely. That’s one of the reasons I wouldn’t want t...
By Majordennisbloodnok , 8 hours ago
-
@editor The season to start inviting prospectives to ‘V...
By Toodles , 14 hours ago
-
@bontwoody how long has it been now since you started t...
By Mars , 14 hours ago
-
RE: Bosch CS5800i 5kW - Experience So Far
Yes, over the last few days I've been keeping a very cl...
By Steelbadger , 14 hours ago
-
Absolutely. I am one of those members and I most certai...
By Majordennisbloodnok , 15 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@darrell-p There's another new Forum Member, @wully who...
By Transparent , 15 hours ago
-
RE: Forum updates, announcements & issues
We've had a slight glitch with our security software fo...
By Mars , 18 hours ago
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
If you do suggest you consider repurposing it as a 2 po...
By JamesPa , 1 day ago
-
RE: Say hello and introduce yourself
Fully agree with @cathoderay. My journey took 2 years ...
By JamesPa , 1 day ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
Tim, Yes ChatGPT thought I could get another...
By Mike Patrick , 2 days ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
No problem, @richdorm; glad it helps.
By Majordennisbloodnok , 2 days ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I do already have the same basic setup, all room influe...
By cathodeRay , 2 days ago